  1. I doubt the difference in density or mass/m2 makes much difference acoustically. I thought duraline was just more robust for heavily trafficked areas
  2. Flow restrictors? Under Approved Document G to reduce water use - been part of the Building Reg for may years. Depending upon the type of tap it may be possible to remove the restrictor - otherwise its new tap time.
  3. Mineral wool slabs are treated with a water proofing agent. They have to pass a very extreme BBA test to prove they work, do not allow moisture to pass and get certification. They can normally be used below dpc
  4. This is down to brick and/or block type. Manufacturers will advise, 10m(?) for brick, perhaps only 6m for block (and render?).
  5. Do not use a hybrid flat roof unless insulation between joists is minimal (which becomes almost a waste of time & effort). Old rule of thumb, if you had to go hybrid, was at least 2/3 of thermal resistance above the deck/joists. Not sure with current insulation standards if this still applies. Also requires an highly efficient AVCL at ceiling level which is very difficult/impossible to achieve. BS6229 on flat roofs and BS 5250 on condensation and moisture in buildings both advise against use of hybrid flat roofs. Problems can take many years to become obvious as all well hidden within roof structure.
  6. Lintel, concrete or other, will not affect the U value. It will affect the psi value (linear thermal bridge) which is used to assess the heat loss from this, and other, junction.
  7. There is nothing in the latest Regs on thermal performance that prevents the use of standard catnic type lintels.
  8. IIRC phenolic foam should not be used under timber (ply/chipboard) flooring. Floor would need battening throughout to take it out of load bearing path.
  9. Latest Approved Doc L has U=0.18W/m2K in extension wall. Looking at approx 150mm of mineral wool or 100mm PUR
  10. Might be better spending your money on lower conductivity insulation, 0.032 W/mK. Look for ‘32’ in the product name/reference. Also check that your wall tie with its small cross-section is suitable for 250mm cavity, you may have to look at a heavy duty tie with larger area. Teplo tie may offer little benefit bearing in mind the cost.
  11. Adding insulation under a beam & block floor changes it from a suspended floor to a ‘solid’ floor. This is OK provided there is a correctly detailed DPM under the insulation - possible in a new build but impossible in a refurb or upgrade. The Energystore system is approved for new build only, not upgrade work. As above, an expensive solution looking for a problem.
  12. Why not 175mm mineral wool batt at 0.032 W/mK? Will give U=0.15 W/m2K with aircrete block inner.
  13. Appr Doc L limits the glazed area of an extension, go slightly over and you will have to use high performance glazing/improved fabric insulation and use the area weighted average u-value method to show compliance. Go a lot over and you’ll be using full SAP calculations to show compliance. This may give an idea of overheating but SAP is not a very sophisticated tool in this respect
  14. Full SAP output is used to show Building Reg compliance and create the EPC for new build dwellings. Full SAP calc is also needed for new dwellings created by conversion but normally only to issue the EPC (sometimes needed for Building Reg compliance too). EPC is needed as part of BC sign-off.
  15. Under the 2021 version of Approved Doc L intermediate floors with heated floor systems require thermal insulation (as well as acoustic requirement).
  16. May be yellow glass wool. Waste product was ground to make fibres that were injected into cavity walls and blown into lofts. Can you see individual fibres?
  17. Don’t do it!! Frowned upon by BS6229 & BS5250 and doubt insulation manufacturer would support it without lots of caveats. On your head be it.
  18. I greatly doubt that you would get a UK based insulation manufacturer or waterproofing system manufacturer to promote a hybrid flat roof, not without many caveats! They are specifically warned against in BS 5250 and BS 6229. The Scot Regs push true warm roof detail (and avoid cold deck).
  19. Window supplier need to provide test data to confirm window performance. Calculated U-values can be used but these must be done by a BFRC certified window thermal modeller.
  20. Because it’s an input into the SAP assessment.
  21. Sorry no - been a few years since I worked in that sector. From memory BS EN 13165 on PUR manufacture gives info on gas tight and non-gas tight facings and their effect on thermal performance. Gas transfer into/out of the foam matrix at the edges has little impact on aged lambda.
  22. Most of the blowing agent loss, hence loss in thermal performance, is through the top and bottom faces and is accounted for in the declared lambda value. The foil facings slow this process hence foil faced PUR has a lower lambda than product with glass tissue or bituminous facings. Edge losses are minimal. The foil-facing is a complex laminate of al foil, kraft paper and polyethylene and is adhered to the uncured, liquid foam in the manufacturing process. Adding a self adhesive foil tape to the edges would not be gas tight and would make no difference.
  23. No. Waste of time and tape
  24. 50mm mineral wool slab in brick/brick cavity wall is woefully inadequate. Would expect at least 100mm, probably 150mm under 2021 version of Appr Doc L. As above, timber frame can be insulated in cavity but 50mm clear cavity must be left assuming masonry outer.
  25. 0.16 W/m2K is the worst acceptable for roofs under the 2021 Appr Doc L1 so 0.16/0.15 are both 'OK'. Probably will not help get compliance though if they are that high as the 'notional' house uses 0.11 W/m2K. Would need offsetting by more insulation in other elements.
×
×