15 minutes ago, Mr Punter said:

 

Unless this is a strict planning condition you may find render is more acceptable to future purchasers and lenders.  Probably cheaper and quicker as well.

The cladding is something we don't want to change.

Posted (edited)
1 hour ago, flanagaj said:

I have put the numbers into the knauf calc and I end up at 0.19.  The other issue is that I am using timber clad and not render.

image.thumb.png.a50bae9540bae0360e588161d6a0d6e8.png

 

Change that to medium blocks inside and outside and you get to 0.18. That's a nice calculator actually by Knauf. It is fairly optimistic with the values it's allowing for the airspace behind the plasterboard though but it'll get you through regs which I'm getting the impression is the aim.  

 

 

image.thumb.png.b54363a8a251ca0e9bfc172ab9193c03.png

 

Hemelite blocks are a small bit cheaper too. 

 

image.thumb.png.66c05268a6b4d35faef5ea76488cb64d.png

 

 

 

 

Superglass is a bit cheaper again than Knauf.  

 

 

image.thumb.png.5fc13fbd5d54debf7d277f3d360c4707.png

 

 

 

£51.37 inc VAT per m2 for the blocks and insulation.

 

image.png

Edited by Iceverge
Correcting mistakes made again!!
Posted
10 hours ago, Iceverge said:

it's allowing for the airspace behind the plasterboard though but it'll get you through regs

 

In reality this is more likely to lose heat v solid plaster, as it can allow cold outside air to circulate behind the plasterboard.  This can be very significant and difficult to resolve.  Another failing of SAP.

Posted

No mention of thermal bridging in this discussion of blocks

Is it important , especially through foundations?

Should different blocks be used in foundations?

 

Our build was all masonry construction , and due to ground conditions ended up with a beam and block construction. This meant all masonry walls were thermal bridges, more so than on ordinary foundations. I keep meaning to get a thermal imaging camera to see just how bad it is, and compare internal to external walls.

 

 

Posted

Aircrete block will generally give a much better psi-value than a medium or dense block (in the same detail). In a typical ground floor/wall junction expect the psi-value with dense block to be approx 3 times higher than with an aircrete block.

Posted
3 hours ago, Mr Punter said:

 

In reality this is more likely to lose heat v solid plaster, as it can allow cold outside air to circulate behind the plasterboard.  This can be very significant and difficult to resolve.  Another failing of SAP.

Nothing to do with SAP - its a perfectly acceptable inclusion in the U-value calculation and is covered in the U-value conventions document that supports the Bldg Regs/Appr Docs. Done correctly, to MIs, mass air movement behind the plasterboard will not occur.

Posted (edited)

If you are wanting to go high performance, something like Marmox Thermoblocks can be used at the wall/floor level to prevent thermal bridging, much better than aircrete, but for the rest of the construction go with dense blocks, they're robust, don't crack easily, no silly rules for wet plastering, and also keep the temperature balanced out over the year (thermal mass! yes i said it!)

Edited by MikeGrahamT21
  • Like 1
Posted
17 minutes ago, ADLIan said:

Done correctly, to MIs, mass air movement behind the plasterboard will not occur.

 

OK in theory but this never ever happens on site, which is why the "plasterboard tents" are notoriously freezing.

Posted
31 minutes ago, ADLIan said:

Done correctly, to MIs, mass air movement behind the plasterboard will not occur.

Something as simple as a continuous bead of expanding foam at the foot of the plasterboard, before fitting skirtings, will make a huge difference; this prevents air being sucked in at the bottom of the wall preventing convection airflow / travel around blobs of adhesive when dot and dabbing the boards on.

 

11 minutes ago, Mr Punter said:

 

OK in theory but this never ever happens on site, which is why the "plasterboard tents" are notoriously freezing.

Anything done poorly will always perform poorly, as with everything. Other notorious failures are sealing the slab around rising services such as SVP's when there's a cold ventilated void under block & beam. Heating bills go sky-high when you add all these things together.

