Novice Posted Tuesday at 20:42 Posted Tuesday at 20:42 We have been living in our certified Passivhaus since it was completed in August 2017. It's a relatively large house (approx. 400 m²) and overall has proved extremely comfortable and energy efficient. However, in recent summers we have increasingly experienced overheating in the main living areas. Despite using night purging and running the MVHR in summer/bypass mode, there are periods when we struggle to bring the internal temperature back down. We are therefore considering installing a couple of air-to-air heat pump/split AC units – probably one serving the main living area and another on the top floor. My main concern is maintaining the integrity of the Passivhaus airtight layer when installing them. The wall construction is shown in the attached drawing. The airtight layer is 12 mm SmartPly/OSB on the inside of the 300 mm twin-stud timber frame, with a 38 mm internal service cavity before the plasterboard. Obviously the installation will require refrigerant pipework, condensate drain and probably cabling to pass from inside to outside. I don't want an installer simply drilling through the wall and filling around the services with expanding foam. Has anyone installed split AC/air-to-air heat pumps retrospectively in a Passivhaus or similarly airtight timber-frame building? In particular, I'd be interested to know: How did you detail the penetration through the OSB airtight layer? Did you use proprietary airtight service grommets/collars or tapes around the pipe bundle? Is it better to install a larger airtight sleeve through the wall and pass all the services through that? How was the sleeve/penetration dealt with at the breather membrane and external cement board? How did you deal with the condensate drain without creating an air path? Would you pressure-test the house again afterwards to confirm the airtightness hasn't been compromised? I'd be very interested to hear from anyone who has done something similar, particularly on an existing Passivhaus.
ProDave Posted Tuesday at 21:36 Posted Tuesday at 21:36 51 minutes ago, Novice said: running the MVHR in summer/bypass mode Bypass mode, as it's name suggests, bypasses the heat exchanger. In a hot summer, that will result in HOT outside air entering via the mvhr with no cooling effect. Leave it in normal mode. Then outside air that is hotter than inside, will be cooled by the cooler extracted air. I have struggled to find any time when it is actually advantageous to use bypass mode.
JohnMo Posted Tuesday at 21:42 Posted Tuesday at 21:42 5 minutes ago, ProDave said: struggled to find any time when it is actually advantageous to use bypass mode When inside is hotter than outside. That is the only time.
JohnMo Posted Tuesday at 21:44 Posted Tuesday at 21:44 @Novice what is you normal heat system - ASHP? 1
Oz07 Posted yesterday at 07:56 Posted yesterday at 07:56 10 hours ago, ProDave said: Bypass mode, as it's name suggests, bypasses the heat exchanger. In a hot summer, that will result in HOT outside air entering via the mvhr with no cooling effect. Leave it in normal mode. Then outside air that is hotter than inside, will be cooled by the cooler extracted air. I have struggled to find any time when it is actually advantageous to use bypass mode. Evenings i used to set mine to come on.
Oz07 Posted yesterday at 07:57 Posted yesterday at 07:57 11 hours ago, Novice said: We have been living in our certified Passivhaus since it was completed in August 2017. It's a relatively large house (approx. 400 m²) and overall has proved extremely comfortable and energy efficient. However, in recent summers we have increasingly experienced overheating in the main living areas. Despite using night purging and running the MVHR in summer/bypass mode, there are periods when we struggle to bring the internal temperature back down. We are therefore considering installing a couple of air-to-air heat pump/split AC units – probably one serving the main living area and another on the top floor. My main concern is maintaining the integrity of the Passivhaus airtight layer when installing them. The wall construction is shown in the attached drawing. The airtight layer is 12 mm SmartPly/OSB on the inside of the 300 mm twin-stud timber frame, with a 38 mm internal service cavity before the plasterboard. Obviously the installation will require refrigerant pipework, condensate drain and probably cabling to pass from inside to outside. I don't want an installer simply drilling through the wall and filling around the services with expanding foam. Has anyone installed split AC/air-to-air heat pumps retrospectively in a Passivhaus or similarly airtight timber-frame building? In particular, I'd be interested to know: How did you detail the penetration through the OSB airtight layer? Did you use proprietary airtight service grommets/collars or tapes around the pipe bundle? Is it better to install a larger airtight sleeve through the wall and pass all the services through that? How was the sleeve/penetration dealt with at the breather membrane and external cement board? How did you deal with the condensate drain without creating an air path? Would you pressure-test the house again afterwards to confirm the airtightness hasn't been compromised? I'd be very interested to hear from anyone who has done something similar, particularly on an existing Passivhaus. Didn't Jeremy install aircon with a similar wall make up? You could search his threads i don't even remember his user name.
JohnMo Posted yesterday at 09:04 Posted yesterday at 09:04 He did, think he mentioned the insulation was so well packed it came out as a plug. 12 hours ago, Novice said: couple of air-to-air heat pump/split AC units Why not just one multi split? Remember if its just for cooling you need planning permission, if it's for heating and can also do cooling you do not.
