sense check twin beam calculations
Gus Potter replied to johnhenstock83's topic in RSJs, Lintels & Steelwork
To refine a bit you can buy tubular beam spacers off the shelf. See link say below. https://esteels.co.uk/structural-steel/universal-beam-twin-chs-spacer-touching-separate/ But often the walls don't have a consistent width of cavity.. good design when say knocking holes in walls is about anticipating some of the things that may not be built the way you think they are and generating as many "get out of jail free cards" as you can. The next stage is to note this on the drawings so the Contractor who is pricing the job can see that someone has put a bit of thought into it and tried to derisk it. -
Copy and paste your post to Masons Mortar of Edinburgh and take advice.. these folk know their stuff! Off my own bat. The stone you have looks like much what we encounter down the east coast of Scotland.. not well "sedimented" sandstones or more likely "conglomerate" in other words they tend to not weather well. These houses were built by the gentry for workers, they were not good quality. You need to get your head round the fact that these houses are what they are.. they were built as cheaply as possible for the land / estate owner so they could extract the most they could from their workers.. they are basically shite structurally / in terms of workmanship and let water in! Get it out your head (if you have had that thought) that they are quality buildings...they are not. @Tapster my post is encouraging later. You are trying to now make a silk purse out of a pigs ear!. The Scottish gentry lived say in Edinburgh / Glasgow and built in Ashler commonly ( oh! yes it was the Scots taking advantage of their own! nothing to do with the "English" or the "Welsh" or the "Irish" it was a "big boy" that done it and run away for those who are seeking factual history) .. faced sand stones.. the best.. I'm happy as an SE (and have done so) to convert these Edinburgh Ashler buildings all day long.. You'll see this in most Fife and Ayrshire coastal towns where the middle of the stone has weathered and the mortar is sticking out and that just drives water into the wall. Sometimes with a bit of thought you can recover the situation and live happily ever after. You need lime mortar.. you'll see often recommended a NHL3.5 lime mortar, bin that idea and go for a NHL 2 lime mortar which is supposed to be used for internal work only. But on this type of stone it's the angle of the pointing to shed the rain outwards that matters and acceptance that it needs regular maintenance. The idea is that you use a soft lime mortar that erodes faster than the stone.. you maintain that.. like cleaning your gutters. Eventually the stone will erode and need replaced.. hopefully it won't happen during your tenure.
-
@kelvin is correct. The construction courts / courts recognise that some Clients are experienced, some are domestic (inexperienced) and thus are afforded more protection under the law. Often domestic Clients get into dispute with dodgy builders who have written their own contract. While it can be difficult to argue against the terms of payment it is much easier to hit these builders in their weak spot which can be poor quality work that compromises structural safety. That could be anything from cavity width to incorrect insulation that could cause condensation that could compromise a structural frame. There are lots of ways to tie back bad work to safety considerations.. it's often knowing how you do that and present an argued and reasoned case. I do this with say the NHBC and other warranty providers etc who can be a bit.. (insert your own words) at times to speak. You can often debate to the ends of the earth about the quality of the finish.. but hit them on a structural issues and you often have the upper hand.. you make them rack up defense / consultancy costs and force them to employ their own Consultants.. who often won't touch them with a barge pole.
-
From what you posted that looks like an expensive mess by the SE. These pads and the disruption look like they will cost you a fortune. It also looks unbuildable at a sensible cost. It's not just the structure it's moving electrics / plumbing, cutting floor joists and making good.. the absolute mess it will make during the works that needs to be reinstated at a cost. From time to time I see stuff by other SE's where I think.. fair enough.. but this is ringing alarm bells. The other big one is the sideways stability of the building and the knock on costs. Can you post a full set of plans. By that I mean the whole lot.. all floors and sections etc. If I'm jumping to conclusions and wrong on this I'll say so and take the flack.
