Hello there

newbuild @warrant stage. I have built before and installed ASHP/MVHR, SIP build. This time SIP build but I am struggling with the ventilation as I felt the last system was noisy and I could not sleep with it on.  Is there a website? That would list MVHR by noise output 0r what else could I install. Bungalow 3 bed. Most manufacturers indicate theirs is the best but end user May be more honest. Thanks for taking time to read. 

Link to comment
Share on other sites

If it's noisy it's a good indicator that the unit was either undersized or the ducting was not correctly sized or installed badly.

 

MVHR should at normal flows be almost silent.

 

I think you are looking for the wrong information, getting the design right is key, a quiet unit badly installed will be noisy 

  • Thanks 1
Link to comment
Share on other sites

@Yvonne, do you know what speed your original unit was set to run at? If set for the normal statutory flow levels it could well have been running faster than actually required.

 

Generally, I think most have found that the statutory rate is far higher than needed. As a guide, I generally run mine at just below half the rate suggested by the rules.

  • Thanks 1
Link to comment
Share on other sites

2 hours ago, Yvonne said:

Is there a website?

Yup, you've just found it ;) Welcome aboard! :) 

I've always used box attenuators for silencing, plus I'm always over-generous with duct runs ( doubling-up where others would run a single ) and I've ALWAYS been an advocate of installing the next size up unit vs what is required. 

I've used one cheap bag of shit from EsaveP which was a boat anchor, and then went to Brink ( which are Passivhaus certified ) and haven't looked back. If a job needed a 325 ( with 160mm connections ) I would simply jump to the 400 ( with 180mm connections ) so I could reduce the fan speed for the same duty.

My clients have always, without exception, reported that the units run absolutely silently and still maintain excellent air quality / function very well.

 

As said, the best equipment can be installed poorly ( mostly through lack of mitigation by design ) so choose well when making the final selection. And yes, salesman will always say theirs is the best one. That's been happening for centuries ;) 

  • Thanks 1
Link to comment
Share on other sites

@Nickfromwales, the issue here is that this is a replacement unit. While a quieter unit will help, any installation issues (e.g., lack of attenuators, undersized ducts) won't be fixed.

 

There may also be issues of matching the connections of a new unit with the main ducts currently in situ.

 

@Yvonne, can you share some photos of your installation? Do you know whether attenuators have been installed? They'll usually be either a box or a much thicker section of ducting between the MVHR unit and the distribution manifold (big box with lots of smaller ducts coming out of it).

  • Thanks 1
Link to comment
Share on other sites

5 minutes ago, jack said:

@Nickfromwales, the issue here is that this is a replacement unit. While a quieter unit will help, any installation issues (e.g., lack of attenuators, undersized ducts) won't be fixed.

@jack I'm reading Yvonne's post as saying she's doing a second build, and in the first the MVHR was noisy and she wants to avoid that in the next. But the warranty bit confuses me.

 

@Yvonne who designed and specified the system for the first house?

  • Thanks 1
Link to comment
Share on other sites

21 minutes ago, jack said:

@Nickfromwales, the issue here is that this is a replacement unit. While a quieter unit will help, any installation issues (e.g., lack of attenuators, undersized ducts) won't be fixed.

 

There may also be issues of matching the connections of a new unit with the main ducts currently in situ.

 

@Yvonne, can you share some photos of your installation? Do you know whether attenuators have been installed? They'll usually be either a box or a much thicker section of ducting between the MVHR unit and the distribution manifold (big box with lots of smaller ducts coming out of it).

🙄

 

13 minutes ago, Sparrowhawk said:

@jack I'm reading Yvonne's post as saying she's doing a second build, and in the first the MVHR was noisy and she wants to avoid that in the next.

@jack Do try and keep up, please ;)

 

13 minutes ago, Sparrowhawk said:

But the warranty bit confuses me.

 

11 hours ago, Yvonne said:

newbuild @warrant stage.

@Sparrowhawk Do try and keep up, please ;) 

 

🤣

  • Haha 1
Link to comment
Share on other sites

1 hour ago, Sparrowhawk said:

I have no idea what the warrant stage is. Don't royalty hand them out? 😛

In Scotland, you have to get a building warrant to build.  It's the formal process of building control approving your plans and saying you may start.  Equivalent to full plans approval in England and Wales.

  • Thanks 2
Link to comment
Share on other sites

Our fan unit is quite noisy close up but we put it in a small loft void above a porch so its outside of the main cavity walled building. Somewhere like a garage roof would be another possibility if you have an attached garage.

 

 

  • Thanks 1
Link to comment
Share on other sites

On 24/02/2023 at 22:50, jack said:

@Yvonne, do you know what speed your original unit was set to run at? If set for the normal statutory flow levels it could well have been running faster than actually required.

 

Generally, I think most have found that the statutory rate is far higher than needed. As a guide, I generally run mine at just below half the rate suggested by the rules.

Interesting. I believe @jack and I have similar units. I have a Brink Flair 400. Ours was commissioned by CVC and I’m sure they have the statutory amounts. Our air is a touch on the dry side in winter, so maybe I should turn the flow rate down a bit.

 

On the whole I’ve been very happy with it. In the  rooms where we have spent a bit more and have Lindab Airy valves/terminals it is silent . That includes in our master bedroom, en-suite, guest bedroom, study and living areas. In the other bathrooms and in the kids bedrooms we went for the cheap valves/terminals and it is just about audible. It would annoy me if it was in our bedroom like that, but nobody else has complained.

 

Ours only really gets audible in our bedroom and en-suite when it is boosted, but even then it’s not that noticeable.

 

 

  • Like 1