TerryE
Everything posted by TerryE
Willis heater ASHP backup discussion
TerryE replied to Nickfromwales's topic in Air Source Heat Pumps (ASHP)
@Gav_P, yes, at the moment we only use the Willis. We have prepared for adding an ASHP, but it will only be value for money if I self-fit a budget one. As Jeremy says I am looking at a budget of around £2K, with a payback of ~3 years. But that assumes that I will be doing my own maintenance, and not paying a third party. -
I have mine mounted vertically across my UFH manifolds. By the time that we are down to a sustained external temp of 0°C we need about 8hrs a day to keep our largish 4 bedroom house toastie. (Each deg C drop adds about 40 mins on-time to keep the house in balance). I will be fitting an ASHP next summer because the numbers work and it will be good for peak summer cooling, but the Willis will remain an essential backup component. Why? Because the ASHP won't be a mission critical component in our heating system, so I can take a far more relaxed attitude to maintenance / spairs, etc. At the moment, my Node RED system does a daily calc using the weather forecast, slab temperature profile, etc. to work out the heating profile for the next day - typically a solid block overnight during cheap rate and and extra top-up late afternoon if the weather gets cold. No other feedback. Dear simple. Good enough to keep the house temp better than ±½°C which is good enough for me. -
As far as the external power bus goes, my current thinking is to use something like 20awg multistrand twin. Tuofeng do a decent cable that gets 4½+ ? reviews. This has a resistance of 1 ohm / 30m, which gives an acceptable diversity for the size of my garden. This will get enough power to any of my external projects, including monitoring my supply meter.
5V is a bit marginal unless you go for heavy duty cabling. 60W of devices will require 12A and remember that at a PD of 5V, the diversity will become a big issue. IMO, better to use 12 or 24V and per-device Buck step-down DC-DC convertors (which cost pin money) to drop the voltage to 5 or 3.3V as required.
I think that we've split the discussion in to to separate usecases: The ability to collect periodic aggregate power usage - say every half hour -- mainly so you can automatically monitor and plan your ToD usage and overall power billing. The ability to collect fine grain usage so you can get a perspective on individual device usage. Jeremy's solution is very elegant but is also invasive in that it involves intervention in the primary power circuit, and this is something that I would prefer to avoid which is why I tend towards pulse counting as this still gives me 0.001kWh granularity. In my view, the whole issue of designing power constrained devices is interesting. A typical gaming PC will draw perhaps 300W, a modern laptop with SSD perhaps 20-50W depending on the processor, a RPi about 10W. A pair of NiH battery might has ~ 5000mAh capacity and if you want the batteries to last 3 months, say then the average draw of your device must be around 1.5mA. Whilst ultra-low power devices do exist, many active components have non-trivial draws. For example the PCF8593 has a typical draw of 300mA; the LM393 200mA; the light sensor diode 100mA, so the only way that you can run an device for months on a battery is to do a repeat of <sleep a long time at 10s of μA> then <wake up for a short time and do some measurements>. So IMO, battery powered devices are limited to a small number of periodic monitoring applications. But it is pretty straightforward designing IoT devices with a ~1W power draw. This is why I am currently thinking of stringing a 12V supply around my house exterior and garden to power my devices as needed.
ED, TerryE is also one the core developers of the NodeMCU Lua firmware for the ESP8266 / ESP32, so I am also a very useful resource to know when it comes to programming ESPs and this is also why I prefer to use them over Atmel or RPI0 devices for IoT applications Deep sleep on both the ESP8266 and the ESP32 powers down everything apart from the RTC and a small RAM scratch pad in it. Wake from Deep Sleep is effectively a cold boot, except for any context saved in the RTC RAM and in the Flash SPIFFS. The power draw here is ~20μA. I have yet to check whether pulses are at 0.001 or 0.01 kWh but if they are at the former then a power draw of 30kW through the meter (which is entirely possible at peak) will result in 30,000 pulses per hour, or one every 120mSec or so, and a more typical average busy draw of 3kW will still be waking the ESP every sec or so I need to benchmark how quickly the ESP comes out of deep sleep, but this will be tight and still have high peak draws if it powers the Wifi modem. Perhaps a better alternative here is the light sleep option which draws about 1mA and this keeps the CPU registers and RAM powered but shuts everything else down. GPIO events will trigger wakeup from from light sleep and wakeup here takes under 5 mSec. The big advantage of using a separate chip to do the counting is that you only need to wake up from time to time -- say once every 30mins, interrogate the counter and go to sleep again. @MikeSharp01 Looking at the DS1371 datasheet, it doesn't look as if it can be programmed in the mode that I want. It seems to be driven off the mast Xtal and the counter provides a watchdog function, viz it triggers an event after a preprogrammed number of ticks. Of course there is always the fallback option of using an ATTiny85 to do the event counting, which is even cheaper to implement and will bring the overall power into the battery domain, but this is going to involve getting into Arduino development -- ho hum.
