Iceverge Posted March 3, 2025 Posted March 3, 2025 23 hours ago, MikeGrahamT21 said: I've got a few roofer quotes to just de-tile/de-baton/de-felt the entire roof for me. I think im just gonna go ahead with that. and foam / tape all the gaps I find in the roof insulation This solution is unlightly to fix your issue as you'll still have lots of bulk air movement. Like I said AIRTIGHTNESS is the huge issue here. If I was doing it myself (literally DIYing) I would consider having an external airtightness layer and full fill insulation. However I wouldn't hand this task off to anyone short of an OSD watchmaker in a cleanroom, and even then I would make sure I had mechanical ventilation internally. A dMEV like this would be fine. Open cell spray foam would be an (almost) idiot proof way to give excellent airtightness. You could omit the layer of 45x45 timbers building up the roof and settle for a U value of 0.17W/m2K. This is probably a worthy compromise as an airtight build with any even any hint of insulation ( say a U value < 1W/m2K) will be able to be warmed to a satisfactory level. In your case you could have passivhaus U-values but the drafts will make it unheatable as you've found out. However I would keep the OSB sheathing. Spray foam involves a lot of trimming if done in an open cavity. Also I'm coming to the conclusion every roof should be sheathed for rodent protection, noise and durability in worsening weather. ( I wish I'd done ours) .
lookseehear Posted March 3, 2025 Posted March 3, 2025 Just wanted to send a message to say you seem surprisingly chipper given the absolute sh*t show in evidence here. So many people would just accept this as 'what it is', so kudos to you to get sorting it! I hope you retained a significant chunk of the ££ against the builder. 3
EinTopaz Posted March 3, 2025 Author Posted March 3, 2025 27 minutes ago, lookseehear said: Just wanted to send a message to say you seem surprisingly chipper given the absolute sh*t show in evidence here. So many people would just accept this as 'what it is', so kudos to you to get sorting it! I hope you retained a significant chunk of the ££ against the builder. They're being investigated for tax evasion. Even if they weren't; based on the evidence I wouldn't want to deal with them again after this, even monetarily. Rather wash my hands. Just keep telling my self the good old motto "if you want something done right... do it yourself! 2
EinTopaz Posted March 3, 2025 Author Posted March 3, 2025 59 minutes ago, Iceverge said: This solution is unlightly to fix your issue as you'll still have lots of bulk air movement. Like I said AIRTIGHTNESS is the huge issue here. If I was doing it myself (literally DIYing) I would consider having an external airtightness layer and full fill insulation. However I wouldn't hand this task off to anyone short of an OSD watchmaker in a cleanroom, and even then I would make sure I had mechanical ventilation internally. A dMEV like this would be fine. Open cell spray foam would be an (almost) idiot proof way to give excellent airtightness. You could omit the layer of 45x45 timbers building up the roof and settle for a U value of 0.17W/m2K. This is probably a worthy compromise as an airtight build with any even any hint of insulation ( say a U value < 1W/m2K) will be able to be warmed to a satisfactory level. In your case you could have passivhaus U-values but the drafts will make it unheatable as you've found out. However I would keep the OSB sheathing. Spray foam involves a lot of trimming if done in an open cavity. Also I'm coming to the conclusion every roof should be sheathed for rodent protection, noise and durability in worsening weather. ( I wish I'd done ours) . I don't disagree, it's just not something i'm familiar with and anxious about buggering it up. IF there was someone in the NW that could do this for me i'd be happy to look at costing it and proceeding. Just feels beyond my level of understanding and time availability to DIY on this one. But the U value numbers you've posted there have got me interested for sure.
