JohnMo Posted November 20, 2025 Posted November 20, 2025 17 minutes ago, Beelbeebub said: For a battery, your estimate of 6 to 7kwh in to get 5kwh out implies a round trip efficency of 70-80% which I think is too low it's more likely 80-90% or better. You always have a reserve you can't touch, called depth of charge, my battery is rated at 13.5kWh and has a depth of charge of 100%, so in reality the actual battery is slightly bigger than that. So you need to look at the data sheet and see what you are actually getting, Bit like heat pumps, battery rating isn't always black and white
Beelbeebub Posted November 20, 2025 Author Posted November 20, 2025 21 minutes ago, JohnMo said: You always have a reserve you can't touch, called depth of charge, my battery is rated at 13.5kWh and has a depth of charge of 100%, so in reality the actual battery is slightly bigger than that. So you need to look at the data sheet and see what you are actually getting, Bit like heat pumps, battery rating isn't always black and white i am assuming he is talking about round trip efficiency ie how many kwh it takes to charge a battery so that you can discharge 1kwh. For lead acid batteries it can be 60% round trip ie you only get 6kwh out after putting 10kwh in. LFP batteries are very good in these circumstances with efficiencies in the 95% plus range. This is independent* of the nominal and usable batter capacities * nearly - i believe you get worse round trip efficiencies if you use all of the usable capacity vs a smaller subsection (eg 20-80%) but it's not a huge effect and i believe most data sheets assume a higher depth of discharge 10-100%
sharpener Posted November 20, 2025 Posted November 20, 2025 2 hours ago, Roger440 said: Related, though not directly is the very long payback periods on some of this stuff. If you can see a return in 2 or 3 years, if you have the capital its a no brainer. But 10 years, not so much. Original FIT scheme we signed up to cost £14k for just 3.7 kW but the rates on offer were so high the actual payback was under 7 years - which sounded good then and is still the gift that keeps on giving. I.e. it has paid for another 3.2 kW capacity plus the battery inverter system, and is now making a contribution to the cost of the HP. 1 hour ago, Beelbeebub said: Without a battery the best you are likely to get is 15p all day, and the best import you can get is 25p because you can't time shift without a battery. Well in a sense you can bc you can do all the laundry and run the dishwasher on cheap rates, which with e.g. Cosy is under 15p for 8 hours in every 24. 1 hour ago, Beelbeebub said: To be fair panels are so cheap now that *if you could get a really high export limit*, like 10kw or something you could have a huge array, big enough to export so much elecreicty in the day and summer months that you could build up enough credit to import "off sun" and still end up ahead. But you would need the space for the panel and the high export limit. It took some negotiating but the DNO finally agreed last year to an unlimited export capacity. So with a nameplate capacity of 6.9 kW we have exported about 5.3 MWh in the last 12 months and imported about 5.5 so we are more or less in that postition. 1 hour ago, JohnMo said: You always have a reserve you can't touch, called depth of charge, my battery is rated at 13.5kWh and has a depth of charge of 100%, so in reality the actual battery is slightly bigger than that. So you need to look at the data sheet and see what you are actually getting, Bit like heat pumps, battery rating isn't always black and white That is the fly in our ointment, the Pylontecs stop discharging when the SoC gets down to 10% so effectively we only have 90% of the capacity we paid for. 58 minutes ago, Beelbeebub said: i am assuming he is talking about round trip efficiency ie how many kwh it takes to charge a battery so that you can discharge 1kwh. For lead acid batteries it can be 60% round trip ie you only get 6kwh out after putting 10kwh in. LFP batteries are very good in these circumstances with efficiencies in the 95% plus range. This is independent* of the nominal and usable batter capacities * nearly - i believe you get worse round trip efficiencies if you use all of the usable capacity vs a smaller subsection (eg 20-80%) but it's not a huge effect and i believe most data sheets assume a higher depth of discharge 10-100% Then there is the little matter of the inverter/charger efficiency. When the battery current is at 70 amps everything gets quite warm and this accounts for losses which are possibly another 5% in each direction. 1 1
SteamyTea Posted November 20, 2025 Posted November 20, 2025 (edited) 38 minutes ago, sharpener said: Then there is the little matter of the inverter/charger efficiency. When the battery current is at 70 amps everything gets quite warm and this accounts for losses which are possibly another 5% in each direction. If everything is in the same room, and you know the thermal characteristics of that room, measuring the rise and fall in air temperature would give you a very good idea of those losses. Edited November 20, 2025 by SteamyTea
Beelbeebub Posted November 20, 2025 Author Posted November 20, 2025 Yes inverters have efficiencies, depending on the operating range it can range from 90-97%. Even if you take the absolute worst cases (90% in, 90%out and 95% battery) you're still over 75% round trip. But at more general levels my system can beat 90% round trip efficencies. I think the drop in price of hybrid systems has made them a "no-brainer" for the majority of installations - not least because even without PV you can save by time shifting your demand. Obviously there will be edge cases where it doesn't make sense - but the majority of those will be the result of tarrifs that may not hang around. If the ratio of import/export prices widens or the price of imported electricity rises batteries will make even more sense.
