Everything posted by HerbJ
Setting up / balancing my MVHR
HerbJ replied to ProDave's topic in Mechanical Ventilation with Heat Recovery (MVHR)
I can assist by providing the Volumetric Design Calculations that were produced for my MVHR systems. These were produced using two different approaches for the design target levels for each room - the DIN standards and also the BR Part F Requirements. The reason the bedrooms have different flow rates is basically because they are different volumes... Note, my house is located in England @Bitpipeand I went through the same brain twisting being experienced by @ProDave and I produced this note to rationalise my thoughts at the time. I hope it helps you ( note, the figures quoted were early in our design process and sizes changed during development of the build and the Helios Tool is an online app for calculating design volumes according to the DIN standards) .... I have been contemplating our MVHR designs and it is very clear that both designs are completely dominated by the BR Part F requirements for whole house ventilation. Table 5.1 (b). - for Eastcroft = 364m3/hr and for your house 372 m3/hr ( depending on your measured GIFA). Anyway it seems to me, and to others, that though we will have demonstrate that our systems can meet this requirement for BR , we would never operate the system at this level and the system would be set up for something completely different. Unfortunately, it is this system sizing that most of the less experienced retailers focus on when they sell their systems and thisn drives a requirement for these systems to be sized and operated at this level. I am fairly sure that where Zehnder are coming from by insisting that Eastcroft requires two Comfotair CA550 units, so that they run quietly at a much lower operating point they will never see again after the BC have approved the installation. I have also come to realise that though the DIN designs managed to produce from the Helios Tool are correct, for what I entered but I have probably entered some rooms that may not require individual extract/supply air and this has potentially oversized the system, though DIN does seem to be able to take into account the practicalities of operating systems at various levels - Moisture Protection, Reduced, Nominal and Intense ventilation So, realisng my lack of MVHR experience, I have trying to found some practical and sensible technical approach to sizing MVHR systems and even tried to get a copy of the DIN standard (no joy, it costs 140 euros). Finally, I came across a recent Passivhaus document that was actually highlighted on ebuild only within the last week. I attach a pdf version of the Chapter 5 which provide practical and passivhaus approach to sizing MVHR systems see http://www.ebuild.co.uk/topic/16037-how-to-build-a-passivhaus/page__pid__121081#entry121081 So, I have quickly used this simplified and practical approach to re- look at both Eastcroft and your house. For your house, if we just take the quoted extract rates for your kitchen, Ensuite bath, two family bathrooms, utility room and cloakroom this gives a Extract Requirement of 240m3/hr. Then for supply, I reckon you have nine habitable spaces at 30m3/hr = 270m3/hr. In any case, your house will only have 4 occupants and this should also be taken into account. So, taking the Standard (or nominal setting as per DIN) as 0.3 ACH = 0.3*853m3 ( the volume of your house from Helios) = 255.9m3/hr and the Boost Rate = 1.3* 255.9 = 332.6 mm3/hr. So these "passivhaus" recommendations are not too dissimilar to the Helios Fan supported airflow volumes, according to DIN, on page 4. In Part F the boost rates for extract volumes are for kitchen =48.83m3/hr, cloakroom/toilet = 21.6m3/hr and bathrooms = 28.8m3/hr. so the passivhaus recommendations are all higher except for the cloakroom /toilet which was 20mmm3/hr This starts to provide a little more confidence about sizing of our MVHR systems, rather than to start and finish at Part F Requirements . 38167 HRV Volumetric Design 2015-4.pdf How_to_build_a_Passivhaus_Chapters_5_to_9(3).pdf -
MVHR newbie.. help needed
HerbJ replied to Savage87's topic in Mechanical Ventilation with Heat Recovery (MVHR)
Yes, I installed a Paul Novus 450 in 2016 and it has been operating successfully and quietly since it was commissioned in October 2016. I routinely change the filters. It is installed in a reasonably Plant Room , which is accessed from the garage and is adjacent to the downstairs cloakroom and pantry/utility room. The MVHR unit is mounted on feet, directly to the floor (passive foundation) and not attached to the TF structure, so no vibration induced noise.. I ensured that good sound insulation was installed on walls and ceiling. When in the Plant Room, the MVHR unit is relative quiet in normal operation but the noise increases on boost, but not enough to be uncomfortable when working in the room ( cleaning golf clubs as I was on Monday). Outside the Plant Room, in the garage or house, it is completely silent, though if you have really good sensitive hearing you might just hear a very low noise on boost, when you are in the cloakroom. The MVHR unit has flexible silencers to connect to the steel ducting, which goes to the two plenums in the room above ( see plenum). I have also wrapped both the flexible silencers and the insulated extract duct (from the MVHR to the outside extract grill) with a layer of aluminium foil faced ductwrap insulation, which made a noticeable reduction to sound level on boost. The Plant Room is located immediately, below the Guest Bedroom and there has never been a noise problem. In fact, the inlet and extract plenums are installed in a service cupboard in the guest Bedroom and they are completely silent. The plenums are connected by steel ducting and a large silencer before the inlet plenum and a flexible silencer on the outlet from the extract silencer. All the inlet and extract vents in each room are reasonably silent except for a slight increase in noise on the extract in the Family Bathroom when on Boost. -
I think the info was by me , originally from ebuild. The useful info can be found in a thread called "Wetroom in Kore slab". On the question of mat wells, we have porcelain tile floors directly laid on a poured MBC slab and we created matwels using standard metal tile edging strips, which us matwells approx 15mm deep, which is sufficient for entrance mats. The suitable matting can be bought by the metre to suit
These may help = couple of photos taken ahowing my PV panel installation in an in-roof system. There is more info on the site, including more photos of mine and similar installations so just search
To be honest, I have no hard data but SWMBO does prefer the main bedroom/ensuite to be warm, so I imagine the UFH in these rooms is active for a fair % of time when the weather is really cold. We do have the advantage that 1st Floor every bedroom, the main ensuite and the family bathroom have individual temperature sensors and are controlled to suit. Most of the time, everywhere except the main bed/ensuite is set so that they never come on and they sit happily at 18 to 20C, a couple of degrees below the Ground Floor.
