Russdl Posted January 11 Posted January 11 3 hours ago, ProDave said: usually indicate the expansion vessels(s) have failed. How can that be possible in 5 years? I guess only via dodgy installation/commisioning?
Beelbeebub Posted January 11 Posted January 11 2 hours ago, Russdl said: How can that be possible in 5 years? I guess only via dodgy installation/commisioning? 5 years is a bit on the short side but I have had multiple ones fail, it's one of the most common things to fail in the heating systems I manage. Prob have one or two a year out of 35 or so.
Nickfromwales Posted January 12 Posted January 12 @canalsiderenovation Don't run back into the arms of these dickheads out of desperation. They've not done a good job here, just perpetuated their revenue stream and kept themselves in business. As part of their visit, they should have diagnosed, not just said "fit a bunch of new stuff". FFS. At the ABSOLUTE minimum, they should have asked to charge you for an hours labour, to check the red vessel pre-charge pressure, to ascertain what is going wrong. The system is too young to have major faults, this is a mountain being made out of a molehill IMHO. The issue(s) is NOT diagnosed well enough yet, so we need to know if the discharged water was warm or hot, and if the heating blew this off or the UVC did. Without this info you, and the aforementioned dickheads, are just flying blind. Leave the hot water on via the ashp and use your showers, you'll be fine for the immediate. Turn off the Solic, even though excess PV at this time of year is negligible anyways, which will reduce the magnitude of the situation. 2
Dillsue Posted January 12 Posted January 12 A flip side to the companies approach maybe that the guy that attended for the service is an employee with a set schedule of services to complete in the day with householders taking time off work to wait in for him to arrive. If he gets drawn into doing unscheduled work there's a fair chance he'd mis subsequent appointments and the company would have an unhappy customer or two??
SimonD Posted January 12 Posted January 12 7 minutes ago, Dillsue said: A flip side to the companies approach maybe that the guy that attended for the service is an employee with a set schedule of services to complete in the day with householders taking time off work to wait in for him to arrive. If he gets drawn into doing unscheduled work there's a fair chance he'd mis subsequent appointments and the company would have an unhappy customer or two?? Okay, so I'm self-employed, but have a run of servicing appointments. As real example of a day, I turn up to my first one and find that the boiler was installed with its prv just sticking out the bottom of the boiler and terminating just behind some boxing in the bathroom. Not safe. So this needs to be dealt with. Next customer gets a text message - I'm sorry I'm running late but there's a safety issue. Arrive at the next customers house to find a shite install where the magnaclean has never been cleaned (even the bleed port is filled with plaster from when the kitchen was done years ago). Then, as I close the service isolation valves on the magnaclean, one of them springs a leak and it becomes apparent that when installed the maganclean connector threads had been damaged so as soon as I touch the thing to take the lid of another leak starts. So next customer gets a text. Then I go to a service where I did the installation and I've made up my time and can pick up my boy from school in time 😉 Life in the day of......that's what appointment windows are for ☺️ but every customer was happy to see me, some of whom I'd rescheduled from before Xmas. I find they're pleased to hear if I've found problems and rectify them as that gives them confidence I'll do them same for them. Sorry long ramble.
Nickfromwales Posted January 12 Posted January 12 4 hours ago, Dillsue said: A flip side to the companies approach maybe that the guy that attended for the service is an employee with a set schedule of services to complete in the day with householders taking time off work to wait in for him to arrive. If he gets drawn into doing unscheduled work there's a fair chance he'd mis subsequent appointments and the company would have an unhappy customer or two?? And he should / could have used the opportunity to state all of that and book a return visit in. They didn’t. =💩
Dillsue Posted January 12 Posted January 12 2 hours ago, Nickfromwales said: And he should / could have used the opportunity to state all of that and book a return visit in. They didn’t. =💩 Didn't the company send in a quote for remedial work together with a service report??