Gus Potter Posted November 22, 2025 Posted November 22, 2025 On 20/11/2025 at 11:19, -rick- said: You've said stuff like this a few times and everytime I try to understand what you are getting at but I'm afriad I'm not really getting your point. Yes. If I've not articulated well that then the fault lies at my end. I've copied your post below in plain text and comment in line. I'll have a go at the good points you make. Main thing is that BH is a place where you can discuss without having to watch every P and Q. To quote you: You've said stuff like this a few times and everytime I try to understand what you are getting at but I'm afriad I'm not really getting your point. In case it doesn't come across in the way I indend, the below is not having a go, just trying to understand your argument. Gus: You're welcome to question me, I don't see it as you "having a go" rather just entering into a conversation, a design discussion. If we agreed all the time then that does not bode well in terms of good design. It's OK to disagree! BH is a place where you can explore ideas and sometimes these can be very different view points. Without the mods on BH this wouldn't happen so thanks to them. The pipes buried in concrete (at least in low energy houses) are going to be able to cope with almost anything thrown at them and will last a very very long time.* Agree with the first bit. I did my first UFH system about 30 years ago and from what I hear the pipes have maintained their integrity. I also look after another self build (circa 30 years) house with a similar system and have not observed pipe material degredation, say like Upvc that can deteriorate under UV light. The second part.. you need to be careful as if you don't have good filters / competent maintenance then you can introduce "gunk" i.e bits of rust, a flake off a cast pump that can just put a spanner in the works. And that is why you'll often see me arguing for more loops. If one gets totally buggered then you still have a fall back. A lot of what we discuss here is how to get the maximum efficiency out of a system and the theme here to achieve that is minimum controls, low water temperature, system on most of the time with weather compensation (a technology that has been standard in all heating systems in other countries for literally decades). Agree with the headline points you make. Your first point.. maximum efficiency, I agree.. but efficiency has to be measured over say 50 years. You have to recognise that over time that can drop off a bit. Yes low flow temperatures, this encourages boilers to work in condensation mode. Minimum controls.. totally agree.. but you have to have a flexible loops in the floor which can, as you best guess cope with controls that migh be developed in the future. Weather compensation. Yes that has been around for a while, but I see fundamental problem with this. The first is the cost of updating the software, much is now an app on your phone! The second is that young folk with busy lives don't have the time to fanny about with it. We live in the UK! Our weather can change rapidly , four seasons in one day..where in many other countries it is often more predictable. The response time of UFH makes weather compensation less reliable. Now you may live in a benign part of the UK but there a lots of folk that don't. Even if you add lots of fancy controls on top of the basic system, the fundamentals of the system are such that you should be able to remove those controls and still get a very functional system. Agree. This is the point I've been putting forward, but I've maybe not made it that well. To to reiterate. Build in redundancy in the UFH pipes in the floor and that gives you flexibility as technology changes in the future.. it's called future proofing. Similarly, if the heat demand of the house increases then worst case you need to up the flow temperature in the pipes to compensate. Again, most of the designs talked about here for new builds are based on very low temperature heating. If you can output sufficient heat with the water in the pipes flowing at less than 30oC then if some cataclysimic climate change happened and suddenly we were all living in -20C then upping the temperature in the pipes to 40-45C should still be able to adequately heat the house. You are talking sense here! Yes I have experience of this in the past. The average outside temperature was about minus 20 deg for three days in a row, that was preceeded by a week or so of below zero so things got well cold. Solution was to bump up the flow temprature as you say. Now some may say.. oh it will cuase havoc with our timber floor finishes. I doesn't as generaly in the autumn the moisture content drops! In the summer often you have the heating turned off. Obviously if people want to extend the house then any extension would need work, but thats no real difference to any other system. If you have a low and slow design the system shouldn't care too much where the walls are if they needed to be moved. I do think that any 'smart' stuff added to a house should always be removable while maintaining the basic function of the house. Maybe you lose convenience