Everything posted by Onoff
24V gate - what size cables for 25m in duct run?
Onoff replied to readiescards's topic in Electrics - Other
Imho any underground duct might be subject to condensation internally, more so if the cables run a bit warm. This could conceivably pool at any low point in the duct and affect and cable laying in it. I imagine this is one reason why any cable in a duct should be "duct rated". Paranoia? The regs touch on the issue of condensation, protection against moisture etc. The last bit of duct I ran I even considered running a length of aquarium tube in there so I could periodically pump out whatever, if anything, got in there. I even considered punching some drain holes mid point in the duct, wrapping in landscape fabric and packing gravel around it before concreting. Of course then I worried about the water table etc so in the end did nothing! I just ran everything in 20mm conduit and kept those together with some black dowpipe for neatness when concreting. Just noted that photo was taken in June 2014 @readiescards and it's still not finished! Tell your missus -
What dia Nichrome have you gone for? I faffed making one with Kanthal wire from an online vape store. Although it worked for a bit the wire kept breaking and I burnt the wall wart psu out! I had even done some rough Ohms Law calcs as well. Figure it needs a constant current psu maybe. Got bored and gave up! Even my missus had a go...
Zinga, Galvafroid?
@readiescards, you're not thinking 24V DC for a system with solar charged batteries are you? -
This I think is the opener manual: idv0532a01en.pdf Says on page 3 of the above that the MC824H control panel is compatible with the 36W LFAB4024 and the XLFAB5024 50W. And here's the manual for that: D00011568.pdf The control panel still needs 230V AC to it even though the motors are 24V DC I think you'll find. All the cable sizes / run lengths are in the manual on page 2 of the second manual. -
I retitled this "Compact RCBOs" as it's going away from Wylex.
Ah! I didn't realise the board was feeding sub mains. I thought it was an overkill seeing as you are using Compacts hence no fly leads! For others here thinking wtf, consider a metal cu on a TT system. The earthing arrangement is likely nowhere near as good as with TN systems. The incoming meter tails are stranded copper cores that are sheathed and insulated, in effect double insulated but it's actually wrong to call them that even though the sheath is insulating! They will come in through a plastic gland. Quick CAD sketch (in lieu of my earlier fag packet sketch - felt the thread deserved better): You have in the cu for want of a better word "fly leads" from the main switch to the individual RCDs in the case of a split load board. These fly leads are single insulated. They're also pretty flexible by construction. Add to that the modern move away from two screw terminations in main switches to one bfo screw (bad move imo). That's a big bone of contention on the basis it's easy for it to loosen. NEVER, EVER think that these screws are factory tightened properly, always check. So with potentially dodgy single screws and springy, single insulated, flexible conductors, if one comes adrift it could easily touch the metal enclosure...and that's BAD! Wasn't a huge issue before when a TT enclosure had to be made from "plastic". So the way round this, in a TT is to fit an upfront TD RCD in place of the normal DP main switch. Wire comes adrift, touches the case, TD RCD trips. The 100mA rating is there to give fault protection for the single insulated cables that feed the 30mA RCDs. If you put a normal, no time delay 100mA RCD in front of the line of 30mA RCDs it doesn't guarantee it won't trip first hence the time delay element. Only a TD 100mA provides proper discrimination. There's a lot of confusion over time delay but think of it like this: A fault occurs on an outgoing circuit in excess of 100mA you would think that it should trip the 30mA RCD first if that's before a 100mA RCD. But normal BS EN RCDs (& RCBOs) only have to trip within 300ms. The issue is that the 100mA RCD if non time delay may react quicker than the 30mA RCD. Making the 100mA RCD time delay gives the 30mA a chance to trip first. Hope that makes sense. If you look at the SBS Compact assembly the bus bars take the place of the single insulated fly leads. They're affixed at multiple points and can't really come undone and spring against the enclosure.
It's a belt and braces thing I believe as the double bus bar takes care of a big "worry" but I'll let Dave comment.
Hello Dave, first post! You might want to introduce yourself on here. I'm sure you'll get a few questions direct now!
'Kin how much???
Probably but I was aiming for something intumescent. I have a few tubes of this I was hoping to use: Says it's "tested for air permeability to EN13141-1" whether that has any bearing...
Yes. The picture below from SBS shows a line of Compact RCBOs on the left then two MCBs before the main switch. Subsitute full height RCBOs for the breakers: The busbar along the bottom is in fact two, one for L and one for N insulated from each other. They pick up from the main switch. Only the Compacts are fed like this. The full height RCBO's (or mcbs in this case) are fed conventionally.
That'll be a laugh trying to cut they the foil but not the vcl! Going to give it a go though. Conduit will enter through the hole in the bottom of the hood. It'll need a bead of something around that too. Then all I have to consider is the losses through the conduit itself! Might gel it where it comes up into the conduit box. Taking the Tesco, "every little helps" approach!