I use my electricity consumption actuals the help optimize my usage. I currently have an OVO account with a Smart Meter, and OVO provides decent online reporting of usage by 30min reporting period. A little bit of retro-engineering of their undocumented AJAX API gave me a daily batch script that run downloads these data into my HA MySQL DB (see this OVO Post for more details if you are interested). Unfortunately my fixed rate contract is coming to an end and I am now looking at OVO's over 30% price hike -- ouch -- so it's time to move supplier again, and this time I plan to switch to Bulb which is about 20% cheaper than OVO. The downside is that they are slow in rolling out smart metering, so I am going to lose my ½-hourly rate feed for the foreseeable future. Damn! What to do? So I am planning to implement a meter pulse counter. All modern electrical meters use a LED to flash at either 0.01 or 0.001 kWh unit intervals. (Actually most smart meters measure kVAh not kWh, though in our case nearly all of our load is resistive so the two are pretty close, but that's another story). So how? The key component here is an LM393 Light Sensor Module, which cost £2-5 on eBay. the LM393 is an analogue comparator and this little module has a trim-pot on it so you can set the analogue output threshold on the diode output to convert it into a clean digital signal for input into a GPIO input. The next thing is a WiFi enabled micro to do the pulse collection and reporting, such as an ESP8266, ESP32 or RPi0B. in my case this will be an ESP8266. The micro can either count the pulses directly or you can stick a counter in the way. I good choice here is the PCF8593P. This is primarily used as an RTC, but it also has an event counter mode which accumulates pulse falling edges in an internal BCD counter that is accessible to the micro via I2C. Hence the micro can deep sleep for 30 mins; wake up and read the event count, connect to the Wifi and report the count to my HA RPi3 and go back to sleep again. Don't use a Maxim DS1682 as some articles suggest as this powers up and load the count from EEPROM on the rising edge, then stores the new count back in EEPROM on the falling edge, and this read/store is done every event. This make the device ultra low power and really good for applications such as measuring uptime and up events for devices such as vending machine, but the EEPROM only has a nominal 50K write cycles. Do the math: for this application, the DS1682 will only last a few days before the EEPROM fails. The ½hr cycle for the ESP8266 makes it very low power, but the kicker is that the PCF8593P has a nominal power rating of 30mA, so the circuit has just too much base draw for battery power -- a couple of NiMH batteries with a capacity of 5000mAh will last about a week. ? So I will need to feed power into my external meter box to run the data collector. Bugger. It looks as if I am going to have to bring forward my plan to have a 12 or 24V 5A power bus for all of my garden and yard projects. 60W peak should be quite enough for most if not all of of my planned projects, and 12V is nice to work with thanks to availability of very low price and efficient Buck step-down DC-DC convertors; it is also safe enough to run around the garden with minimal or no safety protection. Comments and advice gratefully accepted.
IIRC we just rang up http://www.kytun.com/page/contact-us/18. We used one of their std slate edge profiles but we got the soffits, etc custom folded. They do std widths which they can fold as you specify. It was only about 10% more if I recall.
I used Kytun soffits and slate edges as well. Zero maintenance. Looks good. My slater thought it was a brilliant system. So it has my recommendation as well.
Where? Hopefully you unpacked it and stored it properly to acclimatise with the house environment. As to assembly, the most important thing is to make sure that you understand the assembly process start to finish before you begin, both in terms of the staircase flights and how you will fix them into position. There are lots of useful step-by-step guides and YouTube videos. so watch them through and dry rehearse it all before you start -- especially if you are doing upper storey fittings. I just googled tk stairs installation instructions and got a lot of hits. Make sure that you have the fixings and tools to hand and in position before you start. Validate dimensions carefully before you assemble anything: for example if your staircase is 5mm too wide for the plaster to plaster surface then it is a lot easier to use a table saw to remove the excess off the stairs and risers before you assemble than to start pulling plasterboard off the walls. You also need to think about how you will safely lift and position the flights whilst you fit them, because the last thing you want is an "oh shit" moment with a bloody heavy staircase over your head that is dangling unsafely. Also if you are painting the stairs or the stringers you might think of applying the base and primer coats before you fit the staircases and this is a lot easier to do when the stairs are sat on a couple of saw horses.