Yes, that's correct. We installed a Jupiter Proprietary installation system - see attached. the ECO-100 PI in the bedrooms with engineered wood floors and the ECO-400 PI in the bathrooms with porcelain tiled floors. It was a relatively expensive option, but the Jupiter system also give some measure of acoustic properties as well,. SWSBO wanted comfort and we both believed that the type of house we built (320m2 in a high value residential area) required UFH on the 1st Floor if we ever decide to sell. It does provide a added measure of comfort, though for most of the time with individual room temperature control, which for the most part is set to provide heat to the Master Bed and ensuite, unless we have visitors (family, grandkids...). l believe there are other BH who decided against fitting upstairs UFH, even if it was only bathrooms, and wish they could revisit that decision! We have experienced no creaks and groans. It operates at a very low temperature . We didn't fit any kind of heating on the 2nd Floor but did install plumbing for future installation of heating. We have the study and a play room/media room on the 2nd floor and it the temperature is acceptable in winter. ECO-10U Pt E.pdf ECO-40U Pt E.pdf
German windows with roller shutters built-in — who makes them?
HerbJ replied to Dreadnaught's topic in Windows & Glazing
All the shutter parts can be found on https://www.jalousiescout.de/- 15 replies
- roller shutter
- security shutters
(and 2 more)
We've just had window film installed and it seems to be working successfully in controlling heat gain. We had 43m2 installed, on South and West facing windows at about £64/m2. We looked at the 3M window film and that was £127/m2. Happy to share details!
Sometimes you wish you'd read BH in more depth and more often....
HerbJ replied to ToughButterCup's topic in Heat Insulation
or do you just like Michael Connelly novels? -
Yes - two double sockets and a TV coaxial/Cat 6 for TV etc. One of the the wall is a 1400mm high X 140mm stud wall, which requires zero zero structural integrity. The studs were not hacked. The carpentry is better than some carpenters work I have experienced.
Something like this? Our electrician installed specific noggins for every back box and support required for the electrical 1st fix - he has more tools than the carpenters! He didn't try to use the noggins in the stud walls that were part of the TF
Point taken - I have corrected my earlier response to make sense of my point on cooling. For inlet heating, this is NOT an uncommon location on some MVHR systems for frost protection, though many like my PAUL NOVUS unit have the frost protection heater mounted internally.
Presumably, this duct heater/cooler would only be in operation as a cooler when the summer bypass is open on the MVHR Unit? So, there would be no issue with throwing away the cooling....
I bought the cheapest unit I could find and it has been working well for over 2 years or so without any problem. it is a unit made by SolarImmersion - see https://solarimmersion.co.uk/
We were required to have fire doors because we have a 3 storey house with an open stair case through the central core of the house. So, all the habitable rooms off this central core all specified as fire doors.
- 31 replies
No, not the linen cupboard just the habitable rooms - all the bedroom doors (off the landing) but not the ensuites .
- 31 replies
Yes, we used the same supplier. All our doors were supplied as door sets, except for some cupboard doors on the 2nd Floor and I should have bought door sets for these! The Ground Floor doors are 926 x 2014 mm minimum, with double doors to lounge, dining room ad kitchen . All Fire Doors The First Floor bedroom and family bath doors are all 826 x 2040 mm, with , the double doors for the linen cupboard and 726 x 2024mm for the guest ensuite. All bedroom doors are Fire doors The 2nd Floor doors are a mix of 826 x 2040mm and 726 x 2040mm, to suit the layout. The two habitable rooms are fire doors.
