2 hours ago, Mulberry View said:

I've raised concern about heat striping

Depends on the depth of pipes, ours are in 100mm screed and there is zero.  So thats should not be a concern.  Even when I used the boiler at 34 degs there were none. 

 

300mm is generally fine, one thing it does bring is a fall off of heat transfer at very low flow temps, so to counter that on 7 to 10 deg days I just flow at 29 and in Cosy periods and the runs are good.  Have a WC curve that runs 29 to 32 (10 degs to -5 degs).  Running 29 degs gives a very stable run time of over 3 hours and also excellent CoP, just finished a run I did as I was getting free electricity, ran in manual for 3 hours and got a CoP average of 6.6 at one point it was doing over 7.

 

2 hours ago, Mulberry View said:

but I am minded to want closer pipe spacing as I'd prefer some headroom

At 300mm spacing you can very easily hit very high room temps, just flow too high for too long and you go into melt down.  Just use the chart I posted on 30 Aug to work out how little flow temp increase you need to add to increase output hugely.

 

If you are concerned just drop the spacing to 200-250mm, but tighter in bathrooms due to the limited floor area

 

  • Replies 91
  • Views 3.3k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • I know the feeling, but from the other side. I'm totally swamped with design and install work I simply struggle to keep up. Despite the negative stories, there's definitely the demand out there. I hav

  • Mulberry View
    Mulberry View

    Just to update this, I've put it with an independent heat-loss consultant who has done a much more thorough heat-loss analysis. Very comprehensive and far more believable. I'll be sharing his details

  • Mulberry View
    Mulberry View

    I've paid £195 for a heat loss analysis with a hefty report. £295 for the UFH layout and for that he's going to route the manifold supply and returns too.   Honestly, I think he'll pay for h

Posted Images

5 hours ago, Mulberry View said:

The designer has gone for 300mm pipe centres

FWIW, French regulations specify a maximum of 250mm between pipes - more here:

 

 

Edited by Mike

300mm pipe spacing does seem big, on tile flooring you'll notice the heat spacing unless you have really thick screed.

 

Id opt for smaller and dial back the temp.

  • Author

So, back to the original point, Supply and Return pipes to/from the manifolds. What type of pipe is best to use here? I'm installing 25mm (26mm?) that will be within the PIR, with 150mm PIR under it. There is about 30m of linear length to reach both manifolds, so I'll need 60m of pipe in total, which I understand needs to be insulated despite it being installed into PIR? Is it just 25mm Pre-insulated MLCP?

 

As for the design, the designer was certain that 300mm spacing would meet the heating requirements, but I've had him do 200m spacing to be on the safe side (150mm in the Bathroom). I don't really ever want to do this again and certainly don't want to have to use plug-in heaters if it gets chilly!

 

There are 2 manifolds as this simplified the routing. The M3 manifold is at the lowest ground floor level, the M1 manifold is 1m higher in terms of ground floor FFL. The bundle of pipes running along the hallway to the WC and Utility will be in conduit as they are just transit pipes and the heat they emit is not required before the rooms.

 

This design saves 400m of pipe compared to the earlier designs. The ASHP will be against the wall in the top-right of this drawing, so the manifold connections are the hardest part here really.

 

UFH-V3.thumb.jpg.61ace1bd7f21e442c1b6cfd0541615f4.jpg

I would do it in 28mm hep2o, zero issues with noise or pressure drop. You maybe would be ok with 22mm but for the cost difference just cover all basis. 

 

16 minutes ago, Mulberry View said:

The bundle of pipes running along the hallway to the WC and Utility will be in conduit as they are just transit pipes and the heat they emit is not required before the rooms.

 

You can do it that way, and that's the way you would do it if you are running every area on its own thermostat, but are you? Sounds like a waste of pipe and conduit to me.

 

19 minutes ago, Mulberry View said:

which I understand needs to be insulated despite it being installed into PIR?

 

Insulation on pipes when run inside PIR - what is the insulation doing that the PIR isn't doing already? no idea why you need the additional insulation.

  • Author
19 minutes ago, JohnMo said:

I would do it in 28mm hep2o, zero issues with noise or pressure drop. You maybe would be ok with 22mm but for the cost difference just cover all basis. 

 

 

You can do it that way, and that's the way you would do it if you are running every area on its own thermostat, but are you? Sounds like a waste of pipe and conduit to me.

 

 

Insulation on pipes when run inside PIR - what is the insulation doing that the PIR isn't doing already? no idea why you need the additional insulation.

 

The insulation thing intrigued me too. I asked AI, which told me that PIR is great at stopping heat from travelling downwards, but isn't so good at preventing it travelling sideways through the PIR boards and that the sleeving on the MLCP pipes somehow performs differently! Who knows. Not me that's for sure.

 

I do know that I have to be able to create 90° bends halfway along the pipes, to transition as needed without fittings.

 

It's not as difficult as you seem to think, and AI seems to be telling rubbish.

 

No 90°corners: it easily curves 90 or 180.