-
Lots of agreable points here @OwenF To paint a bit of a picture I think Alan has in mind a single storey relatively light weight timber framed structure going on top of a basement, say a formation depth of 4.0m, insulation on that with a concrete box on top. This is a bit different from a heavily loaded raft (basement slab) say where you may want to recognise that the pressure bulb under a raft can be quite extensive and extend to a considerable depth, just say 2 times the maximum slab dimension.. Atkinson et al? Being pragmatic you could take the view that what you are digging out to form the basement is heavier than what you are putting back, thus the stress at formation level is similar or less. Now let's also say that the local geology and superficial deposits are pretty well understood. But due to the natural variation in soils you could end up being unlucky and build on the only rubbish bit. Now if that was to be the case then you could maybe even pick this up during a walk over survey.. notice a depression in the ground say as the soil has been loaded more histrocally than what you are intending to put back. If your formation is a 4.0m then investigating to 6.0m should cover most risks given the loads at formation level in this case. I often lean towards trial pits as you can really get down and dirty with the soil, also you expose a larger surface area of soil that you can "feel", look at, smell (if confident ground is not contaminated) and get a better idea of the strata etc. Also great point for @saveasteading on another post.. you can do some soakaway tests etc at the same time. Jury is out on this one, can only suggest this may be a requirement of a specialist basement designer, best thing to do is ask what they are going to do with the results. They may have a perfectly and sensible reason for doing so on this kind of design. On something like this I would want to try and understand as much as I can about what is lying say up to 2.0m below the formation as a perched water table / local artisian pressure is always a risk. For self builds the cost can run away if you need to indulge in extensive bracing of the excavation and have to manage ground water. If in good ground you could assess the stand up time, and try to mitigate the temporary works cost. With a fair wind you could just batter back the excavation.. simple if you have the space to do so. A contractor pricing this is often going to assume the worst and price accordingly as it is a one off self build. Their mind set is often.. it is a one off so if I lose a bit I'll not get the chance to get it back on the next job. If you plan out the works, sequence and provide the Contractor with good information it should help drive the cost down. There is a risk (will be in the contract) in that if it all goes south you'll have to pay more. But you may not end paying any more at the end if it does go south than if you accept a price from a contractor initially based on the worst case. Also if you have good ground information you'll be in a better postion to push back against a Contractor if they hit for unjustified extras.. you can say.. I gave you the info.. it's your fault for not reading it. I bet you've told so many people so many times.. set aside a meaningful percentage of your budget, give me the resources to do my job properly and I'll probably, nine times out of ten, easily cover my fee and could save you thousands or more.. If you look at the figure mentioned above we are talking a couple of thousand each way.. but imagine what it could cost if you encounter something in the ground that you could have discovered for that small extra amount of 1 - 2 thousand. That difference could get swallowed in a day or two on site with especially if you need a sudden re design.
-
Reinforcing a 1st floor timber floor by adding additional joists
Gus Potter replied to TimL's topic in Floor Structures
Sometimes there is an easy way around this. Below is a screen shot of part of one of my designs where I'm strengthening a floor. The additional joists are shown in green hatch. You'll notice that at the top of the drawing that the sistering joists don't extend to the wall head. The roof on this job is a pole plate roof so there were issues around extending the joist to the wall head that I needed to avoid. The sistered joists are well fixed to the existing. The objective is: 1/ The big bending forces near the middle of the joists are resisted by the double timbers, old and new. 2/ A lot of the deflection is reduced by the doubled timbers where the bending stresses (near the middle of the span) are high. To prove this works you: A/ Check the double timbers for strength so they don't snap near the middle of the span. B/ That the deflection is ok.. how much they bend down by in the middle. C/ That where you only have the existing single part of the joist bearing onto the wall that is can take the extra shear loads arising form the extra load you are adding to the floor. D/ That the bearing strength of the existing timber on the wall plate is ok in terms of transferring the extra load to the wall head. E/ That any door / window lintels etc under the wall plate / wall under the joist ends can take the extra loading. You may find this approach works so long as you are not adding too much extra load to the floor... say by using a concrete screed for the UF.. a lightweight overlay UF should be possible. I would ask an SE say to have a proper look at this as they could easily save you more money and hassle than the amount you need to pay them. Given the size of joists you have (40x210mm) you may find the above works. You may need some extra noggings (dwangs) to stop the joists twisting at the ends. The above is one solution but you can often tweek it to avoid having to but a ledger piece to the wall or form extra pockes in the masonry.- 13 replies
-
- floor joists
- joist hangers
-
(and 1 more)
Tagged with:
-
2-Ply Glulam Beams - Nails?
