  1. Thanks John @JohnMo but too late as I've exceeded my 30 minute window to edit, I know how to it now though!!.
  2. Sorry John, Don't know as I just read a lot about Evohome in Automated Home.
  3. Some one might do a few tests on one of these boilers, @ j_s ? The Boiler is dispatched with (Hydraulic Operating Mode) D.170 set to 2 (dP constant) and D.171 (target pressure value set to 200) If so, or whatever mode your boiler is on, Note D.015 (pump speed), D.029 (flow rate), D.040 (flow temp), D.041 (return temp) and Target Modulation. Change D.170 to 3 (Spread dT), Set D.172 to 20C (Target spread value), take another set of readings after say 10 minutes. If using Weather Compensation, switch it off if possible, set the Boiler Target Temp to 62C , wait for say 5 minutes after target temp is reached and take another set of readings, (D.170 set to 3) Please state if a LLH is installed or not.
  4. Where are you seeing this efficiency figure?, I didn’t come across it in the MIs. What you can do is something like these tests, ensure boiler/system up to temperature. Test Results. (calculations, in brackets) Target Modulation 78% (boiler output (0.78*30,23.4kw) D.029 Heating flowrate 1575LPH. Flow/return temps D.040/D.041, 62C/47C. (Boiler Output 1575*(62-47)/860), 27.47kw. This consistently shows ~ 10 to 18% higher output than that from target modulation, which I presume is the actual % boiler output. Gas meter readings were taken exactly 3 minutes apart and the consumptionX11x20 to give the energy input in kw, cant find the figure now but it gave a efficiency of 91% based on the target modulation but 106% based on the flow & dT, so maybe that’s where Vaillant are getting their efficiencies from. When/if you do these tests, compare them with the Vaillant figure, might be interesting. I would appreciate if you would carry out the tests sometime as requested and post them in the more appropriate Topic , “Vaillant Ecotec Plus 630 dT” Thanks. John
  5. That's Net Efficiency based on the lower heating value of the fuel, natural gas wet gas loss is around 10% to 11% and to attain a true 100% efficiency would require the flue gas temperature to be as low as the combustion air temperature IMO.
  6. Honeywell don't pay much attention to these findings since their Evohome continuously cycles the boiler and even smart roomstats with TPI? control do similar.
  7. Maybe something a bit like Ideal Vogues "Super Efficiency" ??, this was their reply to someone who was seeing very "poor" efficiencies of less than 65%, at least Ideal arn't claiming 100% +. A bit off topic but is your boiler their latest offering of the 630 where you can run in one of several hydraulic modes, one of which is temperature spread?
  8. Came across this in some old book from long ago where it states that "The height of the vent above the CWSC (water level) should be 4% of the head from the bottom of the HW cylinder to the CWSC water level + 150mm" This obviously refers to water at 100C as the expansion is 4% (or very slightly higher) when heated from 15C to 100C. If its easier, 40mm per 1M head can be used instead. (40/1000=4%) My HW cylinder, like a lot of others is installed in the hot press on the landing with the CWSC in the attic, water level ~ 3M above the bottom of the HW cylinder. The theoretical height of the vent should be (3*40)+150, 270mm, if the cylinder was located downstairs with say a 5M head then the vent height should be (5*40)+150, 350mm My vent is 350mm above the CWSC water level but I have seen several where the vent is resting on the CWSC top and ~ 100mm above the water level. Someone asked me years ago why the above vent height is required and I reall don't know. Its not a expansion allowance, my 135L CWSC measures 450mm from the bottom to its normal level so, 3.33mm/L, I have a 150L HW cylinder which would expand by 6L if heated from 15C to 100C, a rise of, 6*3.33, just under 20mm (vent pipe level will rise by the same amount), a long way from the overflow. even a 300L HW cylinder with a expansion of 12L at 100C would still not reach the overflow as the level would rise by, 12*3.33, 40mm, still leaving ~ 50mm to overflow. Of course, normally the HW cylinder never reaches these sort of temperatures.
  9. If you can believe the below, then any run time of more than 3 minutes per cycle has a negligible effect on boiler efficiency.
  10. There's bags of headrom there to do that, its amazing that none of the plumbers spotted that, that's just basic stuff, you could do that yourself in less than hour. Did any of the plumbers look up there in the attic?.
  11. Lowering the level in the cistern is the same as increasing the height of the vent pipe above the water level, if the present height of the vent (where it turns down) above the water level is say only 0.25M and the water is just dribbling then it means that the imbalance or differential pressure across the H is 0.25M, so increasing the distance beteen the waterlevel and the top of the vent by either raising the vent pipe or lowering the water level should have the same effect IMO, rem its a U tube we are talking about, anyway there's reall nothing to be gained with this cistern.
  12. Do the LEDs flash when changing modes/settings, don't know if this is for your particular pump or not but its showing pulsating LEDs in PP or CP mode?
