How much can I safely store in my loft?
Gus Potter replied to vcps2021's topic in General Structural Issues
Hello all. Hope this helps give you some pointers for typical fink trusses, attic storage and what extra load you can put up there. The truss manufacturers often design to BS 6399 loadings unless told otherwise. Below is a typical example of the ceiling loads for an uninhabited attic. Roughly to convert N (Newtons) to kg you divide by 10. Thus an imposed load of 250 N/m^2 is 250/10 ~ 25kg per square metre. An imposed load can be your holiday stuff, hats and sun cream, or xmas decorations.. basically stuff that can get moved about and remember that you have to hold a heavy suitcase so there is you body weight to add. Now once you add in the weight of the chipboard flooring say 12 - 15 kg /m^2 = say 100 to 150 N/m^2 you are left with only being able to put about 10 to 15 kg of stuff up in the attic all spread out. Naw! really? You may ask.. I'm 15 stones (about 100kg ~ 1000 Newtons) so why does the ceiling not collapse when I go in the loft? Simplistically prefabricated trusses are designed to be as economic as possible. The truss manufacturers take advantage of the properties of timber which are different from steel. One key thing about timber is that is can carry a short term "shock load" like you at 15 stone without breaking. This is shown above as 900N ~ = 90 kg. You'll see an allowance of 75% for load sharing. This recognises that often you won't put all you weight on one bit of timber for any length of time and that there will be noggings (dwangs) and so on that shed some of the load to the adjacent timbers. But when a timber is loaded over a long time it starts to creep and is less able to sustain long term stresses, it is after all mostly celulose. You can see this in say old roofs that have sagged. This will also happen to your ceiling and can manifest in cracks. Also, as the timbers sag too much they can introduce other unwanted forces into the small nail plates (called second order effects) and they will "protest". Sometimes you can add a bit more load locally if you have some "load bearing" walls below, but let's be cautious for now. I'm not saying you can't start using your trussed rafter roof to carry extra load. There are a few ways you can simply strengthen some of these roofs. There is a temptation to start using the space more regularly, put electrical sockets in, maybe a bit of insulation. When you come to sell the Surveyor says.. hold on where are the permissions and calcs for all this. If you are going to put a more solid floor in please bear in in mind the above and make sure you can easily strip it all back out if need be. Please do not cut any trusses as this falls under BC regs and the scope of a building warrant in Scotland. One other point to bear in mind is this. While all may seem fine to begin with if you start pushing your luck and eating into the safety factors that were used in the truss design then you could get a serious failure when we get a big snow fall. It could be xmas time with a house full of kids! In summary if you have any doubt get an SE in, even if it is to reassure. Then enjoy your additional space. -
Ask your SE how they feel about the following. Lift the existing boards, clean the top of the floor joists, wire brush , hoover the top so that you get a good rough clean surface. Apply a liberal amount of structural glue to top of joist. Pilot drill and counter sink holes in ply and screw fix down to top of joists at 200mm centres. Glue to be a true structural glue such as Cascamite.. not D4 as a popular on BH. The screws are to provide the compression while the glue hardens, the glue does the work. Now you have turned the joists into a quasi "T" beam. The SE will probably need to do some calcs by hand (a few pages mind) as you don't get off the shelf software for this, and also, as it's a bit off the wall they may need to spend some time "researching ".. great job for a graduate though wanting to build their portfolio as you have to go back to basics. Now you have your structural deck. Give it a bit of time to condition, get the heating working. Next tile but use a decoupling matt? ... plenty info on BH from the pro tilers on how you do it. Lastly make it clear to SE and Architect that you will accept any liability if the tiles crack and offer to pay SE as you have "heard" that it can be quite complex to design. The SE may just say.. oh I have an old spread sheet that I used to use, give me a couple of hundered quid and you take responsibility if tiles crack. On short span floor like this tile cracking is much more likely to occur due to shrinkage (drying and swelling) of the substrate rather than deflection of the structural members.
-
End of Cover Page Hello all and @Heather85uk Bifold doors, sliding doors, deflections and goal posts! Hopefully this part overview will help some BH members weave their way through what can be a bit of a mine field, but exciting too once they are installed and working! I have linked to Heather’s post as Heather has provided a few calcs (copied below) from the SE and in the spirit of BH I have taken the liberty of adapting and simplifying Heather’s calcs to “tell a story”. Heather, I hope you don’t mind. @Heather85uk There is plenty info on BH about limiting deflections and other good practical stuff, but I hope that it may be helpful to take a few steps back to see what causes these deflections and how you can start to get a design to work. Although the post is about bifolds, sliding door openings much of the following can be adapted by anyone who is contemplating making a hole in their house and needs a beam and/ or some columns to hold things up. Lastly, before the nitty gritty / the following is very much a simplification. Please don’t “ladle” into your SE as often there are other considerations to account for. Most SE’s should be willing to explain so just ask.. If they can see that you have put some effort into grasping some of the basics then they will often return the favour and more. Also, if you can get your head some of the concepts I hope it can help you get what you want at a reasonable price. Maybe, the following will give you more leverage when negotiating with door, glazing suppliers. To get started here I have taken Heather’s calcs and simplified the loads as it makes it (I hope) easier to get a feel for things. I have used these calcs as the deflections seem a bit “off”. A good refreshing thing I find about BH is that it’s a forum for solving potential problems. Heather’s calcs show a beam that is what we call simply supported. Imagine (I’ll ask this as this seems to be a common trait we share on BH) you have a ruler and prop each end on a pencil. Load it up and it bends. The pencils at each end allow the beam to rotate at the supports. This is called a “simple support” The diagram below is what we call a bending moment diagram and this represents the bending force in the beam (ruler). You can see that the largest bending force occurs in the middle, just like the ruler. You know intrinsically that if you overload the ruler over it’s length it will often tend to often snap in the middle where the largest bending force occurs. You can also see that the bending force is 251.2. The units are kilo Newton metres (kNm) and are close enough to Heather’s calcs for practical purposes. The diagram below is what we call the deflected shape. This is pretty much a representation of the shape the beam will take up when you load it. It’s a little different on the curve from Heather’s as I have converted the point loads to uniform loads. The deflection value of 22.2 mm is the amount the beam will bend in the middle and is close enough to the value shown in Heather’s calcs for the story! What we have above is similar behaviour to say a concrete lintel, a solid timber floor joist, a metal web joist and so on. The key thing to draw from this is that when a beam has a simple support at the ends it forms a shape like this and has a distribution of bending forces parabola shaped. If you have point loads then the parabola gets distorted to a greater or lesser extent. Heather mentions a “goal post”.. two