or a little efficiency, but things should still work. Again, in the vast majority of cases, the systems discussed here are of the type that could be removed without significantly reducing the basic function of the house. Therefore, it is easy to offer any future buyer of the property the option to have all smart systems removed before they complete any purchase. So these shouldn't have a negative impact on the price of the property. More sense! Smaret sytems. I have two zones in my own house. One zone is radiators, the other UFH. I control these with the Hive sytem.. I think most folk can cope with that. What they can't cope with is lots of home automation. * Plastic pipes don't corrode and UFH systems should have much less metal in them overall reducing corrosion of other parts and build up of gunk. They can be flushed if there is a problem. Even in the unlikely event of the pipes developing a problem, retro fitting radiators or even electric heating to affected rooms would be unlikely to dramatically change the sale price of the house. Ah.. if you have to retro fit rads that is going to be expensive.. My own house is designed with areas of glass. there is not that much room to retro fit rads.. that is the beaty of UFH as it keeps the wall clear. Also retro fiting rads can be very expensive.. how to you get the pipes to the rads? I do see a concern about whether rafts can be relied on to last as long as traditional foundations, but this has nothing to do with UFH. This is an interesting question. The first thing I would say is that common to popular belief SE's / insulated raft specialist that do this kind of design in the evolving self build market don't rush out to pick faults in others designs, or claim to be the best. A good example is Advanced Foundation Technology (AFD) and Tanners in Ireland. I have been deisgning rafts for a long time, decades, so kind of know what I'm doing. In summary though there is a time and a place for a raft foundation. Sometimes the ground moves and the last thing you want is a strip foundation. A well desinged raft can perofrm just as well as a strip foundation if noit better. The big and evolving challenge for me as a raft designer is to deal with the thermal bridging, how and where you set up the UFH. Do you integrate in the "raft" or put it in say the screed. Each site is often different so you need to try and sort that while making the raft structurally ok. Much of the time it comes down to the way self builders are set up and the sequence of works. This actually often drives the desing cost wise. To finish. Hope the above helps, if not keep asking.
ProDave Posted November 22, 2025 Posted November 22, 2025 For the record I installed UFH in my first self build 23 years ago. There was no forum to discuss things with then, I was flying on my own. We installed UFH upstairs and down, each room on it's own thermostat and zone, driven from an oil boiler. No mains gas available and I had not heard of heat pumps. That system is still working. It has had normal maintenance, several motorised valve actuators replaced (WHY are they the most unreliable bit of a heating system) One pump replacement, and one thermal mixing valve replacement. And normal boiler servicing. What I learned from that is many (most) system designers are NOT experts. We were advised to have UFH pipes in the downstairs hall AND the upstairs landing. The hall rarely called for heat and the landing NEVER. That system should go on forever if you can get parts, when the mixer valve failed, it was hard to find a replacement, it is not a design of manifold that is for sale now. 2
JamesPa Posted November 22, 2025 Posted November 22, 2025 2 hours ago, ProDave said: What I learned from that is many (most) system designers are NOT experts. Love that statement, I think the discussions on here and elsewhere bear it out. Of course there are many exceptions, people who take the trouble to learn/re-learn the necessary physics, think about the job, question what they are being told, seek to understand, and continually to improve their understanding. The rest are just painting by numbers guys (some of whom cant even read the numbers) bluffing their way through. 1
-rick- Posted November 22, 2025 Posted November 22, 2025 (edited) 12 hours ago, Gus Potter said: The pipes buried in concrete (at least in low energy houses) are going to be able to cope with almost anything thrown at them and will last a very very long time.