Fitting with insulation above it is just wrong. You can set it on top then screed it, or put it in special floorboards. Or painstakingly depress it into the pir. Or use eps as a top layer as I think you could tread it in. What floor finish will you have?

Ducts are not only unnecessary but counterproductive. The 'highways' as they seem to be called are both flow and return, so it is not all at peak temperature.

 

Norwich is too far, but anyone in SSE is welcome to some of the huge amount of oversupply of pipes we were specified, I think 40 to 60m long. Not insulated, as they should not be except your short run from heat pump to manifolds.

 

 

Where are your flow and return pipes running to and from - do you have a route planned?

  • Author
1 hour ago, JohnMo said:

Where are your flow and return pipes running to and from - do you have a route planned?

 

This is them sketched by me on an earlier layout plan. Ignore the pipe layout and manifold positions on that plan, this was an overlay to show my proposed position of the M1 manifold and the omission of the M2 manifold in the middle, along with routing of the supply/returns.

 

Where the omitted manifold is shown there, the supply/returns need to turn up out of the lower floor, ascend by 600mm then turn back into the Kitchen floor. The 600mm vertical section will need to be contained in a battened out wall.

 

ManifoldProposal.jpg.c5a70b18d2133f9626b2292c9983dc30.jpg

Edited by Mulberry View
Added the attachment. Duh.

So question, instead of through the house, why not around the house, buried in trench then though wall to manifold.  Would certainly do the manifold in room M1.2 in 28mm.

 

Are you intending to run as a single or 2 zone system?

  • Author
1 hour ago, JohnMo said:

So question, instead of through the house, why not around the house, buried in trench then though wall to manifold.  Would certainly do the manifold in room M1.2 in 28mm.

 

Are you intending to run as a single or 2 zone system?

 

How would running these pipes around the house benefit? I can't see how it would shorten or simplify the routes unless I've missed something obvious?

1 hour ago, JohnMo said:

why not around the house, buried in trench 

Heat loss would be greater unless using  the horrendously expensive pipes made for the purpose. Even then, indoors would be less wasteful of the heat.

We used 2 layers of insulation and cut them into the lower one.

 

 

2 hours ago, Mulberry View said:

 

How would running these pipes around the house benefit? I can't see how it would shorten or simplify the routes unless I've missed something obvious?

I thought you had elevation changes to contend within the house, thought it maybe easier routing overall outside Or just route them beside the UFH pipes, why bother insulating at all inside the heated environment, any heat loss is going into the house.  In cooling mode atmospheric air is excluded, so no condensation to make either. Assume your hot water cylinder is in room M3.4? If so why are you bothering with an UFH loop in that room? It's always going to be warm, ours sits in an unheated loft space room is 6m x 4m it's always the warmest place in the house.

  • Author
21 minutes ago, JohnMo said:

I thought you had elevation changes to contend within the house, thought it maybe easier routing overall outside Or just route them beside the UFH pipes, why bother insulating at all inside the heated environment, any heat loss is going into the house.  In cooling mode atmospheric air is excluded, so no condensation to make either. Assume your hot water cylinder is in room M3.4? If so why are you bothering with an UFH loop in that room? It's always going to be warm, ours sits in an unheated loft space room is 6m x 4m it's always the warmest place in the house.

 

You didn't read what I wrote alongside that pic! LOL.

 

Regarding the internal level changes, they are also outside, we have a tricky plot and an even trickier shaped building. They need to be inside really.

  • Author
1 hour ago, saveasteading said:

Heat loss would be greater unless using  the horrendously expensive pipes made for the purpose. Even then, indoors would be less wasteful of the heat.

We used 2 layers of insulation and cut them into the lower one.

 

 

 

How did you go about cutting them into the lower one?

 

I have 150mm PIR already laid. My plan was to lay the supply/returns, then add the top layer of PIR around and over the pipes. It felt like it'd be easier than trying to carve channels in the already laid layer?

It was messy.

Laid the first layer which was eps.

pipes laid in exact positions,incl up to their end locations, which is important as they don't bend easily.

Mark with black pen

Cut with jigsaw or multitool. 

Insert pipes.

Adjust as necessary

Bag up lots of messy eps.

Lay pir over the top.

 

Around and over sounds OK to me. 

Cut boards close the the pipes and fill the gap with cutings or loose stuff.

 

Cutting PIR is horrible. I borrowed a very good multitool with a blade that just stopped short of going through. Handsaw and jigsaw weren't good.

I was doing this myself  as I didn't expect the professionals to care about precision at cut outs. I was right... it was a huge rush and very approximate.

It all gets covered in dpm so they get away with it.... usually.

 

 

  • Author
1 hour ago, saveasteading said:

It was messy.

Laid the first layer which was eps.

pipes laid in exact positions,incl up to their end locations, which is important as they don't bend easily.

Mark with black pen

Cut with jigsaw or multitool. 

Insert pipes.

Adjust as necessary

Bag up lots of messy eps.

Lay pir over the top.

 

Around and over sounds OK to me. 

Cut boards close the the pipes and fill the gap with cutings or loose stuff.

