Laundry room sink / appliance plumbing wobble…
marshian replied to Omnibuswoman's topic in General Plumbing
Just a comment....... I like solvent weld pipe far more than I like gasket fittings but when using solvent weld I always consider how I'm going to be able to either remove the section or rod / hose out the pipework in the case of blockages - washing machine powder can build up in pipe work if "someone" over doses the machine on a regular basis (I think this is amplified by cooler temperature washes). In fact the think about future access / maintenance applies to a lot of plumbing in homes. -
In a DHWP set up the flow to rads or UFH stop - the heat source re-charges the HW cyl and then the system reverts to heating House doesn't or shouldn't lose much temperature in the time it takes to do HW unless it's a massive tank
-
It seems that way initially but like most things but you do get you head around it eventually Unheated rooms will steal heat from wherever they can - let me help with an example My house (stupid T shape) has front bedroom above front hallway both having 3 external walls and with the added bonus of north facing - being a "lets not be wasteful with energy sort of chap" (Mrs Alien says "tight b'stard") I didn't heat the front hall for most of the time just bringing it up to temp for the few hours we might use it (arriving and leaving). The Rad in the bedroom above had to have much higher flow rates as well as a higher set point than the other bedrooms (one because of the 3 external walls and two because some of the heat was being stolen by the hall below) Now you might say but heat rises and yes it does but a better statement is that heat always moves to cold and it doesn't care if down is a direction it can move in. So now I heat the front hall to 17 deg - it's cooler than the rest of the house but it does have an internal door to separate it - as a result the bedroom above needs a lower flow rate to the rad because the difference between the two rooms is much narrower So by all means run rooms at lower temps but consider the impact on rooms above or below is all I would say - if you size rads or UFH for low flow temps to provide the heat needed based on a heat loss calculation you could find that the room won't reach target temp if it's having it's heat stolen by a room above or below or even beside it.
-
Blimey 34.5 litres a min is 2070 litres per hour.... that feels like a heck of a lot of flow.
-
Modern pumps are a real head fug - they are a bit to damn clever sometimes My limited understanding is the faster the pump speed the smaller the delta between flow and return so you give the emitter more time to get rid of the heat (That's the impact in my house) but in your case where you are trying to get the emitter to give off more heat it may well prove effective - guess testing and monitoring are required Having said that constant curve is what I settled on (mainly because the flow on proportional settings changed from when I first set the pump up to maybe a week or so later - some learning logic I think)
-
Just to add to @JohnMo's comments - Covered very well below with a bit of the maths Hell yes - Been there done that - "Smart TRV's" that can call for heat from the boiler even if only one room needs it will result in massive energy wastage as the boiler fires up and then potentially short cycles until demand increases
-
You might not need to split the circuits - Heat Geek did a video on pump distortion not that long ago
-
Every house I appreciate is different and responds accordingly but I was running 2 deg setback in most of the rooms for 4 hours at night and 5 hours in the day and in a week of relatively stable OAT's I used more energy on the setback days than I did on the 24/7 (if anything the setback days were slightly warmer although I was only looking at the average temp between coldest and warmest temp across 24 hrs (it could have been colder for longer on the warmer days) It's one of those experiments that you do for fun
-
I know that on my house set up (all rads) setback temps (2 deg setback) just don’t save me any energy - the reheat from setback uses more energy than maintaining a stable temp 24/7 perhaps if I used either a smaller setback or a larger setback it might be different but if I used larger setback I might as well just go back to a schedule and a smaller one seems pointless
-
A booboo may have been made
marshian replied to Post and beam's topic in Air Source Heat Pumps (ASHP)
I'm running pure WC mode but I still have a hallway thermostat - it's acting as a master off switch if the house ever gets to a temp that heating is not required because the hallway has the only rad that is undersized for the area and heat loss (Includes full height stairwell and unheated upstairs landing) -
A booboo may have been made
marshian replied to Post and beam's topic in Air Source Heat Pumps (ASHP)
Oh yes sizing for 35 v 45 results in a significant increase in rad size as I found out I specified DHWP and WC on my boiler install and got S plan............ To give the installer credit he recitified the error and we got there eventually but fundamentally it was what he knew and he thought it would be fine.......... He also couldn't read a WC curve properly until I explained it... Trouble is installers talk a different language to customers - when you talk their language they don't always think you actually know what you want. -
