Ecodan standby power consumption

Featured Replies

  • Author
55 minutes ago, joth said:

Fascinating.

Do you have freeze-stat disabled?

What is the outdoor temperature when it's drawing it?

 

I will put a dedicated CT on mine just to confirm...

Freeze stat is disabled. It pulls 200w as standard 24/7 which the rep at Mitsubishi didn't seem to think of as an issue, even when I pointed out that at £0.3/kwH I'm looking at throwing a good £400 away after discounting hours where it is actually used.

 

Apparently keeping the oil warm is all part of the 'protect the compressor' ethos. I assume that it easier for them to configure the system so it does that 24/7 rather than design something which turns itself on/off with the weather conditions and the scheduled use set by the homeowner.

 

Strange that this hasn't been discussed on here before but it seems that more and more threads are being identified where this problem is discussed - appears to be a widespread yet little know and poorly understood issue.

  • Replies 274
  • Views 62.3k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • SteamyTea
    SteamyTea

    To my mind, reducing parasitic loads is vital for reducing energy usage.  Why I worked so hard on doing it.

  • A circulating pump running all the time could use 200W, and that should be obvious by the small noise it makes.

  • This background / compressor heating load is certainly something I was not aware of and a question you should all now ask of the manufacturer before deciding which ASHP to use.  A 200W background load

Posted Images

2 minutes ago, LA3222 said:

Strange that this hasn't been discussed on here before but it seems that more and more threads are being identified where this problem is discussed - appears to be a widespread yet little know and poorly understood issue.

Going to be discussed more now that

 

2 minutes ago, LA3222 said:

£0.3/kwH

Except it is kWh FFS.

  • Author
8 minutes ago, SteamyTea said:

Going to be discussed more now that

 

Except it is kWh FFS.

Ha. The SI unit police has got me - I try to be careful because I know you are on the prowl waiting to slap a ticket on offenders, this one slipped through👀

14 minutes ago, LA3222 said:

It pulls 200w as standard 24/7

That's 200W.

And I guess 24/7 is unitless 😂

  • Author
1 minute ago, joth said:

That's 200W.

And I guess 24/7 is unitless 😂

Damn. Two in one day....I'm off to go work on the bathroom😅

23 minutes ago, LA3222 said:

SI unit police

It is a derived unit, from the SI units for kilograms, metres and seconds.

Do we know whether the consumption occurs only in standby or whether it's a continuous load even when the compressor is working.

 

If it's the former then potentially it's not so serious provided the system is heating or turned fully off most of the time.  I'm not trying to excuse the waste, just trying to understand how big it actually is.

20 minutes ago, JamesPa said:

If it's the former then potentially it's not so serious provided the system is heating or turned fully off most of the time. 

Yes but to turn it fully off means turning the power off, and there was mention of 2 hours warm up time required?  So not an easy "solution"

 

Until told otherwise, look for an ASHP with a scroll compressor which don't seem to need this heater?

Is this 200W real? I mean like a resistive load with a power factor of one? A crankcase heater would be but a compressor might not. My fridge and freezers  have a PF of around 0.5 so they show up on simple current clamp meters as drawing twice as much power as they are billed for.

You're correct in thinking that this doesn't show up on the official sCOP figures.

 

If true the your standby loss / their warranty saving. 

 

Mitsubishi also advise really terrible heating circuit designs (mixing headers) to avoid callbacks due to insufficient flowrate on the space heating circuit. Again your COP loss / their tech support saving.

 

Air conditioning manufacturer with a bodhe product and an amoral UK sales outfit?

 

26 minutes ago, Radian said:

Is this 200W real

Hopefully we will find out with a bit more investigation.

How low could a compressor motor go in the power factor. 0.5 is appealing.

11 minutes ago, SteamyTea said:
39 minutes ago, Radian said:

 

Hopefully we will find out with a bit more investigation.

How low could a compressor motor go in the power factor. 0.5 is appealing.

but it's not being "motored", it's a resistive heater at that point...

3 minutes ago, dpmiller said:

but it's not being "motored", it's a resistive heater at that point...

