Sunil237 Posted November 13 Share Posted November 13 Received my structural calcs today and I'm not so sure of the solution provided by the structural engineer. I have an extension going up which is 10m wide x 5.5m deep with a flat roof, and a bifold of 6.4m on the rear wall. The engineer has specified a length of 6.84m 250 x 150 x 8 RHS but it shows a deflection of 25mm which I'm concerned about as I need to minimise this for the bifold. Any suggestions on improvements? I have already suggested to make the steel longer as I'll be charged for 7.5m either way and the wall has plenty of space. thanks Link to comment Share on other sites More sharing options...
JohnMo Posted November 13 Share Posted November 13 Go back to structural engineer to seek clarification of the deflection? Link to comment Share on other sites More sharing options...
Sunil237 Posted November 13 Author Share Posted November 13 Thanks John, I have queried this with him but wanted external thoughts too Link to comment Share on other sites More sharing options...
markc Posted November 13 Share Posted November 13 As John said, plus RHS isn’t the best section to minimise deflection as the “flanges” are only 8mm top and bottom agains the added self weight of 16mm of web (2x8mm sides. yes a RHS looks better but it would really need a pre camber before install. Link to comment Share on other sites More sharing options...
nod Posted November 13 Share Posted November 13 The last two that we have done have been done with a 12 mill hit and miss welded plate on the bottom of the steel Which gives 0 deflection and has worked fine Hes probably probably added the deflection due to the lack of weight above it Which is no use to you Five mill of movement will cause the doors issues Link to comment Share on other sites More sharing options...
Conor Posted November 13 Share Posted November 13 Our engineer's solution was a 203SHS with 14mm plate welded to the bottom for 5mm deflection of 5m. Beam sat behind the insulation and only the steel plate formed a bridge. Link to comment Share on other sites More sharing options...
Sunil237 Posted November 13 Author Share Posted November 13 4 hours ago, markc said: As John said, plus RHS isn’t the best section to minimise deflection as the “flanges” are only 8mm top and bottom agains the added self weight of 16mm of web (2x8mm sides. yes a RHS looks better but it would really need a pre camber before install. What would be the better alternate type? Link to comment Share on other sites More sharing options...
Sunil237 Posted November 13 Author Share Posted November 13 That @nod and @Conor, in my calcs he did say a shelf plate is optional. I have asked him to include this. Am I summonsed to use the same thickness as the RHS or just go thicker? Link to comment Share on other sites More sharing options...
nod Posted November 13 Share Posted November 13 31 minutes ago, Sunil237 said: That @nod and @Conor, in my calcs he did say a shelf plate is optional. I have asked him to include this. Am I summonsed to use the same thickness as the RHS or just go thicker? No the span will have already dictated the the thickness of your steel We hit and miss welded plates on three sides at our previous build Six years on No cracks or movement 1 Link to comment Share on other sites More sharing options...
scottishjohn Posted November 13 Share Posted November 13 question why RHS and not RSJ of larger thickness material what is the attraction of a box beam? are the flat roof joists hanging on this as well? 8mm seems thin to me and not suprised at deflection in that length plus easy to to weld or bolt in extra thickness to centre of RSJ if still worried about deflection when all said and done it is the vertical part that gives the strength and flat plate is cheap and easy to fill with insulation Link to comment Share on other sites More sharing options...
markc Posted November 13 Share Posted November 13 2 hours ago, Sunil237 said: What would be the better alternate type? A UB (universal Beam) has a thin web (vertical) and thicker top and bottom flanges making it stiffer when vertically loaded. As mentioned above, adding a bottom plate to Box section will greatly improve its resistance to deflection because you are increasing the bottom flange Link to comment Share on other sites More sharing options...
scottishjohn Posted November 13 Share Posted November 13 1 minute ago, markc said: A UB (universal Beam) has a thin web (vertical) and thicker top and bottom flanges making it stiffer when vertically loaded. As mentioned above, adding a bottom plate to Box section will greatly improve its resistance to deflection because you are increasing the bottom flange I would respectfully disagree it is the centre web that gives the rigidity ,so height and thickness of that gives the strength ,top and bottom are to give it sideways rigidiity to keep centre web vertical even a plastic 12" ruler is stiff wehn on its edge try hitting your knuckles with it edge on ,then do same with it flat Link to comment Share on other sites More sharing options...
saveasteading Posted November 13 Share Posted November 13 23 minutes ago, scottishjohn said: It is the centre web that gives the rigidity , Sorry, no. The web (the central vertical bit) is there to keep the flanges apart. Then it has to resist deflection but that is secondary. Increasing the distance the flanges are apart increases the lever for the flanges, and making them thicker gives strength....but it's a class for another time. There is permanent deflection from the load above the beam, and that doesn't concern you ( it bends and stays put, and the door gear can be fixed kevel). Dynamic deflection from the doors moving is your concern. (Loading and unloading). There is no such thing as zero deflection. Thus it may well be ok, but probably needs clarification. 1 Link to comment Share on other sites More sharing options...