 

Edit to add, if you're D & D in an airtight house then this is moot.

Posted

Has anyone got examples of Dot and Dab blowerdoor tests(not gamed!)? Did anyone get below 2ACH ?

 

When it comes to passivhaus airtightness the build types I've seen to have achieved those levels are wet plaster, tapes membranes/boards in timberframe, ICF, SIPS. 

 

 

Two one offs were @Gone Wests Icynene TF and an archive building somewhere in England that used Passive purple paint. 

 

I haven't come across any dot and dab getting below 0.6ACH. 

 

 

 

 

 

 

Posted
15 hours ago, Iceverge said:

 

Change that to medium blocks inside and outside and you get to 0.18. That's a nice calculator actually by Knauf. It is fairly optimistic with the values it's allowing for the airspace behind the plasterboard though but it'll get you through regs which I'm getting the impression is the aim.  

 

 

image.thumb.png.b54363a8a251ca0e9bfc172ab9193c03.png

 

Hemelite blocks are a small bit cheaper too. 

 

image.thumb.png.66c05268a6b4d35faef5ea76488cb64d.png

 

 

 

 

Superglass is a bit cheaper again than Knauf.  

 

 

image.thumb.png.5fc13fbd5d54debf7d277f3d360c4707.png

 

 

 

£51.37 inc VAT per m2 for the blocks and insulation.

 

image.png

Thanks @Iceverge!  That is perfect and you have listed suitable materials that come in cheaper than my estimators quote too 🙂  If we had a bigger budget then I'd look to improve the U value further, but if I don't keep costs down, we'll have to sell when we have finished the build.

Posted
51 minutes ago, Iceverge said:

Two one offs were @Gone Wests Icynene TF and an archive building somewhere in England that used Passive purple paint. 

Yes, we achieved 0.47ACH with only the Icynene, combined with the 15mm OSB3 exterior racking, as the airtightness. We didn't use any tapes or membranes in the structure at all. The windows and doors were sealed using two strips of Compriband and the Soudal SWS system.

  • Like 1
Posted
6 hours ago, MikeGrahamT21 said:

If you are wanting to go high performance, something like Marmox Thermoblocks can be used at the wall/floor level to prevent thermal bridging, much better than aircrete, but for the rest of the construction go with dense blocks, they're robust, don't crack easily, no silly rules for wet plastering, and also keep the temperature balanced out over the year (thermal mass! yes i said it!)

 

That's exactly what I have planned for my build.  I also have a couple of dense block internal walls which will sit on Thermoblocks.  One of these will be built from blocks laid flat, so it will be 220mm thick & will have 220mm Thermoblocks beneath.  The idea is, if there's any money left, I can hang a floating staircase from this wall.  & I'll have super THERMAL MASS - there, I said it too.  Now we'll both be in trouble when @SteamyTea reads this thread.

 

Here's my detail.  Yes, I know my Arch Tec has drawn the air brick at the same level as my patio, with virtually no insulation below DPC level & the periscope sitting in the middle of the cavity instead of up against the outer leaf.  I have already told him off.  He really is rubbish. & I engaged him in May, & I'm still waiting for my second draft drawings. 

 

 

Section showing marmox.jpg

Posted
4 minutes ago, Tony L said:

Now we'll both be in trouble when

Not as much trouble as when you find out it will only increase your energy usage.

  • Haha 1
Posted
1 hour ago, Tony L said:

 

That's exactly what I have planned for my build.  I also have a couple of dense block internal walls which will sit on Thermoblocks.  One of these will be built from blocks laid flat, so it will be 220mm thick & will have 220mm Thermoblocks beneath.  The idea is, if there's any money left, I can hang a floating staircase from this wall.  & I'll have super THERMAL MASS - there, I said it too.  Now we'll both be in trouble when @SteamyTea reads this thread.

 

Here's my detail.  Yes, I know my Arch Tec has drawn the air brick at the same level as my patio, with virtually no insulation below DPC level & the periscope sitting in the middle of the cavity instead of up against the outer leaf.  I have already told him off.  He really is rubbish. & I engaged him in May, & I'm still waiting for my second draft drawings. 

