  • 4 months later...
  • 4 years later...
In relation to this topic. I’ve installed ledger boards in the past with resin bolts and had good success.
I haven’t ever wet plastered behind the ledger boards. Would you just wet plastered the area behind the board before installing it or the whole room? Obviously difficult if there is no floor in yet.
I plan on using ledgers with my design and eco joists on 400mm centres.
I remember once spacing the ledger off by 25mm behind the each resin bolts and had so the electrician had an easy route down for his cables. Do we think this is advisable or should be avoided? I have a concrete ground floor so imagine most of the socket ring main and lighting coming down from the first floor void.
Excellent plan for your sparky but I'd worry about the cantilever effect of having the ledger off the wall. Some calcs might be prudent I think.
You could always pre chase the routes for cables behind the ledger and drill an angled hole through the ledger to take the cables.
The area just behind the ledger should be fine. You could always carefully not bother and just slop some airtight paint above and below it afterwards.
 I hear what you mean regarding the cantilever. I will have a word with the sparky and see if a pre planned conduit run or chase could work behind the ledger.
In regards to airtight paint. Do you mean seal the top and bottom edge of the ledger to the blockwork? Would an airtight silicone type mastic be good for this if the timber shrinks? Never used airtight paint direct to blockwork/timber. Am I right in thinking you’re talking about applying it at this junction, prior to plastering?
Yup, airtight paint would give you the option of bringing the airtight layer up and well clear of the floor construction to meet the wet plaster later on.
Airtight sealant would work but you might find it tricky to plaster right to the line of the sealant.
Dilute the airtight paint 5:1 with water as a primer before applying the top layer .
You could always use airtight paint entirely behind the ledger before you attached it to the wall.
Don't forget to put some mastic or sealant in the holes the bolts go into the wall too and to airtight paint the chase behind the ledger.
Edited by Iceverge
That all sounds pretty sensible and practical. A much easier approach then trying to get the plaster in to skim a meter strip around the whole joist band area.
Will look into airtightness paints next.
My eco joist supplier is able to provide my joists with an amount of ‘trimmable’ ends in order to get the best fit.
In reality it is much more difficult building up all the masonry 2 storeys without the first floor to work off. We’re about done now so looking forward to putting a roof on and installing a floor.
No need to do this is have thought.
Just build the walls say 1-2 courses above the first floor height, partially chase them for your services. Paint on airtight paint , fix ledger, fit first floor. Carry on as normal.
Thinking about it, drilling concrete, cleaning the hols and inserting resin fixings is a ball ache.
Would it be easier to build in m10x180mm bolts to a mortar bed with 50mm washers in the cavity side. And leave 80mm protruding inside
Drill 20mm holes in the ledger for some shuffle room and bolt in place.
  • 10 months later...
Holy thread bump......
Coming to this thread as we’re in a similar situation. 2 storey (plus loft) house being built in masonry (Celotex 7.3kN high strength blocks) which will be rendered on the outside and wet plaster on the inside. Floor will be Posi-joists which I always assumed would be done using joist hangers. Spoke to one of the brickies/foremen on site who mentioned that they would be using resin anchors rather than joist hangers as it’s easier to level up using a laser level – compared to joist hangers.
Not sure I fully understood it when he mentioned and spent the weekend reading up about it on ChatGPT and Gemini. The unanimous verdict was not to use the resin anchors into the Aircrete blocks as the fixings were going to come loose in the long term and masonry supported joist hangers are the way to go. Spoke to the builder / boss man who confirmed he was going to use joist hangers. Feels like a win but I’m not sure reading some of these comments. We are aiming for an airtight house with parge coat/wet plaster inside and silicone render outside. Is there a preferred way to go? I don’t want squeaks/mechanical fixings failing on me in the next 10-15 years.
Bin the aircrete and the PIR.
Dense blocks and mineral wool batts in the cavity will out perform it in reality.
Too late for that - the ground floor blockwork is already in using the aircrete blocks and PIR. No plans to change it now as the materials for the first floor have also been ordered already.
14 hours ago, Oz07 said:
Why hangers instead of building into the wall?
Can you enlighten a simple mind like mine how that would work - trying to learn all the different variants of putting joists up!
I have done similar using resin anchors to face fix a timber ledger to the wall, then timber to timber joist hangers for the joists.  It means you have more freedom in floor height and better airtightness.  Your blocks should be fine for this as the ledger will have fixings every 400mm.  Cleaning the drilled holes with brush and blower is key to a very strong fixing.
Do the fixings in vertical pairs, 75mm down from the top of the ledger, and 75mm up from the bottom, and repeat until you have run out of money to buy more resin and bar. You'll only get one chance to do this right, so invest in the important things.