- 1 reply
There was nothing in the installation instructions for ours, and in fact the unit is in a sheet steel carrier. We've never had any issues with this configuration and our electrician (who wired it up) didn't raise any issues at the time. IIRC, in terms of the physics, you need fero-magnetic medium which will generate local eddy currents and the local resistance then draws a lot of localised power (= local heating) within the medium. You really need something like cast iron or a steel+copper/aluminium laminate structure to produce decent eddying. BTW, steel is fero-magnetic. What I will do is to take the temperature of the cutlery (about 15cm) under a heating pan to see if there is any noticeable warming and report back
The other thing that I really like about the induction hob is that the energy is converted into heat in the pan itself, and hence the thermal spill below is minimal and managed by a small fan internal to the low profile unit. This low profile means that we have a 900mm draw unit directly under the 4+2 hob set up, with a large 900 cutlery draw and two pretty deep utensil and pan drawers directly under the unit. Ergonomically, this is brilliant.
Well I do have a couple of rings fed from an external propane cylinder as backup. (Complete with the GS cert for the installation). We did use them a coupe of times before Jan decided that she far prefers the immediacy and cleanliness of the 4 ring induction hob. Ditto me. We have turned it off at the bottle as we never use them. IMO, there's little point in installing a gas supply in a passive house because you can't really avoid installing an electric supply and the marginal installation costs / daily connection charge / annual maintenance are far higher than any delta in using electricity, even without PV but especially with.
Jason, I feel that both you and @pdf27 have similar concerns, and ones that I can only partially answer. This is almost as a consequence of policy / strategy on my part, and of "walking on the shoulders of giants". I saw that Jeremy's thoughts evolved in the course of his experience of controlling his own house system and he's rejigged his system 3 times and may do so again when he and his wife are in continuous occupation. So I decided to adopt a lazy and evidence-based approach, that is rather than develop and implement a complex fully featured system only to have to rework it later. Jan and I decide to do this in a number of phases so that each was "good enough for now", and then only implement subsequent phases once we had the experience, data and understanding to do so. IMO, there isn't a good rule book that we can use for this class of house design. Phase zero was to do appropriate design validation and modelling to ensure that the house as system had suitable macro characteristics for use to control and keep it within a comfortable living range. This convinced me that a simple Willis-heated UFH system would be capable of maintaining the house over the winter period, but that there was a question over whether we could cool the house enough over peak summer. Ditto using the 2×SunAmp for DHW. Phase 1 was using the Willis heater, circulation pump and 2×SunAmps controlled by a NodeRED instance on an RPi with a simple ON1/OFF1 ON2/OFF2 scheduler and a dozen DS18B20s collecting sensor data every 2 minutes (for 10 months now). I adjusted the ON and OFF times manually based on average outside temperature as required which was maybe a couple of times a week. We can't have PV so optimising this around a cheap E7 tariff just seemed economic sense. This experience and the data showed us that our house worked and performed within an acceptable tolerance of our design predictions. The summer heat wave has underlined that we do need an ASHP -- something that wouldn't really have been cost justified based on our data purely for the winter heating problem. However this is still desirable rather than essential. Unfortunately, I want to place it against the side of a new summer house style shed that we will be building maybe next summer as part of landscaping our rear garden. I don't want to have to move it, so we can't install it until after these rear ground works are completed. If we have to delay it another year then this isn't really a big concern for us. Also unlike a conventional central heating boiler, the ASHP isn't a critical system (as we can heat the house happily albeit more expensively with the Willis) so I can take a more cost aggressive view on its purchase and maintenance. So Phase 2 is to add autonomous control, and I will do this in the next month or so. This is a software only exercise adding a some extra nodeRED / Javascript modules; the interface is tablet / phone friendly browser-based, so just like my chromecast, Jan or I can configure the system through one of the various Android devices that we carry or have to hand. From our experience last winter, I am confident that a two period heating regime will give us a good level of control; that is where the OFF1 and OFF2 times are fixed and the ON1 and ON2 are set based on a daily adaptive calculation of T1 and T2 from three input: the daily average internal temp, the maximum internal ripple, and the average external temperature. We will always have a T1 and T2 to calculate, but sometimes their value will be 0. Incidentally some have expressed concerns about the "what if I drop down dead" scenario doing this sort of approach, but I have a son and son-in-law who both work in IT and are already dabbling with this technology themselves. I am sure that they can take over maintenance if needed. Phase 3 will be the addition of the ASHP and its integration into the heating system. My current thinking is that I will treat this very much the same as the Willis in terms of house control. I will set it to a specific fairly low output by setting the output temperature from the ASHP so that it gives say ~2kW and have a fixed number (say 3×) ON/OFF scheduling cycle, with the T1,T2,T3 set to produce a good thermal balance and acceptable ripple. The reason that I can do this is that the ASHP circuit is coupled to the slab UFH circuit through a plate heat exchanger (PHE). On the UFH side I know what the circuit flow rates are (as I calibrate these from the ΔT from the 3kW Willis element); I can measure / integrate the corresponding ΔT in and out of the PHE to compute the actual heat input from the ASHP into the slab; that is I am treating the ASHP as a black box heat source / sink. These total heat figures will plug into essentially the same control algo as for phase 2. At a tuning level, I can experiment with numbers of heating cycles / ASHP settings, on a day-to-days to find a good set to use, but I won't attempt to use these actively in house control. As I said previously we minor solar gains in winter in our house, so unlike Jason I don't have to adjust for this in my control system.
