MikeSharp01 Posted April 24, 2025 Posted April 24, 2025 It's time to insulate water pipes and I am looking for the best options given the vast array of products out there and where to insulate, we have several water mediums to consider, some like anything to do with hot water - including UFH, are obvious but the cold water supplies not so obvious. Should I, for instance, routinely insulate mains / softened potable cold water to taps, basins, cisterns etc? The house is very well insulated and air tight.
Nickfromwales Posted April 24, 2025 Posted April 24, 2025 The black neoprene and cheap grey EPS stuff are near identical in thermal performance, which I was surprised by, so I now install EPS internally with wall thicknesses to suit the application. I seldom insulate the cold pipes tbh, as plastic pushfit (Hep) pipe seems to be a world away from copper in terms of condensation risk. Plant rooms need everything insulating imo as the temp differences there are the most adverse, so defo the cold mains supply to manifolds but only in a 9mm or 13mm wall product. Insulating the hot pipes where there is no hot return (in such a dwelling) seems pointless too tbh, so I just put hot & HRC together in the same insulation to wrap them up nice and toasty (25mm wall) and then call it a day after that. Very different advice would be stated if this was a typical uk home with pipes under voids / in cold attics etc obvs. 2
Nickfromwales Posted April 24, 2025 Posted April 24, 2025 UV resistant neoprene for outdoors stuff, to an ASHP for eg, but also the neoprene doesn’t get munched on by rodents for some reason whereas EPS outside is a buffet!
Iceverge Posted April 24, 2025 Posted April 24, 2025 44 minutes ago, MikeSharp01 said: It's time to insulate water pipes and I am looking for the best options given the vast array of products out there and where to insulate, we have several water mediums to consider, some like anything to do with hot water - including UFH, are obvious but the cold water supplies not so obvious. Should I, for instance, routinely insulate mains / softened potable cold water to taps, basins, cisterns etc? The house is very well insulated and air tight. It's 's a waste of effort insulating any pipe that is only occasionally heated up like pipe runs to basins etc in my opinion. Anything that's permanently hot like a hot return loop or pipes attached to a cylinder need to be well insulated. As for cold, it depends, if you are showing no evidence of condensation on them I wouldn't bother. 1
saveasteading Posted April 24, 2025 Posted April 24, 2025 Polyethylene, which I think the cheap ones are, gets munched, and I think shrinks and stiffens over the years. But it's much cheaper. I don't know what the difference is between what is called "economy" and " bylaw quality".
nod Posted April 24, 2025 Posted April 24, 2025 58 minutes ago, MikeSharp01 said: It's time to insulate water pipes and I am looking for the best options given the vast array of products out there and where to insulate, we have several water mediums to consider, some like anything to do with hot water - including UFH, are obvious but the cold water supplies not so obvious. Should I, for instance, routinely insulate mains / softened potable cold water to taps, basins, cisterns etc? The house is very well insulated and air tight. Sort of wish I’d used these
saveasteading Posted April 24, 2025 Posted April 24, 2025 5 minutes ago, nod said: wish I’d used these What are "these"?
