Airtight test damages door?
Nickfromwales replied to alayton's topic in Mechanical Ventilation with Heat Recovery (MVHR)
Yup. I know of at least 2, with another one coming up in 6-8 weeks. A good blower team will ( should ) have a frame which goes into an opening which has no door in it yet, so they should be able to do this with a bit of ingenuity? 2” PVC electrical tape can be applied first, then AT tape onto that. There’s loads of ways to do this and mitigate against damages etc. -
It needs to be a VERY thin membrane suitable for use with the liquid screed, so that it allows the screed to completely encompass the UFH pipe. Leave lots of slack / small folds in the membrane to allow it to be able to move and wrap as tightly as possible around the pipes. If you don’t leave this slack the membrane will tent over the pipes which you don’t want.
UFH pipe layout design - any improvements?
Nickfromwales replied to Tom's topic in Underfloor Heating
@Tom Easy to mitigate with insulation on the flow pipes where they congregate Don’t let them pick on you OK -
Yes, totally agree. I’ve made no reference to VCL, as I’d need to know about detail of the rising walls too to be able to comment. If it’s a draughty shed, like my home office / man cave, I’d just deal with the worst of the cold bridging and open a beer. Adventitious airflow will do the rest. If folk don’t allow air through in winter then the ? will hit the fan regardless. I’ve gone with metal uninsulated roof panels, one piece 6.4m lengths, over 5x2’s @400mm centres. I used roof membrane 1500mm wide and tripled it ( overlapping every 500mm ) as I couldn’t get the metal in time. Bone dry atm, with joists ( treated ) exposed and painted with the grey floor paint. As it’s Baltic in there, during the warmer weather I will install 75mm in between the joists, with a 25mm timber ( like a doorstop ) to allow me to push the insulation up and prevent it touching the membrane. I purposely kept the membranes very taut during fitting in case this was necessary. I’ll then install 30mm PIR in 8x4 sheets over the joists and infill PIR to kill the cold bridge of the joists, and then foil tape, and prob then just paint white or leave as foil ( as both will reflect light ). Joints between 8x4’s of PIR will be foil taped for the hell of it. That will be my lot for the roof. I will then pull off the external membrane wrapped around the outside of the stud frame / walls, I’ve not yet installed the 150mm feather edge thankfully, and fill those voids with cheap rock wool and then reinstall the membrane and fit the cladding at the same time so it stays dry. “It’s just a shed, Rodney”.
That's how most SIP's roofs are done. There needs to be a solid deck to walk on to be able to EPDM a large flat / sloping roof, as the compressive ( point load ) strength of the rigid insulation would be insufficient to take a mans weight ( foot / knee etc ). Also a requisite when installing PV with Nickelson plates etc as you would also not want to introduce cold bridging through 250mm+ long mechanical fixings. The detail there needs to be; a compressed sandwich with layers bonded ( where there can be no ventilation to ridge etc, eg no gap between the insulation and the deck board + EPDM ) or counter-battens and a gap for ventilation and then the deck board + EPDM.
As oak does not compress under foot at all, nor does any timber for that matter, there will be no discernible difference to concrete other than the smooth finish which will make it feel 'nicer' under foot. Purely phycological imo. I would bond this floor down without hesitation, as the numerous new builds I have been in that have not done this ( eg floating ) have been quite 'noisy' to walk on, even in socks, in terms of the wood moving and creaking / groaning when walked across. Also, I have noticed where the floating floors meet the stairs, and other fixed junctions, the two can never be married successfully when finishing off completely flush. Instead, most floating floor require a timber or metal threshold to allow a fixed item ( such as the bullnose of the last step up onto the 1st floor landing ) to marry to a floating floor. That would bug the life out of me for the rest of my days. That alone would be enough for me to bond the floor down, point 1, point 2 would fortify that decision, eg the then far better heat transfer from the UFH to the wood. That would also lend itself, point 3, to a slightly lower flow temp for the UFH to run at, as the oak would then be 'thermally coupled' to the heated deck. +1 for bonding down.
Don’t be surprised if the electrician asks you if want to take over the installation on his behalf!! The guy will be qualified, working to the spec of the fixed equipment and appliances that YOU have give to him, and will have installed what is correct. 2.5mm2 radial to each oven with its own 20a DP switch is absolutely spot on for anything up to the 16a requirements. Converting now to 4mm is just a waste of time and money. Now we’re getting silly ?. That’s for adverse installations. Never once have I heard any domestic sparky quote or install to that allowance. Cables for domestic ask for an ambient of 20oC to be used, then possibly grouping factors etc may then affect the outcome, but a good sparky will mitigate that simply with segregation. Stick with the 2.5mm and get yourself off to the pub
Not ever heard of cavities being filled with foams. Are we talking about cavity wall insulation here or just using this for crossing T’s and dotting I’s?