Iceverge Posted March 3, 2025 Posted March 3, 2025 2 hours ago, EinTopaz said: Just feels beyond my level of understanding and time availability to DIY on this one By the time you've paid someone to do it properly spray foam would be just as economical. @JohnMo used it in his roof. Maybe he could review my idea and comment. 1
MikeGrahamT21 Posted March 3, 2025 Posted March 3, 2025 I've learned from jobs over the years to always keep a very close eye on builders, i still think Unilin's (xtratherm) CT/PIR was a very easy to use product: 1
JohnMo Posted March 3, 2025 Posted March 3, 2025 On 02/03/2025 at 13:52, Iceverge said: There we go. That should prevent any drafts. @Gone West used Icynene for airtightness on his passivhaus project. There's vastly improved bridging qualities through the rafters and at the wall roof junction too. Pretty similar to what I did. I don't have any PIR where you do. The noggin between the rafters is actually 140mm PIR closing that space. I have 256mm deep rafter and have under drawn with battens, to increase to 350mm. Over rafters I have sarking boards (45 Deg roof) and marine ply (12 Deg roof). All have breather membrane above. Full fill with Icynene open cell. Also have a vapour closed membrane below. All seems pretty quiet and keeps the heat in. Did interstitial condensation calculations and no issues. 2
EinTopaz Posted March 4, 2025 Author Posted March 4, 2025 (edited) Brief update on this one just so the thread and any other troubled onlookers are aware. I've now gone through and inspected the eaves detail for everywhere I can for this extension. Found some horrifying things and insulated it the best I can. Those steps being:- :- Remove all poorly seated wool covering wall plates. :- Seal all gaps between ceiling PIR and wall plate with wool / foam/ tape. :- Reinstate PIR insulation where there was none :- Form Wedge to force wall PIR to be uptight against block :- Seal all gaps between Wall PIR and block with wool / foam / tape. :- Reseat wool covering wall plate and all sealed areas. I'm very pleased to report that this has made a huge difference. I have not had chance to put my thermal cam back on, but you can feel it in the room. It's actually retaining heat through the day now, heating on in the morning for a few hours and you could still feel the residual heat in there by midnight. Perhaps i'd got used to having essentially balls-all insulation in there so im hypersensitive, but very promising so far. and that's without any form of curtain / blinds etc. All the glazing (of which there's lots) is still entirely bare. Not to say im going to stop there, I will be still removing all the roof to fully seal it and add more insulation. But atleast now my horrifying suspicion that I may need to add interior insulation in an already finished room... has been quelled. I'd REALLY hoped I wouldn't have to do that and it looks now that i wont have to, so im very glad for that atleast. Id rather spend the time and money on further improving the roof, glazing and adding exterior wall insulation to the walls if I need to. Anyhow, some more images of fixes for future ref for anyone. Edited March 4, 2025 by EinTopaz 6 1
Nickfromwales Posted March 4, 2025 Posted March 4, 2025 It's staggering just how shite some trades' workmanship and standards are... They just think because they've sweated for the day that it's a good days graft. Good on you for sticking to this and getting the simple measures done to make a job well done, would have been so much easier if they had just given a feck.. 2
EinTopaz Posted March 4, 2025 Author Posted March 4, 2025 2 hours ago, Nickfromwales said: It's staggering just how shite some trades' workmanship and standards are... They just think because they've sweated for the day that it's a good days graft. Good on you for sticking to this and getting the simple measures done to make a job well done, would have been so much easier if they had just given a feck.. What has double-annoyed me about this one was, they were one of the more expensive quotes we had to do the job and we went with them because of how confidence building they were. I.e they continually said things like "we are more expensive but the attention to detail and overall quality will be reflected in the price".... Being a very quality-driven type person myself that really resonated with me. But in reality I could've likely gone with the other quotes, saved £20k and invested that into these types of snags! That said, we can sit here and moan about it and it still wouldn't fix the problem. So rather just get it right and let bygones be bygones. I only care about the comfort level of my family. Not so much about pounds and pennies. 1
Nickfromwales Posted March 4, 2025 Posted March 4, 2025 2 hours ago, EinTopaz said: I only care about the comfort level of my family. Not so much about pounds and pennies. Amen reverend. 🍻 1