Nickfromwales Posted January 12 Posted January 12 1 minute ago, Dillsue said: Didn't the company send in a quote for remedial work together with a service report?? They failed to do due diligence, just an assumed 2x dead EV’s at 5 years old. Sugar coat it if you wish. This is just shit service.
canalsiderenovation Posted January 12 Author Posted January 12 (edited) 21 hours ago, Nickfromwales said: Leave the hot water on via the ashp and use your showers, you'll be fine for the immediate. Turn off the Solic, even though excess PV at this time of year is negligible anyways, which will reduce the magnitude of the situation. We can't leave the ASHP on for our hot water. I wouldn't feel confortable to be honest. Water was literally pi$$ing out of the tundish. Someone asked if it was hot or cold but I can't remember. I think cold.. 28 minutes ago, Dillsue said: Didn't the company send in a quote for remedial work together with a service report?? Yes and no. They did but in the hoo haa of the wrong email/billing issue it went to the wrong email address. I was then able to ask and get this resent which I posted on here. On 11/01/2026 at 18:06, Beelbeebub said: Which part of the system is that leaking tundish linked to? Is it the domestic hot water or the system loop? Is there a pressure gauge for the DHW tank? Leaking tundish is on our Gledhill water tank. The only pressure gauge I can see is the one on earlier photos and pictures. 25 minutes ago, Nickfromwales said: They failed to do due diligence, just an assumed 2x dead EV’s at 5 years old. Sugar coat it if you wish. This is just shit service. I spoke to the company today and have booked them in, hopefully Wednesday. I know @Nickfromwales you will be cursing me but frankly we are stuck. We have visitors later this week and an Airbnb booking so it is a case of sucking it up because the timing could not be worse. We used the gym showers tonight but we dare not turn on the hot water ASHP and have a lot of water coming out. So this is what I am going to ask: 1. We want to keep those expansion tanks. Told they need replacing but saw no evidence of this. We want to check them/see this (if they remove them is there a way of checking they have failed if they remove them)? The service form says they need replacing so this indicates they have failed. Do companies routinely replace them or pump them back up?? 2. We will explain what happened with the pressure dropping to 0, how I topped it up and the leaking tundish. Ask them to check valves are not faulty. Edited January 12 by canalsiderenovation
Nickfromwales Posted Tuesday at 07:28 Posted Tuesday at 07:28 7 hours ago, canalsiderenovation said: We can't leave the ASHP on for our hot water. I wouldn't feel confortable to be honest. Water was literally pi$$ing out of the tundish. Someone asked if it was hot or cold but I can't remember. I think cold.. Yes and no. They did but in the hoo haa of the wrong email/billing issue it went to the wrong email address. I was then able to ask and get this resent which I posted on here. Leaking tundish is on our Gledhill water tank. The only pressure gauge I can see is the one on earlier photos and pictures. I spoke to the company today and have booked them in, hopefully Wednesday. I know @Nickfromwales you will be cursing me but frankly we are stuck. We have visitors later this week and an Airbnb booking so it is a case of sucking it up because the timing could not be worse. We used the gym showers tonight but we dare not turn on the hot water ASHP and have a lot of water coming out. So this is what I am going to ask: 1. We want to keep those expansion tanks. Told they need replacing but saw no evidence of this. We want to check them/see this (if they remove them is there a way of checking they have failed if they remove them)? The service form says they need replacing so this indicates they have failed. Do companies routinely replace them or pump them back up?? 2. We will explain what happened with the pressure dropping to 0, how I topped it up and the leaking tundish. Ask them to check valves are not faulty. No cursing here, just frustrated for you. As you’re under the gun you’ll want the quickest route obvs. If it’s cold water going out of the tundish then it’s not cut and dry as to what the issue is. The control group (multiblock do-dah that one pipe of the tundish comes from) governs the cold mains pressure to the entire hot and cold system. IF, the water is defo cold then it can mean the cold mains pressure reducing valve has failed, so cold mains water is just being allowed out through the 6bar PRedV, sometimes this will happen sporadically with use of outlets temporarily relieving the issue or network pressure fluctuating. There are 2 places the system ‘blows off’ from, and that’s one. The other is the T&PRV (temp and pressure relief valve) that the other pipe to the tundish comes from, the one high up at the side of the cylinder, usually with a red cap. This operates if the cylinder pressure gets too high, or if the water gets way too hot; bottom line here is, if the hot water is on and the cylinder is hot then the water in the tundish will be the same temperature, eg not cold as you suggest. You’d likely see steam coming off it / out of the tundish if so. Questions are: 1) was the hot water heated or being heated when you say the cold water was detected at the tundish 2) are you sure it was cold? Do consider getting those Tesla valves bought and installed, may be useful to hit different Screwfix’s if one doesn’t have the qty you need in stock, and have these to hand for the chap to fit. Will save you time and