uprights at each side and a beam over the top. Often you find that when you have a big opening you can get some onerous loads. Heather also has some point loads (maybe floor transfer beams framing in) near the middle of the beam span. Often you find that while you can get a beam to work, when you come to check the supports at the sides you find the masonry or timber frame holding up the ends of the beam can’t do the job. You can look on BH about pad stones, cripple studs and so on so I won’t explore further. One solution when the side supports can’t carry the loads is to introduce steel to form the sides, you form a “goal post” and take the load down to the foundations zone using steel which is good in compression, thus you relieve the load on say the masonry or timber frame at the sides of the opening. Steel is good at performing this function, but as there is no free lunch you often get more thermal bridging and you have to fix the steel to the rest of the structure, be mindful of that. Here (below diagram) the sides of the goal post only serve to transmit the vertical load and relieve the load say on the masonry or timber frame. I have replicated Heather’s beam below but with the same size of posts (columns) each side to form a goal post as it’s easier to make a point. “Don’t do this at home” as in detailed design you would balance the sections to match the bending and other forces and so on. The beam is still simply supported so you can see that all the columns are doing is acting like the “pencil supports” and holding up the ends of the beam. There is no bending force in the columns. They only carry the vertical loads from the beam ends down to the bottom of the goal post. The diagrams below show the bending moment diagram and the deflected shape. You can see that introducing the columns as simple supports has made no difference to the deflection. Still 22.2mm as we still have simple supports.. the pencils. We would hope that the ends of the beam and the columns are bolted (fixed) together in some way, if not you need to ask why not? But.. we can connect beams/ columns together in different ways. For example you can use a thin metal end plate on the top beam which bends like an elastic band (that is what I have done above and is called flexible connection) and then recovers (steel is quite bendy stuff!) so this maintains the idea of a pinned connection. Or, you can use a thick plate with bigger bolts, alter the welds etc. (if need be) which makes the connection rigid..a rigid connection. What I have done below is to keep the same arrangement of goal post / beam but changed the beam end connections from a pin to a more rigid connection. The first diagram shows the section sizes. Again, the sections I show are not quite what you do at the detailed design stage but I hope it makes the principles easier to follow. At detailed design you look to see what you can cut from stock lengths, the weight of steel and so on. The bending moment diagram below shows what happens when you change the end connection from a pin to a rigid connection.. Here you can see that by rigidly fixing the ends of the beam to the top of the columns we have reduced the bending effect in the middle of the beam and are asking the columns to now step up to the plate and do some extra work. The columns are now carrying some of the bending force as well as the vertical load from the ends of the beam. This relieves some of the bending force (moment) in the beam and this also reduces the deflection over the doors. Below is the deflected shape with the deflection value. By changing the type of connection at the end of the beam we have reduced the overall deflection from some 22.2mm down to 12.6mm. Getting closer to say Express Bifold deflection spec but still a bit off, but closer, nearly there! What we are doing here goes back to the ruler concept supported on a pencil at each end. If you had three hands then you’ll find that if you can stop the ends of the ruler rotating then it will bend (deflect) less in the middle. The columns act as two of your hands at each end of the ruler, imagine the third hand is applying the load to the ruler.. Nod, markc MickSharpe01 et al.. good points about beams sizes , the loads, hit and miss welding.. plenty good stuff to digest from them and others. Let’s now look at how you may go about getting something to work with Heather’s loads. Below I have picked all the same section / stock sizes, which means that you have a better chance of getting the connections to work and reduce wastage when you buy the steels.. go for the lightest weight of steel at the conceptual design stage and you’ll often run into trouble at the detailed connection design stage and it will end up costing you more. Often if you plump for the lightest beam then the flanges / webs are too thin to resist the localised forces from the bolts. You then end up having to design a complex connection with stiffeners, more bolts and the fabricator will charge you a lot for this extra work, often more than just starting out with a heavier off the shelf beam. As an aside. This is a good example for the self builder renovator. Sometimes it’s much better to go for the “simple stupid” .. stock steel sizes and simple connection design although initially you may feel you are using more steel. You should save money on fabrication and steel erection costs even though you may have to use heavier steels. Below is the deflected shape with the different (356 x171 x 67kg) set of sections. You can see that we are now down to some 9.2mm overall deflection. Yes, we have a bit more steel weight but we are looking for the easy way, stock items, that will also save on labour while considering that we are self builders rather than a large commercial outfit. What I have done above is to change some of the sections and connection types to show what you can do. The top beam is deeper and I have reduced the deflection down to 9.2mm over the 6.1m span. Feeling hopeful! Heather’s loading is roughly split (before applying safety factors) 50 /50 between live and dead loading. This means that as you are building the beam it will bend as you build up the floors and add the walls over the beam. Before you place the order for the doors you want to make sure you know the true opening as built sizes which will include the dead load deflection. Remember here.. your need to cut the brickie some slack. If they can get each side of the opening level to within 5.0mm that is good. A good brickie should be able to sweeten out the coursing too over the beam. Lastly we are using hot rolled steel beams. These too have a manufacturing tolerance and are not truly straight! Bearing the above in mind. Half of the 9.2mm deflection will take place before you order the doors. The other ~ 4.6mm when say it snows or you have a massive party and load up all the floors with live load. Express say 3.0mm not far off the 4.6mm! But the 25mm in Heather’s calcs? Hopefully the above has given you a flavour of goal posts and what you can do. Now one other thing that crops up in Heather’s calcs is a fairly high loading on the beam for a domestic application. You’ll see this in the calcs as being 142 kN. That is about 14 tonnes. This load is expressed as including the safety factors. Without the safety factors the load at the end of the beam will be about 100kN.. that is ten tonnes.. 10 old Volvo cars, not a small load. The load has to be carried by the founds. I hope this helps folk get a feel for goal posts! If you have an old house or say a house on piles and want to form a large opening then you can take the above principles and turn the goal post into a box frame. A box frame can also further reduce the top beam deflection and spread the load on the founds. In simplistic terms you take the load from above, down the sides of the goal post into a stiff bottom beam. This beam spreads the column loads out so the old founds “still think” they have the old wall above. Box frames are also good at resisting the sideways wind loads. I’ll leave that topic for now.. a story for another day if there is any interest. Hope this helps to give you some pointers and all the best with your journey.