EinTopaz Posted March 11, 2025 Author Posted March 11, 2025 (edited) Question for the insulation knowledgeable persons on this thread. Is there an app or perhaps an easy way to calculate how much % improvement i'd get if I add another 50-75mm PIR to the roof? Essentially taking it from 150mm to 200/225mm, assuming it's all airtight and performing appropriately. Just costing it up and it is a bit higher than id hoped, so trying to workout the value proposition of it before I go ahead and buy. Edited March 11, 2025 by EinTopaz
crispy_wafer Posted March 11, 2025 Posted March 11, 2025 (edited) if you know the buildup then get onto ubakus , this will help you model Edited March 11, 2025 by crispy_wafer 1
SteamyTea Posted March 12, 2025 Posted March 12, 2025 20 hours ago, EinTopaz said: perhaps an easy way to calculate how much % improvement i'd get if I add another 50-75mm PIR to the roof? Depends on that you call easy. Dividing the insulation thickness by the thermal conductivity of the material gives you the R-Value. Dividing that number into 1 gives you the U-Value. Then multiply by the metres squared that it covers. The harder part comes working out the variables caused by weather and energy prices. 4 years ago, gas was a third of the price, so adding extra insulations hit the diminishing return earlier. Bet there are a few that wish they added more now though. Weather, which drives the temperature difference is also fickle. While we are getting warmer, globally, it is not evenly distributed. The UK is predicted to get warmer and wetter (generally good for agriculture) but not so good for house temperatures. The only real way to model this sort of problem is to create a mathematical model that allows different parameters to be varied, sometimes changing one parameter will effect a second, or third one i.e. more summer showers may reduce solar gain, increase evaporation loses and increase wind speeds. So care has to be taken. 1
EinTopaz Posted March 12, 2025 Author Posted March 12, 2025 On 11/03/2025 at 13:57, crispy_wafer said: if you know the buildup then get onto ubakus , this will help you model thanks, taking a look now - do you know how to add an air gap in the buildup for ubakus? I couldn't figure out how to add one.
mistake_not Posted March 12, 2025 Posted March 12, 2025 4 hours ago, EinTopaz said: thanks, taking a look now - do you know how to add an air gap in the buildup for ubakus? I couldn't figure out how to add one. 1. New layer 2. Select the various menu 3. Select the air type 1
Iceverge Posted March 12, 2025 Posted March 12, 2025 (edited) 5 hours ago, EinTopaz said: thanks, taking a look now - do you know how to add an air gap in the buildup for ubakus? I couldn't figure out how to add one. Just type "air" into the search box and it'll pop up. Ubakus is a great tool. In fact it's been my favourite computer game for about 5 years, (Sad I know 😢). However caution is advised with the stationary air and moisture accumulation calcs of the software. It makes a static computation and assumes perfect workmanship. The real world is massively more complex, dynamic and messy and anything short of a supercomputer would fail to produce useful results. In the case of "Stationary Air" anything more than ~16mm(......ish, from memory) will be enough to create convection currents in the air ruining the benefit of a stationary gas as an insulant. This is why old double glazing ,without the exotic gases we use now, had this narrow gap and instead of say 25mm or 40mm. Likewise you'll need to make a hermetically sealed box for the air not to move to make it truly stationary. This isn't practical in a wall buildup despite what many manufactures claim. Edited March 12, 2025 by Iceverge 1
EinTopaz Posted March 13, 2025 Author Posted March 13, 2025 17 hours ago, Iceverge said: Ubakus is a great tool. In fact it's been my favourite computer game for about 5 years, (Sad I know 😢). However caution is advised with the stationary air and moisture accumulation calcs of the software. yeah, i love stuff like this. Visual layers of how I can spend fewer £'s in the future ultimately. It is a game On that subject, I looked to add external wall insulation as a test (if I wanted to go that route and render etc) and realised quickly that this would be entirely pointless as I have the 50mm airgap between brick and PIR....so my assumption is EWI (external wall insulation) won't work on a cavity wall UNLESS the cavity is entirely filled. I remember a few posts ago perhaps you mentioned about infilling the cavity here with closed cell foam. I'm interested in doing this, just not sure how I prevent it from going up into the eaves. How do people seal the cavity to prevent this happening, do you know?
