All makes sense, but the limited flow rate will naturally cap output ultimately. So ok for now, but may be an issue later when installer has been paid and moved in to other things and may be difficult to re engage.
Daikin Altherma 3M heat pump no longer starts the compressor
JohnMo replied to AL Ken's topic in Air Source Heat Pumps (ASHP)
If it ran before it should run now. 1. Walk system have you left any valves closed? 2. Did you change any settings prior to or during new parts being added. 3. Don't see on any of you screen shots, what the set point is - if you have a thermostat jumper in place, the compressor is waiting for the return temperature to drop low enough to get a start permissive. Depending on the target set-point and system dT this may not ever be achieved. Have you altered the target - what is set too? Increase it does compressor start? -
I would replace as much for copper as you can - multi layer ok for UFH pipes not sure I would allow it elsewhere. Hep2O is bad enough and they have pretty much full bore connectors, the multi layer connectors I have seen all look have reduced bore.
MVHR Enthalpy Exchangers, BS or SB?
JohnMo replied to LnP's topic in Mechanical Ventilation with Heat Recovery (MVHR)
Is this really a real issue, the bypass is on one side of the system and simply provides a bypass around the heat exchanger. The bypass doesn't cross between the flow and return paths. To get smell transfer, 1. Either piping/ducts are mixed up and giving cross over in the system on the house side. Get two sheets of toiler paper, on wet rooms the paper should be sucked up and stay in place, on dry rooms it should be blown away - check every terminal. 2. The outside terminals are allowing exit air, to be reintroduced into the suction stream. Do you have the minimum distance between terminals outside (see manufacturers instructions) or do you have combined inlet outlet terminal? 3. Are the outside and inside MVHR nozzles connected to the right parts of the system - easy to check, left and right hand units easy to mix up, so be careful check manufacturers name plate and instructions. Does the outside terminals suck and blow as you would expect, same for the house side terminals? 3. The heat exchanger in not right, you are on your second one, so unlikely unless a major manufacturing issue, you could ask supplier to fit a normal HE for test purposes? 4. A seal within the MVHR unit is comprised allowing flow and return air to mix. Would require full strip to find out and unless done by supplier your warranty could be void - so do last2. A seal within the MVHR unit is comprised allow flow and return air to mix. Would require full strip to find out and unless done by supplier your warranty could be void - so do last Test as much as possible with unit on and nothing removed - then its not your fault or becomes easy to blame you. -
32mm and 1.25" are the same nominal size, so I assume the writer is actually saying install 32mm copper pipe instead of the multilayer? Thought you were in Europe, so no idea why they refer to imperial sizes, which aren't specified in the UK any more (not for the last few decades anyway) let alone in Europe. Generally sounds a bit of numpty. Quick search "Expanded mode" on a Vaillant heat pump system is a setting that combines weather compensation, room temperature influence, and traditional thermostat on/off switching. It will aggressively heat to meet a target temperature and then switch the heating system completely off once the target is reached, turning it back on when the temperature drops below a certain threshold. So run it like a boiler - not great for running costs and he's one of the experts?
In Scotland you pay by council tax band generally not by m3. There are two rates, one for water and the other for waste water. Water charge is £463.20 and waste water £537.45
Looks like your head losses are pipe related maybe all the elbows used etc. I would put a Wilo 7m head pump in, then you get the ability to dial in the correct settings to get the flow you need and have some flexibility.
Really depends on depth and company. We are 34m depth fully steel pipe lined and was under £5k, the pump and filter package is site dependent our 40L/min pump and filter system was about £3k. So £8k all in. Annual service is about £100 to £150. Water and drainage being off grid saves us £1k in charges to the council.
I had to add an additional pump for DHW due to distance cylinder is away from ASHP and some existing pipe sizes. Just add to anywhere in the circuit, on CH side only not in the DHW part and run at a fixed speed. The original pump will then just modulate as needed, the secondary pump just makes up for the lost or missing head of the original pump. If you install near the 3 port valve you can select the secondary pump on only when DHW is off, either via a relay or if valve has it the secondary contacts.
We are also private water, no-one checked anything. There was nothing on our plans that stated how water was being sourced. There is only so much the inspector will look at, where water is being taken from isn't something likely to even be on the radar.