 

 

Section showing marmox.jpg

I am interested in this.  If you are having a ground bearing slab, is it worth running a single course of insulated block either below DPC or above DPC.

 

What benefits does this provide?

Posted
19 minutes ago, flanagaj said:

I am interested in this.  If you are having a ground bearing slab, is it worth running a single course of insulated block either below DPC or above DPC.

 

I shouldn't think so, but I don't really know, because I didn't learn about ground bearing slabs before I designed my house.  I should think with a ground bearing slab, you'd have a continuous platform of insulation to separate the top part of slab (including the bit the walls are built off) from the bit that's in contact with the ground.

 

In my case, I have concrete foundations with trench blocks, & the trench blocks support a beam & block structure, so my inner masonry leaf would have a direct connection to the ground, through low R-value materials, were it not for the Marmox blocks.

 

Perhaps I should have left this question for somebody more knowledgeable than me to answer, but it seemed to be directed at me.

 

Posted
1 hour ago, flanagaj said:

, is it worth running a single course of insulated block either below DPC or above DPC.

 

What benefits does this provide?

It reduces thermal bridging at the wall/floor junction, so helps with SAP calculation. 

I'm sure I remember reading an old thread on here that discussed relative performance of a row of marmox blocks versus lightweight, if you can find it

  • Like 1
Posted (edited)
8 hours ago, flanagaj said:

but if I don't keep costs down, we'll have to sell when we have finished the build.

It looks like from my end you have done your very best but are in a bit of a bind. The key thing here is not to blame yourself. Many find themselves in your position where you come to discover that the design packages you have don't cover all of the design and the interfaces don't fit up. 

 

Your strategic risk is that you make changes from what has been approved "in outline".. the BC inspector turns up later and says "you have changed stuff" and there is going to be no completion certificate until you justify the changes. Your design team to date are likely to wash their hands and set you adrift. At that point you may not be even able to sell the house. 

 

Have you considered trying to find a supportive designer that will take say a half day talking to you on the phone, then another two / three days reviewing your design, doing some fag packet calcs.. trying to to get their head round what you have done and the way forward, then at least another day talking to you on the phone, thrashing out you options. Call that 6 days work @ £400.0 a day = £2.4k

 

You'll need a very experienced designer, one that undestands structures , maybe with a building background and with a bit of Architectural flair. 

 

Now that may seem a lot but even if they save you a weeks work and a day or so for a good trades person and a labourer then they have washed their face. 

 

 

Edited by Gus Potter
  • Like 1
Posted
13 minutes ago, Gus Potter said:

It looks like from my end you have done your very best but are in a bit of a bind. The key thing here is not to blame yourself. Many find themselves in your position where you come to discover that the design packages you have don't cover all of the design and the interfaces don't fit up. 

 

Your strategic risk is that you make changes from what has been approved "in outline".. the BC inspector turns up later and says "you have changed stuff" and there is going to be no completion certificate until you justify the changes. Your design team to date are likely to wash their hands and set you adrift. At that point you may not be even able to sell the house. 

 

Have you considered trying to find a supportive designer that will take say a half day talking to you on the phone, then another two / three days reviewing your design, doing some fag packet calcs.. trying to to get their head round what you have done and the way forward, then at least another day talking to you on the phone, thrashing out you options. Call that 6 days work @ £400.0 a day = £2.4k

 

You'll need a very experienced designer, one that undestands structures , maybe with a building background and with a bit of Architectural flair. 

 

Now that may seem a lot but even if they save you a weeks work and a day or so for a good trades person and a labourer then they have washed their face. 

 

 

It's fine.  I've got back to the TA regarding the blocks and he is liaising with the company who did the SAP calcs to find out whether a medium density block will result in the target 0.18 value.

