Everything posted by Conor
I think your being fed conflicting and incorrect info. There are two types of ground bearing raft foundations. The more traditional, a concrete raft is poured directly on top of the excavation (with appropriate compacted material etc), then walls are built on top of that. After that, insulation is then fitted on top of the raft and finally a screed finish. The other type is an insulated raft, where EPS forms are laid and concrete pour also forms the finishes floor (and needs to be appropriately floated) Both can be done in a single pour. The variable will be the total loading from the supporting walls, you may need a thicker ring beam around the edges. In our case, we will have 400mm thick ring beams and a 200mm thick main slab. To do this, we are excavating down to the required depth, putting down 100mm of sub base, compacting. We'll add extra stones to the main floor part, so we only need the 200mm of concrete. We then build 400mm high formwork, lay our services, tanking membrane, mesh and pour concrete. Similar for an insulated raft, but the EPS forms are thinner at the load bearing parts, forming deeper channels for the concrete. Be aware that there are quite low loading limits for EPS. We only found out at the end of the design process that an insulated raft wouldn't work, as no matter how we designed it, we were always outside the safety limits of the EPS, so have gone for a traditional raft. It's working out needing less steel and labour, if a little more concrete. On balance, faster and cheaper. Make sure your engineer knows enough to get their job done, ours didn't!!
Package Quote vs Constituent Parts
Conor replied to Tony K's topic in Mechanical Ventilation with Heat Recovery (MVHR)
No need to think of it as one system at all. Especially the MVHR... It has nothing to do with heating and its sole job is to maintain good indoor air quality (whilst recovering some of the heat energy). So you can go to one of the many online companies that will do a design and supply you with all the components, BPC for example. You can then chose whether to fit it yourself. A lot of systems now just use semi rigid ducts that go back to a central manifold. Would just be a matter of pulling ducts through the house, hardly highly skilled. The units themselves are almost out of the box, screw to the wall, connect up and go. You'll just need somebody to wire it up, and you'll also have to commission it properly. Plenty here have done it and will give you loads of advice. Expect to pay anywhere from £2k for a supplied system for that size of house. Double that to £4k for supply and fit. Same goes for UFH... It's just pipes under the floor. Wunda will design your layout and sell you a kit. You can then install all the pipework yourself and have it terminate at the plant area. Let's say £1k for supply only. Then your left with the ASHP and cylinders etc... At this point it might be worth getting a plumber in to supply and fit. Fyi monoblock units are much simpler and cheaper than split, if a little less efficient. So, lets say £5k for 5kw ASHP and pipework connection to buffer tank and controls. Buffer tank, cylinder, controls, room stats etc, all traditional plumbing and you could get that all done for £3k or so. Maybe £5k if there are lots of pumps, manifolds etc required. But shouldn't be on a 100m2 house. I'd question the need for a buffer tank, but I'll defer to the likes of @Nickfromwales The supply and fit prices for all these new things are sky high as it falls under that new/different/eco category which means companies can charge a fortune. I've heard of people paying £15k for an ASHP... That's about £7k materials and £8k labour for a couple days of work. At a guess, if you did things seperately, and even paying for partial installations, no reason why you couldn't get that all done for about £10k-£15k. Edit: I've just spotted the post above and I swear I wasn't copying John! -
Where to put the electricity meter
Conor replied to MortarThePoint's topic in Consumer Units, RCDs, MCBOs
I had many discussions about this. It's normally front elevation, or on side within 2m of the front. Cannot be on a return wall or separate kiosk. Internal consumer unit must be within 2m of the meter. For me, building with ICF, this is a pain in the balls as I'll have to use an ugly surface mounted box, or hack away at my insulation. I might just chance it with the kiosk I built when they come round to make the temporary installation permenant... -
Ok, from my point of view from the water industry. We'd always avoid doing this. And you'd never have the water pipe in the same bedding material as the sewer, especially below. The scenario is that a leak in the waste system could enter the water pipe if it were at the same level or lower and in the same bedding material as the waste pipe. (This scenario can easily happen if you have a leaking pipe and low pressure or no water event, when the hydrostatic pressure in the ground is greater than in the pipe) This has happened in public water supplies and lead to serious health incidents. You will need to bury your water pipe at about 900mm deep. See what the invert requirements are for your waste and take it from there. If the water pipe is more than 400mm (100mm bedding for each service separated with clay) deeper than than the required depth for the water pipe, you'll be fine.