- 3 replies
-
- 4
-
-
-
- bifolds
- deflection
-
(and 1 more)
Tagged with:
-
Ah.. When the builder lowered the levels did they alert you to the fact that you have corbelled brick found? Looks like you (builder) has excavated a tad more than you should have? Remember that external walls tend to hold up the roof too! I would ask an SE to have a look and at the same time they may sort out your screed levels. Sorry.
-
@cian It depends on what you want to do. Are you having to move to London due to say work or do you just want to chase the dragon of making money on property. Unless you have some serious funds behind you, local London contacts it could be a tough ride if you go at it the wrong way. You are really are entering the den when you play with the London boys / girls / etc ! There are a few folk on BH who have London experience.. I think! However, if you take a pragmatic view it can be great fun and rewarding. Cian. Maybe get some experience of self building / renovating a flat not in London if you can. Turn a profit on that before you stake the big bucks. Prove to yourself that you can develop something off your own back, turn a profit without relying on rising proprety values. That is the test! Do that, gain experience and you are on your way. It's also about the contacts you make. Build trust with a few trades folk, pay on time, they will return the favour..take you seriously.. introduce you to their contacts such as.. Plumbers, Sparks. the skip hire folk.. Once you get a network like this in place and have worked at it then you can look at the next stage with less risk of losing your shirt.
-
Deflection of 25mm from SE, problem for sliding doors
Gus Potter replied to Heather85uk's topic in RSJs, Lintels & Steelwork
Hello Heather85uk. No need. This subject crops up on BH a fair bit. The calcs raise a number of questions and you mention that the steel section is part of a goal post. There are a few permutations of "goalposts" and each permutation can influence the deflection and the choice of beam depth / width and so on. I think you need to take a few steps back first to be able to understand more of the principles, then you can go back to your SE with a bit more knowledge and ask why you have what you have. For example I can see that the beam is designed as simply supported, but why? The deflection is shown as overall deflection but is not split out into live and dead load defection and so on. If you wish can you provide a bit more info. It would be helpful know what is forming the posts each side and what they rest on at the bottom. Maybe a cross section that shows the wall thickness, buildup and materials. Also are your founds cast and how far have you got with say building the substructure? Are there height restrictions on the beam depth over the doors? Although this topic has been explored to some extent on BH if I can I'll write a general post over the weekend that explains more about the structural behaviour of the different types of goal post arrangement for those who are less familiar with the subject, how the different permutations influence the deflections, twisting effects and so on. I'll try and tailor it to your situation if possible and hopefully this will help you find the right solution for your build stage. You may have already read this thread on BH about door deflections. -
Legit to shorten a galvanized roofing strap?
Gus Potter replied to epsilonGreedy's topic in Roofing, Tiling & Slating
Ok to shorten in terms of galvanising / corrosion. Think about it this way. Dive into you local B&Q say, look at where they have had to drill the extra odd hole in the galvanised purlins to hang a banner / AC unit.. the SE's etc are not all round in droves. Just make sure that if you are shortening it you are not reducing it's intended tying capacity. Check the nailing specification and so on. -
No good outcome as they are all into identity politics and some other stuff that does not fit with a modern democracy. For a while I was an advocate for nuclear, great base load capacity until I designed an air cleaning plant housing structure for the decomissioning of Bradwell Power Station. The decomissioning costs are truly horrendous, not just for our kids but our kids kids if you want to do it in a safe way. Hydrogen may well work out but there are many things to develop. Take the basic boiler burner, the flame speed is much faster. The molecules are smaller so we will get a good few accidents due to leaks. Yes we can extract hydrogen from natural gas but we generate some not so nice by products that we need to deal with. Although much was made about Scotland being the "wind capital of the world" the reality is that the shallow off shore waters off the Southern part of the UK are currently more cost / carbon effective. For example the transmission losses are reduced that is why we build power stations close to the centre of population density. However Scotland has a lot of good water that could be pumped / syphoned using the earth's gravity to the South where there is the demand to produce the good grain etc. It's also about sharing our UK resources in a practical way in the short term. There is no doubt that we will improve the efficiency of ground source heat pumps but if every one puts one in their back garden (if you are wealthy enough to afford a garden) then what will the Blackbirds eat? The grass won't grow, there will be fewer worms for the birds chicks? Chill the ground and you invite the unforseen. The reality for me is that unless you get China / USA to change, anything we do needs to be done in such a way so as not to reduce our financial clout on the world stage. If we have no "buying power" then no one will listen to us? It is going to take a brave set of polititians to grasp this nettle, we may, I think need to wait for something really bad to happen before we get real action rather than the gesture politics we see at the moment.