* Agree with the first bit. I did my first UFH system about 30 years ago and from what I hear the pipes have maintained their integrity. I also look after another self build (circa 30 years) house with a similar system and have not observed pipe material degredation, say like Upvc that can deteriorate under UV light. The second part.. you need to be careful as if you don't have good filters / competent maintenance then you can introduce "gunk" i.e bits of rust, a flake off a cast pump that can just put a spanner in the works. And that is why you'll often see me arguing for more loops. If one gets totally buggered then you still have a fall back. 12 hours ago, Gus Potter said: Even if you add lots of fancy controls on top of the basic system, the fundamentals of the system are such that you should be able to remove those controls and still get a very functional system. Agree. This is the point I've been putting forward, but I've maybe not made it that well. To to reiterate. Build in redundancy in the UFH pipes in the floor and that gives you flexibility as technology changes in the future.. it's called future proofing. I think these two statements is the crux of my disconnect with your points. With all UFH there is a potential for a kinked/damaged pipe during install but once the floor is down and the pipes are known intact then I don't think there is anything to worry about with them. If gunk gets in they can be cleaned. If some lump of metal gets stuck in there then that loop can be isolated and a mildly corrosive liquid can be put through the loop to dissolve the metal. PEX is pretty much inert and as long as it's intact once the concrete sets you shouldn't have issues. (If the concrete moves sufficiently to cause problems then you have a bigger issue than the pipes). I know there have been issues with some other materials used in the past, but PEX has been standard for a long time now and it's properties are well known. I still don't see why you would want redundancy in terms of extra loops. To me this is violating the idea of keeping things simple. We see a lot of designs on here that only have a few loops. If you want to build in loop redundancy you either add one more loop, which if you have to isolate one loop would still leave quite a large area unheated which is not a satisfactory answer or lots of extra loops which pushes up costs quite a bit and maybe reduces overall efficiency. My argument is that a failed loop (post install) is a very low probability and in the event it does happen having extra loops doesn't really buy you much over just running the system with a higher flow rate/temperature to compensate, neither option would likely be satisfactory. *A failed loop at install time likely leads to a repair being made before the concrete has fully hardened and certainly before any finished floor surfaces are laid. 12 hours ago, Gus Potter said: A lot of what we discuss here is how to get the maximum efficiency out of a system and the theme here to achieve that is minimum controls, low water temperature, system on most of the time with weather compensation (a technology that has been standard in all heating systems in other countries for literally decades). Agree with the headline points you make. Your first point.. maximum efficiency, I agree.. but efficiency has to be measured over say 50 years. You have to recognise that over time that can drop off a bit. Over 50 years you would likely be replacing the heat source and controls 3-5 times. Each time flushing the system of any build up. I'd argue that over the life of the pipes the overall efficiency is likely to increase as technology improves and the mechanical/control aspects are replaced with newer technology. 12 hours ago, Gus Potter said: Similarly, if the heat demand of the house increases then worst case you need to up the flow temperature in the pipes to compensate. Again, most of the designs talked about here for new builds are based on very low temperature heating. If you can output sufficient heat with the water in the pipes flowing at less than 30oC then if some cataclysimic climate change happened and suddenly we were all living in -20C then upping the temperature in the pipes to 40-45C should still be able to adequately heat the house. You are talking sense here! Yes I have experience of this in the past. The average outside temperature was about minus 20 deg for three days in a row, that was preceeded by a week or so of below zero so things got well cold. Solution was to bump up the flow temprature as you say. Now some may say.. oh it will cuase havoc with our timber floor finishes. I doesn't as generaly in the autumn the moisture content drops! In the summer often you have the heating turned off. There is a limit to the amount of heat you can put in a floor due to finishes but if you've designed for low and slow then there should be a very siginifcant margin that could be used to compensate for other issues at the cost of efficiency before that being a factor. 12 hours ago, Gus Potter said: * Plastic pipes don't corrode and UFH systems should have much less metal in them overall reducing corrosion of other parts and build up of gunk. They can be flushed if there is a problem. Even in the unlikely event of the pipes developing a problem, retro fitting radiators or even electric heating to affected rooms would be unlikely to dramatically change the sale price of the house. Ah.. if you have to retro fit rads that is going to be expensive.. My own house is designed with areas of glass. there is not that much room to retro fit rads.. that is the beaty of UFH as it keeps the wall clear. Also retro fiting rads can be very expensive.. how to you get the pipes to the rads? It entirely depends on the layout of the property. The cost of installing a rad is likely lower than digging up the floor to fix a damaged loop and there are lower cost electric options. Edited November 22, 2025 by -rick-
