Everything posted by JohnMo
Lots of questions The basics and that's where you start from. First it's about pressure drop management, a higher pressure drop the fan in the MVHR have to work harder to give a set air flow. Second when you use a plenum and individual pipes to rooms, the strings in parallel, so you will have one single run which sets the pressure drop - it's generally the longest pipe run and the highest flow rate. This is the route you need to concentrate on and get low. Then make sure all other routes do not exceed that pressure drop. Noise comes from two sources A. Fan noise - as mentioned above B. Duct noise from air velocity. This is generally managed by looking after pressure drops. So get your data sheets, look at pressure drops for ducts, bends and terminals. Get data sheet for fan speed/pressure charts for the MVHR. Before you do that you need to understand each terminal flow rates. You can massively reduce duct length by using coanda terminals. These will throw air from one side of the room to the other following the ceiling before coming down.
I would be doing that anyway - panel are £120 per kW plus mounts, so wouldn't you.
Yes - not really that important l on the design stage, but very important at the 'as build' stage, make sure all assumptions are correct as well as everything else.
Interesting couple of days with the new heat pump.
JohnMo replied to MikeSharp01's topic in Air Source Heat Pumps (ASHP)
Think you maybe over thinking stuff. A heat pump cycling is a reasonably normal thing. If it runs for 10 to 15 mins it over comes any startup losses. As long as it's not 5 mins later you have no issues. Quick restarts are down to setting startup dT correctly. Don't get bogged down, thinking it's bad in mild conditions. It isn't. -
I was happy to minimise pipe in floor and designed in loopcad. The insulation values at the time didn't get down to my levels, and even then at -9 had a design flow temp of 35 deg. Actually the highest flow temp I need doing WC is about 32. Just installed a new smaller heat pump, as previous one didn't modulate well at all (it's being reused for hot tub). The last few days the CoP has been (in order they appeared) Average 4.5 day temp CoP 5.11 Average 6.8 day temp CoP 5.68, Average 5.6 day temp CoP 5.8. Still fine tuning WC curve, so performance is improving. Even with 4 poor running days, my weekly SCoP is 4.56. in a weeks time, I expect that to closer to 5+ even with more snow on the way for NE Scotland. Heat striping - pipes are 100mm down and by the time the heat gets to the surface you cannot feel any difference in temperature. It also works acceptably well in cooling.
Either find an installer that will play ball or just cut out the middle man and DIY the install. R290 Haier heat pump 4kW or 6kW from Wolesely are £2100 and £2300 including vat. Do a direct cylinder for DHW heat via immersion on cheap rate and a simple time switch. About £500. Connect ASHP directly to UFH and run WC. Two pipes, strainer on return (supplied with ASHP), couple flex hoses and isolation valves, job done. £200.
We have 200mm of PIR insulation below our bedrooms and carpet, UFH will keep the rooms circa 18, we open the doors if we want them the same temperature as the rest of the house. You may flow up to 35, but surface temp is only a couple of degrees warmer than the room, most the heating season. A nice layer of insulation (carpet and underlay) just stops that temperature reaching the surface. Net effect is rubbish heat output. It doesn't matter how long you wait.
We have standard carpet (wife insisted) and UFH underlay and it kills UFH performance pretty much. It's a bit like wearing a good overcoat on a cold day, you stay warm the cold doesn't get in. We run full weather compensation however. But as you have thermostats run at a set flow temp, you may have to wack the flow temp up x degrees and it should work fine. You would need to fine a happy spot via trial and error. Dig a bit deeper in your pockets and get proper carpet, dump your thermostats, run weather compensation and your energy savings will pay the extra needed for proper the carpets.
Passive house Shepards hut ?
JohnMo replied to Waterworks's topic in Energy Efficient & Sustainable Design Concepts
Why that much? Over thinking things. You can use passivhaus principles for any build. Main things are thermal bridges, continuous insulation, form factor, airtightness. So you need to consider ventilation. -
Add it the outside if you wanted. Do people in the UK buy by the ft² or m², thought they bought by number of bedrooms and that was about it. Hence big builders building shoebox sized houses with loads of bedrooms.