-
In almost all cases for a domestic dwelling (not flats which often share a common stack) it is a BC requirement. Here is some info which I hope helps BH members. In Scotland for example the regs point you to BS EN 12056 part 2 which is to do with drainage inside buildings. Comply with this code and you are well on your way to complying with the regs. There used to be great stuff and diagrams in the regs to help self builders /renovators but these are getting progressivly stripped out. Here are a few thoughs / observations. If you get a feel for the principles then you can adapt to suit your needs. Often you see a drain pipe poking out the roof..with a grill on top to prevent birds nesting and so on.. the top of the main stack. This open vent serves two purposes. One is to prevent excessive suction building up in the main drain line serving your house the other is to prevent over pressure in the line which will blow the traps.. and worse. Pressure can build up in a main drain line; if the wind is blowing the wrong way down stream (other folk doing daft things like facing a vent stack into the wind), if you have a blockage and a build up of gas (could be a gas leak too and the gas migrates into the drain! nice to vent outside than into your house) down stream if say your neighbour has been putting nappies down the drain. They get the drain folk in and they put a pressure washer down the pipe.. I'll leave the rest of the description for now as to much information can be uncomfortable. Commonly though it's suction that causes the issue. There are a number of ways you can design a drainage system. Some work on what we call "full bore flow" this is more common in the EU except for some roof drainage systems in the UK... you often see these full bore roof systems described as "syphonic systems" in the UK, some toilets work this way but just within the "bowl". Mainly though in the UK we design the drains in our houses (system iii) to not run full bore and thus they don't generate this true syphonic effect. But they do still generate some negative /positive pressure. When you pull the plug on the bath the water flows and pretty much fills the pipe. As the water moves down the pipe it compresses the air in front of it. If you don't relieve this compression it can blow the traps on say a sink in another room and thus fumes will enter that room. Some air passes over the top of the water in the pipe as it is not running full bore but often not enough. Commonly a sink trap has a shallow seal of water so we are only taking about a small amount of pressure, much less than say a car tyre or you blowing up a balloon. Once the bath is nearly empty if the pipe run is long then you have this body of water still moving down the pipe and this creates a suction effect behind it which keeps drawing water. This "residual suction" can be enough to stop the bath trap from filling properly at the end of the drain cycle and not creating a proper water seal. This means that when you say next flush the toilet the smells come out the bath trap rather than venting out through the stack. If the seal is completely broken (the trap is not filled enough) then you invite "lingering" odours from your own house and that of your neighbours unless you have your own private sewage system, in which case it's you own personal "gas". One way we get around this is to fit an air admittance valve on branch lines, say on a long run to a kitchen sink or ensuite bathroom. This works a bit like a snorkle in reverse. It is sensitive enough to let air in but not pressure (smells) out. This allows the trap to fill properly from say the last bit of water in the bath and create a seal. Now one problem arises with AAV's is that the regs require them to be set above the level of the spill over point. For example in a bathroom the idea is that the home owner will see the sink spilling over if they have a blockage rather than the AAV leaking and causing hidden damage. Now that all makes common sense. Some of the building regs are really good! But this does not fit well with modern bathroom and kitchen design as no one seems to want a "box in the corner" of their new sleek vanity unit or kitchen work top. I mentioned adapting previously. Sometimes you can implement an old solution that was commonly found in tenement flats. This is called a "loop vent". Here you create a circuit of pipe in a loop. The top part of the loop does not carry water, it just lets air circulate. Have a look on the internet for loop vent design.. kitchen designers with island units have picked up on this, reinvented the wheel and are punting this as some kind of great new invention. Ashthekid.. hope this give you and BH folk some background info. Oh, and there have been a few other posts on BH about pipe gradients etc...
-
Can you turn the cross walls into load bearing walls? It already sounds like you are intending that the cross walls should provide lateral stability to the external walls. i.e they are shear walls. Build these in timber frame if you like. Roughly where the ceiling ties join the rafters can you stick in a purlin running in the direction parallel to the long walls? The purlin is supported on the cross walls. The purlin can sit above or below the node point to the ceiling tie / rafter. These purlins take out all the spread out of the roof and carry the majority of the vertical load. Not you have relieved most of the load off wall that is causing problems and you can work on it as and when you like. It's (the ropey wall) pretty much left to carry it's own self weight and a small portion of rafter load from the bottom two or three feet of slates / sarking. The same principles can be used for loft conversions where the roof is required to carry heavier loads. This may work fine or you can often adapt the principle to suit the layout.
-
Hello Rob. There are no daft questions, it's daft not to ask in fact. I hope this helps to add to your research knowledge. To add to the great informative comments from other posts I'll touch on the structural side of things. I'll do a bit of general stuff first (tell a story) and then focus a bit on what you have. A bit of background on agricultural buildings... lets go "back to the second world war" Very roughly.. and there are a good few bits missing from the following but I've written this to take you hopefully on the "Build Hub Journey" When this war started the steel industry were a bit more advanced in the quality of the material they were producing. They went to Churchill (well not him really but it sounds good) and said.. look we need steel for the war effort. We have moved on from making steel in our back garden and now have "quality control" so our steel is more reliable and less varaible in quality. As it is less variable allow us to reduce the factors of safety we need to apply. This way we will use less steel for building domestic structures and there will be more available for making tanks etc. I will stand corrected but the Gov said OK. Now the concrete folk said...hang on that's not fair as we are all at war.. let us too reduce our safety factors..but they were still making concrete in their "back garden". In essence in a war situation Chuchhill said OK although there was no rational safety basis for doing so. The only basis was that we were in a war.. frankly, if we had lost it we would have much more to worry about than safety factors of concrete and steel design. Moving on..Rationing was still in place after the war and for a while folk still had ration cards, eating powdered eggs and so on. Folk wanted to see some improvement.. There was a push to mechanise farms, improve production. farmers made hay. Barns were needed to house grains and live stock. No one gave two hoots about the quality of the barn stuctures as the populase were restless and demanded a higher standard of diet. The demand was immediate not least politically. Over the next few decades the insurance industry clocked that they were having to shell out for barns say that were say "falling down" too often. Maybe they woke up to the fact that farmers are quite canny, were stuffing them and "having a laugh".. One part of the solution was to start to bring agicultural barns into the "building regs" They started to codify the design. One other driver for this was also that a lot of kids / young men were getting killed on farms back then. It was what we would call today "carnage" What then happened to some extent was that the farmers went "mental" and said if you impose these regs on us the food price is going to go up. I think a compromise was reached where the farmers got a half way house and this manifests today in the modern agicultural code BS 5502 part 22.BS EN 5502. A key thing about this code is that agricultural building design is based on lower loadings, a lower what we call "occupancy rate" , and have no proscribed deflection limits..the amount it sways / deflection. Deflection is critical if you want to use the same frame for a house. It may not fall down but it will move so much that it will burst your cladding fixings and the place will leak like a sieve. Have a look at modern cladding systems, they all have caveats on deflection. If that is not enough then go back to the loadings and occupancy rates.. they are often not compatible with the regs for modern housing roof loads and so on. As an aside jump now to 1980's. Here (and it still happens from time to time) we were getting a lot of "fake sections" from Asia. They are hard to spot, they look like a BS standard sections.. put a micrometer on the flanges and they are thin! Also they had a lot of impurities in the steel which compromises the welding. They are a "shoogly peg" to hang your new house off. Rob and for all. In reality nine times out of ten you''ll find that the frames are of no use structurally. If you want to delve down an SE will want to look at the base connections, have to make safe assumptions on the quality of the steel / oak frame / timber / concrete degredation / the size of the founds. Then the SE has to look at whether they can sign off on the fact that what you have will last for another 50 years which is often a lender requirement. Also remember that in the case of timbers when you alter the ground level, moisture content and let in air you can promote decay in timbers. timbers buiried in the ground will last for hundreds if not thousands of years.. look at some of the old oak piles etc found in the Thames.. all good until you let the air get at them. To sum up. I would start out by investigating the ins and out's. It's a pity that the planners in some cases insist on the retention of a building frame that has no historic value and is no longer serviceable. They fail to recognise that by trying to retain a frame that has outlived it's service life is actually bad for the environment, can prevent young folk getting on the housing ladder and so on. Rob. Lastly you have a fair mix of frames and different constructions. If you want post some photos of the concrete clad frames.. would be interested to see what you have to work with. Oh and if you are converting an old barn there were just as many chancers cutting corners in the past as there are now so proceed with that in mind.