nod Posted April 24, 2025 Posted April 24, 2025 2 hours ago, saveasteading said: What are "these"? Pipes that come with the insulation on Every pipe in the house is ready insulated Saves time
Nickfromwales Posted April 24, 2025 Posted April 24, 2025 2 hours ago, nod said: Pipes that come with the insulation on Every pipe in the house is ready insulated Saves time Same we do with the MVHR ducts where we heat / cool (temper) the airflow to rooms. TBH I don't insulate everything any more, so putting insulation on where needed afterwards seems the most cost-effective. I work out the lengths of the hot & HRC run, walk it out, insulate in and tape it up well, and them pull it in in one go; we use band or 50mm waste pipe clips around the insulation to fix it into place vs clipping the pipes and then having to stop/start the insulation. 1
Iceverge Posted April 24, 2025 Posted April 24, 2025 The physics doesn't work out for insulating pipes in a radial or trunk and branch setup. The insulation doesn't stop the transfer of heat, merely slows it. There is simply too little water in the pipes, too much surface area and too little depth of insulation to meaningfully retain any hot water in the pipes between uses in a house. In other words it will cool to room temperature whether you insulate it or not between average tap usage intervals. Your time is far better spent on minimising the volume of water in your dead leg by short runs and thin pipes etc. There is a difference where the pipe is always hot like a HRC ( a symptom of bad house design in my opinion) which should be massively insulated or pipes coming from an UVC. These continuously loose heat as it is internally replenished. Another thing to consider is heat loss through convection. Any pipes rising vertically from a permanent source of heat will be prone to this. It may be desirable in the case of a preheated hot water manifold ( I did this ) but usually it's not ( I accidentally did this for my control block for the UVC).
Nickfromwales Posted April 24, 2025 Posted April 24, 2025 10 minutes ago, Iceverge said: a symptom of bad house design in my opinion ...or practical necessity in anything bigger than a flat. On a project we just fired up such a system, and the kitchen sink is appx 5m from the UVC. As the taps are modern EU regulated offerings there is a 9 second delay to get premium hot water to that outlet (15mm). In normal occupation the HRC will keep a fair amount of the primary hot pipework warm / hot throughout the day, so I will assume this will reduce to maybe 4-5 secs, but if not this may end up getting added to the HRC. For the small running cost per annum (likely entirely offset if you have PV) it is a great thing to open a tap and the hot water is available instantly, particularly for low volume / high frequency outlets such as a hand wash after using the loo or rinsing something at the kitchen sink. I do like the option for the Quooker hot (as well as boiling) water doo-dah at the kitchen sink, if that meant you could otherwise do away with a HRC, but it's always down to the individual case / client and distances from UVC > outlet. We always discuss this very comprehensively before getting the tools out, so expectations are managed and nobody can whinge afterwards (if the water is slow to arrive at these modern, low-flow rate taps etc, for eg).
marshian Posted April 24, 2025 Posted April 24, 2025 6 hours ago, Nickfromwales said: Very different advice would be stated if this was a typical uk home with pipes under voids / in cold attics etc obvs. Indeed I have Copper pipes under a suspended ground floor and running in a very well ventilated void - these are all insulated (CW, HW and CH Flow and Return) Copper pipes above an insulated cold loft that is ventilated - these are all insulated (CW Tank Feed, HW F&E The only pipes between loft and floor that are insulated are the flow and return to the HW Tank from the boiler and All pipework in the airing cupboard All HW, CW and CH flow and returns inside the heated envelope are not lagged mainly because they are boxed in or under the first floor - I did consider it
Adrock Posted March 1 Posted March 1 Sorry to resurrect an old thread but it's a very quick question, I've seen HRC mentioned a fair few times but have no idea what the abbreviation means. Can someone enlighten me?
Russell griffiths Posted March 1 Posted March 1 34 minutes ago, Adrock said: Sorry to resurrect an old thread but it's a very quick question, I've seen HRC mentioned a fair few times but have no idea what the abbreviation means. Can someone enlighten me? Hot return circuit 1
MikeSharp01 Posted March 1 Author Posted March 1 45 minutes ago, Russell griffiths said: Hot return circuit Yes so you pump hot water round the house with take off points at each sink, shower etc returning it to the tank. Its much more common in commercial buildings but if you have it it means the Hot water is almost instant at your tap! It is costly in energy terms and if you have it then very good insulation is needed for the pipework especially in a highly insulated house.