ProDave Posted November 22, 2025 Posted November 22, 2025 I was visiting a relative recently, she had an extension several years ago with UFH in the extension. But the UFH "never worked properly" so after a couple of years, she had radiators fitted in those rooms and gave up with the UFH. I had no part in that discussion or decision. But following that visit it seems her boiler is set to heat "hot and hard" for 1 hour at a time. No wonder the UFH failed to do anything sensible. 1
Gus Potter Posted November 24, 2025 Posted November 24, 2025 On 22/11/2025 at 12:51, -rick- said: I think these two statements is the crux of my disconnect with your points. Ok it looks like we are still in love but just disagree on some points. That is the great thing about BH. On 22/11/2025 at 12:51, -rick- said: (If the concrete moves sufficiently to cause problems then you have a bigger issue than the pipes). Ah, but as an SE's we design for around 25mm settlement, often differential settlement over a 50 year period. This is a common value for most UK house builders. I design raft ( semi passive) slabs for intitial plastic and drying shrinkage, on a standard smallish house this can be 10 - 15mm. Unless you really know how your SE has designed the slab / foundation then your UFH pipes are vulnerable. You can't have you cake and eat it! To expand. The concrete found / slab moves so it is a "bigger issue". What it means is that you need to know and understand what you are putting your UFH on and account for that. Unless you want to pay a lot more for your underbuilding.. which is nuts. I love the challenge.. design and who is availble to build it. I can design lots of stuff but if the Client can't find someone to build it at a reasonable cost then it's a waste of time. Funnily enough it's not that hard if you look and understand how the structure acts as a whole.. but the big problem in the market is that every designer is acting in isolation. Often they are conservative which drives up the cost of the build. But if they work together then the cost should go down! On 22/11/2025 at 12:51, -rick- said: I still don't see why you would want redundancy in terms of extra loops. It's mostly to idiot proof it! The UFH design look great on paper but life on site and a bit of rain makes for potential problems. If you are willing to stand over the Contracotr on site, then yes you may realise the design. On 22/11/2025 at 12:51, -rick- said: your argument is that a failed loop (post install) is a very low probability No it's actually really high as unless you have put in the pipes yourself, contractors don't give a shit. If they kink the pipe they will just straighten it out so it looks good. You won't see it. That is why you see lots of regular and experienced members saying their UFH works well, as they are aware of the pitfalls and have supervised it the right way. I can tell you I also work with UFH that has been put in by developers and the pipes, radius bend are a complete disaster. On 22/11/2025 at 12:51, -rick- said: There is a limit to the amount of heat you can put in a floor due to finishes but if you've designed for low and slow then there should be a very siginifcant margin that could be used to compensate for other issues at the cost of efficiency before that being a factor. But you can't design for low and slow when you then put rugs on the floor! This means you need to up the flow temperature which technically can breach the design values for the rest of the floor finishes, say engineered timber. Do you know how much a large sofa insulates UFH? It's a lot but no one on BH has acounted for this. Ok to complete, see if you get a joint leaking in the middle of the floor.. that is going to cause complete havoc! You can't easliy fix this! As a designer I design from the ground up, I have my SE hat on, my cost hat on and my Architectural hat on. I look at all the variables, how folk want to use the house. You have to have a deep understanding of how all the components fit together, the materials and so on. But as self builders you ain't going to be doing this as your day job. But it is well within you remit to think.. see this stuff I'm installing.. will if still be ok in 15 -50 years time ot more and if not is some surveyor going to come round and knock value off my house. On 22/11/2025 at 12:51, -rick- said: It entirely depends on the layout of the property. The cost of installing a rad is likely lower than digging up the floor to fix a damaged loop and there are lower cost electric options. No, as you have to run pipes to it. One of the great things about UFH is that it frees up wall space. So retro fitting a rad can be much harder than you think. Also rads tend to run at a higher temperature.. how are you going to make that work? From my end on the face of it your quick retort sounds good but practically.. just how are you going to execute that? and how much do you think that will cost? Why not just follow my advice and put in an extra loop, redundancey. My gut feeling is I'll never convince you... but hey ho, it's your money, not mine!
