This might have been asked before but speaking to a number of companies it seems they recommend a branch system with rigid ducting versus a radial with semi rigid? For those who have installed MVHR which route did you go down?

Link to comment
Share on other sites

I did a mix of both as we have a three story building. I used a mix of 160 and 125mm galvanised ducts to each floor. Then branched off using tees to semi rigid or to a manifold then semi rigid. Advantage is lower pressure losses an quieter system. Disadvantages, much more time consuming to install.

PXL_20211013_075551060.jpg

PXL_20211013_075645288.jpg

Link to comment
Share on other sites

Semi rigid 90mm via plenum box.  Ease of DIY install, but also very quiet in use and no cross talk.  Most of mine is also going through Posi rafters and there was not enough room to install rigid.

 

If doing rigid, use metal pipes only, most plastic bends the radius this too tight and you get a large pressure drop.  Blumberg may be the exception, as their bends have a larger radius.  You will also need an attenuator at each outlet to stop cross talk.

Link to comment
Share on other sites

7 hours ago, Conor said:

I did a mix of both as we have a three story building. I used a mix of 160 and 125mm galvanised ducts to each floor. Then branched off using tees to semi rigid or to a manifold then semi rigid. Advantage is lower pressure losses an quieter system. Disadvantages, much more time consuming to install.

PXL_20211013_075551060.jpg

PXL_20211013_075645288.jpg

Hi Conor, what size is your flexible duct 75mm or 90mm?

 

 

Link to comment
Share on other sites

6 hours ago, Gone West said:

I designed a branch system using rigid plastic ducting.

 

P8030031.thumb.JPG.b3ebe1021396cdf4f040ee8571e644e1.JPG

 

P8030033.thumb.JPG.0ec41bd5943b1b0974b0a3d09bee3bbf.JPG

 

How does the plastic piping interface with the metal silencers, any issues?  I'm planning on doing similar but without getting my hands on stuff it's hard to know about how interchange the plastic is with metal fittings.  Could I ask what sealant you have used on the pipe joins please?

 

Link to comment
Share on other sites

1 minute ago, crispy_wafer said:

How does the plastic piping interface with the metal silencers, any issues?  I'm planning on doing similar but without getting my hands on stuff it's hard to know about how interchange the plastic is with metal fittings.  Could I ask what sealant you have used on the pipe joins please?

It was a while ago now but IIRC the metal silencer had a rubber 'O' ring on the outside which sealed against the inside of the ducting and I don't remember any problems.  I bought all the ducting etc from i-sells. I used Titebond PU gel adhesive to to glue the ducting together.

https://www.axminstertools.com/titebond-greenchoicetm-polyurethane-construction-adhesive-311ml-952217

 

  • Thanks 1
Link to comment
Share on other sites

  • 1 month later...
On 05/02/2022 at 10:44, epsilonGreedy said:

Is pressure drop a real concern given that most MVHR owners run their system at the lowest trickle rate once past BC inspection?

I didn’t know that. Is the BCO’s flow rate / Air Change requirements excessive then?

Link to comment
Share on other sites

26 minutes ago, Rishard said:

@Gone West- not an mvhr question but, What are the bowl looking things you have your lighting cables running into in your voids? Thanks

Intumescent fire hoods for lighting. They offer some acoustic benefits also, as they are fully encapsulating the fitting, plus the acoustic insulation can go over / all around them.

Edited by Nickfromwales
Link to comment
Share on other sites

@Nickfromwales- cheers, I thought they may be something for fire safety. Is there a discussion somewhere stating pros/cons of first floor insulation for a near passive house? I’m sure I read somewhere about people leaving it out? Seems daft as like you say, acoustic insulation will be beneficial. Apologies for straying off piste of the mvhr discussion. 

Link to comment
Share on other sites

23 minutes ago, Adsibob said:

I didn’t know that. Is the BCO’s flow rate / Air Change requirements excessive then?

Your commissioning agent should set the trickle rate accordingly, but you can then set the flow rate per setting. So say factory set position 1 may be 35%, but you can then alter that to 25% for eg after sign-off. Just buy cheap humidity and CO2 monitors and check you haven't dropped to low.

Link to comment
Share on other sites

3 minutes ago, Rishard said:

@Nickfromwales- cheers, I thought they may be something for fire safety. Is there a discussion somewhere stating pros/cons of first floor insulation for a near passive house? I’m sure I read somewhere about people leaving it out? Seems daft as like you say, acoustic insulation will be beneficial. Apologies for straying off piste of the mvhr discussion. 

Digression is a popular pass-time here lol. BCO may well request acoustic attenuation between rooms and floors, so, as you say, its daft to leave it out as walking upstairs would otherwise convey a lot of unwanted noise to the lower floors.

Edited by Nickfromwales
Link to comment
Share on other sites

15 hours ago, Rishard said:

@Gone West- not an mvhr question but, What are the bowl looking things you have your lighting cables running into in your voids? Thanks

They are plain compressed glass fibre hoods, not intumescent fire hoods, that I used for all my downlighters. I used them to keep the insulation away from the lights. I bought them from TLC many years ago but they don't seem to sell them any longer. They were about 250 to 300mm diameter IIRC.