Consensus is that in the north of the UK you can complete a modest house for £1k/m² (if you get your hands dirty) or less. We're in NI and are aiming for £1k for finished areas and £500 for basement as it will be a shell only, so £850/m² overall for 300m² = £255k. And not a penny more lol. Bear in mind there are economies of scale.... A 200m² two story house will cost 50% more than a single story 100m² house (before furnishing etc) rather than double. (I could be totally wrong)
We're building a full footprint basement as part of our project. We looked at various scenarios (split level, partial basement, no basement but bigger footprint) and the full basement came out best value for money. I think I calculated it as an extra £400/m² compared to standard ground floor build, but we get an extra 100m² of space. - we have a limited footprint to work with, in order to get a 4 bed house, we either need a bedroom on ground floor or in a basement. - we are on a sloping site, so have to deal with a 1.5m fall from front to back of house regardless. - rear aspect of basement will be at ground level - we will have a utility/laundry room, plant area, cold storage room, plus a large "store" that could be used as a gym/play room/study etc in future- no money for that now but have included an escape window at least. -hope fully having a dumbwaiter (3£k) from 1st floor to laundry room. Otherwise navigating two flights of stairs with laundry baskets would be unnaceptable for my partner (mobility issues) - costs have come back and raw construction cost is about £10k more than building the same 100m² at ground level - about £6k of that is tanking and £4k ground works. It's a standard concrete raft with ICF walls- exactly that same as if it were at ground level. -expect to be another £5k of additional costs in form of extra retaining walls and drainage/landscaping costs. We will be able to have a (sparce) completed basement at passive standard for less than £1k/m² -Our heat pump will be approx 10m from the plant Room.... As long as the pipework is internal, right diameter and insulated, it doesn't matter really. -mvhr is having to go in a hallway as needs to be on an external aspect wall. -to save money and embrace the basement feel... We aren't having suspended ceilings, walls will be painted block, (ICF walls will be lined with ply) electric fittings will be surface mounted, floor will be poured resin or vinyl. No skirtings etc.
Smoke problem from neighbours
Conor replied to Savage87's topic in Mechanical Ventilation with Heat Recovery (MVHR)
Run it in extract only mode* *I'm really, really, not an expert I'm just repeating what my MVHR designer neighbour told me once. In theory it shouldn't work very well, but it does, apparently. -
Normally you start the ICF one course below DPC level on top of your footings. You'd then use water proofer in your concrete for the below ground block and first course of ICF. This acts as your dpc. If your Brockie has no experience of using ICF, you're probably much better teaching yourself online and doing that part of the work. It's not at all like block laying.
You'll need an engineer (+drawings) plus building control approval before you start. When we did similar in our last house, we had an interred "T" beam put in along where the supporting was was, and new joists spliced in where required. Ceiling was then reboarded. The inverted T beam allowed the beam to be inserted without having to remove existing joists. Builder just had to cut a notch though the joists and slot in the new beam.
50mm of EPS will be about 0.5 and 150mm PIR will be 0.12. huge difference. Our "garage" will be made with ICF and I'll put in 100mm EPS under the slab... Its more for keeping a stable temperature all year round rather than aiming to have it as a heated space.
Modern Agricultural Barn conversion. Anybody done one?
Conor replied to Roger440's topic in Barn Conversions
100% agree. Nightmare. When we propose pipeline routes, we always assume land within 10m of a petrol station, workshop or similar is contaminated, and we make sure the pipeline goes on the opposite side of the road. It's just not worth the risk. -
So, here's my story. We originally wanted an insulated raft for our build (2.5 story ICF build Inc 100m² basement). Loads of promises etc from the sales people. When the SE started her calcs, it turned out we'd need massive ring beams (1200mm and 1700mm wide and 400mm deep in places) as well as loads of steel. It was all because of the limits of the EPS300. The option of making the entire raft with eps300 was silly money, £11k I think. If you are doing a concrete build (ICF or block, with concrete floors) over 1.5 stories you might find that a traditional raft will work out simpler and cheaper. Our design now is a simple 200mm thick raft (250mm at edges) with only one layer of mesh, so much faster and cheaper to build. We'll then have 150mm insulation and 100mm screed. Don't get me wrong, an insulated raft is a great idea, just be aware of the limits of loading onto EPS. Be wary of the insulation form people saying it's a simple matter of a xxxmm thick raft and a bit of steel...
Plywood is definitely the most rigid. I use structural softwood ply all the time for little bits of furniture. Door panels will be a lot more rigid and light if you use ply sheets bounded by a thicker pine frame. But that's a whole load more effort.