It didn't change a thing (well all that did happen is the room that needed the highest flow lost temp because it was being shared out to other rooms and it's the last in the circuit) So I reverted it to a dumb boiler and manually set the flow temp - still did the same thing ramping up randomly mid burn cycle - often causing + 5 deg trip. Then I needed to do HW cycle so manually increased the flow temp First thing boiler was only slowly increasing temp (because range rated to 4 kWh - ahh bugger need to undo that setting - Increased range rating to Max because it's one button press in the menu. Then boiler reached my previously set max flow temp cap of 45 deg. So that got changed for 70 Deg and then the boiler froze as I was trying to exit the menu - it was doing HW so I just walked away and left it to heating water (it's happened once before and the solution was to turn the boiler off at the main switch) So when it finished the HW I powered down the boiler (made a cuppa and then switched it back on) house needed a top up heat wise so I range rated it back to Min and waited for it to fire. Guess what happened next? It fired - ramped up to 58% and over the course of 2 mins modulated down to min 10.6% and sat there at min for 17 mins and 30 secs - used 0.103 m3 of gas which by my calcs is 3.98 kWh....... It didn't miss a beat for the rest of the day. This morning however it was back to it's old tricks - starting to really get on my wick now So I switched off the boiler waited 5 mins and then waited for it to fire for the next cycle and it respected the min range rating again. So now every time it starts to play up I have a solution to the issue - it's not pretty and I don't believe it's acceptable but I have some information now to go back to Viessmann with to point out that it still has the same problem it had before (and crucially what resets it back to how it should operate) It doesn't seem to matter what pump speed I use Constant Curve 1 or Constant Curve 2 the only difference that makes is the DeltaT at the boiler is 9 deg C with CC1 and 5 Deg C with CC2 Pump in CC1 5.5 w 1.1 m head 0.4 m3/hr Pump in CC2 16 w 3.1 m head 0.6 m3/hr
-
Well it hasn't 😞 so I'm going to put my thoughts down and maybe a proposal for consideration from the great minds of Build Hub The "niggle" now only occurs between 6 deg OAT and 12 Deg OAT So lets cover the data I can provide Pump Pump Speed 0.5 to 0.6 m3/hr set on Constant Curve Watts 15 Head 3.1 m Rads I have 13 Rads all with TRV's in the house table below explains what they are room sizes Heat loss at -2.5 Deg C OAT and how they are set up (Because there are issues with getting the flow rate low enough for some rads and solar gain with some rooms) I regard the circuit as well balanced both upstairs and downstairs I have a pressure relief by-pass but it's fully closed as the circuit never shrinks enough to need it. Boiler Viessmann 100-W "Heat Only" 16kW set up with Weather compensation and DHWP (Using an outside temp sensor and HWD box) It's piped up as X Plan It's running a delta between flow and return at the boiler of 6 to 7 deg C at Weather compensated flow temps Weather Compensation Curve When it's not in the OAT temp range where I see the niggle this is how the boiler behaves Good Days On CH the boiler fires up when the flow temp drops "X" deg below WC Target (Gut feel is X = -7 Deg C below target temp) It will do an initial start at 58% modulation and then over 90 secs drop down to the lowest modulation level that enables the boiler to maintain the target flow temp typically 10.8% It will then run happily at that level until the flow temp exceeds the target by "Y" Deg (Pretty sure "Y" is 5 Deg C above the target temp) Bad Days When it's in the "Niggle" window its behaviour is different during the burn Even if the Boiler is range rated to min (19 out of 100 in the menu = 10.8% or ~4.0 kWh) the boiler ignores the range rating Initial start up is identical to above but very quickly into the period after the start it starts to miss-behave - modulation swings between 10.8% and 30% This frequently results in the Target temp + "Y" being reached during the higher modulation and the boiler shutting down before it's fully refreshed the water in all the rads that were open for heat. My thoughts are that the return temp is changing as some rads have quite a large flow and a decent delta between flow and return and some other rads have much smaller deltas and the boiler is trying to maintain the target flow temp so modulating up and down to provide a stable output. If you read all that - thank you. Proposal So I had a thought what would happen if I set all the rads to an elevated flow rate said sod the balancing control - leave the TRV's to manage the room temps and flows and bring back into play the by-pass (just in case all the rooms hit target temp and TRV's shut down the flow). Part of me says I should just try it and see what happens Part of me says the TRV's will end up managing the flows as they close and the flow rate in the system and the return temps will be the same so it won't change a damn thing. Anyone think anything else will happen?
