moldy Posted June 25, 2019 Share Posted June 25, 2019 Does anyone know a wall make up that could achieve a U-value of 0.1 where the overall width from finished external to finished internal is max 350mm? Link to comment Share on other sites More sharing options...
wozza Posted June 25, 2019 Share Posted June 25, 2019 (edited) Try this: https://www.cba-blocks.org.uk/u-value-calculator/ I don't think you would get that low with brick and / or block. Kingspan have a calculator, might be worth trying. Edited June 25, 2019 by wozza 1 Link to comment Share on other sites More sharing options...
A_L Posted June 25, 2019 Share Posted June 25, 2019 (edited) @moldy, you are going to need something like 250mm of PIR/PUR in a timber frame with 50mm eps insulation on the outside and ewi render directly applied (no cavity) Edited June 25, 2019 by A_L typo 1 Link to comment Share on other sites More sharing options...
jack Posted June 26, 2019 Share Posted June 26, 2019 15 hours ago, moldy said: Does anyone know a wall make up that could achieve a U-value of 0.1 where the overall width from finished external to finished internal is max 350mm? Is there a specific reason for targeting such a low U-value? It's pretty aggressive - lower by some way than you need to meet the PassivHaus standard. If you're willing to accept a slightly higher value, your options will be far greater. Link to comment Share on other sites More sharing options...
Gone West Posted June 26, 2019 Share Posted June 26, 2019 15 hours ago, moldy said: Does anyone know a wall make up that could achieve a U-value of 0.1 where the overall width from finished external to finished internal is max 350mm? I can't see how it would be possible with brick and block. We have wall U values of 0.09 but that is with a 495mm overall thickness I-beam timber frame. 1 Link to comment Share on other sites More sharing options...
Conor Posted June 26, 2019 Share Posted June 26, 2019 An ICF wall with a 150mm core and 200mm EPS will give you 0.15. for u value of 0.1 you are talking a 450mm thick wall. 1 Link to comment Share on other sites More sharing options...
SteamyTea Posted June 26, 2019 Share Posted June 26, 2019 http://www.aerogel.uk.com/wallboard.html could save a bit of space Link to comment Share on other sites More sharing options...
Mr Punter Posted June 26, 2019 Share Posted June 26, 2019 With brick and block you may get 0.12 - 0.13 with rigid insulation, insulated plasterboard and lightweight block inner leaf. 1 Link to comment Share on other sites More sharing options...
scottishjohn Posted June 26, 2019 Share Posted June 26, 2019 don,t think the energy saving would EVER pay for the extra cost of the extra insulation I had a few discussions with kingspan tech guy on insulation for a water tank and diminishing returns for extra insulation once up to 150mm of pir ,it would never pay to go any thicker assuming no air leaks . which will probably explain why cold store walls made from pir are not any thicker Link to comment Share on other sites More sharing options...
Ian Posted June 26, 2019 Share Posted June 26, 2019 You'd get there in the required overall thickness by having a 140 timber frame filled with PIR and with a 150mm layer of external PIR insulation then a ventilated rainscreen timber facade 1 Link to comment Share on other sites More sharing options...
scottishjohn Posted June 26, 2019 Share Posted June 26, 2019 2 hours ago, Ian said: You'd get there in the required overall thickness by having a 140 timber frame filled with PIR and with a 150mm layer of external PIR insulation then a ventilated rainscreen timber facade If you changing from block build then 200mmsips panels +50mm exterior+cladding/render then on inside +25mm service cavity+ and 37 or 50mm foam back plaster board. lots of ways to do it --not sure once walls are down to 0.12 there is any real need to go lower Link to comment Share on other sites More sharing options...
Gone West Posted June 26, 2019 Share Posted June 26, 2019 4 minutes ago, scottishjohn said: not sure once walls are down to 0.12 there is any real need to go lower It's not a question of need but want. Where we live having wall and roof U values of less than 0.1 meant not needing to have a conventional central heating system ie UFH or radiators. This was one of our wants. I ran a lot of iterations of PHPP to arrive at this value. This is of course dependent on shape of house, weather etc, but works for us. 1 Link to comment Share on other sites More sharing options...
scottishjohn Posted June 26, 2019 Share Posted June 26, 2019 3 hours ago, PeterStarck said: It's not a question of need but want. Where we live having wall and roof U values of less than 0.1 meant not needing to have a conventional central heating system ie UFH or radiators. This was one of our wants. I ran a lot of iterations of PHPP to arrive at this value. This is of course dependent on shape of house, weather etc, but works for us. that,s absolutely your right and choice . but most decisions are usually a cost versus benefit compromise that's the only reason for my comment Link to comment Share on other sites More sharing options...
Simplysimon Posted June 26, 2019 Share Posted June 26, 2019 On 25/06/2019 at 17:37, moldy said: Does anyone know a wall make up that could achieve a U-value of 0.1 where the overall width from finished external to finished internal is max 350mm? why are you constrained to 350mm? a 350mm i beam filled with cellulose will give you 0.1 u value but will have cladding on outer surface Link to comment Share on other sites More sharing options...