Iceverge Posted November 14 Share Posted November 14 I was always of the impression that in a horizontal "I* beam that the top and bottom sections did all the work. It's how in my head I explained this. The bid in the top was being squashed together, the bit at the bottom was being pulled apart and the bit in the middle was just making sure they stayed put. Without knowing the different yield strength of metals in compression and tension I do wonder why beams aren't built asymmetrically to gain maximum strength for minimal material. Link to comment Share on other sites More sharing options...
saveasteading Posted November 14 Share Posted November 14 (edited) 2 hours ago, Iceverge said: why beams aren't built asymmetrically to gain maximum strength for minimal material. They can be and are, for big structures. The standard ones are "hot rolled" through formers from a yellow hot balk of steel. But beams can be welded from flat plates which can be whatever thickness and width is required, in which case they don’t even have to be parallel. Your picture shows the possibility of increasing the web height from a hot rolled section. Castellated beams are cut to zigzag halves and moved relatively sideways and welded together. The weld is visible in your picture. The circle option is a prettier effect, with some offcut waste resulting. Very strong and allows services through. Also note plate girders on victorian bridges, made from flat steel plates riveted together. Edited November 14 by saveasteading 1 Link to comment Share on other sites More sharing options...
scottishjohn Posted November 14 Share Posted November 14 I guess we are not going to agree ,but even the picture you show above shows the centre web is biggest giving the strength the other picture with holes in the beam is to decrease weight as at its hieght it is big enogh to take the load as for victroisn bridges etc that was their only choice as no rolling mills or fancy steels and no welding Im sorry you are just wrong if load is vertical then a tall centre web will take the load in a thinner section tha huge flat plates at top and bottom of beams you dont believe me then do the steel rule test i suggested above and see how weight it will support if truly vertical and not allowed to bend sideways or look at a truck chassis the main beams are always about twice the height of the top and bottom plates and usally a C section again to save weight for load required even better look at a 100ton low loader chassis and see how that is made and they get serius loading with all the transient loads of roads or look at aircraft wing main spars plenty examples of what i am saying is true Link to comment Share on other sites More sharing options...
saveasteading Posted November 14 Share Posted November 14 1 minute ago, scottishjohn said: Im sorry you are just wrong @scottishjohnA relevant degree and 50 years working with steel buidings wasted? Maybe I'm explaining badly. I was expanding on the query by @Iceverge so maybe it doesn't coincide with your post. 3 minutes ago, scottishjohn said: biggest May be the confusion here. 8 minutes ago, scottishjohn said: if truly vertical Is the other confusing factor. It will buckle unless restrained. Link to comment Share on other sites More sharing options...
Sunil237 Posted November 14 Author Share Posted November 14 10 hours ago, markc said: A UB (universal Beam) has a thin web (vertical) and thicker top and bottom flanges making it stiffer when vertically loaded. As mentioned above, adding a bottom plate to Box section will greatly improve its resistance to deflection because you are increasing the bottom flange Thanks, I can see their thoughts on adding a plate 10 hours ago, scottishjohn said: question why RHS and not RSJ of larger thickness material what is the attraction of a box beam? are the flat roof joists hanging on this as well? 8mm seems thin to me and not suprised at deflection in that length plus easy to to weld or bolt in extra thickness to centre of RSJ if still worried about deflection when all said and done it is the vertical part that gives the strength and flat plate is cheap and easy to fill with insulation Not sure why they have suggested an RHS over RSJ, with the multiple opinions here about the two I will ask them to check which one is more suited for for my purpose. Yes flat roof joists will be mounted on this - using posijoists. thanks for the other info too Link to comment Share on other sites More sharing options...
Sunil237 Posted November 19 Author Share Posted November 19 This is the reason the structural engineer chose RHS For such a long beam on the inner skin we would not recommend using a UB section, as they are prone to twisting and torsion, and would likely need a really large section size to overcome that, which probably wouldnt look great. RHS beams are not prone to torsion due to their shape. Should I still pursue a UB? 1 Link to comment Share on other sites More sharing options...