Self build offgrid strawbale house in Scotland
JohnMo replied to Pord67's topic in Introduce Yourself
Is it worth the hassle building from straw bales? The walls of the building are pretty cheap no matter how you build them especially if you are doing most the work yourself. Why not a more conventional system?- 59 replies
- straw bale
- offgrid
(and 2 more)
Just remember most the sites quoting this stuff, are also selling it, bigger price for item equals more profit. Most claims in the UK are marketing BS, same as MVHR based cooling systems - people still fall it. I like reading technical manuals and understand what I am getting, before parting with my money. If I lived in the centre of Europe I would buy an Enthalpy exchanger every time, but I am located near to the coast in Scotland, so weather changes frequently - we do not gets weeks and months below zero. I also tweaked down flow rates to suit house and number of people in it. -
You will a kicker at the bottom of the slates anyway to stop capillary action drawing water up, plus you don't want the states touching the EPDM either, as over time you will end up with a hole somewhere. So it's never going to be a perfectly flat transition
In Scotland to get a building warrant you need a structural design certificate that covers the whole build (or all the structural calculations and pay to have them reviewed) and an as designed SAP EPC. If you both those boxes ticked how you actually build isn't really that relevant, is my take on the system. So would suspect getting an architect and structural engineer that understands the build system, is the challenge, not the warrant.- 59 replies
- straw bale
- offgrid
(and 2 more)
Most if not all MVHR units have in-built frost protection. If you have no preheater, the system just monitors temperature across the heat exchanger and either stops or modulates down the in coming air to keep unit away from freeze zone. As temp recover the unit increases speed to normal and repeats this until normal inlet temperature resumes. I don't see any ill effects of this down to -9 degs, and have two units operating this way. -
Just read the article - this bit jumps out "A problem can occur in homes which are very large but under-occupied, and for this reason an enthalpy exchanger could be a better solution" A different solution is to set the MVHR flow to an appropriate flow rate to suit house and occupancy levels. -
More like a few hundred plastic straws in matrix. Real advantage of enthalpy units is in prolonged sub zero temperatures where internal air can become increasingly dry. I monitored our air for 2 years with a normal exchanger, the air never gets to the really dry stage and we are in Scotland. So not sure I would bother getting one for the aded cost and benefits in the UK -
How much timber cladding is too much timber cladding?
JohnMo replied to JCL's topic in New House & Self Build Design
101% you have bought too much. But you can always build a shed, so 102%, but you can always build a log shed, so 103%.... No such thing as stupid question, sometimes. -
To add - You need to assess if the steel is connected to the outside world. If it is this method will allow you to insulate the steel. Notching will have everything flush and leave a cold bridge.
Independent battery storage comparison??
JohnMo replied to BotusBuild's topic in General Alternative Energy Issues
And it is?- 29 replies
- battery
- whole house
(and 3 more)
It isn't the cheapest - but for it ticked lots of boxes other system just didn't do when I installed. Main thing is invisible change over in a power cut and the PV string inverters just continuing in a power cut, just as they did with mains available.- 29 replies
- battery
- whole house
(and 3 more)
Do you need them to move or can they be fixed?
Been thinking about how best to do this system I would do 3 zones - one for each manifold, so no actuators are needed on the manifold, retain you pumps and mixers, but control pump on manifold with the zone thermostat - no wiring centres are needed, but install if you have them (if you want). It may be way easier to install a buffer, but size to about 100L. This will keep boiler happy. Nibe (they do heat pumps) have good design buffers, there are a couple on eBay at the moment at decent prices. Buffers can be installed in various ways, I would recommend a 2 port setup. So a 2 port is just that, you use only 2 ports. One at top, one at bottom buffer. Each port has an oversized tee, so if using 22mm pipe do a 28mm tee at each port. This gives a hydraulic separation between heating and boiler. So you operate the two sides independently, the buffer you add a thermostat and the thermostat controls the boiler only. Set to about 15 degs above max UFH flow temp this allow UFH mixer to have some authority. Boiler has one job keep buffer happy. UFH just draws from buffer, but when boiler is on, will draw water direct from the boiler and flow and return will by-pass the buffer, as zones switch off, excess flow from boiler will pass through buffer. For DHW you have a 3 port diverter between buffer and boiler. Boiler flips to DHW, runs flat out to charge cylinder cylinder, buffer continues to feed the UFH. At end of DHW, boiler moves to charge buffer. You don't need zone valves if you don't want them. The other option is a fully open system, no buffer, no mixers and feed whole lot from a good boiler that does weather compensation. You may need to add additional pump to the system return. But you need to be prepared to fully balance system, adding zones will miss with a lot of settings and you would run full WC.
GivEnergy AIO. This is AC coupled and in a power cut just continues as if there hasn't been a power cut up to 6kW continuous and I think 7+kW transient. 13.4kW usable power, so really a 15-16kW when comparing. Use mine with Cosy. Morning slot charge to 100%, afternoon slot have set 3 charge slots to make most of any solar and night slot charge again to 100%. All done via GivEnergy app. You can either set your own slots to charge or it has full integration with Octopus, just add your API and the control does the rest. Charge rate is 6kW which is needed after heavy use for the night slot to charge to 100%. My max cost for electricity is Cosy cheapest slots all year round.- 29 replies
- 2
- battery
- whole house
(and 3 more)
Each method works, but I did perimeter insulation at full depth of insulation and screed, my thoughts were less chance of a thermal bridge due to gaps. I used 70mm PIR which was the maximum use for my wall build-up instead of the normal blue stripes. You could add a thin layer of sand or use thin eps insulation as a sacrificial layer below the DPM.