They are very different materials, aerogel is a fibrous soft material, compacfoam, is a solid EPS, looks EPS but rock like. You can drill it screw into it etc. treat it more like wood than insulation. So fixing self drilling screws direct through compacfoam into the steel. Then if you wanted plasterboard screw into to the compacfoam or foam into position. Aerogel I bought it but I ended up using PIR, but @Nickfromwales suggestion of compacfoam is way better. We did upstands for our roof lights with it, easy to use
Any reasons not to go with a Nibe ASHP?
JohnMo replied to Great_scot_selfbuild's topic in Air Source Heat Pumps (ASHP)
Observations Just tried to find a price for the Nibe, only price I got near, suggested circa £6k, so 3x the price of my Haier 4kW. Will it perform any better than my Haier, possibly not. Yesterday was between about 4 degs and 8 degs, and it just ticked away all day at an average CoP of 5.6, peak CoP around 6.3 (flow temp around 26-27). -
You can work it out knowing your heat loss and then W/m² Just use this as a baseline, you may need to extend the W/m² and the MWT - mid way between flow and return temperature. -
2x air source heat pumps - Scotland
JohnMo replied to BintyAndTheBeast's topic in Air Source Heat Pumps (ASHP)
Run in WC mode everything is always calling for heat. The fan coils just modulate their output to match room conditions by changing fan speed not water flow rate. So all good -
Looking at room temperature the line is steady climb, which is good, but suspect your flow temperature is way to high. A 2 Deg rise over 12 hrs is very fast for thick screed. Your +15 degs I would be setting sub 25, maybe 20 to 23, your -5, 28 to 30. Start low, and move up. A hot house is a horrible place to be, especially when it's a thick floor and it doesn't cool for an absolute age. At 10 degs your house will not need or very unlikely to need heating, when dried out. Your running 30 degs, that is nearer what you will need at -5. -
Nibe (and others) use an energy integral, so if they are cycling they use a fancy time, to degrees of heat delivered calculation, so they can provide a higher than target temperature, to get a decent run cycle and time off, while still managing the energy delivery to house. Basically ensure short cycling is never an issue and energy delivery is on target. -
Your form factor is good, it's a rectangular box. So U value effect is different from a poor form factor (like our house). I would look at a slight bigger scale than just the walls, so floor windows/doors and roof. Get a bigger picture. Note: Passivhaus required U value changes with form factor.
I say look at modulation - can it run all day long at most weathers? As in not cycle? -
Very unlikely for it to be any warmer than the room itself. The heat from the pipes will only migrate so far before it runs out of energy
Who in right mind remodels a kitchen in under 10 years, 20 years isn't that likely. Most kitchen units have a decent long warranty. We have been in our house for 5 years now, redecorating isn't even on the horizon, remodeling a perfectly good kitchen is unlikely ever in my life time. I would possibly build another house first, that's unlikely also. May upgrade a laminate work top but nothing else likely. Your just planning for thing unlikely to occur, adding complexity likely to go wrong.
For me the following comments The floor array hasn't been sized for room output - they have just filled the floor with pipes, so zero design effort. You should really design output to match room design loads just the same as you do with radiators. As it is designed, you may/will need room thermostats to manage overheating, this drives a buffer and other complications. Suspect you will not be able to set room temps by water flow balancing alone. As mentioned dedicated hall loops aren't needed. But may be needed if you need to manage each room temperature via a thermostat. WC and bathroom are next to each other, you could easily share loops. So one loop serving both rooms. To add to this, suspect the utility could also share the same loop. Take into bathroom first, then WC and the utility and then back to manifold. WC will actually need little or no heat as it's internal room surrounded with heat areas. Spiral or up and down makes very little difference as dT (flow return temperature difference) is only 3 or 4 degs, plus floor temp is way below body temperature, so you will not feel it.
Our 4kW can put out around 20L/min of flow if required. It's currently doing around 2kW and the flow rate is around 6-7L/min. So zero need for additional pumps. We are heating 192m² UFH floor area plus a fan coil in another 24m². So do you need the pumps, possibly not, assuming you are flowing the same temperature to each floor area covered by each manifold and don't need mixers. Even then your ASHP should be able to drive an electronic mixer to reduce temp to the lowest flow temp temperature, and do it all without additional pumps/buffers etc. Maybe start a thread, with your details and bottom out what you do and don't need?
Bigger is better, but only if all are the same % oversized, so don't over egg one room and neglect others. Otherwise you end up gagging back one room and still flowing a higher temp at ASHP.