money in the long term and they’re quite cheap. These make a proper service / inspection an absolute doddle, and diagnosing issues becomes much easier too, vs having to fully drain down and refill both heating and hot/cold systems every time there’s a need to check / top up the expansion vessels pre charge pressure or identify potential issues etc. Now it’s down to cost and time I guess, but as you’re a rental then I think it’s best to not roll the dice. My 2 cents is to get the 2x cold (white) expansion vessels changed, but to also increase the volume. It seems what you have is not sufficient for this to be long/term reliable, and you don’t want to keep pushing this fault along waiting for it to go again. May as well fix it properly, once. Either change these out for the next size up, or add a third 24L vessel to this setup is my advice. I imagine heating by immersion a lot through summer etc gets this tank super-hot routinely and takes it to its upper limits. Adding more volume is one solution. Setting the temps on the immersion a little lower is another. Eg if you have sufficient hot water during winter from the ASHP, when not heating from solar / immersion, then the temps could be dropped so the safety devices aren’t being pushed to their limit all summer. Without being there I cannot rule out a stray mixer tap back-pressurising the cylinder, but do you know if the cold mains (strictly) only comes in at the plant room and that goes to the control group on the UVC? If both points are so, then the whole house hot and cold supplies should be “balanced”; this is something you could ask the ‘engineer’ when they call out. It’s very easy to just change broken things without finding, or curing, the reason they broke. That’s my concern.
canalsiderenovation Posted Tuesday at 08:45 Author Posted Tuesday at 08:45 1 hour ago, Nickfromwales said: Questions are: 1) was the hot water heated or being heated when you say the cold water was detected at the tundish 2) are you sure it was cold? Yes hot water was being heated at the time. And no, I am not sure it was cold at all. 1 hour ago, Nickfromwales said: Do consider getting those Tesla valves bought and installed, may be useful to hit different Screwfix’s if one doesn’t have the qty you need in stock, and have these to hand for the chap to fit. Will save you time and money in the long term and they’re quite cheap. These make a proper service / inspection an absolute doddle, and diagnosing issues becomes much easier too, vs having to fully drain down and refill both heating and hot/cold systems every time there’s a need to check / top up the expansion vessels pre charge pressure or identify potential issues etc. Can you send me the link of what is needed and I will order now and ask the guy to fit them. He may not given that they haven't quoted but if it is something he can do at the same time then hopefully it won't be a problem. What do I ask the guy to do, just so I am using the right language when I ask him to do it. Annoyingly I paid the deposit so those tanks have been ordered already. 1 hour ago, Nickfromwales said: Setting the temps on the immersion a little lower is another Is that the temp on the hot water tank? Like the bottom under that white cap, if so we adjusted that a few years ago. Our hot water temp never goes over about 55 degrees. 1 hour ago, Nickfromwales said: do you know if the cold mains (strictly) only comes in at the plant room and that goes to the control group on the UVC? It comes in at the utility and all the tank and ASHP stuff is in there so presume so. The Airbnb is a seperate but attached ensuite room to our house so any issues impacts us and them.
Nickfromwales Posted Tuesday at 09:58 Posted Tuesday at 09:58 1 hour ago, canalsiderenovation said: Yes hot water was being heated at the time. And no, I am not sure it was cold at all. Can you send me the link of what is needed and I will order now and ask the guy to fit them. He may not given that they haven't quoted but if it is something he can do at the same time then hopefully it won't be a problem. What do I ask the guy to do, just so I am using the right language when I ask him to do it. Annoyingly I paid the deposit so those tanks have been ordered already. Is that the temp on the hot water tank? Like the bottom under that white cap, if so we adjusted that a few years ago. Our hot water temp never goes over about 55 degrees. It comes in at the utility and all the tank and ASHP stuff is in there so presume so. The Airbnb is a seperate but attached ensuite room to our house so any issues impacts us and them. Ask them to supply a 3rd vessel. The valve is in the first page of this thread with Screwfix part number visible
Nickfromwales Posted Tuesday at 09:59 Posted Tuesday at 09:59 Ask these guys for a full diagnosis of the fault, and why it’s occurred, and the solution. Otherwise you’ll be doing this over and over again. 1
Dillsue Posted Tuesday at 11:08 Posted Tuesday at 11:08 12 hours ago, Nickfromwales said: They failed to do due diligence, just an assumed 2x dead EV’s at 5 years old. Sugar coat it if you wish. This is just shit service. It's not sugar coating, it's just a balanced view. Constant slagging of the company/engineer could well cost them work and be the start of a bad reputation if the OP doesn't consider the possible flip side.
canalsiderenovation Posted Tuesday at 11:50 Author Posted Tuesday at 11:50 1 hour ago, Nickfromwales said: Ask them to supply a 3rd vessel. The valve is in the first page of this thread with Screwfix part number visible Got it. Is it just one I need? And where do these need fitting?