 

Cutting PIR is horrible. I borrowed a very good multitool with a blade that just stopped short of going through. Handsaw and jigsaw weren't good.

I was doing this myself  as I didn't expect the professionals to care about precision at cut outs. I was right... it was a huge rush and very approximate.

It all gets covered in dpm so they get away with it.... usually.

 

 

 

That's always my concern, nobody cares as much as I do, it's why I have trouble handing anything over!

 

I know many of these things don't actually matter, but I feel better if they're done right. Plus, despite being a competent DIY'er, I've never done this stuff, it's all new to me and I'm not a "tradie".

 

Thanks for your words, it's helpful.

  • 2 weeks later...

Saveasteading's method is the one I would follow here. Cutting the flow and return into the lower insulation layer and keeping them out of the screed makes any future leak far easier to find and avoids a weak spot in the floor. I would also pressure test those runs and mark their route on the wall before the top layer goes on, so nobody puts a fixing through them later.

@Mulberry View

Can I ask - what set-up will you use for splitting the flow from the HP? A ‘primary’ mini-manifold so you can control how much flow goes to each ‘secondary’ manifold?

2 hours ago, Alan Ambrose said:

@Mulberry View

Can I ask - what set-up will you use for splitting the flow from the HP? A ‘primary’ mini-manifold so you can control how much flow goes to each ‘secondary’ manifold?

You don't really need the additional manifold as you can manipulate flow with the individual loop flow meters.

  • Author
On 26/10/2026 at 02:39, stevenlee said:

Saveasteading's method is the one I would follow here. Cutting the flow and return into the lower insulation layer and keeping them out of the screed makes any future leak far easier to find and avoids a weak spot in the floor. I would also pressure test those runs and mark their route on the wall before the top layer goes on, so nobody puts a fixing through them later.

Funny you've said that, I'm back here with more questions.

I have opted to do just that, I've chased the pipes into the lower layer of insulation. I decided that I would prefer to lay the 80mm top sheet of PIR in the more reliable way and being able to go straight over the pipework sat better with me. In fact, chasing the grooves for the pipes to sit in has been pretty easy. Messy, but not that hard.

Here is the first pair curved up the wall in the Mech room and heading off to do the longer of the 2 runs...

UFH Supply Pipes Laid 001.jpg

...and here are those pipes passing into the adjacent room. I cored each pipe individually through the blockwork internal wall. I have begun the chasing for the next pair that will run alongside up to the point seen here, but will veer off the other way towards the second manifold....

UFH Supply Pipes Laid 002.jpg

From there, they pass through a third room in the same way, but then have to turn up and into the adjacent space, 600mm higher. I cored through the wall diagonally to reduce the amount of bending needed...

UFH Supply Pipes Laid 003.jpg

Here, they're left long in the Kitchen because I've not put any insulation down yet. But they are pointing in the direction of travel according to the red-line sketch I posted earlier.

UFH Supply Pipes Laid 004.jpg

I set my Circular Saw to 45mm cut depth and made cuts 45mm apart. Cutting the majority of the material out with a wood-saw, then following with the little yellow Surform seen in the first pic, which fits nicely in the groove and makes short work of really tidying the grooves. I have left 40mm between the pipes where possible. Messy, yes, but very do-able.

I hope what I'm doing is OK, and yes I'm thinking of pressure-testing the pipes and am researching how that's done, so any ideas are welcomed. I think I need to link the MLCP pipes together at the "manifold end", then pressurise at the other end, presumably with some sort of blanking arrangement with a gauge and schrader valve built in?

  • Author
On 26/10/2026 at 08:45, Alan Ambrose said:

@Mulberry View

Can I ask - what set-up will you use for splitting the flow from the HP? A ‘primary’ mini-manifold so you can control how much flow goes to each ‘secondary’ manifold?

That's something I don't yet know. I need to get properly engaged with an ASHP supplier, but am trying to get the screed in first. I will leave 2 pairs of MLCP pipes unterminated in the Mech room in readiness for whatever is used to split them. Is this not a common occurrence?!

  • Author
22 hours ago, JohnMo said:

You don't really need the additional manifold as you can manipulate flow with the individual loop flow meters.

Presumably there'll be a supply and return to/from the ASHP, how are these usually split to feel 2 manifolds, as I have?

5 minutes ago, Mulberry View said:

That's something I don't yet know. I need to get properly engaged with an ASHP supplier, but am trying to get the screed in first. I will leave 2 pairs of MLCP pipes unterminated in the Mech room in readiness for whatever is used to split them. Is this not a common occurrence?!

That sounds suboptimal. What size are these pipes?

I'd try and pick up the phone and talk to a few installers before you screed unless you want a significant chance that the installer doesn't want to use what you put in.

8 minutes ago, Mulberry View said:

Presumably there'll be a supply and return to/from the ASHP, how are these usually split to feel 2 manifolds, as I have?

You don't need to split, you can take flow to the first manifold and out the other end of the manifold to the next manifold. The return the same thing. Your flow meters split the flow as you need just the same as a larger single manifold would.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.