- 31 replies
Standard practice for most developers, together with creative use of NMA's and change of conditions, which normally involve slipping in new plans with wholesale changes to the original approved plans. My wife is Chairman of the Parish Council Planning Committee and it seems that a good proportion of Planning Application in this area are retrospective by Developers "gaming" the system . She has s a case at committee tonight - new build in green belt was given approval as a replacement dwelling in 2017. The developer didn't build anything close to what approved and is putting in retrospective planning application for a house that must be 50% bigger than the house approved ( which was 50% bigger than the original dwelling). The construction has been stopped by enforcement after the neighbours reported it and the developer has already withdrawn one retrospective application in 2018 and is trying again after removing the garage ( there was no garage on the original application??) It's a game and developers are very good at it...
I also would recommend this course of action. It is the least line of resistance and stress. Also, use the the" Certificate for zero rated VAT" when dealing/communicating with contractors, ideally pre-contract. I went into this in some detail with HMRC and several things were made very clear HMRC will NEVER refund VAT incorrectly charged. It must be properly accounted for and refunded by the contractor. It is unlawful to charge VAT in contravention of the applicable Regulations. If a contractor unlawfully charges VAT and refuses to correct the invoice and refund the incorrectly charged VAT. then the final step available would be to take the contractor to the small claims court and make a claim for the unlawfully charged VAT
The locks on our Gaulhofer 3G French windows and EVVA EPS Cylinders. I haven't noticed any draught or window coming through in any circumstance, though we are not that exposed. Ditto the lock on our Gaulfofer 3G Front Door, which is a Q Line cylinder Lock?
MVHR air flow rates
HerbJ replied to lizzie's topic in Mechanical Ventilation with Heat Recovery (MVHR)
Well done. Fingers crossed for you? -
MVHR air flow rates
@lizzie No, you are on the right track . Using your layout drawing information, I calculated your floor area as 124.4 m2, so if you have high ceilings then your calculated volumes seem OK. Using my calculated floor area of 124.4 m2, the Part K minimum ventilation requirement in accordance with Table 5.1(b) - 124.4x0.3x 3.6 = 136 m3/hr, which highlights that your house has been well over-ventilated on a day to day basis at the design rates of 220 m3/hr taken from your attached documents. The reason that you have more extracts than most houses is that you have extracts in the plant room and your Master Bedroom, which were not really essential and do not need to have such high airflows in those two rooms. If you use the passivhaus/din method for sizing the airflow for normal situations then assuming 5 people living in the house gives supply airflow of 5 X 30 = 150m3/hr and using 50m3/hr for the kitchen, 30m3/hr for the bathrooms and utility and 20 m3/hr for the toilet this give s total extract rate of 160 m3/hr ( ignoring the dressing room and plant room for the moment). So, not too much out of balance. Also, all within the Part K requirements. So what I would do is to set these extract rates above for kitchen, bathrooms and toilets which all meet or exceed the minimum BR extract rates for these rooms)and use a lower rate of 10 m3/hr for the dressing room and plant room (both small rooms) = total extract rate of 180m3/hr. For the supply rates use 40m3/hr (2x20m3/hr) for the living room, 35 m3/hr for the snug and 35 m3/hr for the Master Bedroom and 30m3/hr for each of the two bedrooms = total supply rate of 170 m3/hr. Use these rates to set up the system for Setting 3, with your F7 filter in place. Then, set Settings1, 2 and 4 as detailed in your Operation Instructions. I would operate the system on Setting 2 on a day to day basis, when there are just two of you (and then dog) in occupation. It will be much quieter at all settings, more comfortable, cost less money to run and should give you everything to want..... and of course it complies with the BR. Hopefully, with your enthalpy HE , you will also see more comfortable RH% I am sure that my thoughts set out above will be picked apart by others reading it and they will identify any issues with what I have summarised. Again best of luck -
MVHR air flow rates
+1 to @JSHarris I've just a quick look at the info you attached earlier So, you have 4 settings, pretty similar to that described by @JSHarris Setting 1 is your unoccupied house setting - named "moisture protect" in your details - this should be set set at 30% of BR Flow, - currently it set at 50% of Setting 3 Setting 2 is named "low" setting - this should been set at 70% of the BR Flow - currently it set at 74% of Setting 3 Setting 3 is named "living" - the BR flow rates , which I believe that was used for all the flow volumes measured - BR Flow = 100% and the subsequent setting for Setting 1, 2 and 4 - Setting 4 is your "boost " setting - this should be set at 130% of the BR Flow - currently it set at 152%% of Setting 3 All your Design info is on your layout drawing, including design flow rates for each supply and extract outlet, together with m2 area of each room ventilated. In short you have supply rate in total of ( 4x40 + 25 + 30) = 215 m3/hr extract rate in total of (4 x 20+2 x 22 + 2x45) = 212 m3/hr It seems you have been operating at Setting 3, which is the 100% BR rate and that is greatly overventilating the house. A better setting for day to day living would be Setting 2, with Setting 3 only used when you are cooking or drying clothes or having a party. Setting 4 should be used when using bathrooms etc. I don't know who created the "air flow details" spreadsheet? was this your installation/commissioning man after he commissioned the system? This requires reviewing against as some of the settings do not seem to be consistemt with the recommendations in the manual extracts you attached. Best of luck