I heat from 00:00 to 07:00 (or bring the start time back if this is too much). This means that the slab is nice and warm under foot when we are pottering around at breakfast. The GFL room temperatures peak at around 11am and then fail by about ½°C by about 3pm, though we don't really notice this as we tend to be quite active in the house. If we need a top-up we do this from around 2:30 to 4:30 typically so the temperatures again peaks around 7pm and the house is at a comfortable temperature whilst we are sitting around in the evening. So this cycle is 21 kWh at cheap rate and 6kWh at peak rate, and the overall ripple is a little over ½°C. If the low point is uncomfortable then the easiest thing to do is to raise the overall temp another °C or so and keep the same profile. Sorry but this is wrong in my experience -- the main area of our slab is 10cm with the UFH at 5cm deep and pumping in 3kW on a top-hat profile still has quite a delay before enough heat reaches the slab surface to start raising a material amount -- probably about 3-4 hours, and that only starts the heating in the room which is why the peak room temp occurs some hours after the heating has stopped. OK, if you have a 5cm screed with the UFH embedded then the slab will be more responsive, but MBC-style construction were the UFH is fixed to the rebar mesh before poor has long time constants, so you either need to adopt Jeremy's very low (but largely constant) temperature with a simple area stat or my daily computed total and a fixed heating plan.
You are really losing me in this argument. If you mean design freedom then perhaps I can understand more. There is only a control (as in control system) issue if this type of arrangement is acts to constrain the control regime. In our case at the dead of winter we only need to maintain the floor at an average ~2°C warmer than the target environment temperature to maintain overall heat balance. We could easily heat the floor to 4 or even 6°C above room temp with our pretty standard UFH layout in terms of heat output (if we wanted to live in a dry sauna), so this design constrains nothing. All of the control parameters are still tunable: the heat input into each circuit, the flow speed, the min/max ontime, the on spacing. The control algo i about 100 lines of javascript. This is the easy bit. The main PITA in nodeRED is implementing a simple control panel. And BTW, you don't need to have any weather forecast terms in the control. We have a stone skin; this plus the cellulose-filled Larson strut frame give one averall decrement delay of well over a day, so we can just plug in actuals.
Not true. The whole point is that you reformulate the heatflow equation in radial form so that you work in (r,x,t) space instead of (x,y,z,t) space. The package will still form a mess over (r,x), but because dropped one of the curved dimensions, the effect is to drop the computation load a couple of orders of magnitude. Not really; just stick with the normal design guidelines which will be either 100mm or 150mm centres. What you do need to get right is the number of loops (you don't control them separate so they aren't really zones). But again here most people stick to just under 100mm since the UFH pipe comes on rolls which are a multiple of 100m and doing anything else creates wastage as you really don't want to have any joins in the concrete. You do get a pretty strong temperature gradient along the pipe which is why IMO you should always do a loopback layout so that the hot and cooler runs alternate but still give an overall uniform heating effect. One for @JSHarris to comment on really, but this will vary from heat pump to heat pump. AFAIK, what they control is the output water temperature which nothing to do with the environmental control. Perhaps the main difference between Jeremy and me is that he has gone the off-the-shelf approach and I do all my control in nodeRED on an RPi, so he is constrained by different implementation strategies. The time constants are on different timescales and the mechanisms sufficiently decoupled that the systems don't "fight". It's all pretty stable.
