Everything posted by JohnMo
Pump speed is just a tool to get your required flow rate. Speed is adjusted to over the system resistance, if you have the flow rates you want and speed is to high you are just wasting electric. Nothing to do heat transfer, except providing the motive force to move the water at your set flow rate Temp, on its own isn't the whole story, it's the combined outcome of flow temp and return temp, so the mean flow temp that sets the kW output. Flow rate alters the mean flow temp. You also have floor covering u value to add to the mix. The more resistant the higher the mean temp needs to be for a give kW output.
Solar, MVHR and ASHP
JohnMo replied to Risemead's topic in Energy Efficient & Sustainable Design Concepts
I would be addressing your insulation values if you need that much power to heat your house. Whatever PV you install will give an abundance of electric April to September and then next to nothing when you need the most. Mid winter you can goes days with zero output. Also you really need to see, what lots of solar will cost you (payment to DNO) and if they actually let you. Your best bet is G99 route to approval, which limits export below 16A. You will need to ask for permission prior to install/ switching on. If you are connected to the grid permission is mandatory irrespective of your intension to export or otherwise. Same can also be true for your battery depending on how it hooked up. -
As @jack says without heat loss calculations you are just shooting in the dark. I am installing a 6kW heat pump and it will heat our house 192m2 and a summer house, 16m2. I expect it to be using around 50-60% of its capacity even on the coldest day. Sounds good, but doesn't really mean anything as far of how much your house is expected to require in terms of heating. There is a calculation spreadsheet in boffins corner on buildhub
Last year I had lots of zone on at differing times, this year I have all zones on if any zone is on and I am using 25% less mostly, in some months 40% less gas. The issue with just one zone on is the boiler cannot get rid of the heat quickly enough, so stop starts runs for a very short period and does this quite a lot. So efficiency drops of a cliff. I tried lots of things a monitored gas consumption and the weather to build a trend so I could understand what worked best.
Dealing with condensation…
JohnMo replied to HughF's topic in Mechanical Ventilation with Heat Recovery (MVHR)
Atamate_SDAR+Paper+2019+(1).pdf -
Think you have answered your own cause. Best two fixes are PIV or MEV. PIV, one central unit in loft or elsewhere, one supply outlet. MEV, centralised extract unit taking air from all wet rooms, can get them so they only when required and close down or open extract points as needed. PIV is either on or off, MEV, ventilation only as required, if specified correctly. You can retrofit trickle vents, or vents in the walls of dry rooms, but get them so they auto open and close based on humidity. MVHR without airtightness is a waste of money. -
Complying with condition of Planning re: Fencing mature trees
JohnMo replied to MarkW1979's topic in Planning Permission
I went to a great deal of trouble to fence everything off, in the end no-one seemed to be that bothered. Whether its a case that they see your trying to do the right thing and playing the game. Our architect out together a statement (cut and paste from something he found on the internet) on what we going to be doing, to what BS standard, I cut some words out that were not practical and it went through fine. Basically ours was 4" posted, wired, and orange mesh about a 1m high, with signs from Screwfix say keep out. -
Not sure I agree. A house on an open flowing weather compensation system is simple. No actuators, no thermostats, you don't need mixers (in many cases) and in most situations a single pump is used, with the boiler or HP modulating its speed. You can calculate the heating slope etc, so limited faffing getting things correct. There is a study linked to on here, were 3 situations were tested. Heat pump via buffer, buffer control by on/off thermostat - CoP 2.7. Test 2 Buffer with HP on weather compensation, CoP around 3.5. No buffer, open system HP on WC, CoP around 4.2. All tested at 7 degC outside temp and same simulated building loads. So has the UK had WC, but we are too daft to use it. Plumbers install a boiler on Y plan and flow central heating at the same flow temp as a cylinder. Then on UFH mix the flow temp down. We stuff our houses full of on/off thermostats, run a boiler or heat pump way to hot and then wonder why we have gas boilers that run at 80% efficiency, when they are capable and designed to give 110% efficiency. And ASHP that give a CoP of 3 (if your lucky) when they should be getting over 4-5.
It's not an easy one as two identical houses, will have differing heating needs depending on what the owners feel is right. You may be happy with 19 degrees, the next person not happy unless it's 22. This gives a different curve and different heating profile. Mixing in load compensation with WC is fine in concept, but with low temp UFH leads to over and undershooting, the system response is out with the controller parameters.
Correct heat pump sizing for passivhaus
JohnMo replied to markharro's topic in Air Source Heat Pumps (ASHP)
Before saying you need xxkW, you need to look at the various performance tables of different heat pumps, as one 3 kW heat isn't he same as another, they give different rating to suit what they want to sell. Main issue isn't really the size anything up to about 6kW should be ok. Main issue will be have a design that doesn't require a buffer for the shoulder season, so engaged always open system water capacity is important, roughly 40L. That will allow the HP to run without short cycling and for defrost. If you can get your head around a single zone heating system, that where you need to heading, simple weather compensation your install can be very simple. -
Sorry no photos You will have timber strapping on the wall. Prior to install of cladding, basically close the gaps at the bottom with mesh. So once the cladding is in place there are no gaps.
Good representation of what I was trying to say. Short and fat a good place to dilute supply water with return water. Result hot water from HP going in and warm water going out. With a 4 port there should be no need to have the two pump flow rate matched. They are hydraulicaly seperates, so basically two systems meeting at the buffer. Look at a three port also.
To add a volumiser needs one open loop/radiator downstream of it
A 4 port in normal operation, all water goes in to and out of a buffer. A 2 port only the excess water flows through the buffer. The buffer is always open to the flow and return. If everything is closed downstream of the 2 port buffer all water flows through the buffer. Just the same as a 2 port. A 4 port hydraulic sepereration across buffer a 2 port no hydraulic sepereration. That's the main difference, plus less mixing. So in defrost the heat pump would just pull on your buffer volume in either case. A volumiser either sits in the flow or return circuit only. Does not give hydraulic sepereration. But in defrost the HP can use the stored volume