-
System boiler size dilemma...any advice?
marshian replied to Rick734's topic in Boilers & Hot Water Tanks
Interesting point - maybe there is something I can improve as our current SUDG windows and doors were fitted in 1997 so are coming up for 28 years old................Question is how much better because there are no drafts from around the closures (the window seals are good) they haven't gone yellow like some cheap windows do. I'm thinking its going to be mainly thermal improvements in the glass and gas between the panes and they aren't big windows (circa 1.7m2 in total apperture area for each one) I'm guessing the payback for that level of capital investment would be a bloody long time -
System boiler size dilemma...any advice?
marshian replied to Rick734's topic in Boilers & Hot Water Tanks
Link to Urban Plumbers Heat Loss Calculation Video on YT Watch it - you have most of the dimensions you need and for building fabric there are plenty of resources on the net for W/m2 I started to build my own spreadsheet years ago which was actually fairly accurate on the rooms I did but then I found I could pay £12 for a single use of Heat Engineer software and plug all the info in there and get a very accurate result (Provided you understood the inputs) however they now charge £100 for single use so I can't recommend them anymore. In a nutshell it's just Math but be very careful with ACH (Air Changes per hour) many on line tools massively over egg this element and as a result heating systems are over sized. -
System boiler size dilemma...any advice?
marshian replied to Rick734's topic in Boilers & Hot Water Tanks
Oh and I do think those calcs are a little on the strong size Based on Heat Geek Guidelines Quick and Dirty from your earlier calcs Says for Renovated property with CWI and over 75mm of LI - best case 40 W/m2 worst case 65 W/m2 So Your worst case would be 11.5 kW best case 7.5 kW (not including HW Demand) I have an early 80's 4 Bed detached house which is a stupid T shape so lots of rooms with 2 or more external walls and my overall W/m2 is 35 Improvements post construction are CWI, 300 mm of LI, SUDG Windows and Doors, 52 m2 of 75mm PIR under the suspended ground floor - not much more I can do to it now. -
System boiler size dilemma...any advice?
marshian replied to Rick734's topic in Boilers & Hot Water Tanks
Heat loss calcs A great video by Urban Plumbers covering how to do a basic heat loss calc - worth watching There are other tools on the net like Heat Punk who offer online modelling of heat losses @Jeremy Harris Tool on here is often highly praised but I've never used it All fine until the end - based on the above you need a 16kW boiler max -
Can’t change flow temperature on glowworm energy c30
marshian replied to johnhenstock83's topic in Boilers & Hot Water Tanks
No problem at all - glad the internet could help PS bloody crazy for GW to have a parameter default set at 75 on a condensing boiler -
System boiler size dilemma...any advice?
marshian replied to Rick734's topic in Boilers & Hot Water Tanks
Twice in a day........... 3rd party controls don't add efficiency they kill it - manufacturers advertise it as "Smart" but what it really does isn't Size the boiler to one that modulates down to your house heat loss at whatever the worst OAT in winter for your area is. If you can size it to modulate lower than worst case even better but unless it's a huge leaky gaff you'll have to settle for worst case heat loss because in any half decent house with std improvements of CWI, current regs Loft insulation and double glazed windows and doors you are going to struggle to find a boiler that can go lower than worst case. Size the rads to the meet individual room heat loss at sensible low flow temps Run Weather compensated with DHWP and balance the circuit and you won't need TRV's as anything other than limiters for solar gain -
Help with new heating and hot water system!