Any sofa supplier recommendation?
TerryE replied to TerryE's topic in General Self Build & DIY Discussion
Yes, we had one in our old farmhouse. They are cheap and value for money. Good for a teenager's room, rental accom, or anywhere if you are really constrained on budget, IMO. We used the sofa in our old living room and it served its purpose, so no complaints, but to be honest we found that it just wasn't that comfortable to sit on -- which is partially why we went to the other extreme in the new house. -
Voluntary Registration of property
TerryE replied to Piers's topic in Party Wall & Property Legal Issues
We split our plot to build our new property and since we bought it 15 yrs before registry was required in South Northants, we had to register it at the same time. This was when we discovered that one of our neighbours (or at least her nephew who arranged the sale of her property) had included a path that belonged to our property in her cottage's LRO registration (but never told us) 15 years previously. It didn't matter that the path was explicitly detailed in the original 1913 deed of sale as part of its hereditaments, the LRO took the position that the original registration took precedence unless varied by agreement or court order. What a costly and time-consuming PITA that was to sort, though in the end we decided that bribing the neighbour with an "inconvenience payment" to cooperate and sign the TP1, also having "no registered boundary disputes" was going to be cheaper and easier than the adversarial route. Also one side of our property was shared with another three neighbours and when we planted a laurel hedge 30 years ago, the shared fence posts were on a taught-line. 26 years later we looked at the recorded boundary and it was all over the place (and a couple of neighbours have moved they fenceline behind the cover of the hedge). Again in practice, he who registers first defines the boundary. So my advice is do register your property as soon as practical, and be prepared to discover issues when you do so -- ones that might take time and effort to resolve. You don't want to do this when you are working to a deadline. Because of all of the complications, this cost us about £2K in legal fees in the end and IMO our solicitor was incompetent. (E.g. they handn't bothered to read the 1913 deed of sale and it took me 5 mins to find the relevant paragraph -- after it was all settled and the handed over the old deeds). -
Well maybe not conceal, but a fairly mute in wall plate comparable to an MHVR venturi. How about something like http://www.justfans.co.uk/catalogues/silent.pdf. I am sure if you shop around, then you should be able to find something with a better acoustic spec.
How about an in-wall 200mm vent between the snug and the hall? You can get "silent" fans (e.g. ~25-30dB) which can shift maybe 2m³/min which will be enough to stop the room overheating.
In my old house, you closed doors to keep the "coziness" in and the cold drafts out. In my new house, we rarely close doors because the rooms can overheat when containing a high body count, and start to feel a little stuffy. (You get so used to the "fresh air" feeling of an MVHR house that it is noticeable if the warm breathing body count exceeds the planned airflow and so the CO2 count starts to rise even slightly.) So we often compromise and leave them ajar. The one mistake that we did make was the positioning of our bedroom MVHR inlet, which is diametrically opposite the door into the hall. The issue here is that we have an ensuite which has its own extract effectively on the oppsite side of the same wall as the inlet, so the flowpath between outlet and inlet bypasses the body of the room. I leave the bedroom door about 1" ajar which cures the issue, but this does mean that the hall nightlights do shine through the crack into the bedroom.