-
New Member from Cork Ireland building ICF House
Gus Potter replied to Blynchy's topic in Introduce Yourself
Hi Blynchy. BH is a huge resource. It's stunning how much real practical info is here. There is a great mix of folk here. You'll always learn something here. I do each time I visit. Sounds like you are starting out on a journey. Best thing to do is to try and get familiar with the search function on BH..it's not google.. not commercial (so far) so you can find some really eclectic and valuable stuff. You'll need to spend a bit of time raking about but in doing so you'll pick up info on a pile of stuff and the next steps once you get moving on the build. A bit of time spent here will probably save you a fortune. Don't forget that building something yourself should be fun too. All the best. -
Builder cut 4.5cm off joists due to floor level screw up
Gus Potter replied to Loz's topic in General Structural Issues
Hello all. A lot of the following is general info which I hope will be of help if your builder has not done what they should have, or "done what they think is helpful"..some builders do this.. believe it or not. There are a lot of young (still some older ones too) builders that are really keen to please and keen to do the right thing. Their heart is in the right place. Yes it's an interesting subject this..for a good number of reasons. Unfortunately for Loz.. it's Loz's house we are talking about / discussing. Loz.. I was prompted to make the post about the timber grade as for me this takes you back to basics, can take heat out of any potential situation. No point in looking at load span tables etc if you have done something that has changed the intergrity / "provenance" of a component on which the load span tables rely on. Loz.. you mention that the SE is friendly with the builder. This is a normal occurence. SE's / Architect's / Designers / M&E specialists and so on like to work with good builders.. and builders like to work with good designers that can resolve; unforseen on site issues, be able to design and specify easily available materials and so on. That eases the way for everyone.. Also remember that builders can often be members of professional bodies / have extensive professional knowledge. Just because they may wear "shorts to work" does not mean they are unprofessional or lack knowledge! In fact the last few designers I've talked to have all been in shorts! .. COVID you see. For designers and builders (major contractors too) trust and professional respect for each other is built up over time and this has value. In particular, it often drives down the cost to the Client and this is how you get repeat work and recommendation from a Client. Every one is a winner to some degree. In summary don't worry at this stage that the builder, SE, BC officer may have a good friendly relationship. This is far removed from what we would call a corrupt relationship..for which you can not only be stuck off a professional register but also invite a holiday for yourself at a location chosen by our Monarch. Loz and all. Often you find that you know something is not right.. you just know this as a lay person.. you don't need to be an SE say.. trust your gut and ask questions, as you are doing. Loz, the builder may know that too. At one end they may know about the timber grade etc and just tried to pull the wool over your eyes. If they do know about the timber grading it would be a new thing for me though.. Your SE should have some awareness. At the other end they (builder) may have thought they were doing a good thing and solving problems.. helping you out. @saveasteading "Agreed. Mistakes happen and it is sometimes reasonable to find a solution that does not inconvenience the builder. " To add a bit to saveasteading's point. I'll use an example, corollary here. You can often deal with a home warrantly provider who is giving you the "run around". Often you encounter arguements such as "well the cracking you see is visually acceptable" or "some amount of settlement always happens". Dig deep into this and the modern Euro codes introduce a way of designing where deflections and settlements are more open to interpretation provided the structure remains safe! What this means is that often the domestic home owner has an expectation that is not met.. the developer/ builder is off the hook to a large extent unless the home owner is willing to spend a lot making a counter argument. Loz..you could find yourself in the position where the onus falls on you to make the case showing that you may have a "bouncy floor" and or a ceiling that cracks in a few years time for example. One key to unlocking this is to find something that you can point to that has compromised the structural safety. This is non negotiable as it is a UK legal requirement. Nail this and you often find that all the other arguments made become mute. This gives you the big stick as often to fix a structural safety issue you have to strip out and reinstate. Basically you cut the feet from under them. Loz in your case this timber grading thing may be the key to resolving this. Now you have the big stick and you can decide how to use it. But go gentle, particularly if it's been a genuine mistake. Always remember that if you use the stick half way though a project then if you make a mistake later then the builder etc will probably return the favour with a bit extra! Always ask yourself "what is fair and reasonable behavour? Be wise. Loz..Here are a some choices the SE may have. 1/ Be competant to visually grade the timber in it's cut down state (old school stuff but can be done still), recheck the strength / deflection which will now probably fail on overall deflection and look at the vibration. Then produce the calcs and evidence followed by sign off. 2/ Get a certified person from a timber merchants / producer (grade it and then perform the above checks) to do it for them.. the rub will be to make sure that the visual grading will still also be CE compliant.. good luck to the SE on that one. 3/ Chuck in the towel and look for another solution. Loz.. as promised.. here is something worth exploring. If you can accept a small reduction in the ceiling height then bolt onto the sides of the joists you have new 195 x 45 timbers. Alternate which side you bolt the timbers to. Bolt them all the same, say on the left hand side and you will get a rolling effect which is not desirable. Your SE should know this but the builder possibly won't. For the technically minded this rolling effect will happen as you shift both the centre of gravity of the section and the shear centre of what is now a composite section. Loz looking at the floor you have the joist sizing is probably governed by what we call the bending moment and deflection. In other words are the joists strong enough in the middle not to snap under load as they get bent and are the joists stiff enough so that the floor does not bounce too much. Where the joists frame into the supporting walls then you have what is called "shear effects". There is a good chance that the SE can show that at the ends of the joists they will still be ok in shear even though they have been effectively notched on top. Simon mentions this too but unless you have some other loads acting on the floor from above it all may be fine when the SE checks the shear at the joist ends. To expand on other posts on doubling up joists and so on. On the practical side when you offer up the new joists put plenty glue on the top side so they stick to the flooring . Now get the builder to run upstairs and screw the flooring to the new smooth surface of the extra joists before the glue takes up.. this will mitigate the squeeks. Yes, you'll need new noggings mid span (dwangs) but that is a small price to pay. I think you could resolve this fairly easily. It won't cost too much cf knocking holes in the masonry, potential disturbance to the masonry, lifting the floor and so on. Often the key here is to find the big stick. Show you have one and avoid using it, mainly because you often still need to finish the job. Also, if your builder has just made a genuine mistake then it's a fair and moral thing to do. Lastly Loz if your SE comes back and says the joists are failing at the ends due to shear then there are other options open such as using a ledger piece and so on. To finish on a positive note. Many projects encounter problems which can be resolved with a will and in an equitable way. -