Nickfromwales Posted yesterday at 09:20 Posted yesterday at 09:20 I’ve done this umpteen times, with all kinds of services; matters not a single jot what service(s) it is / are . For the split AC on my current clients build I simply used offcuts of 92mm MVHR duct as the sleeves, taped these to the interior AT layer, fed the pipes and cables through, and then the duct will get pumped full of Illbruck FM330 AT foam to complete; the foam seals for AT but is also, in a nutshell, liquid PIR insulation to boot. Condensate cannot be terminated internally I assume? If not, just send that through the same oversized duct. Externally I just use a mastic such as CT1, or similar NON silicone sealant, and bond the duct to the external medivent board, leaving a load of it as excess. Then push the outer membrane into the mastic, smooth with a tool, then go over the lot again until mummified. I’m home today but back on site tomorrow, so I’ll post some pics for you. Very easy to do, so don’t be intimidated by this at all 2
Novice Posted yesterday at 20:50 Author Posted yesterday at 20:50 Many thanks for all your replies. 22 hours ago, JohnMo said: @Novice what is you normal heat system - ASHP? UFH on ground floor only, from ASHP. 11 hours ago, JohnMo said: He did, think he mentioned the insulation was so well packed it came out as a plug. Why not just one multi split? Remember if its just for cooling you need planning permission, if it's for heating and can also do cooling you do not. It will probably end up being one multi split, which will also provide heating.😉 11 hours ago, Nickfromwales said: I’ve done this umpteen times, with all kinds of services; matters not a single jot what service(s) it is / are . For the split AC on my current clients build I simply used offcuts of 92mm MVHR duct as the sleeves, taped these to the interior AT layer, fed the pipes and cables through, and then the duct will get pumped full of Illbruck FM330 AT foam to complete; the foam seals for AT but is also, in a nutshell, liquid PIR insulation to boot. Condensate cannot be terminated internally I assume? If not, just send that through the same oversized duct. Externally I just use a mastic such as CT1, or similar NON silicone sealant, and bond the duct to the external medivent board, leaving a load of it as excess. Then push the outer membrane into the mastic, smooth with a tool, then go over the lot again until mummified. I’m home today but back on site tomorrow, so I’ll post some pics for you. Very easy to do, so don’t be intimidated by this at all Thanks Nick, this is very helpful and will probably be the technique I will use. Would appreciate so pics of the detail. 12 hours ago, Oz07 said: Didn't Jeremy install aircon with a similar wall make up? You could search his threads i don't even remember his user name. I will trawl my archive and see if I can find the info from Jeremy’s blog
JohnMo Posted yesterday at 21:07 Posted yesterday at 21:07 10 hours ago, Novice said: UFH on ground floor only, from ASHP. If you have a heat pump already can you not use it for cooling? On 08/09/2026 at 21:42, Novice said: couple of air-to-air heat pump/split AC units – probably one serving the main living area and another on the top floor Instead of new A2A just add some fan coils and use the UFH in cooling mode?
-rick- Posted yesterday at 21:20 Posted yesterday at 21:20 10 minutes ago, JohnMo said: If you have a heat pump already can you not use it for cooling? Expanding on this. What is your heatpump make/model? Most modern (<10years) heatpumps can be set to cool, though some may require 'enabling' with a dongle, code, or similar. Seems like it would be well worth exploring this before spending money on any new system. You might have to make some adjustments to your existing system but shouldn't be that big to at least get ufh cooling (which is not the same as full A/C but does make things a lot more comfortable in hot weather).
Novice Posted 16 hours ago Author Posted 16 hours ago 9 hours ago, -rick- said: Expanding on this. What is your heatpump make/model? It is a Panasonic WH-MDC06G3E5.
Gone West Posted 16 hours ago Posted 16 hours ago 23 hours ago, Oz07 said: Didn't Jeremy install aircon with a similar wall make up? I don't remember him doing that, but I do remember he had a Genvex MVHR with a built in A2A heat pump which did heating and cooling through the ventilation.
Nickfromwales Posted 16 hours ago Posted 16 hours ago 9 minutes ago, Gone West said: I don't remember him doing that, but I do remember he had a Genvex MVHR with a built in A2A heat pump which did heating and cooling through the ventilation. He did retrofit a split AC in the upstairs landing area, 100%, as they were getting uncomfortably hot in the ‘warm’ times of the year. He also said, even in a sympathetic micro-climate, that not having space heating (a-la the PH ‘way of things……”) would have led to divorce. 1
Gone West Posted 16 hours ago Posted 16 hours ago Found it. https://web.archive.org/web/20200923185500/http://www.mayfly.eu/2015/09/part-thirty-eight-heating-and-cooling-controls/ 1
JohnMo Posted 16 hours ago Posted 16 hours ago 20 minutes ago, Novice said: It is a Panasonic WH-MDC06G3E5. It should do cooling out the box. Your first stage would be getting UFH in cooling mode. For that we need to understand a little more about your heating system. Single zone run from Panasonic controller, or multi zones with thermostats, mixer/pump on UFH manifold or none?
