6 hours ago6 hr Get some tape on the ends of those pipes as you uncoil it before any shite gets in them.
6 hours ago6 hr Author 30 minutes ago, Russell griffiths said:Get some tape on the ends of those pipes as you uncoil it before any shite gets in them.Yes, I did that straight away, I'd just cut those ends and took the pic before I re-taped them!
3 hours ago3 hr Author 3 hours ago, -rick- said:That sounds suboptimal. What size are these pipes?I'd try and pick up the phone and talk to a few installers before you screed unless you want a significant chance that the installer doesn't want to use what you put in.The pipes are 25/26mm MLCP.
3 hours ago3 hr Author 3 hours ago, JohnMo said:You don't need to split, you can take flow to the first manifold and out the other end of the manifold to the next manifold. The return the same thing. Your flow meters split the flow as you need just the same as a larger single manifold would.So are you saying it's wrong to install these 2 manifolds in "parallel" configuration and I should instead be installing them in "series"?
3 hours ago3 hr 4 minutes ago, Mulberry View said:So are you saying it's wrong to install these 2 manifolds in "parallel" configuration and I should instead be installing them in "series"?You can do either, really depends on you routing options. But your previous images shows 2 sets of pipes doing the same route to the first manifold, so why not just do one set of pipes to the first manifold and extend to the next manifold.
3 hours ago3 hr Author 18 minutes ago, JohnMo said:You can do either, really depends on you routing options. But your previous images shows 2 sets of pipes doing the same route to the first manifold, so why not just do one set of pipes to the first manifold and extend to the next manifold.My last sketch has really confused things, apologies for that. So I've done it again over the correct layout design to represent what I'm well advanced into laying... Ignore the previous version. Does this make more sense?! The long run is around 20m, the short one is 8m. Edited 3 hours ago3 hr by Mulberry View
2 hours ago2 hr I have not read the whole thread but wondered why you ruled out running the pipes in the ceiling void?
2 hours ago2 hr Author 2 minutes ago, Mr Punter said:I have not read the whole thread but wondered why you ruled out running the pipes in the ceiling void?Mainly because it was suggested to run them this way, but I do have a tricky service route to the furthest manifold with a steel beam in the way.
Just now1 min 7 hours ago, Mulberry View said:what I'm doing is OK,Very neat. We had to hack ours out in a hurry. Laying the surprisingly stiff pipes to their curved route then cutting (hacking really) underneath. I'm not showing my pictures.