Builder cut 4.5cm off joists due to floor level screw up
Gus Potter replied to Loz's topic in General Structural Issues
Hello Loz. Sorry to hear about you dilemma. Your starting point here is to take another step backwards and understand what the implications are in terms of what happens to the declared strength of the timber when you rip a bit off the top / bottom / sides along the length. Typical structural timber for extensions and the like comes in grades.. you'll often see it stamped C16 or C24. When it is produced each length is put through a stress grading machine which applies a force. Sensors measure how much the timber bends or if it just snaps. If it comes out the end of the machine with the correct reading it gets a stamp to say what grade it is. Now timber has knots / wane / the grain weaves about and so on. You could say have a piece of timber with two knots near the centre but good grain top and bottom which passes the grading. Cut 40mm off the top and now the knots are in the high stress zone for bending so the timber can fail. In summary if you rip a bit lengthways of a stamped piece of timber the grading is no longer valid. You can notch it but there are rules which apply to where and how much you can notch timbers. Point this out to the SE / BC officer and see if they will still pass the joists given that the stress grading is probably invalid. -
Freeholder withholding consent for alteration
Gus Potter replied to bupieker's topic in Surveyors & Architects
Hello Pierrick. Welcome to Build Hub. Here are a few thoughts. Are you sure the walls you want to take away are "non load bearing". A key thing here is to recognise that although the walls you want to take away may not be carrying any direct vertical load from above they may be providing lateral stability to the walls that are carrying vertical load. For all. If you take a ruler, stand it up on and press down from the top then the ruler bends. Remember how hard you pressed down. Now get someone to hold it steady in the middle and press down again. You'll find that the ruler will take about four times the vertical load. The maths of this can be attributed to the mathematician..Euler.. a pretty famous guy if you are an SE. Now if you look at how many bits of wall are to be removed to form the open plan area you have to ask the question.. are any of these walls contributing to the stability of the vertical load bearing walls? The next thing to do is to look to see if the non load bearing walls are contributing to what we often call the sway stability of the building. When the wind blows for example it pushes the building sideways. This has to be resisted by the walls or structural frame which could be say a steel frame working alone, or a steel frame with stiffening panels between the columns or a brick building with internal stiffening walls. Pierrick I think you need to establish this first. If you don't at some point someone like me is going to ask the same questions. If it turns out that you can demonstrate that your proposals will be structurally safe then you have taken the high ground. This seems like a case where you are in dispute with say a home warranty provider. They partly rely on a war of attrition to grind folk down, hope they run out of money etc..if you get the structural side sorted then you can turn this around..run up their fees and this can concentrate their minds. Once you have the structural stability side sorted then you have the fire regs. Now an SE should be able to deal with this also. If they can show that structurally, even though the walls are "non loadbearing" that they have maintained/ remediated the fire protection between the floors for example.. by say producing drawings that show how they have maintained the fire protection where you have removed the non load bearing walls. In other words when a non load bearing wall is removed it can leave a gap in the ceiling which needs filled in properly. Make sure you can comply with the rest of the regs before paying for an SE. Once you have this SE support in place you can then press then for a proper response. -
services trench Services under a stone building
Gus Potter replied to saveasteading's topic in Barn Conversions
Hello saveasteading. That's interesting what you're doing so would like to hear more! I was wondering if that stone you have is Chert. Not sure though, but the way the face splits looks a bit conchoidal. If so it will be pretty hard as you know. Also, the surface is smoother so the lime mortar gets less of a grip thus although a hard stone each piece can come loose easily once you start say coring with the associated vibration. I've read a few of your posts (and responded after a fashion) and appreciate your knowledge. I wonder. If you have seven holes to do then it's sods law that some will locate under parts of the wall where you are changing the loading a bit and thus introducing more concentrated loads.. say by widening doors, near piers between windows and so on. "We will be protecting and filling that eroded edge." Have you worked out how you are going to protect the exposed edge of the wall? This could well be your starting point so if you nut that out a solution for the service penetrations may just offer it's self up. In an ideal world you want to leave the origonal stone in place.. maybe just because it's a good moral thing to do and keeps the ethos of saving a steading? Here is a few thoughts for all. Often on BH you hear much about clay soils which shrink and swell, they can be prone to long term settlement and so on. Trees for example can remove moisture from the ground causing the clay to shrink. When you cut down a big tree the moisture content of the soil can rise.. the clay swells up, often with great force which can lift things in an "undesirable" way. Sands and gravels are a different animal. Being simplistic (big subject) they are not generally prone to swelling and shrinkage. I'll leave frost action out as this is also an expansive subject but important if you have a BC officer who insists on a certain foundation depth to prevent frost heave.. So sand and gravels..can be good news but there is often no free lunch, well there can be but.. Sands and gravels derive much of their ability to bear load, say from a house foundation by the "friction" action between the particles. Each particle has a mass and this rests on the one below and presses / interlocks against the one each side so friction / interlock is generated. In the ground the stresses act in three dimensions, up.. down, left and right. If you fill a glass with sand and push down from the top it will bear weight. Take the glass away and the sand column will collapse. This is often called "confining" . In other words for a foundation the ability of the sand / gravel to bear load is partly determined by not just what is below but also to the sides and above. Importantly if you lower ground level you loose the dead weight of what is above (surcharge) and this can have a significant