Conor Matthews Posted November 11, 2017 Share Posted November 11, 2017 I have just bought a property which was newly built in 2013 , shortly after being occupied the property was fire damaged. The UFH system was decommissioned shortly after the fire which extensively damaging the wooden joists & rafters however did not impact on the floor slab. The building was left exposed to the elements for the past 4 years, my question , is the UFH pipe work in the slab still fit for purpose ? Link to comment Share on other sites More sharing options...
ProDave Posted November 11, 2017 Share Posted November 11, 2017 Hi Conor I have split this post into a new thread as it was not really related to the existing thread you posted it in. My gut feeling is since most UFH uses plastic pipes, it is highly likely the pipes may have been heat damaged where they exit the floor slab into the manifold. A careful examination of that area, and if they look okay a pressure test will confirm their integrity. 1 Link to comment Share on other sites More sharing options...
PeterW Posted November 12, 2017 Share Posted November 12, 2017 Hi Conor - like @ProDave I would suggest the best course of action would be to pressure test the loops. I would expect any damage would have been caused to the exposed pipework at the manifold so I would check that first. Removing the manifold will create you a few issues but I would want to test each loop to a minimum of 4 bar wet pressure and leave it for 24hrs to show any leakage. You may end up digging out some of the pipework near the manifold to extend the existing loops if they were damaged but that is par for the course in this sort of situation. 1 Link to comment Share on other sites More sharing options...
Nickfromwales Posted November 12, 2017 Share Posted November 12, 2017 A photo of where the pipes exit the slab may help. Close ups please. Oh, and welcome aboard . Link to comment Share on other sites More sharing options...
Conor Matthews Posted November 12, 2017 Author Share Posted November 12, 2017 14 hours ago, ProDave said: Hi Conor I have split this post into a new thread as it was not really related to the existing thread you posted it in. My gut feeling is since most UFH uses plastic pipes, it is highly likely the pipes may have been heat damaged where they exit the floor slab into the manifold. A careful examination of that area, and if they look okay a pressure test will confirm their integrity. Hi Dave, Apologies for jumping in on your previous tread, it's my first time joining a forum so I am not 100 % sure about the protocol and how to post questions. I examined the pipe work from the slab to the manifold its absolutely perfect, I'll send photos after my next site visit. Their was no fire damage to the ground floor and 95% of the first floor joists are without fire damage the bulk of the damage was confined to the roof. The manifold was removed , I was going to blow air down the lines to figure out the flow and return and then hook up a new manifold and run a pressure test - what's the recommended pressure to use ? Many Thanks conor Link to comment Share on other sites More sharing options...
Nickfromwales Posted November 12, 2017 Share Posted November 12, 2017 Just hook it up to the cold mains as that's pretty much the highest pressure it's going to see. 24hrs per loop if you want to save fittings or tee them all together. One of these will be fine Link to comment Share on other sites More sharing options...
PeterW Posted November 12, 2017 Share Posted November 12, 2017 3 hours ago, Conor Matthews said: I was going to blow air down the lines to figure out the flow and return and then hook up a new manifold and run a pressure test I reckon it will have water in it as there is nowhere for it to go, so I would flush it with clean water to find the loops if you use a pair of JG Sp****it appliance taps you can normally get them to push onto the pipe and then hook the hose to that - as soon as you work out which loop is which, run the hose through them for a few minutes to flush out any crud. Link to comment Share on other sites More sharing options...
Nickfromwales Posted November 12, 2017 Share Posted November 12, 2017 1 hour ago, PeterW said: I reckon it will have water in it as there is nowhere for it to go, so I would flush it with clean water to find the loops if you use a pair of JG Sp****it appliance taps you can normally get them to push onto the pipe and then hook the hose to that - as soon as you work out which loop is which, run the hose through them for a few minutes to flush out any crud. If it's 15mm UFH pipe not 16mm . It needs to be a reliable positive connection for pressure testing. Link to comment Share on other sites More sharing options...
PeterW Posted November 12, 2017 Share Posted November 12, 2017 1 hour ago, Nickfromwales said: If it's 15mm UFH pipe not 16mm . It needs to be a reliable positive connection for pressure testing. Yep however to flush them out and fill full of water it’s not that important but I agree @Nickfromwales for the pressure test you need to get the right size ... Link to comment Share on other sites More sharing options...
Onoff Posted November 12, 2017 Share Posted November 12, 2017 Might be something written on the tails faintly that will tell you the spec and diameter. Link to comment Share on other sites More sharing options...
Nickfromwales Posted November 12, 2017 Share Posted November 12, 2017 2 hours ago, Onoff said: Might be something written on the tails faintly that will tell you the spec and diameter. Usually not enough pipe to see the print as its repeated every metre, so just get a 15mm olive and see if it's snug or loose. 1 Link to comment Share on other sites More sharing options...