I install gate valves at regular / strategic points in my plant room installs, particularly where there’s an ASHP and antifreeze, so when needing to do routine maintenance or repairs, my clients only have to drain the bare minimum of primary water off. ?
My thumb still hurts.
You can get longer staples too, 60mm iirc. Boom. There goes the dynamite ?
I've never bothered tbh, and I've done loads. I took up one floor ( in a failing Everest summer room extension ) and that had been screeded over foil PIR. A lot of dark patches in the foil, but no issues with the screed, and no degradation of the PIR as far as I could see. It's only an issue whilst the screed is freshly laid and curing, and once cured it all plays nicely. Only real need for membranes atop the insulation is where you are having a liquid screed or a very wet concrete pour afaic. Take a core sample and see how thick the concrete is. He should have suggested this before giving that advice!! Yes, as long as it's the correct EPS with a compressive strength. EPS comes in various 'grades' so you'll need to tick that box. I'd go 150mm EPS > 100mm PIR and 80mm screed. If you want a really good screed layer, PM me and I will give you my mates details. He travels and has done all my screeding for over the years. Very good team and I've not once had to self level before tiling. All set out with lasers and to a tolerance of a couple of mm.
Agreed Just my option removes the TS and uses the existing footprint ( slab ) for buffering so that is hidden in the floor and consumes no additional internal footprint.
Yup. Those are what I’ve installed for every one of my high spec / “passive” projects. Regular TMVs are nigh-on fully shut at their lowest setting, and you can hear them ‘whining’ too which is a further annoyance. Way less pipe = way less water volume so not great at all ?. Anything less ( further apart ) than 150mm centres is also not recommended when utilising an ASHP as the primary heat source, and this is even more important in PH settings. Less system volume means bigger buffer or loads of short cycling. Much longer times to raise temps too. Current project all in at 100mm centres, apart from kitchen and utility at 150 as they are ‘inboard’.
Adjusting flow temps per floor is usually dictated by which types of emitters you have, so there is no hard and fast rule there. If screed / slab ground floor, and aluminium spreader plates 1st floor, you 100% need higher flow rates for the spreader plates as the losses from what is a much poorer emitter need to be mitigated against...by increasing the flow temp. I have done many like this, and, for eg, have had to run ~30oc ground and as high as 45oC 1st. Screed over block and beam on both floors may permit a unified flow temp, but as the heat rises the 1st floor in that scenario would likely need lower temp flow compared to the ground Water is being pumped around the UFH loops and back on themselves continuously at the rate that is set by the manifold pump and the calibrated flow rates per loop. Then you have the primary pump delivering heated water to /from the manifold, therefore a 2 storey dwelling with UFH on both floors would typically be utilising 3 or 4 pumps, dependant on the location of the TMV's. These pumps will need to be operating reliably at different potentials, so the basic requirement here will be for hydraulic separation of these pumps / circuits. The primary pump(s) will typically be single speed and flowing to / from the manifold(s) relieved by the calibrated or differential ( automatic ) bypass where they start the return path, but the secondary side ( manifold pumped loops ) will be constantly changing in potential, eg with fluctuations caused by changes in demand per loops / zones / by the actuators opening an closing. Also, with this approach and subsequent hydraulic separation, the flow rates through the loops cannot become influenced ( over whelmed ) by both pumps running directly in series ( the pumps never 'see' each other. Also good to note that pumps need to 'suck' water through TMV's, so you cannot have one remote TMV and then tee off to 2x pumps to give flow to 2x manifolds. You would need a 6 tapping buffer with 4 of those dedicated to 2x flow and 2x return for the 2 heating zone TMV's. Just a lot of extra fuss, confusion and all can be avoided by just blending and pumping at each manifold, like it's always been been done for a VERY long time. Also, if you don't want convection heat flow to the upper floor, remember that a 2 port zone valve ( my preference ) or a single check non return aka anti-gravity valve will be required. Next; to blend ( control ) water to the loops accurately, there needs to be a guaranteed supply of water that is cooler ( TMV manufacturer will give specifics for the required % of differential necessary to promote effective operation ) than the heat source input flow temp ( TMV ) setting. That is not going to be so if you are attempting to feed back / group the returns via to the buffer as you will be causing stratification ( multiple circuits flowing in and out for feeds, plus the same from the flow and return of the heat source ) and removing that guaranteed cold(er) water 'supply'. Water flow will take the path of least resistance, so the returns will just pull that mixed up body of water and add it to the return that goes into the remote TMV at the buffer. That is why the cooled returns from each loop are usually immediately grabbed by the local TMV at the manifold for use for blending where it needs to happen. It's only Nu-Heat which seem to like this option, plus a few renewable installers where TS's have been installed, and I've not seen anything resembling good results from that from type of arrangement with what I've seen ( on live installations ) to date. With UFH installs of mine coming up for 20+ years of reliable operation, I shall not be changing course with my ( standard?) method any time soon. PS. For anyone building to passive / very high spec, the type of TMV required for flow temp control if sub 30oC has a capillary wire from a thermo-probe which controls a TRV like haed on the manifold blender. If you move away from this you'll lose that type / accurate type of control too. Ivar is my weapon of choice, and you can see the setup with the capillary wire / probe / TRV here
Ideal Vogue 26kw or Logic+ 24kw System Boiler?