impact on how much load you can put on the soil. Now to generate friction between the particles we need mass and this comes from the density of each particle. But we know boats float..hopefully.. Archimedes. Now if you have a house and the water table is well down then you get the full mass of each partical of sand acting on it's neighbour. Raise the water table and now the relative density of each particle is roughly halved.. thus half the bearing capacity. SE's use this as a rule of thumb and it's one of the first questions asked.. where is the water table (and where could it be in the future) if building on sands and gravels. That's a bit of theory but applicable to say an old steading and also virgin ground. You also can get a bit of a "cementing effect". Here for example minerals will weave their way between the particles of sands and gravels and create more of a bonding effect so you get friction and bonding. It's very hard to test for this as testing is often intrusive and breaks the bonds and by the time it reaches the lab say it's lost it's mojo! We know these old buildings have stood for years but it's harder to prove why from basic tests. But we know they stand up. On a positive note.. a building will use every alternative load path to stay up before it falls down..but don't erode this factor of safety.. it's last resort stuff. Turning back to the practical side and in particular a typical Scottish steading construction. These were buildings to house animals / sometimes folk too and thus you can imagine that when they were build no one could forsee that they would have the value they now do. You have a "water proof" outer skin, random rubble interior and an inner leaf of stone that is less dressed and often less well bonded. The walls vary in thickness depending on their height and amount of buttressing from the interior walls. For these walls to work in simplistic terms they have to function in a number of dimensions. When you load the wall from above the load spreads out sideways. Often the vertical load is not central on the wall head so this causes a shearing effect between the layers as they work to share the load. When the wind blows the walls bend and this also causes a shearing effect between the layers in both a vertical and horizontal direction. For the keen this is sometimes called "complimentary shear". Remove material from one side of the wall and you loose the surcharge.. you invite movement between say the inside and outside of the wall. Vertical shear effects are introduced and the wall may protest. To quantify the above.. fairly recently a Black House fell down on one of the Islands. It was built on sand / gravel and lets face it although they sound great they were built with the few resources available at the time. They have an different way of dealing with driving rain permeating the walls but it's a good example of what you need to watch out for when doing up old steadings. Here apparently the builder had excavated out the inside down some 400mm, just to the level of the stone found. But removal of that small amount of surchage caused the sand to weaken on the inside, vertical shears built up in the wall, the layers delaminated and the thing fell down. Maybe the builder had a machine in, maybe there were some big boulders that were "eased" out when no one was looking" Who knows the whole storey. Luckily no one was hurt. If you've read this far then thanks and if you are thinking about doing up a steading in Scotland then I hope this helps. If you can grasp the basics it's a great journey and can give you confidence. Saveasteading.. sounds like you have a fairly robust structure so you may be fine. Would be interested to see how you are going to protect the exposed part of the wall and so on. Maybe as I said earlier it's a case of starting at the end, edge protection for frost / support and working back from there? Oh and do you know what stone it is and where it came from? -
Hello offthepiste. That's a good size of a house! If you are inclined to take everthing with a pinch of salt then here is some fun stuff you can check out when taking on a renovation of a victorian house. Imagine you are a prosperous Victorian (or small developer).. you commision a house. The Contractor would often turn up with a pattern book with different designs; room sizes, roof shapes, ceiling heights, cornices etc. You would pick what you liked. The builder would then look up a book that told him that if he made the walls X inches thick, used floor joists Y inches thick and foundations Z inches wide it would all be ok... if the ground was suitable. The builder would then give you a cost for this. Now for the founds. These were hand dug down a bit until the soil looked about right. Then often a labourer would go round with a tamper and whack down the soft spots. But they drank a lot in those days and worked six days so if your founds were done on a Saturday or a Monday then maybe like a British Leyland car.. they used to say..avoid a Friday and Monday built car. The mason would then come along, slap down some mortar and often build a stepped foundation. The rest of the house would go on top. Remember though that the Victorains built some substancial structures and had some pretty nifty mathematical methods of structural analysis available to then .. it's just that from time to time the house building market lagged behind as it still does in some respects, particularly when considering the quality of workmanship. One key is to understand fully how the house is built and what materials have been used in it's construction. Also, what it rests on on ground wise, the slope of the ground round about how the drains work and other environmental factors such as big trees and if you neighbours have done something that may "upset" your house. Get to the bottom of this and you can you can move forward in an informed way. You know that as soon as you start introducing insulation into this old house you'll change the "moisture" regime.. and that has to be managed / designed to achieve the outcome you wish. From a SE point of view the Victorian builders used rules of thumb. One for example is take the span of a floor joist in feet. Say 14 feet. Divide 14 by 2 gives 7. Add 2 inches = 9 inches. Thus as a rough guide for a 14 foot span you'll need a 9 x 2 in joist at 18 in centres. At that joist spacing you can also add a bit of extra dead load. You can stretch them to 2 ft centres. For a rafter it's the same but you only add one inch to the depth rather than two. We still use many of the old rules of thumb when doing preliminary fag packet sizing. Now we use metric units in the UK so the preliminary sizing formula look a bit odd. If you can get a handle on how the house stays up then that will help you. Hopefully the above will give you an insight. This will then give you a feel for where you can add load, say heavy water tanks, where you maybe want to review and spend money to the best effect. There is also what we call building stability.. what stops the house from moving sideways but I'll leave that for now. Hopefully the above will give you an insight. Once you nut out the basics.. ground, super structure, insulation and moisture control you can then start to develop how you are going to mitigate the energy usage / "carbon foot print". Lastly, if you have been lurking on BH for "tooooo long" you'll know that it's time to step up to the plate and post some photos! All the best though.. sounds like a great adventure.
-
Spot on. One key is to make sure you enjoy the journey and have as much fun as you can. Learn as much as you can by doing your research. Post some photos and you'll get plenty input from BH members.. All the best.