Gus Potter replied to Mulberry View's topic in General Construction Issues
Good question. Hope some of it helps someone, especially those designing their own TF in principle and some of the things you need to think about..I make some general comments. The two diagrams you posted look as they do.. but odd in some ways. Starting from the top. 1/ The grade of Glulam 28c.. your TF supplier? They I assume will have priced for this on how they operate / cost / lead times but a 28c often carries a significant price premium in one way or another compared with a 24c or a 24h grade which is less strong but is made from more readily available timber. I would ask the question.. is it cheaper to use a 3 ply in 24c or 24h and can it be fitted in? Ok.. you may ask what is the difference between the suffix c & h? A Gluam beam is built up from layers of timber glued together. When a Glulam beam is subject to bending forces only (usually from a floor) and rests directly on say on a wall head we can make the beam out of stronger timber on the top and bottom and put weaker timber in the middle. This means we combine different strengths (grades) of timber hence the c = combined so more economic. The h grade means that we use the same strength (grade) of timber for all the beam laminations so it is homogeneous = h Now in some cases, say for a beam resting on a wall this is ok.. but it is often NOT ok when we want to connect a glulam to something else using say Simpson Strong_Tie connections or a steel beam unless you design on the weakest bit of wood! and if you do that then why pay for a higher grade of beam when you could make it thicker say. Big heads up.. if you have a separate SE make sure they know what the TF designer is assuming! Nail spacing horizontally (600mm) . This looks a bit far apart to my eye. I would go for 250 - 300mm centres. Now this may seem a bit trivial to the naked eye but it matters when you do your design checks. A closer nail spacing means that you can treat the two Glulams as acting together (compositely) so you get more bang for your buck in terms of performance. The spacing shown looks odd. Ask the question.. basically has the detailer not implemented the SE's design? The nails are all shown with the heads on the same side. This is not good practice. Also the nail length is indicated as 75mm. 75mm less 45 mm only gives you a point penetration into the Glulam behind of 30mm which goes against the principle of nail design. I would specify a 90mm long ring shank nail for this. Ask why they are all from the same side, not opposing and appear to short. The distance of the nail down and up from the top and bottom of the Glulam. If we are using solid timbers nailed together then we often stagger the nails above and below the horizontal centreline of the beam by about 25-35% of the depth of the beam, it varies depending on beam depth so this figure is representative. We do this as solid timbers tend to "cup"over time. In other words the middle bows in or out from the centreline. You can often see this in old solid timber joists where the sides are bowing.. cupping. Cupping happens when the older wood shrinks differently from the younger wood. Now Glulam beams are not supposed to be too succeptible to this type of cupping behaviour when surrounded by air of the same moisture content on both sides. But if not they will cup to some extent. If you nail the beams together in the way shown you could cause them to cup and split the lamination.. now you have a problem! Suggest you go back and ask the TF designer if they have thought about this and can confirm that for your application all is ok given the 30mm nail point penetration which raises an eyebrow. Last but not least.. you are going to be fixing a ceiling and floor to the top and bottom of the Glulams possibly. The floor in particular serves to brace the tops of the joists to stop them twisting sideways and if you stop this you get a good stiff floor. Now the flooring nails will likely compromise the nails you show in terms of code compliance. That is why I sugest earlier that the nails are staggered above and below the horizontal centreline, it keeps them away from the flooring / noggings / ceiling nails. Suggest you go back to TF detailer and query. Check the specification and point penetration required by the flooring manufacture and you may find the TF and flooring spec clash. For all. At the end of the day once you get your head round the principles of how timber works then it's a great material to build a house from. The above is a bit tecky but if you think about it much is common sense! -
Your Rockwool is probably a good balance. The important thing is to install it properly, no gaps and not pack the wall tighty.. it needs a residual air gap.... see installation instructions. Following the installation intructions is probably the most eco freindly appoach.
-
Exposed steel columns: mitigating thermal bridge
Gus Potter replied to ectoplasmosis's topic in Heat Insulation
Not a lot, probably less than the door / window handles and the letter box on the front door. Forget it and move on. -
Beam helper on stair stringer
Gus Potter replied to MortarThePoint's topic in General Construction Issues
If your half landing at the bottom is buttressing the upper set of treads / stringers against horizontal movement then you actually can show you need minimal fixings at the top. Think about a ladder against a wall with someone holding the bottom still. The load at the top of the stringer is horizontal only (as the top of the ladder can slip down the wall) which in your case is pushing against something solid. If you are confident your half landing can resist the horizontal loads then your problem is solved! All you need is a few fixings at the top of the stringer to stop the stair moving left or right in the plane of the top landing. Does this work? -
Hiya. Well done you! it seems you are now getting into making big design decisions on the structure and how that interacts with all the other elements of the design. That all sounds great on paper but in practice unlikely to work given the nature of self building. It's your first self build so you have a huge amount to learn. I joists are good for carrying bending loads, say a floor. They are generally less appropriate for compression loads, say where you have openings with point loads from above. My advice is to avoid as the detailing and connection design will be horrendous / costly and unlikely to be "self" buildable. Take the hit on thermal bridging and consider standard solid studs or something like a space frame. @Kelvin has done a cracking job using a space frame and has lots of practical knowledge on how you make it work and the pitfalls.. to avoid.
