8 minutes ago, joe90 said:


why bother, just use 19kg (like I do) then swop them after BC chap is long gone (I still say he is wrong).

I don't have any 19kg cylinders.  If I have to do that I will but I would probably have to pay a hire charge on yet 2 more cylinders as last time I tried to swap cylinder sizes Calor would not play ball. So I will stick to 47kg unless it become an insurmountable issue.

Link to comment
Share on other sites

57 minutes ago, joe90 said:

I would just argue that the regs say “opening window “ yours is not (and the calor website confirms this).

I am convinced (from my previous dealings many years ago) that you could have a non opening non vented window right behind the cylinder and it would be allowed, but I cannot find anything that actually shows that.  My BC is a "show me where it says you can" kind of person where I am arguing the "show me where it says you can't"

 

So unless I can find anything showing a non opening window right behind the cylinders I am stuck.

Link to comment
Share on other sites

1 minute ago, ProDave said:

So unless I can find anything showing a non opening window right behind the cylinders I am stuck.

I think I am more stubborn than you ? I would quote the Calor site to him about sealed openings which is what you have, if you contact Calor they may even confirm it in an Email fir you???

Link to comment
Share on other sites

2 minutes ago, joe90 said:

I think I am more stubborn than you ? I would quote the Calor site to him about sealed openings which is what you have, if you contact Calor they may even confirm it in an Email fir you???

Did I miss a bit?  I only see reference to "opening windows" in the calor document, is there a reference to "non opening" or "sealed" windows that I missed?

Link to comment
Share on other sites

3 minutes ago, Russell griffiths said:

I was going to say exactly the same, get a smaller cylinder. 

Yes but I can feel the blood pressure rising as I bang my head against a brick wall talking to a stubborn BCO.  It just adds to the "after completion" list.......

Link to comment
Share on other sites

58 minutes ago, epsilonGreedy said:

On a related point, do the LPG bottle regs allow a bottle and ASHP to be collocated at an outside wall?


I hope so, mine is ?. Don’t see why not, no mention of electrical devices on the regs above (and my BCO didn’t raise an eyebrow).

  • Like 1
Link to comment
Share on other sites

This page https://www.calor.co.uk/home-energy/new-to-lpg/my-options/lpg-installation-options?tabname=lpg-cylinders

 

Makes reference to the distance sideways to windows, air bricks etc being measured from a "gas bottle valve" not the edge of a cylinder.

 

Now if only I could find a reference to the vertical distance to a window being measured from the valve rather than the drawings implying the top of the cylinder handle?

Link to comment
Share on other sites

Diagram 44 Page 67 of part j shows that the opening part must be 300mm vertically or 1m horizontally AND shows that a non opening part of the window can be nearer.

 

 

Edited by Temp
  • Like 2
  • Thanks 1
Link to comment
Share on other sites

Dave. 
We’ve put flues through baffled sections of non opening windows before, blanking them with non-combustible material and intumescent mastic type seal to complete the picture. 
The reason they don’t show a non-opening window is because they don’t care about a non-opening window. Carry on with the 47’s and tell your BCO to suck it. 

  • Like 2
Link to comment
Share on other sites

10 hours ago, Temp said:

Diagram 44 Page 67 of part j shows that the opening part must be 300mm vertically or 1m horizontally AND shows that a non opening part of the window can be nearer.

 

 

Perfect

 

20473417_Screenshot_2020-12-04ADJ_LOCKEDpdf.png.739c55c175b1d00e64c6e867cbb498e8.png

 

Not only does it show a non opening window, it also males it clear the distances are measured from the gas valve on the cylinder, not the top of the handle.  So I suspect I would be okay even if my windows opened.

 

So I will proceed on that basis that I now have a pretty picture to show BC when they object and grounds to argue it.

  • Thanks 1
Link to comment
Share on other sites

  • 3 months later...

Starting this back up. 

I have a couple of issues raised this morning when the gas man turned up to look at sticking in my lpg pipework. 

 

The first one is the distance vertically to a combustible material, my house is a bungalow and he was concerned about the height from the top of cylinders to the soffit and facia board, my soffit is timber, I cannot find any drawings that say anything about the actual fabric of the building is more about openings. 

 

Please see pic. 

Any thoughts @ProDaveA0978614-D25B-4C57-9129-6DCDA204961E.thumb.jpeg.f25990c0113caab8d063d9bd927ab123.jpeg  