Not totally sure, it may act as an inductor, with thermal energy being a by product. @Radian would know more. 

18 minutes ago, SteamyTea said:

Not totally sure, it may act as an inductor, with thermal energy being a by product. @Radian would know more. 

Very much doubt that, not at 50Hz anyway. But there was some talk of the motor windings being used to double-up as heaters? So maybe some higher-frequency PWM applied to the compressor motor which would almost certainly have a lower PF.

 

The utility companies meter would only register real power so if that was used to establish the vampire load that would clinch it. Alternatively many of the smart sockets with power monitoring can be made to expose VA and VAR if they are reflashed with Tasmota. That's how I got the insights into my fridge freezer power use (all three plugged into same smart socket):

 

image.thumb.jpeg.aa589664d015ccd1446cd70dc5f432fc.jpeg

 

Edited by Radian

Just now, Radian said:

Alternatively many of the smart sockets with power monitoring can be made to expose VA and VAR if they are reflashed with Tasmota

All the best plugging a 32A heat pump into a tuya wall socket 😅

My Eco Dan uses 300w constant until I turned it off at the wall! 😁👍
 

 

80BE8FCF-6C2E-4A54-8137-EE64708F0ED3.png

AEC76D7D-DE93-4B81-8851-C6570FA48C42.png

I probably only need it on in BST 3 hours a day to top up the Hot Water. I’m going to create a workaround with a 4 ch relay that schedules the heat pump to come on 4 hours during mid day and 1 hour of that use the external boiler function to block the HW and Heating inputs that way its warming the oil before kicking in. 
shame I have to create a work around think this function would be built into the FTC Eco mode but I found that the Eco mode doesn’t do anything or make any changes to how the system functions .

5 hours ago, JamesPa said:

...And another here https://forums.moneysavingexpert.com/discussion/6298830/dimplex-ashp-running-cost with figures for Daikin, LG and Dimplex all of which seem to have quite high standby consumption if this post is to be believed.  

 

Not exactly. Dimplex and Daikin ASHPs are stated to have a vampire load.  LG's are stated not to have perceptible vampire load (BY ME!).  I happen to know that the Daikin ASHP referred to is about 10 years old so what is stated might not be true for contemporary units.  

7 hours ago, ReedRichards said:

 

Not exactly. Dimplex and Daikin ASHPs are stated to have a vampire load.  LG's are stated not to have perceptible vampire load (BY ME!).  I happen to know that the Daikin ASHP referred to is about 10 years old so what is stated might not be true for contemporary units.  

Apologies for my skim reading!

8 hours ago, Kenway said:

My Eco Dan uses 300w constant until I turned it off at the wall! 😁👍
 

 

80BE8FCF-6C2E-4A54-8137-EE64708F0ED3.png

 

 

 

I don't understand this graph, as it's plotting kWh against time. Is that kWh per hour? Also known as kW (averaged over an hour).

If so, yes that does seem to be 300 W  😮 

 

 

I've just put a dedicated CT clamp on my ecodan and it's happily drawing 3.7W.  And it's been below 5ºC overnight.

 

Something fishy going on here.  I'll leave mine logging add day, and force heat some extra DHW later once PV is going, and see how the power profile looks.

 

 

 

Edited by joth

9 hours ago, Radian said:

Very much doubt that, not at 50Hz anyway

May be a DC voltage as it is an inverter unit.

Just did a back of fag packet thought experiment calculation on the real COP on a 5Kw9_9 (COP 3) unit (worst case) with 300W vampire load load and assuming 6 months of heat and DHW and 6 months just DHW comes out at 2.02! 

^yep DC injection would do it.

 

I've just re-read the TUV report for the CE-iVT9, and it quotes standby at 9W and the crankcase heater at an additional 33W

4 minutes ago, MikeSharp01 said:

5Kw9_9

Fluttering your eyelids won't get you extra marks, did not help Angela Rainer.

 

Did you make any assumption on the time to heat i.e. DHW heating for 5 hours, CH on for 14 hours.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.