saveasteading Posted 5 hours ago Posted 5 hours ago 23 minutes ago, JohnMo said: soak aways are huge, compared to normal I'm interested. The regs show ever bigger areas where permeability is poor. On sand they don't seem to acknowledge that the water won't reach the end. So in our case we used perforated pipes heading different directions to spread it.... phase 2 and 3 extensions to the zone, the drawings and calcs got us the approval, but are 'yet' to go in.
joth Posted 5 hours ago Posted 5 hours ago 23 minutes ago, JohnMo said: Set up to run long run for periods, this helps a lot. Plus our ambient outside helps. And down-sizing the ASHP to allow these long runs at a low deltaT without short cycling, isn't it? Our ASHP is way oversized so will bordering short cycle (5 min runtime, 10min period) when just cooling the slab to ~16deg. I'm still getting COP of 3.5-4. But it's powered from PV - if I could double the COP it would give me about 30p more SEG payments per day on these hottest days.
JohnMo Posted 5 hours ago Posted 5 hours ago 5 minutes ago, joth said: And down-sizing the ASHP to allow these long runs at a low deltaT without short cycling, isn't it? Our ASHP is way oversized so will bordering short cycle (5 min runtime, 10min period) when just cooling the slab to ~16deg. I'm still getting COP of 3.5-4. But it's powered from PV - if I could double the COP it would give me about 30p more SEG payments per day on these hottest days. Last year on our 6kW heat pump it cycled, depending on load, we averaged around 4 to 5 CoP over the day depending on a few factors doing cooling. This year with a 4kW it can run low and slow, our dT was about 2.5 degs. Yesterday's whole day CoP was 7.3 including standby time/energy. We only cool if there is solar gains, so we have plenty of PV also. So it free. It would almost always get clipped from PV also, if we weren't using it, so it really is free. 1
Michael_S Posted 3 hours ago Posted 3 hours ago Not sure if we can calculate an EER, we have a heat meter but not sure if it counts backwards..... Gonna add some more fans to the rads and overvolt them a bit to see if we can get some more airflow - I know you can get actual sit on rad units but the fans are less than a quid each compared to about £100 for a unit that will only do about 1/3 the length of a fad and is probably louder too. Currently we are using our second hand heath robinson heat pump - hoping to move to a 'proper' set up but MCS sound rules mean our preferred placement is max 55db that seems to strictly limit the number of 8-10kw units available and the one that seems to be best fit (Grant) does not cool. Does anyone know of any other units that fit the 8-10kw and 55db or less sound power criteria and do cooling? Thanks
JohnMo Posted 59 minutes ago Posted 59 minutes ago 1 hour ago, Michael_S said: Not sure if we can calculate an EER It's the inverse of CoP, so if calculating CoP you just get a negative figure, exactly the same calculation. Take the negative away you get EER.