BotusBuild Posted March 12 Share Posted March 12 16 hours ago, BotusBuild said: My DIY H or C manifold under test using my DIY tester at 2.5 bar Damn. Having been filled with water for nearly 2 weeks, just hanging around at atmospheric pressure without a sign of a drip, applying the 2.5 bar showed a small weep where the brass 90 at the top connects to the manifold. Time to undo, re-PTFE and tighten up again. Will just air pressure test this time along with soapy water sprayed on the joints. Meanwhile, the other DIY manifold is on test 🙂 1 1 Link to comment Share on other sites More sharing options...
Iceverge Posted March 12 Share Posted March 12 Did you wrap HDPE tape around the olive too? Just a wrap or two. I find it helps the whole thing slide into place as the tape is really just a lubricant. Link to comment Share on other sites More sharing options...
Mr Punter Posted March 12 Share Posted March 12 I have asked a plumber to make up a manifold for cold mains water and he is suggesting 28mm copper. I will post a picture if he gets it done. Link to comment Share on other sites More sharing options...
BotusBuild Posted March 12 Share Posted March 12 2 hours ago, Iceverge said: Did you wrap HDPE tape around the olive too? Yup 😞 Link to comment Share on other sites More sharing options...
SimonD Posted March 12 Share Posted March 12 8 hours ago, BotusBuild said: Time to undo, re-PTFE and tighten up again. Just as a tip, don't wrap the thread with ptfe, you don't need it and it might make you think you've tightened the compression fitting enough when you haven't. You only need to wrap the olive. Personally I hardly ever use PTFE tape any more preferring to use a jointing compound. 2 Link to comment Share on other sites More sharing options...
joe90 Posted March 12 Share Posted March 12 I find it amazing how many people use ptfe tape on threads that have nothing to do with water tightness. Link to comment Share on other sites More sharing options...
Russell griffiths Posted March 12 Share Posted March 12 Ptfe tape is not required on a fitting with an olive the olive makes the seal, the mistake people make is tightening in up until the get a squawking noise from the fitting, it then feels tight and they stop. what the fitting actually requires is lubrication to allow proper seating of the olive without the squawking noise. @BotusBuildimho 2.5 bar is not adequate for a test. Link to comment Share on other sites More sharing options...
joe90 Posted March 12 Share Posted March 12 8 minutes ago, Russell griffiths said: what the fitting actually requires is lubrication to allow proper seating of the olive without the squawking noise. +1 👍 Link to comment Share on other sites More sharing options...
BotusBuild Posted March 12 Share Posted March 12 The problem is not with the compression joint. It is where the 90 joins the end of the manifold. My olive joints are just fine 🙂 But thanks for the input. Link to comment Share on other sites More sharing options...
Russell griffiths Posted March 12 Share Posted March 12 I would ditch the tape and use a liquid product like locktight 577. Link to comment Share on other sites More sharing options...
sharpener Posted March 13 Share Posted March 13 4 hours ago, Russell griffiths said: Ptfe tape is not required on a fitting with an olive the olive makes the seal, the mistake people make is tightening in up until the get a squawking noise from the fitting, it then feels tight and they stop. what the fitting actually requires is lubrication to allow proper seating of the olive without the squawking noise. Yes, +1. A single drop of 3-in-1 on the thread before you fit/tighten the cap nut means much more of the torque you apply is turned into axial force that in turn compresses the olive. I also find the thinnest of smears of old-fashioned jointing compound on the olive is all that is required for a perfect seal yet easy to dismantle. The rightful place for PTFE is mostly in the tool box, occasionally for male-female threaded joints. Link to comment Share on other sites More sharing options...
crispy_wafer Posted March 13 Share Posted March 13 I've been pottering about with hep over the last couple of evenings, getting the Hep down from the 1st floor void into the plant cupboard in and orderly and tidy fashion is proving a challenge, I know its only a plant cupboard, but it will look crap and bug me forever. To resolve I can think of two options 1) cut the hep up in the void and install 90's on each and run copper tails down the wall to the manifold, or 2) install the manifold in the floor void and just run supply and drain tails down the wall. Have an access hatch in the ceiling so I can poke my shoulders, head and arms in there should I need to. What do you think? Link to comment Share on other sites More sharing options...
BotusBuild Posted March 13 Share Posted March 13 I would choose option 1. IMO better to have access to the manifold in the plant room than having to scrabble around in a void. Easier to isolate just one pipe (assuming you have isolators on the manifold). 1 Link to comment Share on other sites More sharing options...