Beelbeebub Posted November 24, 2025 Author Posted November 24, 2025 As someone who is slowly retrofitting radiators and fan coils to replace a failed UFH install (not for any of the reasons Gus cites though) - whilst adding a radiator is the simplest and cheapest option, it is not always simple or cheap and I have the advantage of preexisting distribution pipes to individual room manifolds. I'd also say that the floor finishes argument is not an issue in new builds because the low heat loss makes the target flow temps low to start with and you don't need to jack them up much to compensate for any furniture reducing output. We had our "bare" floor areas cut at least in half by rubber playmates, foam sofas and beanbag on the floor, rugs etc. And still the flow temp was 30C or less and the surface temp was onky a degree or so above target air temp. In fact the issue we had was as it was a concrete finish the slab temp to hold 22C was often no more than 23C, which feels a bit cool on bare feet (hence the rugs). It was only on the coldest of days (like -10c) that tge floor temp ever got to about 25C and didn't feel cold on bare feet. Of course, retro fitting may require much higher floor temps to cope with higher losses
-rick- Posted November 24, 2025 Posted November 24, 2025 (edited) 10 hours ago, Gus Potter said: Ah, but as an SE's we design for around 25mm settlement, often differential settlement over a 50 year period. This is a common value for most UK house builders. Just to be clear, my understanding of this statement is that one part of the building may end up higher/lower than other parts. You are not saying you expect a crack with a step of 25mm in the middle of the slab. Obviously the big crack in the middle of the slab would break UFH pipes but if you have a crack that big then it's likely big enough to affect more than one loop and certainly going to cause you many other problems. If its just the overall building moving then the pipes should be fine. They are designed to withstand normal concrete movement/expansion/contraction. 10 hours ago, Gus Potter said: I design raft ( semi passive) slabs for intitial plastic and drying shrinkage, on a standard smallish house this can be 10 - 15mm. Unless you really know how your SE has designed the slab / foundation then your UFH pipes are vulnerable. You can't have you cake and eat it! The UFH pipes are designed to deal with this. Plastic has some flexibility. There are installation details you need to install around movement joints, etc. Plastic won't handle sharp cracks with significant movement but expansion/contraction measured in mm per m will be fine. 10 hours ago, Gus Potter said: No it's actually really high as unless you have put in the pipes yourself, contractors don't give a shit. If they kink the pipe they will just straighten it out so it looks good. You won't see it. That is why you see lots of regular and experienced members saying their UFH works well, as they are aware of the pitfalls and have supervised it the right way. I can tell you I also work with UFH that has been put in by developers and the pipes, radius bend are a complete disaster. There will always be bad contractors and poor installs. If you have a contractor that doesn't give a shit causing lots of problems then adding an extra loop or two to the design isn't going to save you. Given we are talking about decisions made at the design stage, rather than spending money on more loops, extra/larger manifolds and a less efficient system as a way to mitigate against a poor contractor you would be better off finding a better contractor/organising better supervision. Requiring a full flow test of each loop after install would be one way to ensure the pipes are good at install without adding a lot of extra steps (so long as your contract was tight enough to force the contractor to fix any issues). As I was saying the if the pipes are good at install then there is little that will go wrong in the following years. Getting a good install is a problem with any system (see the amount of people we have on here having issues with non-ufh heating systems). One caveat, if you install in a thin screed then there is always the possibility of putting a drill through a pipe but if you put drill through a pipe in a thin screed the process of repairing that is much easier than an unknown fault in a more deeply buried pipe and, unless you were the one drilling, someone else is paying for the repair. 10 hours ago, Gus Potter said: Ok to complete, see if you get a joint leaking in the middle of the floor.. that is going to cause complete havoc! You can't easliy fix this! Firstly, UFH is laid with no joints. If there is a joint the only reason is that it is there because of a prior repair. I've seen others here talk about having a joint to fix a problem with long term success so the prospect of a joint failing (that only exists in case of prior error) doesn't seem to me to be a good reason to specify a more expensive, less efficient system up front. 10 hours ago, Gus Potter said: But as self builders you ain't going to be doing this as your day job. But it is well within you remit to think.. see this stuff I'm installing.. will if still be ok in 15 -50 years time ot more and if not is some surveyor going to come round and knock value off my house. Sure, please take me through a scenario where a surveyor sees a problem that leads to a significant reduction (>5%) in the value of the house where that problem would have been prevented by installing extra UFH loops. 