- 26 replies
-
- timberframe
- i-beam
-
(and 2 more)
Tagged with:
-
Beam helper on stair stringer
Gus Potter replied to MortarThePoint's topic in General Construction Issues
Ah now I see! Have to say.. you're quick with the representations and thinking on your feet.. do you want a job? The more screws / nails you put into the head of the stringer the more likely it is to split... leave it alone. We have all sorts of rules for timber fixings, edge and end distances, the load direction and how the load is orientated to the direction of the grain. What you propose is messy. Can you.. Using a structural glue and screws (provides clamping for the glue and a bit of redindancy in case the glue is duff) to thicken the stringers on the inside with MARINE PLY not OSB. The grain of the outer ply should run horizontally. Say stringer is 33mm thick + 18 marine ply = 51mm. Make the ply cover a good area of the stringer, may past the next tread down. Bolt a 70 x 50 x 6.0 thk steel angle to the vertical leg of the angle that sits inside the bottom flange of the UB. Suggest 2 no M10 8.8 bolts though the short leg into the angle section you show. The 75mm leg runs parallel to the stringer. Drill the 75mm leg of the angle and fix that through the ply and into the stringer using short M8 x 40 long coach hex head screws. My first guess is that you need 4 coach screws per angle as the stringer length is pretty short I seem to remember from your previous posts. The long leg keeps the fixings away from the end of the stringer. The ply prevents spliting of the stringer end. Below is a screenshot of the edge and end distances you need to comply with based on BS 5268 part 2 2002. Note the load direction.. you have clocked that earlier when you recognised that some of the fixings may not be doing much. If in doubt always assume the worst load direction. d = the diameter of the bolt. Some bits from the table are key.. edge distance.. the top coach bolt needs an edge distance of 4d so it doesn't split the top of the stringer off. The bottom fixing is pushing into the grain (meat of the stringer) so only needs 1.5d. You want to keep the coach screws 7d from the end of the stringer (as the grain is at an angle to the load direction) to be conservative. 7 * 8.0 mm dia = 56mm. For steel with a drilled hole the edge distance is 1.4d = 1.4 * 8 = 11.2 mm... say 12.0mm 12mm + 56 = 68 < the 75mm leg of the angle.. and there you have a compliant connection even once you take into account fabrication tolerances. If push comes to shove we can use more detailed calcs to refine the connection design.. keep it simple and avoid. I mentioned 4 screws. They need to be 4d apart vertically = 4*8 = 32 mm. If you draw that out you may have room for more fixings in the vertical plane if need be so. For all. The above table is a handy reference if your learning about TF construction. -
Beam helper on stair stringer
Gus Potter replied to MortarThePoint's topic in General Construction Issues
Hiya.. The glue thing is ringing alarm bells here! I'm not saying it can't be done.. just before you do something like this you need to really understand how the materials are behaving. Also imagine you came back to me and said.. Gus can you prove that is ok by calculation? Now that would cost you a lot and it may not be possible without physical testing. Try and seek out an alternative if you can.. do one of your great 3D models as can't quite picture what you intend at your end. Simpson et al have a huge range of bracketry so keep looking and you may find one that fits the bill.. with some load data tables. -
Good for you. There is lots to learn, but if your approach it in the right way it can be great fun, personally and financially rewarding. Have you had a look at your permittted development rights? You probably have but that is a good starting point. Even if you don't comply they help you identify where you don't and that leads you to the next step as to what you need to do to remain compliant with the regulations. Where are you in the UK as PD rights differ.
