Barney12 Posted August 26, 2017 Share Posted August 26, 2017 Due to space constraints I want to put an electric towel rail on the wall at the end of the bath. Obviously that's going to be Zone 1. An IPX4 electric rail doesn't seem to hard to find but is it acceptable to use a flex outlet plate sealed with silicone to achieve the required protection? I can't seem to find an internal IPX4 rated flex plate? Thoughts? Link to comment Share on other sites More sharing options...
PeterW Posted August 26, 2017 Share Posted August 26, 2017 I have the same issue and the sparky is running the cable back out to a box with one of these in it http://sinolec.co.uk/en/rewirable-socket-plugs/1211474--ip68-waterproof-3-pole-plug-and-socket-cable-connector-32a-450vac.html Link to comment Share on other sites More sharing options...
Jeremy Harris Posted August 26, 2017 Share Posted August 26, 2017 (edited) AFAIK, there are no approved IPX4 flex outlets readily available (at least I've not seen any) and you cannot legally make a non-IPX4 outlet into one by just adding sealant - it has to be tested and approved as complying with the ingress protection rating. So, the answer is to run the cable outside zone 1, to a point where you can then fit a standard outlet. With a bit of ingenuity you should be able to run the cable neatly, whilst retaining the ability to replace it. Buried conduit in the wall, that slopes down to the bath end, with the outlet plate fitted above the lowest point, would seem to be OK. You could run the conduit and cable into the rear of the plate to make a neater job. Replacing the cable would be easy enough, as heat-resistant flex is quite stiff so should poke up a bit of conduit easily enough. Looking at the regs I can't see any obvious gotchas with such an arrangement. Edited August 26, 2017 by JSHarris Link to comment Share on other sites More sharing options...
Barney12 Posted August 26, 2017 Author Share Posted August 26, 2017 As it's mounted on a stud wall can I simply run the cable through the wall to a flex plate on the other side of the wall thus outside all zones? Link to comment Share on other sites More sharing options...
PeterW Posted August 26, 2017 Share Posted August 26, 2017 14 minutes ago, Barney12 said: As it's mounted on a stud wall can I simply run the cable through the wall to a flex plate on the other side of the wall thus outside all zones? Yep thats my other towel rail..!! Link to comment Share on other sites More sharing options...
Jeremy Harris Posted August 26, 2017 Share Posted August 26, 2017 (edited) 22 minutes ago, Barney12 said: As it's mounted on a stud wall can I simply run the cable through the wall to a flex plate on the other side of the wall thus outside all zones? Yes, this is what I've done with one of ours, it runs through the stud wall, via a short bit of conduit, to a time switch mounted on the wall on the landing. Just make sure that there is a slope such that water cannot run along the cable to the termination point Edited August 26, 2017 by JSHarris Link to comment Share on other sites More sharing options...
Onoff Posted August 26, 2017 Share Posted August 26, 2017 IP55 towel rail's are available btw. As are ones where the "flex" is hidden in the fixing bracket. Link to comment Share on other sites More sharing options...
Nickfromwales Posted August 26, 2017 Share Posted August 26, 2017 2 hours ago, Onoff said: IP55 towel rail's are available btw. As are ones where the "flex" is hidden in the fixing bracket. The lower one is the cable transit. Link to comment Share on other sites More sharing options...
lizzie Posted August 26, 2017 Share Posted August 26, 2017 48 minutes ago, Nickfromwales said: The lower one is the cable transit. Like your towel rail. I am just starting to look. Any recommendation for suppliers? Link to comment Share on other sites More sharing options...
Nickfromwales Posted August 26, 2017 Share Posted August 26, 2017 @lizzie Its not my bathroom . I'm just a guy that fits these wonderful things The pics I post are from clients houses as I'm a self employed tradesmen who, one day, may get to join the lucky home builders here. That one came from a reseller, ( bathroom showroom ), but you can purchase one from somewhere like This directly. Not cheap, but it is a nice unit. Link to comment Share on other sites More sharing options...
lizzie Posted August 26, 2017 Share Posted August 26, 2017 1 hour ago, Nickfromwales said: @lizzie Its not my bathroom . I'm just a guy that fits these wonderful things The pics I post are from clients houses as I'm a self employed tradesmen who, one day, may get to join the lucky home builders here. That one came from a reseller, ( bathroom showroom ), but you can purchase one from somewhere like This directly. Not cheap, but it is a nice unit. Thanks Nick I will explore.I am Welsh love your felinfoel dragon logo? Link to comment Share on other sites More sharing options...
Nickfromwales Posted August 27, 2017 Share Posted August 27, 2017 3 hours ago, lizzie said: Thanks Nick I will explore.I am Welsh love your felinfoel dragon logo? Tastes better than it looks Link to comment Share on other sites More sharing options...
SteamyTea Posted August 27, 2017 Share Posted August 27, 2017 So does welsh lamb in a kebab Link to comment Share on other sites More sharing options...
Jeremy Harris Posted August 27, 2017 Share Posted August 27, 2017 (edited) 5 hours ago, Nickfromwales said: Tastes better than it looks I remain unconvinced. I must have consumed many gallons of the stuff in the Copper Beech at Abercraf over the years, and I rather think it deserved it's alternative name, "Feeling Foul"................ Edited August 27, 2017 by JSHarris typo - used English spelling by mistake............... Link to comment Share on other sites More sharing options...
Nickfromwales Posted August 27, 2017 Share Posted August 27, 2017 2 minutes ago, JSHarris said: I remain unconvinced. I must have consumed many gallons of the stuff in the Copper Beech at Abercrave over the years, and I rather think it deserved it's alternative name, "Feeling Foul"................ "Many gallons" means you kept going back for more ?? 1 Link to comment Share on other sites More sharing options...