10 hours ago, Gus Potter said: No, as you have to run pipes to it. One of the great things about UFH is that it frees up wall space. So retro fitting a rad can be much harder than you think. Also rads tend to run at a higher temperature.. how are you going to make that work? From my end on the face of it your quick retort sounds good but practically.. just how are you going to execute that? and how much do you think that will cost? It really depends on the layout. We are talking low energy homes here so any room shouldn't be losing more than 2kw of heat. Any room big enough to get close to that level of heat loss is likely big enough to have multiple loops in it anyway so at least some of the loss from a defective loop can likely be made up by increasing the flow rate to the remaining loop(s). So many options to make up the rest. Normal radiators, baseboard radiator (electric if water pipes too difficult to route), AC fan coil installed high up (or on other wall blowing air to where it's needed), an electric panel heater installed on the ceiling above the cool area raditating down (not a great idea but a possibility). These options vary from a few hundred to maybe 2k for the most difficult. Not enough to seriously affect the price of a house. 10 hours ago, Gus Potter said: Why not just follow my advice and put in an extra loop, redundancey. The point I'm trying to make is that I'm not at all convinced that having an extra loop solves any of the issues you mentioned and that it comes with downsides. The likelihood of a spare loop being in just the right place to adequately cover for another failed loop is not high. If you install lots of short loops vs fewer long loops then you are adding quite an extra cost and potential efficiency loss/design complexity (how do you route all those pipes from the manifold without causing overheating?) and my argument is that this doesn't seem justified by the risk of loop failure. 10 hours ago, Gus Potter said: My gut feeling is I'll never convince you... but hey ho, it's your money, not mine! I was hoping my comments would solicit others to speak up as I don't have practical experience on this. I'm open to being convinced but I would like to see some detail to back up your argument. To reiterate, I am arguing from the perspective of a new install in a modern low energy home. Retrofit in a high energy home might be different (not really thought hard about it). 3 hours ago, Beelbeebub said: As someone who is slowly retrofitting radiators and fan coils to replace a failed UFH install (not for any of the reasons Gus cites though) - whilst adding a radiator is the simplest and cheapest option, it is not always simple or cheap and I have the advantage of preexisting distribution pipes to individual room manifolds. What was the reason for failure? Edited November 24, 2025 by -rick-
Beelbeebub Posted November 24, 2025 Author Posted November 24, 2025 Pretty much every single UFH install checklist has a flow test (in that you fill the pipes with water so obviously you pick up any glow issues then) and a pressure/leak test - usually 24h. If any leaks or damage are detected the whole loop is replaced - it's never advised to joint the pipes. As Rick said, a bad install wil have problems, but that is true of any aspect of any building. I remember seeing a YT vid where an extension had some settlement and when the builder dug down the foundations had been filled with rubble including empty paint tins and bottles with just a skim of concrete over the top.
-rick- Posted November 24, 2025 Posted November 24, 2025 12 minutes ago, Beelbeebub said: Pretty much every single UFH install checklist has a flow test (in that you fill the pipes with water so obviously you pick up any glow issues then) and a pressure/leak test - usually 24h. If any leaks or damage are detected the whole loop is replaced - it's never advised to joint the pipes. I was thinking a bit more rigorous than the standard as I'm not sure the standard pressure type testing would pick up a restriction/kink that easily (good for catching more servere damage). But it's hardly a huge deal to attach a circulating pump and measure flow/pressure.
Beelbeebub Posted November 25, 2025 Author Posted November 25, 2025 19 hours ago, -rick- said: I was thinking a bit more rigorous than the standard as I'm not sure the standard pressure type testing would pick up a restriction/kink that easily (good for catching more servere damage). But it's hardly a huge deal to attach a circulating pump and measure flow/pressure. When I installed mine, I filked each loop via a hose and checked the water flowed out nicely as a way of checking for restrictions. The I pressure tested the system. I was also careful laying down the loops not to kink the pipe. One loop did get kinked and was lifted out and repaid with a fresh coil (the kinked coil was reused for a shorter loop where the knik was cut away) - took about 30 minutes extra. Given most of the loops require the flow valves winding in to restrict them anyway, even if there was a mild restriction as long as you can get the flow required by upping the pump settings and winding the restrictions down on the other loops it isn't a major practical issues (though a bad one from an installation quality perspective) 1
-rick- Posted November 25, 2025 Posted November 25, 2025 5 minutes ago, Beelbeebub said: I was also careful laying down the loops not to kink the pipe. One loop did get kinked and was lifted out and repaid with a fresh coil (the kinked coil was reused for a shorter loop where the knik was cut away) - took about 30 minutes extra. So why are you replacing this system if you took the care to make sure the pipes were all good? 5 minutes ago, Beelbeebub said: Given most of the loops require the flow valves winding in to restrict them anyway, even if there was a mild restriction as long as you can get the flow required by upping the pump settings and winding the restrictions down on the other loops it isn't a major practical issues (though a bad one from an installation quality perspective) Good point. It's one of my arguments that the pipes in general have a lot of potential to increase output so extra loops aren't necessary. I was thinking that if you wanted to rule out any kinks to pipes that while it would work might have the potential to cause problems in future then a more thorough test might be justified.
