On 03/05/2026 at 15:54, JohnMo said:

Had my cooling on this year already, one fan coil and UFH, flow rate 14.5 to 15 degs, zero condensation from fan coil

To be fair, last week with the easterly flow DPs were very low across the board despite the solar warmth.

 

I have just bought a bunch of computer case fans and and going to see how they work with our double rads and flow temp controlled to be above dew point; we will probably run the dehumidifiers in the summer when we have excess PV so minimal cost which should also help with this issue - at the expense of some additonal heat input from the dehumidifiers.

Posted
On 03/05/2026 at 14:55, LiamJones said:

@Dave Jones have you ran condensation drains to your FCUs if you’re running above dew point? If you have, do you think you needed to? I ran flow/return to upstairs bedrooms in case we needed heating upstairs. turns out it’s more of a case of needing cooling up there but I didn’t run drains to them. What do you think? 

 

no, i dont want the loop to be less than 15c to avoid dewpoint on the slab.

  • Thanks 1
  • 2 weeks later...
Posted

WE are running our flow at 16 (checking dew point to avoid condensation) and have some cooling.  We have mounted 8 PC fans under one rad as a proof of concept and it helps creating a small local cool zone, they are silent but we could actually do with considerably more airflow, may try a higher voltage power supply. Currently they are fixed using mini magnets but not that secure so may try mounting them using plastic trim strips.  Heat pump is drawing about 1/3 minimum input on an hourly basis and cycling frequently showing we are basically failing to extract nearly as much heat via the rads as the unit is capable of even at minimum modulation.  Inside air temp is 26C compared to 35C outside but no idea what it would be without the cooling.

Posted

I would tweek it down 0.5 degs at a time, leave for a while and check for condensation. You should be comfortable taking it down a couple of degrees. The lower running temp to will promote more heat uptake and a higher demand, so less cycling. It's a balancing act, so some trial error I am afraid.

Posted
22 minutes ago, JohnMo said:

I would tweek it down 0.5 degs at a time, leave for a while and check for condensation. You should be comfortable taking it down a couple of degrees. The lower running temp to will promote more heat uptake and a higher demand, so less cycling. It's a balancing act, so some trial error I am afraid.

All the rads are ok except the bathroom that is sweating a little, I guess we could just turn that one off?