Nickfromwales replied to Niall's topic in Boilers & Hot Water Tanks
The Ideal are solid boilers, but our budget offering, and typically we install those in rental properties or for 1st time buyers etc. Our weapons of choice are 1) Vaillant, 2) Baxi and 3) Worcester Bosch. I think it's fair to say that WB are making a very good boiler these, but for my own house I'd still go with my long-time favourite; the Vaillant. -
Erm, no. The bigger rooms will already have more pipe, ergo more heat. The UFH design should mitigate through heat loss calcs for each heated space, accordingly. If there’s any doubt, just wind the pipe around at 100mm centres and simply create more volume of heated water per m2, but at the same temp. More loops = more heated area and ( IMO ) looking to heat other areas more by opening up flow is coarse on a good day.
Ah! OK, gotcha. ?. As is then seems the way. Had loads of issues when going to already installed ( by others ) UFH systems, mostly with the TMV not performing properly. Glad you got a result at last.
That adds some clarity. Why have you done that? DHW running at 45oC and heating at 35oC would give you a better CoP, no? That's how I set the most recent up, with just a LLH ( low loss header ). HP is just idling most of the time and has a nice easy life vs kicking in / out t higher temps. Gives a much better operational hysteresis IMO. Was a 7kw HP servicing a ~3.5kw demand at worst case. Ran near silently and I had to keep going up to it to check it was still 'lit and burning' by putting my head in front of the fan. The minimal road noise and surrounding noise pollution ( urban setting ) was enough to nigh on cancel the HP out altogether. I would not have wanted that running harder to heat a buffer and kicking in / out / running louder etc for this instance, and I could not see a notable ( short ) cycle which would have made me do otherwise. Each instance is unique, and this was a decent 'passsive raft' slab with a huge thermal time constant, so may have been different for UFH in screed over block and beam etc. @joe90 would you not consider getting the heating output temp down to see if that boosted CoP? With the buffer charge "not lasting long" I doubt that is doing much to stave off short cycling anyhoo?
Getting water to a manifold 25m away
Nickfromwales replied to saveasteading's topic in Underfloor Heating
If this is internal, then I'd also say run 28mm pipe ( copper or Hep2o ) and insulate yourself. As the delta between the pipe and the ambient temp of its surroundings are minimal, there is no real reason to go for pre-insulated afaic. Also, the pre-insulated pipes have a bending radius of around 1m, varies with external diameter based on how thick an insulation you went for, so near impossible to navigate tight bends also. I am using Primo Uno on an upcoming ASHP install where the runs are circa 30-32m from the heat pump, so I'm maxing out the insulation levels by running 2x Uno with thickest insulation available vs 1x Duo with limited, albeit still very good, insulation. For you, deffo stick with regular pipe and if you use Hep2o you can go very long distances with no joints, and then just slide un-slit sleeves of pipe insulation down each one. Then clip the pipe and insulation into place with either plastic waste pipe clips or powder coated all-round band ( from electrical merchant ).- 14 replies
Custom Self Build (ICF, ASHP, MVHR, UFH)
Nickfromwales replied to Merlolly's topic in Introduce Yourself
Hi, and welcome. Some good choices there already so you're off in the right direction On this point, just remember that a typical 4kwp system will absorb around 28m2 of roof space, so, for eg, if your roof covering is costing £100/m2 you'll have a hypothetical credit note of £2,800 gifted to you from the savings of not roofing that area. Maybe that helps to at least get panels on the roof and DC cables in at the time of roofing, with a view to connecting the remainder of the system downstream / when budget becomes available.