Nickfromwales Posted March 1 Posted March 1 2 hours ago, MikeSharp01 said: Yes so you pump hot water round the house with take off points at each sink, shower etc returning it to the tank. Its much more common in commercial buildings but if you have it it means the Hot water is almost instant at your tap! It is costly in energy terms and if you have it then very good insulation is needed for the pipework especially in a highly insulated house. You don't take it to showers and baths etc, as these are single, high volume, constant flow (at high flow rate) outlets; the time taken to get hot water out of a shower turned on full wallop is very little. Compare this to a small mixer tap on a wash basin, where high frequency, small volumes (at much lower flow rate) of water are used. The wait to get premium hot water from these is significantly more problematic (most wash their hands and rinse off just as the hot water finally arrives and then turn the tap off with a line loaded with nice hot water that you never actually got to use). In a well insulated house, the delta will always be closer, from ambient to pipe, so losses are actually lessened if there are no cold attics or voids under floors where pipework must live. Add to the mix an airtight house with MVHR, and the fact that all the pipes are within the heated and airtight envelope, and then you're going to end up recycling that latent heat back through the heat exchanger of the MVHR unit. 2 hours ago, MikeSharp01 said: It is costly in energy terms I think this is less of a concern than most first think. Factor in the dead legs and excess water drawn off repeatedly, through the water meter, and then if you have solar and a heat pump, then annual energy costs would rise quite minimally (if at all if you are a net exporter). It's a lot of comfort for not much running cost TBH, and once to get used to that instantaneous hot water at certain strategic outlets, (kitchen sink and wash hand basins), you'll soon decide the tiny sacrifice is well worth it. Add to that the fact that I always fit a secondary TMV to the HRC so water no hotter than 48oC arrives at wash basins, and then there's no need to be faffing about trying to get the temp right so you can wash your hands. Just flick the tap to the hot position, and open it each time, and you get the same temp each time, near zero wait, near zero wasted water. HRC pipework is defo a candidate for being as well insulated as is possible, of course, so when plumbing a whole house for a client I take a 15mm DHW flow and a 10mm HRC return to each preselected outlet, and wrap the 2 pipes together in a single piece of pipe insulation, parting them just before the start and end of the run. A piece of 25mm wall x 22mm ID insulation works a charm here, so on a full new build I'll open up a 100m coil of 15mm and same for 10mm and tape the ends together and fasten them to a far wall. Then I'll start to work my way back down the length, for 20-30m or so, then I'll feed that umbilical through the posis and cut and repeat until the HRC runs are complete. The clipping is done around the insulation, not to the pipes, so a bit of all-round patent band ticks the box here. The 15mm and the 10mm can be joined at the basins, terminating immediately before the final 90o bend that feeds the tap, eg so there's near zero dead leg of ambient water to discharge ahead of getting premium temp DHW out. At this point you pretty much open the tap and take your hand off it, and the hot water's flowing by the time you've placed your hands under the tap. I use a Hep2o 15x15x10mm (centre reduced) tee, with a 10mm spigot bend in the centre, so the 15mm hot and 10mm are parallel entering the tee. The remaining 15mm outlet of the 15x15x10mm tee is the pipe that then feeds the hot of the tap.
MPx Posted March 1 Posted March 1 Interesting reading this thread. I always favour a hot water loop (called HRC I've learnt here!) which of course needs good insulation but eliminates that awful wait for the hot water to arrive. Where I differ is that I always insulate cold runs too and not just because of potential condensation. It depends what you want of course, but I like my cold to be cold not room temp. I also typically run the cold close to the hot and I want the minimum heat exchange possible between the two - nothing worse than tepid drinking water IMO.
Nickfromwales Posted March 1 Posted March 1 5 minutes ago, MPx said: Interesting reading this thread. I always favour a hot water loop (called HRC I've learnt here!) which of course needs good insulation but eliminates that awful wait for the hot water to arrive. Where I differ is that I always insulate cold runs too and not just because of potential condensation. It depends what you want of course, but I like my cold to be cold not room temp. I also typically run the cold close to the hot and I want the minimum heat exchange possible between the two - nothing worse than tepid drinking water IMO. I've begun insulating everything, just for belt and braces, but just 9mm thick wall on colds. For any long-ish runs, it'll always be tepid as the amount of water to run to fill a glass will be the same as the dead leg of cold from the stopcock to the outlet. The only way to get cold drinks is to run the tap until your tepid is all down the plughole, insulation won't do anything for this.