Beelbeebub Posted November 25, 2025 Author Posted November 25, 2025 57 minutes ago, -rick- said: So why are you replacing this system if you took the care to make sure the pipes were all good? Oh, I've moved house since then! 😁 The system I put in 14 years ago is trucking along just fine We swapped houses with my parents as they were struggling in their house and ours was designed for "elderly living". Their house was built on the late 90's when UFH was over new (to the UK). It's not the (now common) PEX/PB pipe akin to speedfit. It was a small bore rubber (actually thermoplastic elasomer - think edge of an aerobie or soft touch handles) pipe system. With a clever counter flow design to minimise the temperature variation over the length of the run, which allowed it to be laid "up and down" rather than in spirals. Turns out that isn't an issue anyway. Unfortunately the rubber started failing after about 5 years due to a catastrophic screw up over material compatibility (turns out it degraded when in contact with warm water with dissolved copper ions in it). At that point the company went bust so the "50 year guarentee" was useless. So my parents fiddled the system on at low pressure and temperature for the next 25 years. Interestingly it kept the house warm at a flow temp of below 40C. If it was still operational it would be great for a HP,! Unfortunately my dad's dementia meant he tried to fill the Ch system and forgot how to turn the filler off so it over pressured and burst loads of thr (now brittle) pipes. So it now leaks like a sieve and is mostly decommissioned. Ironically the only but that is still operational is the zones embedded in the slab as the concrete provided the structure to resist the pressure. 2
Roger440 Posted November 26, 2025 Posted November 26, 2025 To return to the original topic, looks like Rachael has indeed binned the ECO4 scheme if indeed the news is reporting correctly. They just call it an ECO scheme so not 100% sure. Good news for the taxpayer. Bad news for me.
JohnMo Posted November 26, 2025 Posted November 26, 2025 4 minutes ago, Roger440 said: Bad news for me. Early bird, procrastination etc...
Roger440 Posted November 26, 2025 Posted November 26, 2025 1 minute ago, JohnMo said: Early bird, procrastination etc... Indeed. Can only blame myself for that. I did, however, think it was a nailed on certainty that the scheme would continue in ever more generous form. But, occasionally, sensible things happen.
JohnMo Posted November 26, 2025 Posted November 26, 2025 But "In the Autumn Budget, it was revealed that the current iteration of the scheme, ECO4, would end on 31 March 2026" So you have 4 months for Eco4, but the BUS grants stay in place for now. So don't seem to be affected.
JamesPa Posted November 26, 2025 Posted November 26, 2025 (edited) ECO4 seems to have been a bit of a disaster so perhaps its not such a bad thing that its been scrapped! Its a shame to reduce subsidies for insulation though, perhaps they intend to take the time to work something up which is more robust or alternatively just put pressure on landlords to upgrade (at their own expense) as presumably a high proportion of poorer households are renters. Actually thats already baked in I think to the RRA and the requirement that rental properties are EPC C or better from (date I cant remember). It will be interesting to see how this develops. Ed Miliband looked very pleased during the budget speech so clearly he doesn't feel 'got at' as some suggested he might. 10 pages of discussion on this forum based on a 'leak'. Was it even a leak or just the newspapers making stuff up to sell their bile? SAtarting a rumour is dead easy. Edited November 26, 2025 by JamesPa
ProDave Posted November 26, 2025 Posted November 26, 2025 There has been a lot of "poor" reporting in the last few days. One being the energy price cap is increasing very slightly, about 25p to most households. BUT hold on, the main stream news does not drill down into details. It turns out gas prices are going DOWN 5% while electricity prices are going UP 5%. That is hardly what you want to convince people to switch from gas to electricity is it? But it gets worse. Why is this happening? Well gas is going down to reflect the drop in wholesale prices. So why is electricity going UP? That apparently is because of all the network upgrade spending so the grid can cope with all the new wind farms and increased electricity demand. At this point my blood starts boiling and steam comes out of my ears. Several people including the PM have told us electricity prices will come down as we build more wind farms. This RISE in electricity prices now, shows that to be a LIE and in fact as more wind farms are built and the grid is expanded, those costs are being added to our bills and prices are going UP because of the extra infrastructure updates. Don't you just hate it when we are fed miss information?
-rick- Posted November 26, 2025 Posted November 26, 2025 6 minutes ago, ProDave said: At this point my blood starts boiling and steam comes out of my ears. Several people including the PM have told us electricity prices will come down as we build more wind farms. This RISE in electricity prices now, shows that to be a LIE and in fact as more wind farms are built and the grid is expanded, those costs are being added to our bills and prices are going UP because of the extra infrastructure updates. I don't mind that we are finding a way to pay for much needed upgrades, but adding it to the cost of electricity is mad and I agree that the messaging is infuriating. Add the cost to gas an remove the costs from electricity. Average person with gas boiler will pay a bit more, those who are electricity only pay less, EV owners pay less. This government (and the previous one) are fixated on not touching the big ticket items that they end up creating huge amounts of perverse incentives that drag our economy down and pile on hidden costs that put off investments and improvements (unless specifically government backed). The worst thing is that I don't think any of the 5? parties currently competing at similar levels in the polls seem to be offering an alternative. 1