deancatherine09 Posted April 16, 2023 Posted April 16, 2023 Hi all, I've had a little look through some similar posts, and then done some calculations to try and back up my thinking! We are building using MBCs Passive Twin-wall system, with passive foundation and Triple-glazed Velfac windows. We had a SAP calculation done for us, and sent this out when requesting ASHP quotes. We got quotes back from multiple companies, and all seem to specify 15/16kW ASHPs, but we can't shift the feeling that this is massively oversized. My calculation was as follows: (Data from SAP report) 8. Space heating requirement Space heating requirement for each month, kWh/month December = 1702.24kWh 9a. Energy requirements – Individual heating systems including micro-CHP) Water heating Fuel for water heating, kWh/month December = 82.86kWh So taking the calculation from another thread, December needs 1785.1kWh, which is 57.6kwH per day, or average of 2.4kW (24/7) And assuming it is running for half the time, 4.8kW requirement from the ASHP? Am I missing something obvious in the SAP report that means we actually need a 15kW ASHP? - as several companies have told us we need such a huge one? Revised SAP Documents - Burbank.pdfFetching info...
jack Posted April 16, 2023 Posted April 16, 2023 On 16/04/2023 at 09:08, deancatherine09 said: December needs 1785.1kWh, which is 57.6kwH per day, or average of 2.4kW (24/7) And assuming it is running for half the time, 4.8kW requirement from the ASHP? Expand It's a combination of ignorance and laziness imo. We had this with our plumber, who had never worked on a low energy house before. He started by proposing a 16 kW unit for our 289 m2 MBC twinwall construction house, then countered with a 12 kW unit when we told him how much energy would be needed. He was genuinely concerned about how much the internal temperature of the house would drop if it took 2+ hours to heat the DHW tank. Nothing we could say would convince him otherwise. In the end we went with a 5 kW Panasonic Aquarea and it's been perfectly fine. That said, if I were doing it again, I'd potentially consider a higher capacity unit. With time of use tariffs becoming increasingly common, the potential to push some or perhaps even all of your heating and DHW into the cheap times is appealing. It's harder to do this with a smaller ASHP. For example, we've been on the Octopus GO tariff for a couple of years. We only get four hours at the cheap rate. It can take up to two hours to reheat the DHW tank, leaving only two hours to pump heat into the slab. A more powerful ASHP would help reduce the time spent heating the DHW leaving more time for slab heating. Alternatively, or in addition, I'd also consider adding a buffer tank for the UFH so that can be heated during the cheap time to act as a reservoir for the UFH for the rest of the day. It's possibly less of an issue if you're considering batteries. They allow more flexible interaction with time of use tariffs.
ProDave Posted April 16, 2023 Posted April 16, 2023 My heat loss calculations showed worst case heat loss was 2.2kW and my house is being heated quite comfortably with a 5kW ASHP So you should be fine with a 6kW ASHP As others have said, a lot of contractors just cannot grasp the concept of a low energy house, and want to specify something bigger so they have no liability if a small ASHP proves inadequate.
JohnMo Posted April 16, 2023 Posted April 16, 2023 Your heat usage is similar to yours, which slightly lower by month, but by hourly average, pretty similar. I am in the process of installing a 6kW machine. What you need to do is ensure at the lowest design temperature, the capacity the chosen ASHP can meet and exceed your max heating needs, so it leaves capacity for DHW heating. Previous experience and detailed monitoring of our gas consumption shows the unit to be a little over sized, but the next size down unit to be a tight fit heating capacity wise. So I would say they units mentioned by your suppliers are massively oversized.
JamesPa Posted April 17, 2023 Posted April 17, 2023 +1 on the thread title. The latest 'mcs compliant' quote I have received is recommending 2 midea 12kW units for a price of £25,086 less the 5k government grant. Their own estimate of house consumption is just short of 17kW, my estimate using mcs assumptions but the correct u values for walls etc is 11kW, and the actual measured consumption during an extended period when temperatures both day and night were -2C (pretty much the recommend design temp here in the south east), is 7.5kW. Oh and they propose to run the system at a flow temp of 55C. I can get a 'discount' of 1750 on the price if I accept within 30 days, entailing a 5K deposit. Need I say more?
sharpener Posted April 17, 2023 Posted April 17, 2023 Do they think you came up the Clyde on the last banana boat or what?
eandg Posted April 17, 2023 Posted April 17, 2023 On 17/04/2023 at 17:00, sharpener said: Do they think you came up the Clyde on the last banana boat or what? Expand Long time since I heard that though unfortunately not that long since I've experienced some chancers in this area - some of the spec/quotes for solar and ASHP from Scottish suppliers has been wild. We've ended up with a 7kW system but one guy specced 13.2kW and wanted 16 grand for it.
Conor Posted April 17, 2023 Posted April 17, 2023 (edited) Your house is basically same U value spec as ours but our house is a bit bigger... Our 9kW heat pump coped admirably with the cold snap in December. In theory we could have got away with a 5kW unit, but glad of the larger one as we only run it 7 hours a day on Economy 7. For a 5kW unit, it would have been running 24x7. Get it modelled in PHPP and use the figures it spits out. The SAP is shite. Edited April 17, 2023 by Conor 1
scottishjohn Posted April 20, 2023 Posted April 20, 2023 if needing a larger ASHP,due to size of house -- is there any savings in costs going for a 3phase unit over a single phase unit as iwill have 3 phase supply
CalvinHobbes Posted May 3, 2023 Posted May 3, 2023 On 20/04/2023 at 22:44, scottishjohn said: if needing a larger ASHP,due to size of house -- is there any savings in costs going for a 3phase unit over a single phase unit as iwill have 3 phase supply Expand I thought you cant use economy 7/off peak on 3 phase?