  • Like 1
Posted
1 hour ago, Tony L said:

 

I shouldn't think so, but I don't really know, because I didn't learn about ground bearing slabs before I designed my house.  I should think with a ground bearing slab, you'd have a continuous platform of insulation to separate the top part of slab (including the bit the walls are built off) from the bit that's in contact with the ground.

 

In my case, I have concrete foundations with trench blocks, & the trench blocks support a beam & block structure, so my inner masonry leaf would have a direct connection to the ground, through low R-value materials, were it not for the Marmox blocks.

 

Perhaps I should have left this question for somebody more knowledgeable than me to answer, but it seemed to be directed at me.

 

A ground bearing slab means the inner leaf is built directly off the foundations.

Posted
On 19/02/2026 at 21:42, flanagaj said:

Now I'm beginning to understand why the original architects wanted 10k and this guy only charged 2k

Watch this like a hawk. You TA is probably in a loss position. 

 

37 minutes ago, flanagaj said:

It's fine.  I've got back to the TA regarding the blocks and he is liaising with the company who did the SAP calcs to find out whether a medium density block will result in the target 0.18 value.

Double check if you have any fire protection and if any changes alter the design intent. 

 

Check if you are changing the exposure rating and make sure this is ok in terms of your detailng and wind driven rain. 

 

Go back and just have a look at what you have done so far. You have learnt a lot. Don't bury you head in the sand and hope it will be ok. If it turns out you have dropped a bollock then now is the time to address. 

  • Like 1
Posted
4 hours ago, Tony L said:

Here's my detail.

Good first go. 

 

A few comments: 

 

1/ Your cavity tray is only one course above finished ground. BC will and I will pull you up on that. 

 

2/ The insulation shown as a triangle just below the cavity tray is unbuildable as detailed . You are concentrating on the technicalities rather than balancing this with what is buildable,  the cost and how you are going to make sure that what you are paying for actually happens on site. Don't blame yourself.. as unless you do this as a day job and have a feeling of build cost there is no way of you knowing this. 

 

3/ You have a wide cavity. Why not thicken the perimeter insulation up to 100 or more thickness. Have a look at how MBC do an insulated raft slab and pinch their ideas. Then you can omit the Marmox block unless you want to spend money. You could be pragmatic and use the same money in a better way and in the round still achieve what you are looking to do. 

 

 

Posted
17 hours ago, Iceverge said:

Has anyone got examples of Dot and Dab blowerdoor tests(not gamed!)? Did anyone get below 2ACH ?

 

When it comes to passivhaus airtightness the build types I've seen to have achieved those levels are wet plaster, tapes membranes/boards in timberframe, ICF, SIPS. 

 

 

Two one offs were @Gone Wests Icynene TF and an archive building somewhere in England that used Passive purple paint. 

 

I haven't come across any dot and dab getting below 0.6ACH. 

 

 

 

 

 

 

I got 1.2 m3 hr whatever that is in ach. Masonry cavity build with dot and dab. Large coated blockwork internally

  • Like 1
Posted
9 hours ago, flanagaj said:

I am interested in this.  If you are having a ground bearing slab, is it worth running a single course of insulated block either below DPC or above DPC.

 

What benefits does this provide?

I understand its pretty good to use aircrete as the thermal break and keep them dry with a dpc. Perform pretty well for lot less £

  • Like 1
Posted (edited)
14 hours ago, flanagaj said:

I am interested in this.  If you are having a ground bearing slab, is it worth running a single course of insulated block either below DPC or above DPC.

 

What benefits does this provide?

 

Ran this through a few times in THERM when doing ours.  

 

It is worth doing a layer of aircrete in line with your floor insulation. You also need to have continuous insulation outside it. They must be kept dry as they loose most of their insulative qualities otherwise . I would make sure the cavity extends at least 1 block below the Aircrete to make sure there is no water ponding there. 

 

 

 

 

This detail would perform very well and is fairly cheap. 

 

 

image.thumb.png.c68126b7614ca930013fd48f3b49c66b.png

 

We filled the whole cavity with EPS beads (ok for use below DPC) so it was a simpler detail to construct. 

 

 