SteamyTea Posted March 13, 2025 Posted March 13, 2025 5 hours ago, EinTopaz said: infilling the cavity here with closed cell foam Why not use polystyrene beads?
EinTopaz Posted March 14, 2025 Author Posted March 14, 2025 5 hours ago, SteamyTea said: Why not use polystyrene beads? Didn't even think that'd work. What is the air gap between the PIR and brick meant to be for? I assumed its to stop any wet/damp bridging. Wont beads allow for damp to transfer to the PIR from the brick? Read all sort of stories online of people having these put in their empty older cavities and having issues with damp, then having to have them removed! 1
SteamyTea Posted March 14, 2025 Posted March 14, 2025 2 hours ago, EinTopaz said: Read all sort of stories online of people having these put in their empty older cavities and having issues with damp Hear those stories about all types of fully filled cavities. Some people on here have used beads, maybe they will come along and comment. 1
EinTopaz Posted March 14, 2025 Author Posted March 14, 2025 (edited) 14 hours ago, SteamyTea said: Hear those stories about all types of fully filled cavities. Some people on here have used beads, maybe they will come along and comment. Yeah true, I suppose it's down to the installation than the material (this thread being a great example of that ha!) Im not sure what other options I have for the walls really. That PIR that's in there ain't coming out without serious re-work. So my only options are to go over the top of that. I assume other people must have been faced with a similar option. Already installed PIR but not a great installation... so what is one supposed to do? Edited March 14, 2025 by EinTopaz
Spinny Posted March 15, 2025 Posted March 15, 2025 An interesting thread. On sealing around electrical boxes in the dot and dab plasterboard - I am not sure I see the benefit. I'd have thought the problem is having cold air getting into the gap behind the board because that is just bypassing any benefit from the insulation in the wall. The issue is airtightness and stopping the flow of cold air into that space. Sealing the electrical boxes might stop you feeling the cold draught but if the cold air is still there behind the board it isn't doing anything to improve the room thermals at all really to seal the boxes. And it could stop you feeling the difference when it is made airtight - i.e. the draft from the electrical boxes disappears. I had/have some awkward spaces to insulate - in the end it took a good carpenter to resolve and fit the insulation nice and tightly. I guess if they can make a nice tight dovetail joint, they can do similar accurate work with PIR. I have a warm roof thank goodness - seems much easier to insulate. I guess that is insulation under the concrete floor slab - adding heating pipes at that stage would have been good I think. An infrared temperature gun and/or thermal camera seems like an essential tool for building work these days. 1
EinTopaz Posted April 8, 2025 Author Posted April 8, 2025 Update on this one, as i'm still battling away trying to improve it where possible. I had a survey done today by a local wall insulation company. I was looking to have the EPS beads put into the walls, specifically in the air gap between the (poorly installed) kingspan and outer brickwork, as I figured that'd probably be the easiest way of dealing with the problem. Unfortunately the news I got was not what i'd hoped. The suveyor said they'd need a 40mm cavity consistently to work with and when they put the camera in ours, they said it was mostly 20mm and in some places, no gap at all, I guess meaning that the kingspan has come away from the block as much as 50mm in some cases. The surveyor said they can't proceed with the EPS beads in this case. Just wondering if anyone on here has come across this and know what options i still have open to me? External wall insulation looks a no go as i still have an airgap between brick and kingspan. So really at a bit of odds on what I can do now. Help!
marshian Posted April 9, 2025 Posted April 9, 2025 OK just a suggestion from previous pictures I can see that removing a row or two of tiles means you can look down the cavities - can you not add suitable 2.4 m length of wood vertically down the cavity with a taper at the end to straighten/push the PIR back to being in contact with the internal wall face - then as they blow in beads pull out each length of wood knowing that the beads already in the cavity will keep the PIR in contact with the internal wall face. Insulation company would then be happy with the consistent gap from an infill perspective? Obviously if you can't push it back with 2.4m length from above then it's a bust from that perspective so a bit of wood 1