flanagaj Posted 18 hours ago Posted 18 hours ago The SE we used for designing our cut roof specified C24 47mm x 225mm for a 5.9m span for a flat garage roof. The timber which arrived was rather crap, not straight and twisted. Whilst doing some googling, I looked at span tables and all of them are saying that even at 400 centres the maximum span is ~ 5m. I have tried contacting said SE a few times and she is on radio silence. I am getting concerned now. How do I double check that she is a registered SE as she has made a number of mistakes now.
Roger440 Posted 18 hours ago Posted 18 hours ago Im no SE, but 6m sounds a rather long span for 225mm. 2
Oz07 Posted 17 hours ago Posted 17 hours ago Yeh I'd probably pause before putting these on. I have a similar issue with 6m garage flat roof. When I eventually found a span table I think it ended up being something like 70x250 or 225 c24 at 450 centres for 6m garage roof span. I'd want to speak to said SE and query it.
JohnMo Posted 17 hours ago Posted 17 hours ago 1 hour ago, flanagaj said: The SE we used for designing our cut roof specified C24 47mm x 225mm for a 5.9m span Maybe use posi joists - ours are 256mm our kitchen span is about 7m (12 Deg angle) and at 600mm centres 1
-rick- Posted 17 hours ago Posted 17 hours ago 1 hour ago, flanagaj said: The SE we used for designing our cut roof specified C24 47mm x 225mm for a 5.9m span for a flat garage roof. The timber which arrived was rather crap, not straight and twisted. Whilst doing some googling, I looked at span tables and all of them are saying that even at 400 centres the maximum span is ~ 5m. I have tried contacting said SE a few times and she is on radio silence. I am getting concerned now. How do I double check that she is a registered SE as she has made a number of mistakes now. Before engaging her you asked for a copy of her credentials and insurance right? What does she claim to be on her communications/advertising? If she claims to be a Chartered Structural Engineer then this is the professional body that you can check with: https://www.istructe.org/
flanagaj Posted 17 hours ago Author Posted 17 hours ago 14 minutes ago, Oz07 said: Yeh I'd probably pause before putting these on. I have a similar issue with 6m garage flat roof. When I eventually found a span table I think it ended up being something like 70x250 or 225 c24 at 450 centres for 6m garage roof span. I'd want to speak to said SE and query it. I'm concerned. Said SE hasn't replied to my emails. Not even the one regarding her issuing the invoice. She was originally tasked with designing a suspended staircase, but after two months of continually asking, I eventually stopped. The cut roof / garage was another job I asked her to do. Her site states she's a civil engineer, but I am thinking I need to validate that is the case. I've just reached out to a local firm for i-joists as I think these are cheaper and I don't need to run lots of ducting.
flanagaj Posted 17 hours ago Author Posted 17 hours ago 3 minutes ago, -rick- said: Before engaging her you asked for a copy of her credentials and insurance right? What does she claim to be on her communications/advertising? If she claims to be a Chartered Structural Engineer then this is the professional body that you can check with: https://www.istructe.org/ No I did not. Agreed. Naive and stupid.
-rick- Posted 17 hours ago Posted 17 hours ago 2 minutes ago, flanagaj said: Her site states she's a civil engineer, but I am thinking I need to validate that is the case. In that case the reg body is: https://www.ice.org.uk/ This is all very clearly stated on the government website. All I'm doing is googling it for you. All these orgs will likely do is be able to confirm that this person is qualified/has active registration. You really need to check the insurance of the professionals use because if something goes wrong that's what you will be relying on. Mortgage companies, buyers will care about the qualifications.
flanagaj Posted 17 hours ago Author Posted 17 hours ago 3 minutes ago, -rick- said: In that case the reg body is: https://www.ice.org.uk/ This is all very clearly stated on the government website. All I'm doing is googling it for you. All these orgs will likely do is be able to confirm that this person is qualified/has active registration. You really need to check the insurance of the professionals use because if something goes wrong that's what you will be relying on. Mortgage companies, buyers will care about the qualifications. Thanks. I've been very stupid here. I've just gone over the T&C's and there is no mention of her active registration. But I'm assuming that just like an individual cannot call themselves a Solicitor or Architect unless there are registered with the associated body. The same applies for an SE.