Nickfromwales Posted Tuesday at 13:49 Posted Tuesday at 13:49 1 hour ago, canalsiderenovation said: Got it. Is it just one I need? And where do these need fitting? One per vessel, so 1x red, plus 2 (or 3) for the white vessels.
canalsiderenovation Posted Tuesday at 15:03 Author Posted Tuesday at 15:03 1 hour ago, Nickfromwales said: One per vessel, so 1x red, plus 2 (or 3) for the white vessels. Thanks @Nickfromwales Also I did some more troubleshooting. I just turned on the ASHP for hot water. The tundish only leaks when I turn the hot water off. So it heats up fine but then when I turn it off (turned it off at 45 degrees), the tundish starts leaking. It is definately cold water.
ProDave Posted Tuesday at 15:17 Posted Tuesday at 15:17 10 minutes ago, canalsiderenovation said: Thanks @Nickfromwales Also I did some more troubleshooting. I just turned on the ASHP for hot water. The tundish only leaks when I turn the hot water off. So it heats up fine but then when I turn it off (turned it off at 45 degrees), the tundish starts leaking. It is definately cold water. This for me is ringing alarm bells that it is NOT the white water expansion vessels at fault. If it were then the tank would be discharging on over pressure and that would be 45 degree hot water from very near the top of the tank. I would still want a plumber I trust to test everything and find out exactly what IS at fault. One thing I did when plumbing my own system is I fitted a pressure gauge on the top of the hot water tank so I can see if it is over pressurising. That is not normally done, but I had one spare. Perhaps when the guys come with their new white expansion vessels you can agree with them, if this does NOT solve the problem they will fit the original ones back and refund that cost? It is sounding to me like "fault finding by substitution" 2
Nickfromwales Posted Tuesday at 21:44 Posted Tuesday at 21:44 6 hours ago, ProDave said: It is sounding to me like "fault finding by substitution" Yup. Zero discernible diagnosis going on here afaic. 10 hours ago, Dillsue said: Constant slagging of the company/engineer could well cost them work and be the start of a bad reputation if the OP doesn't consider the possible flip side. I’m stating facts. They’ve not stayed to diagnose, they didn’t rectify the zero pressure on the heating situation, they’re just swapping out knee-jerk items hoping that the most common fault is the fault here. The flip side is that someone better could come and actually do some investigation, and THEN start handing out invoices or requests for deposits; (requesting a deposit for stock EV’s is crazy). This screams of them not wanting to be left out of pocket or holding the baby if their assumed fix doesn’t fix it. I expect they’ll get paid and be gone, but the issue won’t be gone, just forgotten for a while. Cold water coming out of a heated UVC is not an issue for T&PRV, so it looks like the issue is the 6bar PRV has opened on the multi-block which means it is that which has failed; likely needs to be stripped down and cleaned / serviced, and then tested for normal operation, before anything else gets changed at (likely significant) cost. I’d be asking what makes them think the EV’s “have failed?”. I'd be asking if the fault returns will they then come and fix what it actually was that’s wrong, on their dollar. I'd be asking why after a service you were left with a system with zero pressure in it. Just crap. Seriously?
dpmiller Posted Wednesday at 06:48 Posted Wednesday at 06:48 Do safety/ multi groups not normally have a gauge on? If none is fitted might it be worth the OP getting a gauge and screwing it onto the PRV?
SimonD Posted Wednesday at 08:59 Posted Wednesday at 08:59 2 hours ago, dpmiller said: Do safety/ multi groups not normally have a gauge on? If none is fitted might it be worth the OP getting a gauge and screwing it onto the PRV? No, they don't. You only really put a gauge on the heating side. The multi-bloc should be serviced annually but everyone who does so knows the perils of opening up the various prvs and finding that they don't close back up again. But changing out a faulty multi-bloc is so quick and simple and not very expensive either. You just have to get the right one as cylinder manufacturers spec different prv pressure ratings. Off the top of my head Gledhill slimline heat pump cylinders have a 4.5bar rather than 6bar, for example.