-rick- Posted March 1 Posted March 1 One of the reasons I have noted for insulating pipes is that the insulation can act as a buffer/decoupler from thermal movement and noise (assuming you strap the insulation not the pipes).
Adrock Posted March 1 Posted March 1 Most of the talk in this forum has been about single pipe runs to each appliance and now you're telling me instant hot water needs a different method 🤯 Plumbing definitely isn't more forte. So, if I have manifolds everywhere to I put 15mm pipes from those to each appliance and the ones where I want instant hot water I run a 10mm return to the cylinder? I really need to start drawing out where I'll be putting all this stuff.
JohnMo Posted March 1 Posted March 1 19 minutes ago, Adrock said: So, if I have manifolds everywhere I just simplified all this. We have a 15mm pipe from cylinder to a manifold, then one pipe to each wet room, again in 15mm. The 15mm is branched out once in wet room to each hot water outlet. Our ensuite is about 20m from cylinder so it has a hot water return. Run the same size pipe, in our case 15mm, back to the return pump and then to cylinder. Ideally you want the thermostat on the return pump and a timer.
Nickfromwales Posted March 1 Posted March 1 Have a look at the Grundfos Comfort pump folks. 1 hour ago, Adrock said: Most of the talk in this forum has been about single pipe runs to each appliance and now you're telling me instant hot water needs a different method 🤯 "Most", maybe, which means you need to spend more time looking and reading 1 hour ago, Adrock said: So, if I have manifolds everywhere Manifolds at the plant room only. This is how you delete the large bore dead legs at source. If you have "manifolds everywhere" then these will need to be fed from 22mm and will be the opposite to the solution of reducing dead legs.
-rick- Posted March 2 Posted March 2 12 hours ago, Adrock said: Most of the talk in this forum has been about single pipe runs to each appliance and now you're telling me instant hot water needs a different method 🤯 12 hours ago, Adrock said: Plumbing definitely isn't more forte. So, if I have manifolds everywhere to I put 15mm pipes from those to each appliance and the ones where I want instant hot water I run a 10mm return to the cylinder? As always depends on your situation. Short runs from the manifold? Especially if run with smaller diameter pipe (10mm copper, hep2o plastic, etc), don't need HRC. If you have long runs, especially of 15mm+ pipe then HRC may make sense. I can't find it right now but there was an online calculator/diagram that someone posted before that would neatly show how quickly a tap would take to warm up given length of pipe + pipe diameter. Maybe most of your sinks are close to the manifold so won't need HRC but one is a long way away and for that one you want a HRC (connected to PIR in the room so it only runs when someone is near the tap).
Nickfromwales Posted March 2 Posted March 2 3 hours ago, -rick- said: As always depends on your situation. Short runs from the manifold? Especially if run with smaller diameter pipe (10mm copper, hep2o plastic, etc), don't need HRC. If you have long runs, especially of 15mm+ pipe then HRC may make sense. I can't find it right now but there was an online calculator/diagram that someone posted before that would neatly show how quickly a tap would take to warm up given length of pipe + pipe diameter. Maybe most of your sinks are close to the manifold so won't need HRC but one is a long way away and for that one you want a HRC (connected to PIR in the room so it only runs when someone is near the tap). If I’m buying an HRC pump, and fitting it, with power and controls, then I’d be using it to its fullest advantage. Not just using it for one single outlet (if a new build and you can get insulted HRC pipework in with ease anyways). Get the basins and kitchen sink on the HRC and you’ll never look back.
JohnMo Posted March 2 Posted March 2 8 minutes ago, Nickfromwales said: can get insulted HRC Can you, do they take offence? 1 2