- 5 replies
-
- 1
-
-
- wales
- timberframe
-
(and 1 more)
Tagged with:
-
Hello newby2. No it's understandable that you may have a touch of the "jitters" at first. The main thing is to do a bit of research before you jump to any conclusion. All buildings move about as they are "elastic structures".. they bend, shrink, foundations settle / move about and so on and this manifests often as cracks. This crops up very often when folk are in dispute with say a warrantly provider on a new house. One of my go to references is BRE Digest 251 Assessment of damage in low rise buildings. It's an older document but it's a great guide on cracks in houses. It's 8 pages long and written in plain English. You can buy it for £15.00 from the BRE bookshop, apparently it is also "google able"... For all.. this is a great document to have a read of, whether you are building a new house, extending or just curious. Have a read at this newby2 and it may fill in the missing piece of the jigsaw.
-
Advise required around new roof - not straight!
Gus Potter replied to Ryan G's topic in Roofing, Tiling & Slating
Peter.. your eye is remarcable! the cut ridge tile. Ryan. Technically you could get out all the standards, manufacture's info and see if it complies. That will take a lot of time an effort. Even if you do this you often come up against the phrase " visually acceptable" and that is an issue.. acceptable to whom? Just a question as the photo is not that high resolution. Are there some really narrow cuts in the roof? In other words are the side laps ok? In other words we know that up and down the roof the tiles / slates need to over lap the ones below by a certain amount. But they also need to overlap sideways.. parallel to the ridge by a certain amount. You can get this side lap size from the manufacture's data sheet. If all ok then once it's weathered a bit then it will mostly all blend in. -
Sorry to hear that. Although they are both "technically " right it's a poor show. Assuming you are a domestic Client. Generally the expectation professionally, under the CDM regulations and the consumer protection act is that if you are a domestic client you are afforded some leaway compared with say a builder who is an experienced Client... They should be communicating (that is covered under the CDM regulations) with each other, that is part of their job. Even if they have gone in too low quote wise then as a Domestic Client how are you to know what is a fair rate. It's shoddy on both their parts and they are potentially leaving themselves open to trouble. If you want you can look up some of the things I mention above then.. drop them a pleasant but firm note. It's ok to say you don't understand some things.. but that you do understand that it is their job to make sure all is coordinated and safe. If no response then you may wish to consider binning them both as when it comes to the doing the work you'll probably get no support from them if the builder goes off track. If you do bin them then you'll be in a better position to ask for any monies to be refunded. Hope it all works out, it may just be a hiccup lost email or something else benign.
-
anyone else with a borehole?
Gus Potter replied to Tom's topic in General Self Build & DIY Discussion
Hi Tom. Yes it could be something simple. Check the things you can, even just to know you have not missed something blindingly obvious, before you start spending on fees / further testing etc. -
Hello Internet Known How. As a bit of background you probably know about the "45 degree rule" This is a kind of rule of thumb which assumes that any load from a party wall or foundation say spreads out at 45 degrees thus if you are 3.0m away from a party wall or neighbours found you can dig happily down 3.0m. But this is not always the case and this is where the issues arise. As a bit of background. If you tip out a load of broken jagged brick from a lorry it will form a pile. The sides may slope at some 40 degrees. Tip out a load of round gravel and the pile will spread further, the sides being less of a slope. Tip out a load of custard and the slope of the sides will be pretty shallow. This is called the "angle of repose" and it is roughly related to the shear strength of soils. Much will depend on the type of soil. You could have a stiff boulder clay / good chalk ( goodish shear strength) and this will allow you to dig deeper and closer so long as you don't leave the excavation open for too long. A soft / sensitive / high plasticity clay found often in the South East say can behave a bit like custard under certain conditions so the 45 degress rule can be no longer valid. The bearing capacity of a foundation changes depending on how much soil is above it. If the ground slips you can remove / change this extra weight on top which is confining the soil around the found. You also have to look at where the water table is for example..it can be quite complex as when you change this water level it can make the ground behave in a different way. It would be worthwhile having a chat with your SE and get them on board. They may not even charge you for this and give you good pointers. One aim here is to reign in the Surveyors, focus minds and hopefully speed up the process. Also, by doing so you can show you are acting in a responsible manner and this can carry some weight. On a light hearted note to finish.. if your SE mentions custard then ask if porrage behaves the same.
-
anyone else with a borehole?
Gus Potter replied to Tom's topic in General Self Build & DIY Discussion
Hi Tom A few thoughts.. If you can taste and see the physical rusting you need to get to the root cause of it..on the upside you can be "Columbo" or Miss Marple.. Your starting point is often to look at the obvious and rule things out. Here are few: 1/ Have you done anything in the house that may have impacted on the internal plumbing..is your boiler leaking system water into the potable water?.. do you have modern or old pipework? 2/ Is pipe from the head of the bore to the house ok, is it leaking and syphoning back say and drawing surface ground water in? 3/ Is the cover to the borehole sealed ok. 4/ Is the bore cased at the top and is the casing falling apart. 5/ Is the bore hole pump falling to bits. 6/ How deep is the bore hole. Very deep and it could be in the lower aquifer, shallow maybe in a perched water table..the two behave differently as they can draw the water from far away or close by respectively. Worth a bit of time researching this. 7/ Have a walk about.. in your garden first.. have you been using any fertilisers or chemicals? next.. what have your neighbours been up to? Have any local farmers etc been "improving the soil" or using the likes of iron suplhates? 8/ Has there been development going on round about you that could have altered the ground water regime. 9/ Any factories shutting down (mines used to be an issue but not many of them left) that have been pumping the ground water. When they stop the ground water rises and can flush stuff out to your bore hole. 10/ Has anything been poured down drains you own and other folks too. Drains / soakaways leak so consider this. I'll stop at ten things but if you can rule these out and think of a few more yourself then you could save yourself a bit of cash on professional fees. Just put together a small package of info you have and this will often serve you well. All the best and stick to the bottled water until you get to the bottom of it. -
CPD makes some good points and gives good advice here. Slating turrets is an art. If you want to have a word with the Slater then be familiar as to what is underneath.. maybe the first thing the Slater will do is to blame the joiner! The turret is a key feature and it needs to be right, often they are right over the front door.. not a good first impression. Ask the Slater if it would be ok on their own house? There are full turrets, half turrets and others and each needs a slightly different approach. If you have a full turret and are in a bind then sort out the bit you can see along the lines of what CPD is suggesting. As a fudge.. and only when you have little other options. On the back where it may be hidden you can sometimes get out of a hole if the side lap on the slates is too small by using a thinner slate with a code 3 lead soaker underneath.