  13. Do those PP tests anyhow.
  14. Anyone who is interested in PP settings can do their own calcs here, you can just put in your own pump PP settings. UPS3 PPs Extract.xlsx
  15. That changes things a lot because any blockage in the H now only has only to produce a U tube imbalance (differential head) of that "few cm" to get pumpover, reasons are becoming clearer at last. The combined vent & cold will almost certainly stop that but would still like to see that vent raised a little, alternatively, as a real combined vent&colf feed doesn't have an vent rising over the level of water in the F&E you can just use the cold feed and cap the vent at the H, (install a thumb vent there instead) BUT the cold feed I think, by the regs must be 22mm or more with no isolation valve, boiler must have o/temp proection as well, which yours has. So you couldn't use the existing cold feed but you could plump the existing vent into the F&E and remove the existing cold feed and install a thumb vent there, (or one of those horrible AAVs), personally, I prefer my type but you just may not be able to rise your vent even say 0.5M?. Edit: Can you post a phot of the F&E cistern + water level, you may be able to lower the level in that considerably to give a little extra head, the level only needs to be 80/100mm, expansion will only rise it another 10/15mm.
  16. The PP tests should qualify this, if you assume a present flowrate of ~ 15LPM at 3.7M (CC1) then PP2 will give a flowrate of 11.7LPM at 2.25M and PP1 will give a flowrate of 8.2LPM at only 1.15M. The minimum PP2 head is 1.7M & the minimum PP1 head is 1.0M so even if there is almost a full restriction in the H, there cannot be pumpover (assuming vent ~ 2M above F&E cistern water level) at PP1 and practically speaking no pumpover either on PP2, otherwise the pump is faulty. All will be revealed.
  17. That pump is a relative youngster, PC0945, week 45 2009. My daughters is PC0414, week 14 2004, look at the way its installed! Upright! and still running perfectly, don't know when Grundfos manufactured the cobweb though.
  18. You could check the H (but requires a bit of care) by installing a isolating valve (if not allready) on the F&E cistern mains supply to the ballcock, make up a few fittings and attach a hose or whatever to the vent pipe end, shut the pump inlet valve and carefully crack open the mains to see what kind of flow you are getting through the H and back into the F&E cistern.
  19. If you can do the H yourself then, as you say, why not, at least you will get great satisfaction once you prove it one way or the other.
  20. By running the UPS3 at its lowest setting PP1 then if you are stlll getting pump over, you have a serious blockage problem, a few other thoughts, those UPS3s have a very poor reputation around here, I know several people who will not install them but I would be a bit surprised if it wasn't running properly in its requested mode. That 50W model of 5M Selectric is one of the lowest head pumps so wouldl expect little or no pump over with it. Are you absolutely sure that there isn't a circ pump in the boiler and that is being boosted by the UPS3 . Anyhow try PP1, if still pumping over then problems. Can you post a photo of the pump LEDs when running in CC1 just now and also when/if running in PP1. Also check both isolating vaves on pump fully open.
  21. I would advise to get a plumber (not a salesman) to cut out that H and inspect/clean it out/renew it., If the original pump was a Selectric (a pretty low head pump) then the clean out of the system + the installation of the UPS3 might have started that pump over, you can try and establish the blockage by trying that PP2 setting or, if still pump over, try PP1 even though that will almost definitely not satisfy your circulation requirements but will give some idea of the state of affairs.
  22. Right, if possible, before your plumber arrives tomorrow??. Just to be sure to be sure, check that the pump is on CC1 as shown by the one green LED. Then change to PP2, as shown by the combination of flashing LEDs on the right, see if you've still got pump over.
  23. The plot thickens but first this pump over conundrum. Expansion effect first, a system with 100L of water and a average flow/return temp of 60C will expand by 1.62%, so 1.62L, this will increase the level in the F&E cistern and in the vent by equal amounts (since its a U tube) so ~ 10 to 15mm as 99% of the expanded volume is taken up by the F&E cistern (well named) but the U tube effect means the level in the vent pipe will rise by the same amount even though the vol of water is tiny. With a perfectly clean system there will still be a very very slight pressure loss in that short piece of pipe in the H as the full circulating flow passes through it, if, for any reason a restriction start building up in that pipe then the U tube starts to become unlalanced with the level in the vent rising and the level in the cold feed falling, eventually, if the restriction becomes very bad, the water will reach the top of the vent and start "filling" the F&E cistern, and water will start flowing down the cold feed. Re UPS pump settings, this is very strange, on CC1 the pump head (4.2M) will be greater than 3.0M (CP1 constant setting) until the flow rate reaches 1.3m3/hr, 21.7LPM, and will not fall below 3.0M until the flowrate is 1.4m3/hr, 23.3LPM so there is no logical reason for this behaviour IMO. However, that as it may, one could fill a small book with pump over problems just because the circ pump was changed, As I said previously a few have changed to my 52 year old system exactly as it is, see below, problems disappeared even though there were no blockages apparent in the H.
  24. Its a pity that the UPS3 doesn't at least display the pump power in watts, W, from which the flowrate that then easily be read off from the pump cuves, most A rated pumps now not only display this but display the flowrate as well in m3/hr, very useful for trouble shooting, however, a plug in energy monitor which are very accurate can be bought for £15/£20, the pump cable is removed from its JB after noting the ter. numbers/locations, a short length of cable with a socket is then connected to these ter. points, the energy monitor is plugged into the socket, a 3 pin plug is attached to the pump cable and plugged into the energy monitor, I installed one of these a long time ago for someone and its still permanently monitoring the pump power.
  25. It still doesn't change that "6mm" restriction calculation, have you any idea or can you measure the distance from the F&E cistern water level to the the "crook" in the vent where its turned down into the cistern.
×
×