-rick- Posted 17 hours ago Posted 17 hours ago 2 minutes ago, flanagaj said: Thanks. I've been very stupid here. I've just gone over the T&C's and there is no mention of her active registration. But I'm assuming that just like an individual cannot call themselves a Solicitor or Architect unless there are registered with the associated body. The same applies for an SE. I'm at the end of my knowledge. Hopefully one of the professionals on here will speak up with more details. Everything I've put above can help you verify Chartered engineers but don't think you need to be chartered to practice so long as qualified and that might be an area that's a little harder to check. 1
ETC Posted 16 hours ago Posted 16 hours ago https://www.buildingcontrol-ni.com/assets/pdf/TechnicalBookletD2012.pdf
Mr Punter Posted 16 hours ago Posted 16 hours ago I doubt you will find longer than 6.0m. Can you break the span with a steel or flitch beam? 1
Gus Potter Posted 15 hours ago Posted 15 hours ago 2 hours ago, flanagaj said: The SE we used for designing our cut roof specified C24 47mm x 225mm for a 5.9m span for a flat garage roof. The timber which arrived was rather crap, not straight and twisted. Whilst doing some googling, I looked at span tables and all of them are saying that even at 400 centres the maximum span is ~ 5m. I have tried contacting said SE a few times and she is on radio silence. I am getting concerned now. How do I double check that she is a registered SE as she has made a number of mistakes now. 42 minutes ago, -rick- said: I'm at the end of my knowledge. Hopefully one of the professionals on here will speak up with more details. Everything I've put above can help you verify Chartered engineers but don't think you need to be chartered to practice so long as qualified and that might be an area that's a little harder to check. 1 hour ago, Roger440 said: Im no SE, but 6m sounds a rather long span for 225mm. Hope this helps lift your spirits a bit. The following is a bit of "chat", but also serious at times. Firstly. Well done you for looking up some span tables, what you are doing is carrying out a "sense check", you've clocked that the joist span looks out with normal expectation. I agree you are right to question. Also @Roger440, no dafty is asking.. and I'm pretty sure @saveasteading, @JpManning et al may bring professional opinion to the table. The thing that disappoints me most is this radio silence you are experiencing. There is generally no excuse for this. This is a common complaint on BH, Engineers not communicating or just being downright arrogant. But on the other hand your Engineer may have fallen unwell, this happens more often than you think. I have a long standing Contractor on my books who is mentally unwell, I'm supporting him. His business is suffering, he is a sole company director and employs folk that rely on him for their income. It may be your Engineer is unwell? That said SE's in particular seem to be very poor when communicating with Clients. It's actually a core objective of the IStructE, ICE to communicate with your Clients. I would try and determine if this lack of communication is due to say ill health. You'll maybe feel bad if you give them pelters and then find out they are on their death bed. Ok your joist span looks.. questionable. But your Engineer may have taken the view that it's a garage thus, no brittle finishes on the inside, thus we can tolerate extra deflection, so long as the deflections are not too big we can handle that. If deflections get too big then they can introduce what we call significant second order effects. Us folk with knowledge of structural design get wary about second order effects when we relax standard deflection limits. What your Engineer may have done is to just to design the timbers for strength alone, relaxed the deflection limits, as it's a garage. But if I adopt this approach I'll always tell the Client I've done, why I've done it, get their approval and check to see if these second order effects are significant or not. Now if you have a flat roof on a garage and you can push the spans. Yes, the timbers may be strong enough (just to not break and fall down) , but if they deflect in the middle too much then we have to be very careful the fall is still enough so we don't get ponding of water or snow melt on the roof as this can be dangerous. I would try as best you can to establish communication with your Engineer. Then you can ask what they were thinking was when they designed your garage roof. The may say, I relaxed the deflexion limits to save you money, but neglected to seek your approval for this. 1
saveasteading Posted 3 hours ago Posted 3 hours ago 13 hours ago, flanagaj said: The same applies for an SE. Even more so. What do they call themselves? Change the name of course. Be precise with capitalisation. Then we can advise better without assumptions. Eg J. Bloggs, Structural Engineer and Building Technician, BSc MIStructE. It is a question their insurer must have asked. 1
ToughButterCup Posted 2 hours ago Posted 2 hours ago You might consider asking for evidence of her Professional Indemnity Insurance...... maybe things have got past that stage - just a thought 1
flanagaj Posted 2 hours ago Author Posted 2 hours ago I have asked the SE for her PI insurance and have finally managed to get her to answer the phone and agree to a site visit. Builders are not happy with the arrangement of the separated internal (C section) and external (Non equal angle) lintel specification. The two sections are not jointed together (yes, it mitigates cold bridging), but builders have told me that when they recently did the same thing on another job, the brickwork above the lintel all cracked. Having been outside to look, it's quite easy to see how the external L lintel just wants to topple backwards into the cavity.
Mr Punter Posted 1 hour ago Posted 1 hour ago 58 minutes ago, flanagaj said: Having been outside to look, it's quite easy to see how the external L lintel just wants to topple backwards into the cavity. I have seen these where they are bolted together on site. One of the lintels has some tube / chs welded and the 2 are bolted together. Needs SE design. If the cavity is 150mm or less you can use the HiTherm lintels. Expensive and long lead time on some, but good psi / thermal bridging characteristics.
flanagaj Posted 10 minutes ago Author Posted 10 minutes ago 1 hour ago, Mr Punter said: I have seen these where they are bolted together on site. One of the lintels has some tube / chs welded and the 2 are bolted together. Needs SE design. If the cavity is 150mm or less you can use the HiTherm lintels. Expensive and long lead time on some, but good psi / thermal bridging characteristics. We have used the HiTherm type lintels on the < 2.7m spans, but for the 4.8m / 5.7m openings we had to conventional steels. Hoping the SE can come up with a solution and I can try and get a metal fabricator to site to perform the required welding.
Temp Posted just now Posted just now A steel midspan might allow the existing timber you have purchased to be used.