Posted
My partner started frying some onions in the kitchen, while I was upstairs, I was amazed that the onion smell came out of the fresh air vent in the room I was in.  (my partner had previously commented that when I burn the toast she can smell it from the fresh air vent in her ensuite bathroom with the door closed)
 
Anyone else experience similar?
 
note my own investigations of my MVHR suggests there a sealing issue allowing some 'cross-talk' but before I fix it I was wondering if this smell transfer is normal?
Posted

Yes we have experienced something similar, but it has been intermittment nd I suspect that one source of the "cross-talk" is the external inlet and outlets. In our case they are both on the same external wall about 2.5m apart. Also the MVHR does not seal 100% - I think some of the manufacturers publish figures about this, I recall seeing figures in the upper 90% for sealing against cross flows.

  • Like 1
Posted

If there is 'cross-talk' between exiting air and fresh air input then either there is a leak within the unit or exhaust and intake are too close together on the outside of the building.

  • Like 1
  • 3 years later...
Posted

I’m in the process of designing my MVHR layout and this is definitely something I want to avoid. What are the recommendations for siting inlet and exhaust? How far apart should they be and can they both be in the same side/orientation of the house?

 

@readiescards, did you ever solve this?

Posted
Just now, Adsibob said:

I’m in the process of designing my MVHR layout and this is definitely something I want to avoid. What are the recommendations for siting inlet and exhaust? How far apart should they be and can they both be in the same side/orientation of the house?

 

@readiescards, did you ever solve this?


To ensure they aren’t off balance they need to be on the same wall. Try and get a minimum 1200 horizontal distance between them and vertical separation if possible. Also make sure they are accessible (or don’t have fine mesh on the intake) as you will need to access them to clean them otherwise. 

Posted (edited)
11 minutes ago, PeterW said:

Also make sure they are accessible (or don’t have fine mesh on the intake) as you will need to access them to clean them otherwise. 

Supply and extract on same external wall. 2.5m apart, extract 1.5m higher. Never had any cross contamination.

Fine mesh supply clogged after 9 months.

 

 

Inlet.jpg

Edited by JamesP
Posted

The 'cross-talk' I put down to the internal leaks within the MVHR - there are plenty of routes for the stale air to be sucked into the fresh air feed within the device.  Mine you havn't noticed it recently

  • 4 years later...
Posted

Not sure whether to start a new topic or resurrect this one after 4.5 years, but as I have the same problem I suppose it's best to comment here...

 

But I need a bit of a sanity check from those with experience of MVHR systems!

 

We have a Brink Flair 200 unit (it's the Dutch version, the same as the UK Flair 225, but without the screen) with enthalpy exchanger, and have noticed the same issue as described here. Except it's not just kitchen odours, but even less pleasant ones..!

 

To rule out our internal ducting, we even tested it by disconnecting the house entirely and just attaching two lengths of ducting to the unit. Smells which are sucked into the extract duct (shower gel, cream cleaner, coffee, whatever) come out of the supply duct almost immediately. It's really noticeable and strong. 

 

It's also not due to cross-flow outside -- Brink came out earlier this week and had a look, our installation is within spec. (Plus the effect is too strong and immediate to be external.) They swapped the exchanger core for a replacement, but the problem persists. (Not a surprise, as the smells also transferred with bypass mode on.) Their next plan is to do a smoke test.

 

I'm pleased that Brink seem to be taking this seriously, and the company that sold me the unit has been helpful.

 

Am I right in thinking that this just shouldn't happen? This isn't normal with MVHR or ERV, right -- nobody would want a ventilation system which spreads smells around the house! I clearly have a defective unit, right? Some seal must be missing or loose, otherwise this just wouldn't be occurring.

 

Both my supplier and the man from Brink said they've never experienced this before, just my luck to get the one defective unit! 

 

I wonder what model MVHR @readiescards has/had which exhibited this same behaviour?

  • Like 1
Posted

A normal heat exchanger the air and moisture simply cannot mix, they are two flow paths, the heat exchanger is just a heat exchanger.

 

Enthalpy heat exchanger are different but should only allow humidity cross over between the two streams.

 

So would suspect an internal leak within the unit 

  • Like 1
Posted
2 minutes ago, JohnMo said:

A normal heat exchanger the air and moisture simply cannot mix, they are two flow paths, the heat exchanger is just a heat exchanger.

 

Enthalpy heat exchanger are different but should only allow humidity cross over between the two streams.

 

So would suspect an internal leak within the unit 

“Stinks” of a manufacturing defect.

 

Unit needs a forensic strip down and rebuild, and to actually see / examine every joint and junction.

 

Probably something very simple, there’s not much to go wrong with these things. 

  • Like 1
Posted

Thank you @JohnMo and @Nickfromwales for your fast and clear replies, much appreciated 👍

 

It's good to know that I'm not losing it!

 

The unit was manufactured earlier this year, and it's only been installed and running for a couple of months, so I'm hoping there'll be a quick resolution.

  • Like 1
Posted
1 hour ago, Jolo said:

Thank you @JohnMo and @Nickfromwales for your fast and clear replies, much appreciated 👍

 

It's good to know that I'm not losing it!

 

The unit was manufactured earlier this year, and it's only been installed and running for a couple of months, so I'm hoping there'll be a quick resolution.

Keep us posted please!

Posted

Perhaps check that all vents are moving air in the right direction. eh that the bedroom vent is an incoming not an extract by mistake? 

Posted

Did they check the unit was actually connected correctly?  When I installed my unit I found the terms used to describe the ports confusing.  Could it be something like the supply vents supplying air to the rooms is mistakenly connected to the exhaust air port that should be exiting the house?

 

I would have expected Brink to have checked this on their visit but perhaps they "assumed" it must be connected correctly?

  • Like 1
Posted

Everything is definitely connected properly, I've checked it all about a thousand times, and the bloke from Brink checked it too. I've not gotten around to boxing in any of the ducting yet, so it's really easy to see what goes where, and follow it to its destination.

 

We've also tested the issue by disconnecting the house ducting from the unit entirely, and just putting two single internal ducts on the top -- one on the extract port, one on the supply -- to prove that the problem exists purely within the unit, so it can't be due to anything wrong inside the house.

 

Incidentally, I've also tested by sniffing at the exhaust duct, and the smells do also come through there, so it's definitely mixing air streams inside the unit. (If I'd somehow mixed up the exhaust and supply ports, the smells should only come through one of the "blow" holes, not both!)

 

I'm hoping to hear back from either Brink or the supplier in the coming days, I think they're planning to do a smoke test. I'll keep this thread updated!