scottishjohn Posted November 19 Share Posted November 19 (edited) 21 minutes ago, Sunil237 said: This is the reason the structural engineer chose RHS For such a long beam on the inner skin we would not recommend using a UB section, as they are prone to twisting and torsion, and would likely need a really large section size to overcome that, which probably wouldnt look great. RHS beams are not prone to torsion due to their shape. Should I still pursue a UB? I go back to your first post 25mm deflection ? that must induce alot of strain in the beam and i am not sre how you work with a 25mm bend in the centre of the beam I am not convinced of his argument on torsion (twisting load ) especially if the roof joists which are going to be attached to the beam or done by infilling the beam with wood ,and attach joists to that it could not twist really as it would have no here to go being tight to roof joists If i was really worried about twist then weld flat section to inside between top and bottom of beam ,or bolt sections of "c" section int hat space If all that is loading the beam is the roof then I do not see an RSJ of that size having muuch defelction same could be said of bolting or welding a flat plate of 10mm to inside of box beam maybe you are happy with just packing the bifolds suitably to allow for the 56mm deflection of your box beam ? and yes if does not cause a problem use the full length of the beam ,but if it does bned that much the ends of only held by the roof will probably make a gap under neath them if it bending that much ? must be somewhere on web you can find a calculation sheet for bend of different types of beam plus you can fill the outside web with insulation ,not sure how he intends to insulate a box section but I,m no SE just a guy who has been building all sorts of structures both buildings and vehicles for a long time Edited November 19 by scottishjohn Link to comment Share on other sites More sharing options...
Russell griffiths Posted November 19 Share Posted November 19 I’m going to throw something out there. have you built the opening yet. if not make it smaller. if you haven’t built it yet let us know. Link to comment Share on other sites More sharing options...
saveasteading Posted November 19 Share Posted November 19 1 hour ago, Russell griffiths said: if you haven’t built it yet let us know. The manufacturer has it all worked out and the fitters will work to the spec provided. I'm thinking back to a warehouse where there were sliding industrial doors, hanging from the beam overhead. It's a sort of bellows effect, and made of steel so heavy. If I remember correctly, the manufacturer stated quite clearly what load there would be, changing in complex manner as it is pulled about, and they specify a maximum deflection, otherwise it will jam in the bottom guide runners. The SE designs for that, it gets built and along come the fitters. They fix the top, loadbearing, runner with spacers, in the knowledge that the beam will deflect by the amount specified, or less, and the bottom runner to suit. Thus, the runner may rise slightly in the direction of opening, and the weight cause some deflection that won't be a problem. ie it looked like an uphill runner, but the weight brings it down to horizontal and then a little lower still. I only did a few of these because they are a pain and I generally convinced clients to go to an overhead door. But it was a routine thing and they all worked nicely. If you have proper experts it will be fine. Link to comment Share on other sites More sharing options...
Sunil237 Posted November 19 Author Share Posted November 19 25mm deflection includes calculations to bulk up the figure for safety. The opening is not build yet. I've asked him to provide an alternative calc for a UB. Hopefully something reasonable Link to comment Share on other sites More sharing options...
scottishjohn Posted November 19 Share Posted November 19 (edited) 4 hours ago, saveasteading said: I'm thinking back to a warehouse where there were sliding industrial doors, hanging from the beam overhead. It's a sort of bellows effect, and made of steel so heavy. I,m glad you mentioned this i fitted a new one to my workshop when i split it into units I already had two of them when i built the worsgop and in 30 years they never gave a problenm beiing open and closed many times each day so when I neede another one i went for same again " bolton brady euro fold" it came with the frame work "C" section 6" pillars for both ends with plates on top to bolt too the RSJ main beam ,a 6x6 rsj and no fixings to anything ellse ,just supported on the end "c" beams which are concreted into floor the opening was 5m and the door unit which hung on it was 650 kgs -had to bororw a fork lift truck to fit all this yes there was a track for the doorrollers to go into and ,yes spacers ,but I think that was more to do with allowing for builders getting things wrong than anything else and of course when its open the weight is all at one end and there is no weight supported at bottom just a guide rail for the doors set in the floor If a box beam was stronger or cheaper they would have used that ,,and bear in mind this is a very movable load so there would be twisitng load as well as you open and close it so i think that shows for a given size RSJ is sronger Edited November 19 by scottishjohn Link to comment Share on other sites More sharing options...
Russell griffiths Posted November 20 Share Posted November 20 Build the opening smaller then, stick to around 5m. having built two new houses and multiple renovations with this type of extension on the back I can’t think of a reason for such a big door. we where going to have two sets of 5m wide doors in the back, but went for one and a picture window, and our view out the back is probably better than 95% of peoples, we just couldn’t see it being used fully, and the impracticalities were many. A 6.5m wide opening looks good on the fancy architects plans. but that is all. pros and cons of such a big opening. CONS. future deflection effects door working properly Expensive steel more calculations very expensive door problems with such a door in the future how many days in England will you actually want it fully open smaller reveals on the inside restricts furniture and kitchen layout. PROS. You can show your friends what a big door you have. 2 Link to comment Share on other sites More sharing options...