JohnMo
    200
Everything posted by JohnMo
  1. There are two ways to do UFH, loads of insulation or no insulation at all - the middle ground between the two means high running costs. Both systems work using different mechanisms. Loads of insulation stops downward heat losses, as the downwards heat flow breaches the insulation it never come back, as heat will allow try to move towards cold and the ground will always be cooler than a heated floor, so you want really good insulation. You can run intermittently if you need to. No insulation uses the the ground as a buffer for heat, the zero insulation allow what goes down to come back up. However you just let the heating tick away all heat season. If you switch off the heat is dispersed and you need to rebuffer it all again.
  2. I found the same, but it did a week ago.
  3. Something like this
  4. Sounds like you are making it up as you go. Get a free trial of Loopcad and design it so each room is balanced correctly before you start. Sorry 100mm centres and 17mm pipe and then running your boiler at 50+, to then mix the flow temperature down to supply UFH makes zero sense. Really isn't suitable for UFH. Your downwards heat losses are going to big.
  5. Is a normal way plumbers install boilers with hot water cylinder and it's the least efficient, so everything is run at a set flow temperature. They use either two normal closed valve or a mid point valve. Priority domestic hot water, uses a diverter valve and runs a higher temperature with DHW and with a decent boiler can then run weather compensation for the UFH without mixing valve. Effect of flow temp on efficiency
  6. So assume you are actually going to make the most of condensing mode for the boiler to get very low flow temperature for the underfloor heating and run a second set point for DHW heating - so no S or Y plan?
  7. MVHR isn't really worth the effort and cost at that airtightness. It will just add to the natural ventilation and increase actual heat losses
  8. Suspect nothing fancy, so just pine.
  9. First let's step back a little Airtightness, what airtightness measures will you have in place, are you aiming at better than 3m³/m² at 50Pa airtightness? If not don't waste your money on MVHR. So let's assume you are going airtight Zehnder is(n't?) the only make, Titan make good basic units, plus many others. eBay can save to loads of money. Basics are MVHR to plenum/manifold, semi flexible duct, room terminal via a 125mm to flex duct adapter housing. You can get smart with through flow, instead of direct flow into rooms depending on house layout. Also known as cascade. Second if not going airtight, do demand activated MEV or dMEV. Fan units run at higher loads when needed and low when not. Silent in operations. Add to this humidity activated trickle vents in all dry rooms. Works at very low base flow, as you generate humidity the system will react. Very little additional ventilation heat loss. Easy to install and pretty cheap, no filters to change out (can get pretty expensive) half the running costs as only extract.
  10. Just need to made a little more straight and tidy. Not sure what you did with your lead work than needs putting back where it should be. Maybe add a hopper or similar at the corner and then feed down and across to the other gutter and down pipe.
  11. Yep. A hammer would knock that apart, technical term is pigeon sh!t. Deffo need your structural engineer to visit - be prepared to sack your current builder, I doubt they have the skills to put things right, even when pointed in the correct direction.
  12. Stainless ring grooved nails. Make sure insects can not get in as well as mice etc. Any gaps at corners joints between panels mean wasps can nest. 1. and 2. We just used 50mm battens, easy, no splitting if nailing near ends. Easy to get and cheap as chips. Nails for cladding have plenty of wood to get a grip in 3. We did two nails at each batten. Using standard nail gun. Mainly to limit wood from moving, any warping etc. 4. Whatever looks correct.
  13. Have you not answered your own question - if the controller thinks there is a thermostat it is seeing open connection somewhere. So there must be connection for external thermostat? To get the system to work those terminals need to see continuity, so need a short across the two terminals. Or system needs to be configured within the controller not to look for an external thermostat.
  14. Either your structural engineer, you must have one?, or the structural engineer of the posi joist supplier/manufacturer should be supplying full set of drawings with all supporting calcs, These should be reviewed and approved by your structural engineer. What I like about the Scottish system, is you cannot get to this point, no structural design drawings, no building warrant, no warrant, no build.
  15. Have no rads and no zone valves. You can run circulation pump (within ASHP) in several modes, continuous, when ASHP compressor runs, and in a mode called sniffer mode (pump runs a couple of minutes every so often or when compressor is on). So circulation is controlled by ASHP. Heating is never off, unless in cooling mode, cooling is never off unless in heating mode. As described in my initial reply, I have a 3 port valve in the system and that's it.
  16. Pretty much. Floor surface temp is approx 2 degs hotter than room temp, sometimes way less. So solar gain increases room temp. The closer the room and floor temp get the less energy the floor adds to room. Once at same temp floor no longer adds energy to room. Cooler rooms will continue to take energy from floor. Different story altogether, you have controls. As mentioned there is nothing related to ASHP except flow and return pipes in the house - it doesn't know directly the house temp - but does indirectly via return temp. Just using a WC curve. Cooling is basically a single set point but heat pump just modulates or switch the compressor off as needed.
  17. How does that work then?
  18. This is true, we are now programmed to think a heating systems must have thermostats and time switches, to work. But if make that step and actually leave the heat source manage this for us, it seems to work and does it pretty well. Our heat pump has zero interactions with the house except the flow and return pipes. It's a bit of a leap if faith mentally at first. Even hot (solar gain) and cold sides of house even themselves out pretty much with no input especially when you have UFH.
  19. I have zero thermostats. None. Some of my rooms have sensors, but they are just there so I can see what's going on easily, they are not connected to anything for control.
  20. Do you have twin stud walls? If no do you need a Tony tray? If on hangers do you need to something else
  21. We are the same @Kelvin, French doors. Wind is an issue. We have restrictions built in to doors to stop it going past 90 degs open, but is utter rubbish. Now have a hook and eye to keep door open at 90 degs.
  22. You can also use an adjustable pipe cutter, this gives a nice straight score on the wires to then be snapped off - works better with larger cables (6mm² and above), not so good on small ones as they are too squishy.
  23. I'm with your other half on this issue. We have cat5 points in all rooms, socket next to aerial, they go to simple 8 way switch unit, cost £18. Not sure what the complications add.
  24. Are mixing the term zones with loops? My house started with 6 zones (7 UFH loops). First two months gas bill was equal to the calculated annual bill. Low energy demand heating systems and zones are a plaque. Avoid, don't even say the name zone. Now run a single zone, no actuators, no valves, no pumps, no mixers, no buffers, no thermostat heat pump does it's own thing, expect a SCoP of mid to high 4s. You really don't need a sketch Flow side - ASHP to 3 port diverter, one side direct to UFH manifold and other to cylinder coil. Return - UFH manifold to tee, other side of tee to cylinder coil, then to ASHP, via a strainer. Need to add expansion vessel and pressure relief near ASHP and a filling loop. UFH manifold and loop balance - open all flow meters fully. If the odd room is hot trim flow to that loop only, system is balanced.