100% defo blow the holes out as above, but this will be your builders job and you'll need to impress upon them the job is wanting doing properly where he may say "don't teach me to suck eggs", even if under his breath of in his head..... If they're not on day rates, offer to pick up the tab for the extra hours adding more fixings, which should keep them happy.
Joist hanging off legers is the way forward here for sure, as long as the fixings are at higher frequency AND robust.
Well this is all quite conflicting advice with what ChatGPT, Gemini and the vast majority of the internet sources advise. All the online searching I did discouraged me away from the ledger board approach and said the hangers must be built into the masonry for longevity. The ledger board is only held up using chemical bonds and that the weight of the floor above it would eventually work those bolts loose - especially as I'm using Celcon blocks (which can't be changed).
So I spoke to the builder who has confirmed that he'll be using joist hangers built into the masonry. Much ado about nothing in the end - though I did get to learn something new I guess.
The hangers are just fixed into the Celcon blocks, so out of the fire, and into the frying pan. Just ask your builder to ping string lines for the hangers to be dead straight and level, as that is often 'nearly good', but could have been better. ;)
....."only"..... which are strong as feck.
Ledgers are held up by bolts, not by the resin.
Bolts for the sheer strength, and clamping force, and the resin anchor for holding the bolts (M16 bars) in place.
I'd happily argue that multiples of small fixings using expansion for their means of purchase would degrade the material that the block was made out of, as these are many, and very close together.
@Gus Potter @saveasteading?
You called?
I have only skim read. But I don't see a mention of multiple small fixings... that would apply to a lightweight hanger nailed to  a wall plate though.
This happens to be my preference I think. A timber the same depth or greater than the joist will bolt to the wall without stressing it to much. The deeper it is, the more robust it will all be, and easy.
As above you must watch the builder very closely.
Dont drill too big a hole... the bolt should just fit without force. Threaded rods are usually thinner than stated.
Grind the hole, don't sds it.
Brush out all dust.
Look at the resin mixing and discard it until it is uniform colour.
Turn the bolt as if slowly screwing into the hole this gets the resin fully into the thread. And continue til resin is screwed out of the surface. This also picks up remaining dust.
Don't touch it until it is hard.
Use washer and tighten the nut until the wood just distorts.
Then you use 80p hangers and lots of nails.
OR use heavy duty hangers fixed into the mortar coursing.
Hello all and for
Hope this helps a bit.
This type of thread crops up from time to time on Buildhub. How to fix (connect) floor joists to a wall?
To make an informed decision you first need to go back and determine what the connections are supposed to do. Now the obvious one is that they need to hold the floor up under downwards gravity loads. These loads are the self weight of the floor and most often people, called the imposed or live load.
However, floors often do other stuff. SE's know that a well put together floor acts as a big stiff beam in its horizontal plane (not its depth that you commonly encounter when sizing the floor joists) that can resist horizontal loads. It acts as (what we call) a diaphragm. They are kind of like a bulkhead in a boat that stiffens the structure. We use the floors to provide horizontal restraint to the walls and to shift horizontal loads to a place where we can more easily transfer the horizontal loads in the plane of the floor to the walls and then down to the foundations.
Now as we commonly design for (and take advantage of) diaphragm action we first need to work out what the downwards loads are and then the horizontal loads in the floors that need to be transferred via the joist end connections. Once we know this we can then go about selecting the right connection.. and also know that if we swap out hanger connections and / or use resin anchors in place of another type of fixing say we are not going to do something that compomises the SE design.
Here are some common examples of hangers:
Below is what we call a simple face fix hanger, a joist fixed to a ledger. You can see that this is a light duty type of hanger. It can carry efficiently a downwards load. But it's not designed to carry much say left to right load horizontally. It's definitely not going to be great if the joist wants to pull away from the wall, joist tension.
Below is something a bit more robust. This type of hanger is very common. These can also be face fixed but the image shows the hanger wrapped over the top of the ledger. By doing this wrap over we gain a lot of extra vertical load bearing capacity. You can also see that it may be a bit better if we want the hanger to resist say a left to right horizontal load. But again it will not provide that much joist tension resistance. So much so that the manufacturer does not bother giving a value for this.
Below is something you also see on some floors. By inspection we can see that we could easily push the joist left to right and it is certainly not going to be able to take any joist tension.