BotusBuild Posted March 13 Share Posted March 13 (edited) 16 hours ago, Russell griffiths said: imho 2.5 bar is not adequate for a test. 4? 5? 6? ??? 🙂 Currently testing the good manifold at 4Bar Edited March 13 by BotusBuild Link to comment Share on other sites More sharing options...
SimonD Posted March 13 Share Posted March 13 22 minutes ago, BotusBuild said: 4? 5? 6? ??? 🙂 Currently testing the good manifold at 4Bar The Hep20 guidelines: Quote First carry out a low-pressure water test at 0.5 – 1 bar when the system is just demountable fittings, then a pressure test at 1.5 x the normal working pressure with a recommended minimum of 10 bar for a minimum of 45 minutes. However, if any of our slimline fittings are included with the system, then an 18-bar test for a minimum of 45 minutes should be carried out. https://blog.wavin.com/en-gb/push-fit-hep2o-your-plumbing-faqs-answered Link to comment Share on other sites More sharing options...
Russell griffiths Posted March 13 Share Posted March 13 @crispy_wafer I did this. Link to comment Share on other sites More sharing options...
crispy_wafer Posted March 13 Share Posted March 13 27 minutes ago, Russell griffiths said: @crispy_wafer I did this. now that's exactly what I'm thinking of, whether I can execute it aswell remains to be seen. But thats just perfect for me. How did you finish the ceiling? Cut a rectangle out of the board, or fingers for all the pipes? Link to comment Share on other sites More sharing options...
BotusBuild Posted March 13 Share Posted March 13 That, Mr Griffiths, is a thing of beauty. Link to comment Share on other sites More sharing options...
Iceverge Posted March 13 Share Posted March 13 21 hours ago, Mr Punter said: I have asked a plumber to make up a manifold for cold mains water and he is suggesting 28mm copper. I will post a picture if he gets it done. Anything wrong with the 22mm Hep push fit? Worked well for me. Link to comment Share on other sites More sharing options...
Mr Punter Posted March 13 Share Posted March 13 46 minutes ago, Iceverge said: Anything wrong with the 22mm Hep push fit? Worked well for me. I imagine it is fine but we are feeding 8 flats. We have a new 32mm MDPE supply so we are thinking 28mm copper with 28mm x 28mm x 15mm reducing tees to each of the meters. The 28mm will also have a cold water accumulator. Current setup is 15mm spaghetti, so electric showers tend not be too impressive. Link to comment Share on other sites More sharing options...
BotusBuild Posted March 13 Share Posted March 13 4 hours ago, SimonD said: First carry out a low-pressure water test at 0.5 – 1 bar when the system is just demountable fittings, then a pressure test at 1.5 x the normal working pressure with a recommended minimum of 10 bar for a minimum of 45 minutes. However, if any of our slimline fittings are included with the system, then an 18-bar test for a minimum of 45 minutes should be carried out. Right, so I was able to test to 6 bar using the pump I had. I now have two sealed manifolds ready. I guess the next test will be when I connect them up to the mains in a few months time. Thank you to everyone for your input. PS, I am a convert to the liquid sealant which worked first time on the joint I was having problems with. (High-Tech 35 S 77 PTFE Sealant for Gas and Liquid WRA compliant from my local (non-chain) plumbers merchant) 3 Link to comment Share on other sites More sharing options...
Thorfun Posted March 13 Share Posted March 13 2 hours ago, BotusBuild said: I am a convert to the liquid sealant me too! Loctite 577 makes it idiot proof. I am living proof. 3 Link to comment Share on other sites More sharing options...
Russell griffiths Posted March 13 Share Posted March 13 5 hours ago, Mr Punter said: I imagine it is fine but we are feeding 8 flats. We have a new 32mm MDPE supply so we are thinking 28mm copper with 28mm x 28mm x 15mm reducing tees to each of the meters. The 28mm will also have a cold water accumulator. Current setup is 15mm spaghetti, so electric showers tend not be too impressive. There is a company on e bay, who make up purposes designed manifolds for splitting incoming mains. have a hunt, they look good. Link to comment Share on other sites More sharing options...
Russell griffiths Posted March 13 Share Posted March 13 this sort of thing @Mr Punter 1 Link to comment Share on other sites More sharing options...
Mr Punter Posted March 14 Share Posted March 14 13 hours ago, Russell griffiths said: this sort of thing @Mr Punter Yes I saw those and they look v good value compared to the commercial stuff from plasson etc but we are in a tight space and the plumber suggested Ts from a 28mm. I know not much about plumbing but thought if the purpose designed one leaks you would need to replace the whole thing where with normal fittings maybe not. Link to comment Share on other sites More sharing options...