Just about to puncture in earnest my lovely plasterboard ceiling for 5(6) downlights and in particular the continuous vcl that sits above the moisture resistant plasterboard. I've had it planned to do like this for a while but will my idea to maintain the airtight layer work? So, between the joists its fully filled with 100 + 50mm of foil faced PIR. I'm using TH140 Thermahood downlight covers that measure 185 x 185. A rigid plastic type they are. They have no bottom flange really as per the sketch (the circular ones do but I like squares). So I drill up from below my 60mm dia hole that goes through the plasterboard, vcl and into the foil faced PIR a bit. Then with a long series pop a hole up through the PIR. Into the loft with my 200x200 wooden jig, centre over the hole and neatly cut out the PIR. At this point I have the opportunity to LEAVE the bottom layer of foil intact as the PIR just peels away. That is above the vcl. Ideally though I want the vcl outside the 185x185. So I cut back an exact 185x185 section of foil and vcl and centre the Thermahood over the cut out. I figure just a bead of intumescent sealant around all 4 sides should do the trick or should I invest in some airtight tape? To maintain the insulation I'll be adding a 150mm deep slab over the hole area above the downlight. Plenty of height to do so in what is dead space. There's a good 300mm between the tops of these ceiling joists and the underside of the dormer extension floor joists. Do I need to fill the void outside the tapered sides of the Thermahood? Low expansion foam maybe? Or can I leave this void unfilled? Thinking condensation maybe? Cheers.
SBS DP Compact, single module RCBOs go to 40A. SBS do the bigger, standard height 50A RRCB-B50L. This has flying neutral and earth leads and is £12.
Schematic on a typical SBS Compact RCBO: This from Dave at SBS: "The GARO is a true 2-pole device, but its biggest size is 25A. Probably couldn't achieve 6KA at bigger sizes. Couldn't therefore deal with 32A rings or 40A showers. It is LIVE IN at the bottom only, which shouldn't be a problem in the UK."
Choosing casters - is a nightmare. Have you any advice?
Onoff replied to ToughButterCup's topic in Tools & Equipment
Option 2 -
Bolt the castors on using nyloc nuts rather than screwing them on. -
Swivel casters all round for easy shifting. A couple of those being lockable ones if you ever bring it inside the house. Nylon wheels are cheapest but noisy and can mark some floors. Something like this: http://vi.raptor.ebaydesc.com/ws/eBayISAPI.dll?ViewItemDescV4&item=183012234509&category=26224&pm=1&ds=0&t=1516081030000&ver=0&cspheader=1 -
Garo is a Swedish company and I think the stuff is made in Poland? I think they are line / load side specific so wire 'em up wrong and they go bang. Could be wrong. Have a feeling they had at one time a short circuit capacity of 4.5KA but seem to have upped that to 6 now. I don't know if they are true DP and switch the neutral in the event of a fault. I'll find out! EDIT: They appear to be true DP but only wire one way: Some have a solid neutral
I wasn't saying "fit these Wylex RBCOs" just to be clearon that. I was alluding to the fact that what is a major manufacturer (Wylex) appears to be moving towards the small form / compact / same size as an MCB, RCBO. Wylex are a big name in consumer units but they're just a bought out "trusted" name of yesteryear now under the umbrella of the Electrium consortium. Wylex, Volex, Crabtree, all cu makers & all owned by Electrium. They were all hit by a serious breaker recall a few years back. Note the Steeple, Sector, Alto etc brands. Punted by this that or the other electrical wholesaler as "their" own line. Bites from the same cherry! So you had all these "names" re-badging the same basic kit in what, the name of profit, perceived wider choice by the customer? https://www.electricalsafetyfirst.org.uk/product-recalls/2012/02/electrium-miniature-circuit-breakers/ Then, MK (not Electrium owned) themselves had faults with their main switch incomer issues. https://www.electricalsafetyfirst.org.uk/product-recalls/2013/04/mk-sentry-switches-and-consumer-units/ Even Hager, Square D etc have had recalls. (Don't forget Square D, Merlin Gerin are both Group Schneider). https://www.electricalsafetyfirst.org.uk/product-recalls/2016/10/hager-minature-10ka-circuit-breakers/ - Plain and simple no ifs, buts or maybes ONLY all RCBO cus comply with the regs. OK, the regs aren't law but what else do you have if you don't abide by them? - Compact RCBOs are common in other countries - The ones available here should hold all relevant BS, EN approvals - Some switch both live and neutral off in the event of a fault which is desirable for multiple reasons - Some allow you to wire them with the feed or outgoing circuit either side. - Some don't have the flying earth and reference neutral leads. Means less wiring, neater install in the cu These new Wylex ones are small, given, BUT retain the flying neutral and only allow wiring one way up. To my mind they could have gone further. However.....it's Wylex, many people's favourite. They will likely fly off the shelves. Go back 30 years and I loved Wylex. Personally I would ask your sparks what he thinks of SBS. Dave there is very approachable and would happily chat to him. https://www.sbstradesales.co.uk/technical-considerations/ They have been offering the benefits of compacts for the last 5 years. If concerned that SBS is a small player, maybe without the "clout" of Wylex then go to them but the cu will be more cluttered. As above though even the "big boys" have had recall issues. You could argue their systems will pick up recall issues quicker but then counter that with SBS being a smaller, more personal service company with a reputation to build. They're all mostly made in China anyway! Yes, btw I will be having an SBS cu in my own house. Slight problem in that the wall where it's going isn't there yet.....and you know how long I take!
Is this a major manufacturer finally seeing the light? Single module compact RCBO. Still only one way in/out and still with a reference fly lead but interesting none the less: https://www.wylexreasons.co.uk/?dm_i=8TT,5E1UN,OHEQG7,KUO5L,1 EDIT: Note how it says "fully complies" (with the regs). Adds weight to those of us of the opinion that anything other than all RCBO DOESN'T COMPLY!
until