jack Posted 15 hours ago Posted 15 hours ago On 08/09/2026 at 22:36, ProDave said: In a hot summer, that will result in HOT outside air entering via the mvhr with no cooling effect. That isn't how/when summer bypass mode works. Most (all?) MVHR units with summer bypass should switch to bypass mode only when it's cooler outside than inside, and only when the temperature is above some threshold (to avoid it coming on in winter). Even during a run of hot days, it's a rare situation in the UK when the overnight temperature doesn't fall significantly below the interior temperature of a typical house. It's therefore worthwhile to use summer bypass, especially if you don't want to open windows overnight (due to, e.g., insects or noise). Maybe it's of less use in Scotland because the interiors of houses don't get so hot in summer, but where I live, our bedrooms can reach 30 deg C, even with the underfloor cooling working downstairs. I see no reason not to use every available trick to reduce temps overnight. The one thing I haven't managed to get around to yet is to control the MVHR to boost during the cheap period when conditions are such that summer bypass will be in effect.
Oz07 Posted 11 hours ago Posted 11 hours ago 5 hours ago, Gone West said: Found it. https://web.archive.org/web/20200923185500/http://www.mayfly.eu/2015/09/part-thirty-eight-heating-and-cooling-controls/ I can never access that web archive site. Anyway I'm sure it was mentioned on here. What was his username?
Mike Posted 10 hours ago Posted 10 hours ago 4 hours ago, jack said: That isn't how/when summer bypass mode works. Most (all?) MVHR units with summer bypass should switch to bypass mode only when it's cooler outside than inside, and only when the temperature is above some threshold (to avoid it coming on in winter). Here are Zehnder's criteria for triggering the bypass - all 4 must apply: - The ventilation system must be operating in summer (based on long-term temperature data) - The outside temperature must be 2°C lower than the exhaust air temperature - The comfort temperature must be set lower than the exhaust air temperature - The outside temperature must be greater than 13°C (below this the bypass is always deactivated) Other brands may use simpler criteria.
Gone West Posted 7 hours ago Posted 7 hours ago 3 hours ago, Oz07 said: What was his username? JSHarris?
Novice Posted 4 hours ago Author Posted 4 hours ago 12 hours ago, JohnMo said: It should do cooling out the box. Your first stage would be getting UFH in cooling mode. For that we need to understand a little more about your heating system. Single zone run from Panasonic controller, or multi zones with thermostats, mixer/pump on UFH manifold or none? I have managed to activate the cooling mode option, a hidden setting. It did not work initially, because there is a thermostat wired, for heating only. So I temporarily "disconnected" via the controller (turned off the thermostat setting) and it worked! The UFH is a single zone, which makes it a whole lot easier. Although this works in principle I believe this will not lower the humidity, which a A2A would. So I am minded to pursue the A2A (probably single multi port unit) option to give me greater flexibility and it would also solve the top floor cooling.
Novice Posted 3 hours ago Author Posted 3 hours ago 12 hours ago, Gone West said: Found it. https://web.archive.org/web/20200923185500/http://www.mayfly.eu/2015/09/part-thirty-eight-heating-and-cooling-controls/ Thanks for this, but I am not sure it covers the retrofit of the A2A system.
JohnMo Posted 2 hours ago Posted 2 hours ago 1 hour ago, Novice said: Although this works in principle I believe this will not lower the humidity, which a A2A would. Why do you need to lower humidity? Isn't that what your MVHR does anyway? On UFH in cooling mode keep flow temps at a reasonable level, as once you go below around 14 you can start to make condensation. Start at 16 and keep an eye on your manifold for any misting up. Slowly work down, but wouldn't go below 14.
Nickfromwales Posted 2 hours ago Posted 2 hours ago 1 hour ago, Novice said: Thanks for this, but I am not sure it covers the retrofit of the A2A system. Noted, but I think the exact content is a bit tricky to find. Bear with us! What are the exact difficulties after getting from inside to out? On 08/09/2026 at 21:42, Novice said: Despite using night purging and running the MVHR in summer/bypass mode, there are periods when we struggle to bring the internal temperature back down. This is where the PH ideology is a bit 'over-sold' imho..... You are where 'you are', so let's get this moving We need to know how much heat (energy) you need to move from indoors to out, and in particular which areas are worst affected so you get the balance of problem vs solution as close to perfect as is practicable. On my current (400m2), and next 2 projects (prob 3 now), I have recommended AC to the entirety of the FF, with no wet heating or cooling, for the little bits of space heating but non-insignificant cooling requirements that are anticipated. Solar control via glazing has been observed from concept, but ultimate comfort for the occupants is the goal; excess PV generation will delete any running cost of AC cooling, and any thimble of heating will just get paid for on demand. UFH/UFC to ground floor and DHW is via heat pump #1, AC via heat pump #2 (external units).