CC45 Posted August 27, 2017 Share Posted August 27, 2017 It is a good pint, reared on it so I could be biased but I am addicted to Theakston Old Peculiar....... when is Aldi going to stock it again? Link to comment Share on other sites More sharing options...
Jeremy Harris Posted August 27, 2017 Share Posted August 27, 2017 (edited) 15 minutes ago, Nickfromwales said: "Many gallons" means you kept going back for more ?? Not really. Caving club members from Penwyllt were banned from the other pubs in the valley, particularly the Ancient Briton, so we either went down to Abercraf to drink in the Copper Beech or we didn't drink at all................... Edited August 27, 2017 by JSHarris Link to comment Share on other sites More sharing options...
ToughButterCup Posted August 27, 2017 Share Posted August 27, 2017 31 minutes ago, JSHarris said: [...] Caving club members from Penwyllt were banned from the other pubs in the valley, [...] Frankly, I'm not surprised. It's the only place -in the world- where, showering after a lengthy saunter underground with the club members, that the blokes were (still are perhaps?) joined by the girls in the showers (1973). Nobody even flickered the tiniest reaction. I kept my back to the wall. And my eyes to the ground. I lathered up as much as I could. Reprobates all. Link to comment Share on other sites More sharing options...
Jeremy Harris Posted August 27, 2017 Share Posted August 27, 2017 (edited) 13 minutes ago, recoveringacademic said: Frankly, I'm not surprised. It's the only place -in the world- where, showering after a lengthy saunter underground with the club members, that the blokes were (still are perhaps?) joined by the girls in the showers (1973). Nobody even flickered the tiniest reaction. I kept my back to the wall. And my eyes to the ground. I lathered up as much as I could. Reprobates all. Things did change when the ladies showers and dormitories were added to the cottages at Penwyllt in the late 70's, and the committee seemed to get a bit sanctimonious about mixed showers and mixed bunk rooms after that, to the point of creating a "married" bunk room, and almost asking to see a marriage certificate before allowing couples to sleep there. This was in contrast to some of the Northern clubs. I remember taking my then new girlfriend (now my wife) for her first ever caving trip, up to Red Rose Cave and Pothole Club, at Easter 1986. There the bunk rooms were Alpine style (one very long mattress with boys and girls all snuggled up together) and mixed showers. I well remember coming back from a group trip down Lancaster Pot and then back out through Wretched Rabbit to the beck, when we all went for a shower, where we were all chatting away animatedly. After a few minutes I realised that the "bloke" next to me had bumps on her chest.......... Edited August 27, 2017 by JSHarris Link to comment Share on other sites More sharing options...
Nickfromwales Posted August 27, 2017 Share Posted August 27, 2017 1 hour ago, SteamyTea said: So does welsh lamb in a kebab We both know that most kebabs are made from knuckle and ash . That's why it's better to eat one when your pissed ? Link to comment Share on other sites More sharing options...
SteamyTea Posted August 27, 2017 Share Posted August 27, 2017 (edited) 3 hours ago, Nickfromwales said: That's why it's better to eat one when your pissed One of my dares is to eat one sober, at lunch, with a knife and fork, and in public. I get strange looks. Think I will try some 'Doomsday' on the next one (see youtube for this years chilli challenge). Edited August 27, 2017 by SteamyTea Link to comment Share on other sites More sharing options...
Jeremy Harris Posted August 27, 2017 Share Posted August 27, 2017 With reference to this anecdote: http://forum.buildhub.org.uk/ipb/topic/3478-electric-towel-rail-above-end-of-bath/?do=findComment&comment=54532 I've just found a copy of an archived SWCC Newsletter from 1986 referring to this trip up North: http://www.swcc.org.uk/aboutswcc/newslett/archive/Newsletter_101_1986.pdf There's even a photo of a very much younger me, and a very brief report of our trip down Lancaster Pot, that I've just snipped out: That's me standing right at the back in the doorway to the club house, with John Lister (who was to be my best man a while later) kneeling down in the front. All the others are also visiting SWCC members who went on that trip through Ease Gill, although I can't recall all of the names. 1 Link to comment Share on other sites More sharing options...
Jeremy Harris Posted August 27, 2017 Share Posted August 27, 2017 (edited) I've just found a guy that's made a video of the trip from Lancaster and out through Wretched Rabbit, that same 5 or 6 hour trip we did back in Easter 1986: What's missing is the spectacular bell-shaped chamber that the initial abseil down Lancaster brings you out into. You enter that tight little pothole shown at the start of the video, then it opens out to this (you can just see the base of the narrow entrance pot from the surface at the very top centre): One of the best entrances to a cave system I've ever seen, really dramatic as you leave the narrow bit and then swing out into that big cavern below. I will admit to yelling "geronimo!" on the free fall bit............. Edited August 27, 2017 by JSHarris typo Link to comment Share on other sites More sharing options...
Nickfromwales Posted August 27, 2017 Share Posted August 27, 2017 @Barney12, I rally didn't see this happening @JSHarris, I think this digression should get some sort of BH award. Stunning to see though. Link to comment Share on other sites More sharing options...
Russell griffiths Posted August 28, 2017 Share Posted August 28, 2017 Getting away from kebabs and potholeing can somebody explain a bit more about the ipx4 rating on the towel rail. I have just taken an old towel rail down as I didn't like it being close to the new shower I put in, but to be honest we really miss it so a safe version would be really welcome. The power supply was always on the other side of a stud wall in the airing cupboard so that is ok, the old one just looked so crap it had to go. Cheers off out to get a kebab now it's made me feel hungry. Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now