I was working today on a new build that was having the "professionally" designed and installed heating system commissioned,so I took some time to have a look and talk to the guys.
It was a Mitsubishi ASHP coupled to a "pre plumbed" Mitsubishi cylinder and controls.
The nuggets of information I gleaned, in no particular order were:
The tank was an unvented cylinder for hot water only. Heated to 45 degrees by the heat pump. Once every 3 weeks, on a day of the week of your choosing, it automatically uses the immersion heater to raise the tank to 60 degrees for an hour as an anti legionella measure.
Because of the low grade heat input, they said it would require too large a heat input coil, so it used a plate heat exchanger to heat the tank.
The UFH runs directly from the heat pump. No buffer tank. It either runs DHW or heating, never both together. When in heating mode, the heat pump runs at a low temperature which you can set. They say this obviates the need for UFH mainifolds with temperature control, instead you can use a dumb manifold (cheaper) and just dial up the flow temperature you want for the UFH in the heat pump controller.
The outside unit ran very quietly, and I didn't see it icing up or needing to defrost, it was about 3 degrees today.
I was particularly interested in the no buffer tank, and direct operation of the UFH with a dumb manifold. Certainly something to think about.