Below is a very basic typ of masonry hanger that gets build in. Note the tabs on the top are flat. This type of hanger requires a MINIMUM 3 COURSES OF SOLID BLOCK (675MM MASONRY) REQUIRED ABOVE
HANGER WITH MORTAR FULLY CURED BEFORE APPLYING LOAD.   This masonry above is to stop the tab on the top from unfolding and the joist falling down. You can see that it won't be that good at resisting left to right load or any joist tension load.
If you don't have enough masonry above you can see if something like the below will work. Here the top tab is folded down the back of the masonry. This type of Simpson Strong_Tie hanger is also claimed to
"The SFLHI has been designed to assist in meeting the air leakage requirements as part of the Code for Sustainable Homes. Since the joist is
supported by a hanger and does not penetrate the inner leaf of blockwork, the potential for air leakage is reduced and avoids the time consuming and costly
mortaring and sealing with mastic around built in joist ends."
Also note that there is a short horizontal tie that provides some lateral restraint. Still not that great at resisting left to right horizontal loads though.
Below is another option, different, but I often use these types of brackets as they work in all directions.
Ok, that is a quick run down on connections.. but what about ledgers to use or not?
Well if you want to use a timber ledger the main loads you need to know are the downwards load and if the floor joist to ledger connection is in tension, usually caused by a wind load.
The SE design process for this is a bit iterative. First I look at the loads, then the joist spacing. The joists have some form of metal connection so you can't have a ledger fixing there. I kind of know what will work, if resin anchors then I'll usually look at a 12mm diameter rod as it's a good balance. Now for resin anchors to work you have edge and end distances. Roughly they need to go into the blocks but not too close to the mortar joints. You have to know where the horizontal mortar beds are and so on. To do this kind of design properly you need to understand how things get built on site, know what matters and where adding things to drawings can actually confuse the builder. You have to make the drawing notes easily understood by the builder.
Usually in a dense concrete block most builders, if they follow the drawings can turn out something acceptable at the end of the day. But if you have a lightweight say Thermalite block you can (if the loads are not that high) still use resin anchors. But the installation procedure is more complex and demanding. The holes often need to be under reamed using a special drill bit for example. You need a dilligent and experienced builder for this and if you deviate from the manufacturer's instructions you will likely be in big trouble!
Ok but have you checked with your SE that this is ok. Don't forget.. your builder and you are now making structural design decisions! Thus you are now carrying the can under CDM for example. Best to lift the phone for 10 minutes to your SE and get some assurance that what you are doing is ok.
  • Like 3
Maybe @Gus Potter can answer this better, but I once saw a Youtube about the wire rope used in suspension bridges.
By using multipole strands of relatively small wires a number of properties could be designed in, tensile strength, flexibility, safer failures, easier manufacture etc.
I feel the same way about multiple smaller fixing.  One may fail, but the others should still be able to cope (why a safety factor is used).  They are also easier to fit correctly (I worry about people using adhesives without a proper understanding of the limitations).
Ok to bring this into the domestic context. I upgraded a 1920's conservatory, to stop it falling down. It needed some additonal structural skeleton and some crack stitching ect. The glazing is irreplacable as it the brick plinth at the bottom of the glazing. The roof is a modern abomination.. but fixed that. The top bit cantilevers over the bottom and the steels were rotted and needed replaced. Hat off to the Contractor who managed to install new steels , do other stuff without cracking any of the glass.
The above is a work in progress. But you can see I've put a new timber structure (supposed to look modern) inside and tied the rafters with wire and turn buckles.
Below is a bit off the drawing for the tie wires
image.png.d1f8617f72b6e8463fa94e519994ea1c.pngimage.png.d1f8617f72b6e8463fa94e519994ea1c.png
I selected this wire as it has less strands, less flexible but stonger. The wire you see has a factor of safety of 5.0, some ropes you see often have a factor of safety of 7.. but for good reasons which I won't go into here. So @SteamyTea you are right, the designer needs to select a cable that has the best balance between strength and flexibility.. the more strands, often the more flexible. One strand can fail with less impact, but you generally get a reduction in over all strength with many small strands.. the reasons are complex unless you use a fatter cable.
If I was designing a ballustrade say at around the edge of a balcony I would not use this type of wire. I would go for something with more strands as it's more flexible and workable on site, even if it is a bit less strong. A common offering is a 7 x 7 rope that has 49 strands. The rope you see in the example above has 19 strands.
So do I. There are many that swear by a D4 rated glue.. but this is not a stuctural glue. The D relates to the durability primarily. It does stick things a bit structurally but I won't sign off D4 glue (unless it also has a structural rating) in structural timber applications for example. One default timber glue is to use something like Cascamite.. a resin glue that has been on the market, tried and tested over 40 years.
Edited by Gus Potter