We have similar in water industry - different locks and systems within compounds. It's to stop people getting to areas they shouldn't, E.g. you might have somebody authorised to access a site to deliver materials or check equipment at ground level... But not access heights or confined spaces. This is why you have another level of access protection in place, you can't trust your employees or contractors to be sensible. And this comes from somebody who likes to climb to top of water towers lol. To @eandg you don't specifically need to use security fencing, our site is bounded by a thick hedge on three sides and river on fourth, the broker was happy enough for this to constitute site integrity. Basically you need enough for somebody wandering off and walking on to your site. Block off any holes in hedges or fences with panels, and the main access point any that will be more than enough. I only needed three panels at £22 each and three feet blocks. All delivered for less than £100 so pretty small change in the grand scheme of things. Already have a plan for the panels after the build as growing supports in my veg garden.
Planning requirement for 1.8M panelled fence?
Conor replied to Topic63's topic in Introduce Yourself
Well, if that's a shared access up to the point where it meets your neighbours driveway, then yes, it is a highway, and the fence is adjacent to it, meaning planning would be required. I don't think the fact that it is private matters in this context (not in my experience, bit regions vary). I had similar query at my old house, I got clarification on whether the alleyway to our rear was a highway. They decided no, as there was no vehicular ROW established along it. In my experience, if nobody complains, it'll be grand... -
Agreed. @Jeremy Harris was actively cooling his house the other day (Wiltshire?) and we had our heating on (Belfast). But from those U values, space heating demands will be absolutely minimal. Hot water will be a bigger energy demand. I might wing it with off peak immersion heating of water and just have UFH loops for a future ASHP if it's ever required. I'll also get a gas connection put in (usually free here as long as have an appliance e.g. hob, tumble drier etc) to make resale easier.
Of course. The air coming in would still be laden with moisture, especially where we are in the coast. You're right, one of those water to air copper coil things in a duct would be an easier and more effective solution. There will be a utility room adjacent so getting a condensate drain sorted will be easy.
That would be perfect, I'd be happy with 10c in summer. I'd be installing a single room MVHR to mitigate condensation in the summer. The MVHR would also do the cooling duties in winter. Though I'd need think a bit more about that.
Thanks to insights like this, we're moving away from the traditional over head bris soleil design to something that will provide low sun shading if required. Currently thinking a retractable sail design, anchored from roof above main window to lower level on the outshoot to the SE. Back to topic: roughly how cool could you get a 100mm screed slab down to in a small (4x4m), highly insulated room with a standard UFH loop and ASHP? Is it just like calculating heating load etc but you just invert the temperatures?
We're going to do something similar in our basement in the NE corner. Full insulated with 150mm PIR and a sealed door. Only need to keep it around 10-12c. In winter time that will be achieved with ventilation, like a traditional draft larder. In summer, I'm hoping we can use the UFH (maybe even loops in the walls?) on cooling mode once every few days or so to keep the temp in that range. I might put in a provision for piping for a single Aircon unit like @Jeremy Harris did for his bedroom, Just in case slab and wall cooling isn't enough, but I doubt that will be needed as we won't need it cool enough for meat or dairy.
Manifold system versus hot return system
Conor replied to Russell griffiths's topic in General Plumbing
Yes. You will need to know: Desired flow rate at the outlet. Diameter of pipework - make sure you use internal bore. Length of pipework. Chose your metric. In water networks, we use litres per second. In your case, litres per minute are a better starting poimt. Then enter your data here: http://www.calculatoredge.com/mech/pipeline velocity.htm Then think back to school and calculate the time it'll take over your given length. You'll find that halving the pipe diameter will result in the time reducing by a factor of alomost 4. -
Temporary accommodation on site - when access is tricky
Conor replied to Tom's topic in General Self Build & DIY Discussion
@Tom is upgrading access at this stage an option? E.g widening where possible, drainage works, levelling off. By the sounds of it you're going to have to improve access for construction anyway - concrete and stone deliveries etc. Will make life easier all round by throwing a few grand on a few dozen loads of stone and widening works. -
Loved Fred! Such passion for all things suity, rusty and steamy. That was chimney no.3 to come down. The best thing is the bricks are coming down pretty much undamaged and separated as the old lime mortar is so weak. Almost clean enough to stick straight on a pallet and sell.
Unexpected consequence of Corona Virus - you need your 8.5 month pregnant partner to help you pull the house down as all the hire places are closed and you need a long chain and a VW golf in lieu of a telehandler... VID-20200328-WA0006.mp4
- 13 replies
- 11