We're building on a plot previously occupied by a bungalow which has a single phase supply with 100amp fuse 

 

We have an ashp (16kwh) and are asking UKPN for permission to install but our electrician is telling us that allowing for electric car point in the future etc that we could be looking at a maximum demand a little in excess of 100amps

 

Has anyone experienced this and know what UKPN will say? I'm guessing these calculations are made on an abundance of caution because ashp are supposed to be efficient etc so won't run at full whack and if we did have electric car point in future we would probably charge at night etc so I don't really want to pay to upgrade to three phase if not really necessary given the single phase supply already there currently. 

 

Any thoughts appreciated! 

Link to comment
Share on other sites

3 minutes ago, Newbuildnewbie said:

we could be looking at a maximum demand a little in excess of 100amps

Maybe if you ran everything at once, but in the real world it's not a problem. We have a 100A supply and a 32A EV charger + Induction hob 20A + 16A cooker +++++ but in practice we never get anywhere close to 100A.

 

  • Like 1
Link to comment
Share on other sites

20 minutes ago, Newbuildnewbie said:

Hi

 

We're building on a plot previously occupied by a bungalow which has a single phase supply with 100amp fuse 

 

We have an ashp (16kwh) and are asking UKPN for permission to install but our electrician is telling us that allowing for electric car point in the future etc that we could be looking at a maximum demand a little in excess of 100amps

 

Has anyone experienced this and know what UKPN will say? I'm guessing these calculations are made on an abundance of caution because ashp are supposed to be efficient etc so won't run at full whack and if we did have electric car point in future we would probably charge at night etc so I don't really want to pay to upgrade to three phase if not really necessary given the single phase supply already there currently. 

 

Any thoughts appreciated! 

You'll be very surprised what will run off a 100A supply. Do not forget about diversity when calculating your max loads ( but I assume your sparky would have already done that ).

If you are really struggling, you could always fit a load-shedding relay which would stop ( for one eg ) the induction hob and the EV charger being on simultaneously. That would bag you a spare 7kW.

Link to comment
Share on other sites

8 minutes ago, Nickfromwales said:

https://www.omnical.co/products/hager/ed183/2295794

 

It was a domestic sparky that made me aware of them tbh. Well he was domestic and light industrial iirc.

Had a quick look, can't see how they work, the Hager link gave me a foreign 404.

Shall have to research more later.

Somewhere, I have a current based switch, was going to put it on my hob supply to turn on an extractor fan, but still not got around to it.

I think it could be used with another one to set up as an logic OR, or AND.  That may a cheap solution.

Link to comment
Share on other sites

4 minutes ago, Nickfromwales said:

I thought it was a handy get-out-of-jail card when tipping the max load scales.

Struggling to find details, but it may just be a self resetting breaker.  I cannot see how it senses the total load in the building.

May be wrong.

Can get them for 13 quid, shall let you buy one and see what you can find.

Link to comment
Share on other sites

Just now, SteamyTea said:

Struggling to find details, but it may just be a self resetting breaker.  I cannot see how it senses the total load in the building.

May be wrong.

Can get them for 13 quid, shall let you buy one and see what you can find.

I'll try and speak to my friend and see if he can state what he did / how etc. Agree, there's the square root of feck all info jumping out at me either.

Link to comment
Share on other sites

10 minutes ago, Nickfromwales said:

I'll try and speak to my friend and see if he can state what he did / how etc. Agree, there's the square root of feck all info jumping out at me either.

I assume with the low current rating, it is used with a current transformer.  And the NC contact would hold a contactor energised (wasteful) that would be released and turn off a big load if the max current was exceeded.

Link to comment
Share on other sites

1 minute ago, ProDave said:

I assume with the low current rating, it is used with a current transformer.  And the NC contact would hold a contactor energised (wasteful) that would be released and turn off a big load if the max current was exceeded.

Yes. A last resort, but an option to get someone out of the cack maybe.