marshian replied to bigp26's topic in Boilers & Hot Water Tanks
I never understand why people go for third party controls when a boiler manufacturer offers controls designed to work with the boiler?? (I'm speaking as someone with Drayton controls and a Viessmann boiler but they have no link to the boiler - fundamentally it's just a nice interface for scheduling and the "smart" TRV's make excellent temp limiters in rooms where I can't get the flow rate low enough or rooms with solar gain) Viessmann just go with WC flow temps and DHWP Get a cylinder with a heat pump sized coil and size your rads for a low flow temp (mid 20's to mid 30's) and fit them with pressure independent TRV bodies with flow rates set to the room heat demand and enjoy a quiet efficient boiler which will maintain a sensible temp 24/7 with no intervention from you. PS it really does read like an AI bot question -
Vaillant Ecofit Pure Modulation Question 18kW
marshian replied to Mattg4321's topic in Boilers & Hot Water Tanks
The min outputs are very much aligned to flow temps you are running My Viessmann 100-W 16 kW Heat only (Open Vented) is rated at 2.9 at 80/60 but that increases to 3.2 at 50/30 I'm running it at max 32/25 at -2.5 OAT - it's range rated to absolute min for CH and my data gathering tells me that clearly it's running at 4.0 output under those temps which is perfect for me because house heat loss is a smidge under 4.0kW So in a nutshell the modulation ratio is actually 4.0 but it doesn't really matter to me as it's sized to meet the heat loss of the house with a max of 16 kW which I need to heat HW tank in a reasonable time frame. Ignore the yellow highlighting I used the image elsewhere (Highlighting the importance of knowing what your boiler needs to function properly) -
What's the gap on the other side? (opposite)
-
I wouldn't worry about it - expansion and contraction is normally in the width rather than length - because my flooring finishes at a UPVC french door I have almost zero gap at that end (2mm and I filled that with silicone to stop it being a dirt magnet) Work in progress picture from when I did it
-
Last floating oak floor I did was front hall, toilet, main hallway and dining room as one continuous floor - I removed all the skirting boards and I had cork strips between floor and walls as expansion packers When I had finished the floor I replaced all the skirting and that hid the cork strips For the Lounge which I did a few years later I didn't do it as a floating floor and used hidden nails into the subfloor on every row - I left an expansion gap of 10mm round the edge which was covered by the skirting once replaced Both floors have now been down several years and no difference between them in terms of movement
-
A booboo may have been made
marshian replied to Post and beam's topic in Air Source Heat Pumps (ASHP)
Exactly - it was a real surprise to me how effective "cold to touch" rads are as space heaters in shoulder seasons I was tweaking the balance of my rad circuit this morning (since I increased my pump speed the burn times have lengthened and rooms have started to overheat) OAT was 10 Deg C - target boiler temp was 27 Deg C but I increased the WC curve to extend the burn time so I could get round and measure all the rads Flow Return Diff Room Target Boiler 32.4 25.3 7.1 Kitchen 29.8 26.0 3.8 21.0 20.5 Dining 30.8 27.2 3.6 19.5 20.0 Lounge 31.0 26.2 4.8 19.5 19.0 Hallway 29.6 24.2 5.4 19.5 19.0 Utility 25.8 22.2 3.6 18.0 18.5 Toilet 27.6 23.6 4.0 19.5 19.0 Front Hall 24.4 18.4 6.0 17.0 17.0 Bed 1 28.8 24.2 4.6 20.0 20.0 Bed 2 25.2 21.0 4.2 20.0 19.5 Bed 3 27.8 23.4 4.4 20.0 19.5 Study 28.6 22.8 5.8 19.0 18.0 Bath 29.2 21.6 7.6 20.5 21.0 Ensuite 29.0 22.0 7.0 20.5 21.0