ToughButterCup Posted April 9, 2018 Share Posted April 9, 2018 Our rafters are 225 mm by 47mm. The insulation specified is 200 mm of Kingspan K7 between the rafters (underlayed by 82.5 mm of K18 ) Hence the 25 mm issue. And the 82.5 mm issue I suspect. Architects are like that aren't they? I have 225mm of rafter to fill: should I leave an air gap? (I bet the answer is No) should I fill the gap : 100, 100, 25 and then underlay it all with 60 mm K18 (not 82.5 mm as above) Or do something more intelligent? Which is where you come in. Link to comment Share on other sites More sharing options...
Dee J Posted April 9, 2018 Share Posted April 9, 2018 In older designs there'd be eaves and ridge vents, and that 25mm between insulation and sarking felt would be ventilated. But if that 25mm is within the sealed envelope then by all means fill it with insulation. But don't cut down too much on the overlaying insulation. The rafters need a good cover to reduce cold bridging... Link to comment Share on other sites More sharing options...
Ferdinand Posted April 9, 2018 Share Posted April 9, 2018 (edited) Is there a cost saving opportunity in not using K18 insulated pb? Can it be treated as 2 elements? Would perhaps be cheaper but more interesting to do. Edited April 9, 2018 by Ferdinand Link to comment Share on other sites More sharing options...
PeterW Posted April 9, 2018 Share Posted April 9, 2018 Questions ... Do you have a sarking board ..? Is this flat or sloping ..?? Link to comment Share on other sites More sharing options...
Cpd Posted April 9, 2018 Share Posted April 9, 2018 In my 45 degree pitched roof i have slate breather membrane sarking boards 50mm breather gap with 50mm x 25mm battens atached on either side of the rafters with the 25mm up against the sarking 50mm calotex foamed and taped on top of the battens 120mm calotex up to the inside face of the rafters 25mm calotex full sheets over the rafter ends, fully foamed and taped. Its a PITA of a job, took for ever and was just awful. I have 4 roof vents spread out along the ridge and x2 soffit vents per rafter gap i am happy that its done, i know its been done with 100% attention to detail and will work to its maximum potential but would not do it again. I went with the initial 50mm calotex because i wanted to be sure that at that layer i had a good seal between the vent gap and all other layers of insulation, i did not want any cold air getting between the layers of insulation. Much easier sealing 50mm with foam and tape than a big thick slab of insulation. if there was ever to be a water leak through the slates and somehow past the breather membrane then i wanted a good ventilated gap to keep things dried out as it would be very unlikely to be spotted from the inside. Link to comment Share on other sites More sharing options...
ToughButterCup Posted April 9, 2018 Author Share Posted April 9, 2018 1 hour ago, PeterW said: [...] Do you have a sarking board ..? Is this flat or sloping ..?? Sloping sarking. We have a flat roof too, but one roof at a time will ding dang do for me.... Link to comment Share on other sites More sharing options...
PeterW Posted April 9, 2018 Share Posted April 9, 2018 Right so it should be ventilated above the insulation. Batten on edge will stop you pushing the insulation up to the boards. Link to comment Share on other sites More sharing options...
A_L Posted April 9, 2018 Share Posted April 9, 2018 7 hours ago, recoveringacademic said: Our rafters are 225 mm by 47mm. should I leave an air gap? (I bet the answer is No) should I fill the gap : 100, 100, 25 and then underlay it all with 60 mm K18 (not 82.5 mm as above) Given the sarking board there should be an air gap. Assuming rafters at 400mm centres 200 + 82.5 ha U approx. 0.093, 200 + 60 has U approx. 0.106. A difference of 0.01 in U value has an energy implication of about 0.5kWh/m2.yr Link to comment Share on other sites More sharing options...
AliG Posted April 9, 2018 Share Posted April 9, 2018 (edited) We have sarking but 200mm rafters and no gap. It is ventilated from above the sarking. Putting in three lots of insulation will be unnecesarily expensive. There are three lots of cutting etc. As A_L says 25mm of insulation would make negligible difference. But it may be that yours has been specced for a 25mm gap and 200mm of insulation. The sarking cannot be air tight, it has to breathe, so that gap will not make a difference to air tightness. BTW your design has specified unnecessarily expensive insulation. K7 and K18 can be changed for Celotex or cheaper Kingspan. This will reduce the insulation level by 5% but the cost considerably. Edited April 10, 2018 by AliG Link to comment Share on other sites More sharing options...
ToughButterCup Posted April 10, 2018 Author Share Posted April 10, 2018 Thanks for your help folks. I feel a conversation with the architect coming on. And it doesn't help that sarking means different things to different people Link to comment Share on other sites More sharing options...
bissoejosh Posted April 11, 2018 Share Posted April 11, 2018 Would you consider swapping the K7 for mineral wool? It would be much easier to fit and a huge amount cheaper. You could then use a rigid board on the underside to get to the necessary U values and reduce the cold bridging. Link to comment Share on other sites More sharing options...
Mr Punter Posted April 12, 2018 Share Posted April 12, 2018 I think that sarking is normally 6" x 1" boards with a small gap between for ventilation. It also seems to be sheets of OSB used as an airtight layer over the rafters but I don't know how the ventilation bit works there as I don't think it is very vapour permeable. Link to comment Share on other sites More sharing options...