Link to comment
Share on other sites

1 minute ago, Nickfromwales said:

Yes. A last resort, but an option to get someone out of the cack maybe.

Probably a tick box to get the DNO to accept it and nobody cares or will test if it actually works.

Link to comment
Share on other sites

1 hour ago, Newbuildnewbie said:

Hi

 

We're building on a plot previously occupied by a bungalow which has a single phase supply with 100amp fuse 

 

We have an ashp (16kwh) and are asking UKPN for permission to install but our electrician is telling us that allowing for electric car point in the future etc that we could be looking at a maximum demand a little in excess of 100amps

 

Has anyone experienced this and know what UKPN will say? I'm guessing these calculations are made on an abundance of caution because ashp are supposed to be efficient etc so won't run at full whack and if we did have electric car point in future we would probably charge at night etc so I don't really want to pay to upgrade to three phase if not really necessary given the single phase supply already there currently. 

 

Any thoughts appreciated! 

 

Smart EV chargers detect the max current and will throttle back since thy will be the biggest load and and can wait - dinner can't

  • Like 1
Link to comment
Share on other sites

28 minutes ago, ProDave said:

I assume with the low current rating, it is used with a current transformer.  And the NC contact would hold a contactor energised (wasteful) that would be released and turn off a big load if the max current was exceeded.

 

Also called an intensity relay that:

 

The priority relay is designed to prevent overloading of the building's installation due to the simultaneous activation of many large power consumers (e.g. a flow heater).The coil of the ED183 priority relay is connected in series to the receiver with priority.When this receiver is switched on, an output contact opens and the switch on the receiver switches off without priority.
Bioenergy switch:
• automatic disconnection of the supply voltage (phase cable) from the receiver or group of receivers, in the case of detection of no load,
• automatic operation - disconnection of the power supply for 3 seconds when detecting no load or switching off the receiver, monitoring of the state of the powered circuit and re-application of the supply voltage after detecting that the receiver is turned on (electricity consumption)
• manual operation (switching by means of a switch) - the voltage is supplied to the receiver continuously, without monitoring the load condition,
• parameters of the output relay: 1NO 16 A 250 V AC AC1,
• voltage monitoring the state of the receiving circuit: 15 V DC. also suitable for electronic flow heaters
Output: 1 NC contact, 250 V / 1 A AC-1
rated current range: up to 39 A
Relay operating current: 3.1?And?5.7 A
flow heater: up to 27 kW

Link to comment
Share on other sites

32 minutes ago, SteamyTea said:

Does that mean there is some other kit that goes with it?

 

Best I can find at the mo. Relay on the left translates as "receiver priority" on the right "no priority". I'll try and find it in English

 

903a23143392e46d5cf825545c179725.jpg.3b2fe3678c8ef80a49fbae9f80425767.jpg

 

IMG_20220315_212413.jpg.3b67b5d06ddb523c83ea6b6910a4c415.jpg

Edited by Onoff
Link to comment
Share on other sites

14 minutes ago, Onoff said:

Thinking about it my Triton Body Dryer has the same deal in it if you want to run it and a leccy shower from the same cable.

Delightfull.. thanks for the heads up Onoff.

 

Sparkies use a term called diversity. @Carrerahillmay pop up and explain in detail how this works from the IEE regs point of view and the theory. But in summary I understand (I may just know enough to be dangerous!) that although the sum of all your appliances may exceed 100 amps they are less likely to all need maximum demand at the same time. Also, the fuse (100A) in the cable head is apparently called a sand fuse and does not blow with a short surge. Then often at the local sub station there is a 600 amp fuse.

 

But if you have say one of these electric Ferarris that do ultra rapid charging at some 400 amps? you may be on a loser and need separate phases for example.

Link to comment
Share on other sites

Just now, Gus Potter said:

Sparkies use a term called diversity.

 

Beware the Christmas dinner effect!

 

It's all gone pc now with regard to overcurrent protective devices and say RCDs on the same circuit. Diversity between devices in that context is now know as selectivity 😂

  • Like 1