Beelbeebub Posted Wednesday at 10:11 Posted Wednesday at 10:11 Years ago spoke to the technical director of reliance controls about "servicing" of their PRVs etc Context was a very awkward tenant who insisted that the valves be serviced every year and wouldn't accept that getting a g3 ticketed engineer to inspect and sign off the cylinder etc was sufficient. Upshot was, there wasn’t anything to "service" - you look at the valve, make sure nothing is blocking the pipework etc and there are no visible signs of leak/degradation. I asked specifically about turning the knob to activate the valve and he said you could but there was always the risk it wouldn't seal back properly and you'd have a persistent drip, which would mean the valve would need replacing. From the safety POV the main thing is that the valve opens when the pressure or temp are too high. They are engineered to be highly reliable and fail safe, ie anything that goes wrong makes them open easier than design. The servicing is more to check they aren't leaking and the venting arrangements are still adequate. 1
canalsiderenovation Posted Wednesday at 11:59 Author Posted Wednesday at 11:59 (edited) I have rung the company today and explained that I know they are coming out on Friday to replace the expansion tanks we were told needed to be replaced but that the tundish is leaking cold water and that I don't know if this is or is not linked to the expansion tanks we were told needed to be replaced and the leak the engineer found in the service and repaired (I have no idea what the leak was noted on the service record). They said they made some notes and will pass on to the engineer. I have written down everything from the pressure dropping, wanting to know exactly how they have determined the expansion tanks need replacing, what the issue is with them, the leaking tundish and cause and also asking if they can fit the things recommended on the expansion tanks which I now have from Screwfix. I will go through everything and be really clear. I am wondering if the note of the tanks needing to be replaced (if indeed they do) is something completely seperate to the problems we had with the pressure drop and leaking tundish since (just coincidental timing that it happened so close to the service). We had not noticed any issue with pressure dropping or leaking tundish til after then so maybe, just maybe there were no issues with it when they did the service. Hopefully will have a clearer picture at the end of the week. Edited Wednesday at 12:01 by canalsiderenovation 1
dpmiller Posted Wednesday at 13:46 Posted Wednesday at 13:46 3 hours ago, Beelbeebub said: I asked specifically about turning the knob to activate the valve and he said you could but there was always the risk it wouldn't seal back properly and you'd have a persistent drip, which would mean the valve would need replacing. From the safety POV the main thing is that the valve opens when the pressure or temp are too high. They are engineered to be highly reliable and fail safe, ie anything that goes wrong makes them open easier than design. The servicing is more to check they aren't leaking and the venting arrangements are still adequate Oddly enough my experience with safety valves- autoclave sterilisers as well as other pressure vessels and boilers- is that the insurance engineer absolutely *must* see them lifted at every statutory inspection and will often remove and pump test them as well to verify the opening pressure. It's not unusual to find a valve stuck badly enough that more than the chamber's safe test pressure is required to break it free which is more than a small worry. Yes occasionally one will weep after this, but replacement is the cost of doing business... I routinely lift the valve of any unit I'm working on to confirm it's *not* stuck... 1
SimonD Posted Wednesday at 15:04 Posted Wednesday at 15:04 4 hours ago, Beelbeebub said: From the safety POV the main thing is that the valve opens when the pressure or temp are too high. They are engineered to be highly reliable and fail safe, ie anything that goes wrong makes them open easier than design. The servicing is more to check they aren't leaking and the venting arrangements are still adequate. 1 hour ago, dpmiller said: It's not unusual to find a valve stuck badly enough that more than the chamber's safe test pressure is required to break it free which is more than a small worry I did a boiler service in a very large old mansion - it hadn't been service in donkeys. The boiler was down in the basement with a soil floor and I was a bit perplexed the prv had just been run down the wall to just above the floor. I noticed the system pressure was a bit low so I topped it up. I went to do my gas checks and a gas rate. Got back to the boiler and noticed the pressure guage was up to 3bar but didn't think too much of it at the time. I then started doing my combustion checks and pressure just climbed and climbed until the guage was off the chart. The prv just would not open. I eventually got it to release to a great boom of extremely hot water and a flooding of the ground. Needless to say, I'd always test the safety valves. And it is actually a requirement of G3 servicing. 2