Underlying question for any warm roof. Is the Vapour Control Layer adequate for purpose, adequately installed and 100% sealed against leakage into the roof void?
if the answer is a resounding Yes, a warm unventilated roof is possible.
if in doubt however, ventilation. By way of a minimum 50mm void directly under the substrate timber, plywood or OSB3.
note: a ventilated Softwood under zinc is how it’s been done in Europe. Plywood and OSB3 were not around. The standing seam technique is also relatively new, in the grand consideration of zinc.
if you use OSB3 or Plywood almost every zinc manufacturer will recommend a Structured Underlay such as ISO-Mat Metal. Even if the rear of the zinc has been coated!
by far going with ventilated softwood, Vac Vac treated. (Avoid Copper treatments)
GreenCoat PLX is not susceptible to underside corrosion so you have greater liberty on the support structure.
Aluminium is another proposal. More traditional detailing at penetrations.
Metal cost will undoubtedly have a bearing.
the ventilation void must be increased on lower or longer slope lengths to potentially evacuate moisture build up - a chimney effect.
wet insulation doesn’t perform correctly either.
finally, we live in a wet climate. Moisture retained during construction has to escape. Ventilation
until