Help required wiring my ASHP/UFH


joe90

Recommended Posts

Right guys, in particular order

 

its a Honeywell three three way valve ://heatingcontrols.honeywellhome.com/documents/Installation-Guide/pdf/1083.pdf

 

 I have forced it into DHW mode to test and forced it into heating mode to test, this was confirmed by the command unit.

 

when in DHW mode the three way valve is energised but hot water goes to A (heating), when in heating mode the three way valve returns and the hot water goes to B (DHW). I can reverse the three way valve but this is not what I should have to do!!!!

Edited by joe90
Link to comment
Share on other sites

Ok, so it’s resting position is port B (hot water in installation guide) add power and it switches to port A (heating) in 18 seconds. Returns to port B under spring in 8 seconds. 

 

Is yours plumbed to water on B and heating on A?

 

... and is it powered from the ASHP (terminals 10 & N)?

Edited by Gav_P
Link to comment
Share on other sites

48 minutes ago, joe90 said:

Right guys, in particular order

 

its a Honeywell three three way valve ://heatingcontrols.honeywellhome.com/documents/Installation-Guide/pdf/1083.pdf

 

 I have forced it into DHW mode to test and forced it into heating mode to test, this was confirmed by the command unit.

 

when in DHW mode the three way valve is energised but hot water goes to A (heating), when in heating mode the three way valve returns and the hot water goes to B (DHW). I can reverse the three way valve but this is not what I should have to do!!!!

Ah... when you are in DHW you must be creating a live feed to the valve... so the valve is thinking “oh, here comes the electricity I better switch over to heating, port A”

 

i think you are just giving it a live feed at the wrong time... for DHW, when it should be for heating.

Link to comment
Share on other sites

12 minutes ago, Onoff said:

This is the one I have:

 

20181108_195840.thumb.jpg.92cf8e4c490e5b6f2901860d765be782.jpg

 

20181108_195852.thumb.jpg.97acbb7d0b6ac4c9c380eb391dc9c636.jpg

 

20181108_195941.thumb.jpg.d4057447214c9184b1c7788878f6a32a.jpg

 

Straight out of the box, not wired up and set to Auto it ports to B. Set to Man and it ports to A & B.

Makes sense. Now power = defaulting to DHW (port B). Or override it in manual mode which opens all the doors for free flow everywhere. 

 

When you wire it up it will have 3 options.

1) no power = DHW (port B)

2) 1 signal asking for Heating = (port A)

3) 2 signals asking for DHW & heating = mid position (both ports)

 

i guess! 

Link to comment
Share on other sites

9 minutes ago, Gav_P said:

Makes sense. Now power = defaulting to DHW (port B). Or override it in manual mode which opens all the doors for free flow everywhere. 

 

When you wire it up it will have 3 options.

1) no power = DHW (port B)

2) 1 signal asking for Heating = (port A)

3) 2 signals asking for DHW & heating = mid position (both ports)

 

i guess! 

 

I've no probs wiring it up just this thread made me question whether Honeywell is wired/ported different to the Tower one in at the mo. I tell you what you can tell the quality of Honeywell compared to Tower. Streets ahead right down to the tinning on the wires and documentation. I'm a convert!

  • Like 1
Link to comment
Share on other sites

Lets be clear here.

 

@Onoff has a MID position valve which is normal for a boiler central heating system. It can feed water to either port or BOTH at the same time (there is a clue in the name)

 

What @joe90 needs is a 3 port 2 way valve. It feeds water to A or B but never both at the same time.

 

They are VERY different animals.

 

The 2 way valve is simple, by default it feeds one way, energise it and it feeds the other way.

 

The mid position valve imho is the work of the devil. It is both very clever and very complicated (and somewhat of a fudge) in how it works and it's wiring is very different and more complicated.  A mid position valve will NOT work in this application.

 

If yopu want to understand how the mid position valve works, take a read here http://www.diyfaq.org.uk/plumbing/controls/midpositionvalve.htm

 

So for @joe90 lets not complicate the discussion by talking about mid position valves.

  • Like 1
Link to comment
Share on other sites

In a nutshell it’s this, my ASHP delivers power to the three way valve when it goes into DHW mode and no power when in heating mode. The three way valve i have works the other way round . I can get over this by reversing the three way valve but can’t believe I am the only one to have noticed this!!!. 

 

My command unit cant use the inbuilt room stat if you set the heating water temperature (not use the inbuilt temp which might lead to defrosting), I can get round this by using a separate room stat (with dry contacts!!!). Very annoying.?

Edited by joe90
Link to comment
Share on other sites

9 hours ago, Gav_P said:

Ok... so after this minor deviation... anyone else got any ideas why joe90s heating is all assaboutface?

 

Can only be because the valve is operating the wrong way. The ASHP energises the valve in the DHW state, and de-energises it in the heating state.  This is the normal way diverter valves work, as most of the time they will be de-energised and running the heating.

Link to comment
Share on other sites

2 minutes ago, JSHarris said:

 

Can only be because the valve is operating the wrong way. The ASHP energises the valve in the DHW state, and de-energises it in the heating state.  This is the normal way diverter valves work, as most of the time they will be de-energised and running the heating.

 

Yes mate, cross posted with you. Like you I would assume energised for DHW .

Link to comment
Share on other sites

It may be worth whipping the head off and seeing if the spindle rotates 360 degrees. 

 

If it does, you can turn the head and the spindle 180 degrees and then it will operate correctly. I’ve had this before as I bought a Danfoss mid position that did what you say and it was only when I checked the ports and the head I found it was back to front. The head wasn’t fitted and it looks like someone had reversed the spindle and put it back in the box .... as a matter of course I now blow through them to check ..!!!!

Link to comment
Share on other sites

25 minutes ago, PeterW said:

It may be worth whipping the head off and seeing if the spindle rotates 360 degrees. 

 

If it does, you can turn the head and the spindle 180 degrees and then it will operate correctly. I’ve had this before as I bought a Danfoss mid position that did what you say and it was only when I checked the ports and the head I found it was back to front. The head wasn’t fitted and it looks like someone had reversed the spindle and put it back in the box .... as a matter of course I now blow through them to check ..!!!!

 

Ah ha, I was told you can’t reverse them!!!, will check it out, thanks buddy.

Link to comment
Share on other sites

5 minutes ago, joe90 said:

 

Ah ha, I was told you can’t reverse them!!!, will check it out, thanks buddy.

 

Two screws and the head comes off. Set the ASHP to come on and rotate the spindle to check you get warm water both sides..... then realign the spindle the way you want and put the head back on !

 

on your other point about temperature, ASHPs work by incremental heat rise so they will basically take the water temp up by 3-5 degrees per cycle. 

  • Thanks 1
Link to comment
Share on other sites

1 hour ago, PeterW said:

Two screws and the head comes off. Set the ASHP to come on and rotate the spindle to check you get warm water both sides..... then realign the spindle the way you want and put the head back on !

 

Just tried this before I leave and I have got it off, the spindle only moves about 30’, yes I can get warm weather both sides, it won’t go on the other way round!. I will have to drain and swop it around.