-
Combining EWI and Cavity wall construction on a New build
Gus Potter replied to Iceverge's topic in Brick & Block
Spot on. The truss I show needs some adaptation to make it cost effective for the light loads and thin heavily insulated walls that you encounter in a domestic job but with a fair wind an a bit of lateral thinking / understanding of this type of structural truss it can be the perfect solution on occasion. It's not an unusual concept as we use this from time to time on tall buildings and you see it all the time on motorway foot bridges etc. One of the big costs of these type of trusses lie in the welding cost. No fancy welds that need tested (keeps in the realm of the local fabricator), also don't skimp on the steel section wall thickness at the early design stage as later you could get tripped up when you come to the do the energy performance calculations. Would be interested in hearing what you SE pal has to say and if said has a better idea. -
Well that's a good start! To keep you on the right side of things below are the design loadings from BS 6180 for domestic internal stairs, landings etc. Your on the top line. Often the governing load for the hand rail is the horizontally uniformly distributed load of 0.36 kN/m (~36 kg per metre run of hand rail) and this load usually get transferred to the top of the hand rail. An important point here is that these are unfactored loadings.. thus no factor of safety built in. The other important bit is the deflection of the overall asssembly, from the same code The 25mm deflection is a key requirement. If you want have a test of what you have. Take your hand rail length just say 3.0m and calculate the horizontal force at the top from the hand rail 3.0m x 0.36 kN/m / 2 = 0.54 kN (~54 kg) Get a spring scale ( for weighing fish or something) and apply that load to the top of the uni strut. See how much it deflects by < 25mm Next test for strength using the Eurocode factors of safety. Take the 0.54 kN load and and multipy by load factor of 1.5 = 0.54 x 1.5 = 0.81 kN ~ 80kg Also make an allowance for material defects that may manifest later. Apply a material factor of 1.3 thus 80kg x 1.3 = 104kg ~= 1.02 kN test load. Two things to remember. You are testing the newal post in isolation here and I'm not taking into account the potential bracing effect of the handrail running perpendicular to the newal post down the sloping part of the stair. Some may and rightly say.. it's always stiffer than that once you put things together. I say.. your often right but can you imagine how hard that is to prove? and also you can often shift the problem somewhere else if you shed load from the newal post. On the other hand 104 kg is about 16 stones.. there are plenty folk that are heavier than that.. and if you have a Rugby team partying, a couple of big lads could push the thing close to its design limits. Report back.. check the deflections first in case the strut fails early.
-
Good to see we have both identified how flexible the rod appraoch can be. The zip bolts work in a different way I suspect where they work in tension and the edge of the newal post is compressing against something solid... but few things are that "solid" and often your bog standard stair is far from solid. I made a post a while ago about the forces that you encounter when designing glass ballustrades.. they are significant.
-
Bricks or dense block at this point?
Gus Potter replied to Post and beam's topic in Bricklaying, Blockwork & Mortar
@ETC interesting detail, thanks for providing. -
A 16 dia rod is too bendy. The amount it will flex is related to it's second moment of area Ixx = pi *radius^4 / 4 = 3.142 x 16*16*16*16/4 = 51478mm^4 A 40 x 40 x 5.0mm thick SHS section of has a value of Ixx = 134000mm^4 134000 / 51478 = 2.6 = about 260% stiffer than the rod. A 50 x 50 x 6.3mm thk section 328000 mm^4 328000 / 51478 = 6.3 = about 630% stiffer than the rod. You can see from the above why I mentioned a 50 x 50 section as being something that looks promising. For handrails and the like we need them to not just be strong enough but "feel strong and stiff" to the touch.
-
That's the easiest way!
-
You could do it with the lugs and bolt. I would need to check if 40 x 40 would still work, probably would but not going to say yes without checking. But there is an argument to be made that it is braced both ways by the handrail? .. but then the lower post needs to do more work... technically. The lug welds on the inside will foul the underside of the top flange of the beam. It looks like the beam you have could cope with having a "scuff" taken off the under edge of the top flange locally to let the SHS sit in tight. M10 grade 8.8 bolts should be fine. Mind you I would add a lock nut with a touch of Araldite glue to make sure they don't come lose later. Cut a piece of wood the exact lug spacing you need and take that to the welder. They will use it as the template. I think they will clamp the lugs to the timber and then weld them to the SHS... or something like that. A tip.. the bolts are 10mm nominal diameter. The holes usually 12mm nominal to allow for fabrication tolerances. Squeeze the glue in and around the bolt to fill in the gaps. From memory Hilti do a system like this where you flood the thing with resin so there is no slip.