@pdf27, Assuming that you have a conventional "double-back" layout for your zones and also have access to the Ansys heat flow modelling, then you can easily set up the heat flow model that I did, which is to approximate the slab as a concrete tube the length of a zone run and the radius set by the slab thickness and pipe spacing. This radial symmetry makes give a 2 spacial and one time dimension model which is computationally solvable over 10s of hours. OK, the radial symmetry assumption breaks down in reality because the UFH pipes are not in a cylindrical medium but set in a slab concrete with a insulating surface below and a radiant one above. Even so the model still gave an excellent prediction of the time response of the slab and the heat-off impulse response in the both the model and the actual slab shows that the radial component dominates the heat flow during heating: it's an extremely useful model. To me what this all underlines is that the slab itself is the biggest heat capacitor in the system, so there is little point in adding complexity of external smoothing using TMVs and buffer tanks. So long as you are pumping enough heat per day into your slab then a passive class house with warm slab + UFH + cellulosic filler will stay comfortable. In my experience your divide the year into three broad zones: No active heat management is required (roughly 6 months / year) because the intrinsic heat excess is enough to keep the house at a comfortable equilibrium and MVHR exchange / bypass gives adequate trim. One per day heat adjustment is sufficient (roughly 3-4 months / year). This is my overnight top-up / cool-down. Again so long as this adjustment gives enough bulk heat-balance, the MVHR exchange / bypass gives adequate trim. One per day heat adjustment is insufficient (roughly 2-3 months / year). Here for the mid winter months a single heating period starts to give a daily heat ripple that is noticeable, so you need multiple heating periods per day. For the UK climate range IMO you will never need more than 3, but at 4 the ripple will be less than 0.1°C. At the moment I use the day-to-day average temperature as a control feedback to compute the total amount of daily heat (and in future cooling) needed to apply. Because I use a fixed input heater this maps directly to heating time. If you are on E7 it does make sense to have an asymmetric cycle with a bulk heat overnight, but the tops can be spread through the day. It sounds like you are going to adopt similar ASHP heating scheme to the one that I plan to and @jack has done, which is to set the ASHP output temperature at a low setpoint (in my case around 27-28 °C). You then need to control the mark/space ratio to maintain the overall daily thermal balance. And the CoP at this set point is excellent. (Though if you have kids and use lots of HW and want to use your ASHP to preheat this then this would greatly complicate this approach.) There are a number of strategies here, eg. use a fixed cycle (say 6 hours) and then control the on time or use a fixed on-time and control the off-time to give a variable cycle, but IMO these are all based on macro thermal balance. This will work well for my house, but if you have "acres of S facing glass" then day-to-day highly variable solar gain will become an issue that you need to factor in. Jeremy and I started out at very different design conclusions from a very similar problem analysis and our solutions are conditioned by historic investment decisions. Even so we have significantly converged in our approaches. Jeremy uses a single internal datum, I daily average a couple of DS18B20s measuring room temperature. To be honest, if mid-winter heating was my only concern then I'd stick with the largely E7 Willis approach. Yes, the running cost is maybe £300 p.a. more than using an ASHP, but I have no complex mechanical systems to maintain and to replace every 10 years or so, so there is no cost benefit case here. The real issue that makes me plan to introduce an ASHP is the summer cooling one: for about a month a year, I need to dump heat from the house actively to keep a comfortable internal environment, and I can't do this by an additive heat solution. One last comment. I've mention the impact of solar gain which can throw a "big spanner in the works". You can get very sunny days in December and if you have a large south-facing area of glass, this can be a big pulse of kWh into the house. The other one that causes us fun is visitors. When our kids+family or others come to visit, then just the heat and activities around hosting these guests adds environmental control challenges. For example, 6 people sitting in a room will cause it to start to warm up noticeably!
Sorry if there is any confusion: floor temperature. The relationship between the flow temperature and the floor temperature is highly non-linear both in terms of space and time. It took me ages to get my head around this and it wasn't really until I did the modeling that I got a good feel for it. You just can't use steady state or linear approximations validly. I explained this in a little more detail in: Instead of tightly controlling the flow temperature and therefore putting in a very variable power input, I limit my power input. The slab heats steadily over about 4 hrs radially from the pipe centres before it even starts to approach an equilibrium where the floor temperature has risen enough for the heating to start to tail off. On a 7 hr @ 3kW heat, the final inflow temp is around 29°C and the outflow temp at 26°C, but the inflow temp collapses within a couple of mins of turning off the heat -- as the radial gradient collapses. The floor reaches max temp around 11:00 - 12:00. Conventional Gas and other boiler systems are simply not designed to output a steady power of < 1 kW. You have to add a lot of additional hysteresis to avoid constant start / stop and knackering mechanical components. As to Jeremy's formula IIRC, it is a curve fit from BRE for conventional UFH systems which typically need to output maybe 3× or more than a passive house UFH system. The exponential component is a fit to the convection effects that you will see if your floor is 5° or more than room temperature, but my floor never gets more than a couple of degrees warmer. I ain't going to argue 7 vs 8. They're the same ballbark as far as I am concerned. Maybe J still has the BRE doc ref.
We had a long thread about this a couple of years back. @JSHarris and @SteamyTea were two of the other main actors. The figure drops out of Stefan–Boltzmann as the radiant component dominates heat losses at the small delta T. There are minimal conductive losses on an solid / air interface and a few °C is too small to generate enough instability to create any convective flow in a passive house. In our case we have a mat slate floor which is rough at a micro level and about the perfect radiant surface. The figure would be lower for a carpeted floor, but not as much as you'd think because whilst carpet is a good insulator, the surface is almost fractile and so the effective radiant surface is a lot larger. Certainly looking at the slab temps and our rate of heat loss, this is in the right ballpark.