Hello,
Beginner at loopcad but like to try, put me straight.
Wall/Roof/Floor all ~U=0.11. Windows ~U=0.8
UFH loops to be laid and fixed atop the mesh in the insulated slab before the pour.
I've tried to keep to 3 x 100m loops which will all operate on a single zone.
Low temp batch heated over night by the ASHP.
Top-up on coldest days in the afternoon.
GF area ~110 sqm
Annual Heating Demand is 1800kWh/a (11.4 kWh/sqm a)
Heating load for house is circa 1.5kw (PHPP).
Option to cool UFH water in the summer via ASHP.
36 minutes ago, JohnMo said:
Looks pretty similar to what I did.
Put loads more pipe in bathroom. I would do as close centres as you can.
Roger, thanks. I may also put it under the shower tray in that case, greater area!
2 hours ago, Duncan62 said:
Hello,
GF area ~110 sqm
Hi
have got the dimensions of this area please , as I’m going to have quite a tight squeeze in my small utility room. Would be great to see how much space you’re set up is using and if you’re set on the DHW tank and MVHR units
thanks
I would, and under the kitchen units too.
We used 200mm centres even though not strictly required given low heat-loss.  200mm is also slightly easier to install as you just follow the mesh, which is our case was also 200mm.
We didn't go under any cupboards/island/stairs, can't remember why, I guess MBC advised not to, although in hindsight this is more important for UFH-in-screed than lower temperature UFH-in-slab.  The main thing is to 100% avoid anywhere where they may be fixings into the slab.  TBH, even if you don't you'll still be able to run at very low flow-temps, especually with 200mm centers.
Edited by Dan F
6 hours ago, Nic said:
Hi
thanks
Hello, plant room is 1.9m x 3m
This is a good point that I had thought of last night too.
Installing at 200mm will nicely follow the mesh spacing. Might make instillation easier.
Never understood not putting pipe  under units/ shower trays / baths, Especially if its a 100mm concrete slab.
I just put loops over the whole floor, I didn't take into account any room layout. The slab was 120mm thick so I had 80 mm concrete  to drill /screw fixings into if needed.
i guess the theory is you dont want to warm up food in cupboards or dry out the traps under baths and showers? I avoided putting it under the units for those reasons and also that by doing so got me to give or take 100m instead of way over.
It's a solid slab, the heat will diffuse? through it, that's the whole point.  To my mind your just making it work harder.
This.
@Duncan62 All looks good. You might want to try the serpentine counterflow pattern in LoopCAD. This  places a flow pipe next to return pipe and evens out temperature.
As others have pointed out, less than 200mm centres are more difficult on mesh.
Make sure they follow your LoopCAD drawings. I have good drone shots of my install but only recently discovered that they installed less loops than specified. Two rooms in particular. Also ignored the routing of four loops through adjacent room to reduce the amount of pipes in hallway.
This was the day before the pour, so hard to catch at the time. All my fault as I didn’t supervise after the initial discussion and had a late panic about lowering the French door thresholds and had to get some timber quick.
Edited by Nick Laslett
Once you get to low outputs and flow temps below 30 or so you cannot notice.
I didn't go under any kitchen fixed units, showers or baths, kitchen islands or beds.
A Lot of the, "you better do this or that", only really applies to UFH installed in very high heat leakage houses and/or with little or no insulation below the pipes. Well insulated with heat output of 15W/m2 and below, you can do just about do any centres, any pattern, flow temp varies only by a couple of degrees.
Update.
Thank all.
I have avoided under shower and kitchen cupboards (some of them) simply because I have 3 x 100m loops, which works nicely for buying and fitting.
I shall not do serpentine as it looks (much) more difficult for this mortal to install - and looking over @TerryE posts, will make no difference in low flow temp situations.
3 hours ago, JohnMo said:
I would add an electric towel rail in to the bathroom as well. Other than that it looks good to me
We did the same. You need something independent of the main central heating system so that you can easily dry towels and add some heat to the bathrooms in the shoulder months.
+1, nothing like a warm towel.
Easy install after-the-fact if needed. I like it.
Your UFH risers are coming very close to the side door.  Make sure that you have enough clearance to get the manifold assembly in.
Thank you Terry: I plan to use the bottom side wall in the plant room which is 900mm wide. Enough for a 3x Out and 3x Return manifold + pump?
Yours doesn't look too big?
On 02/04/2024 at 21:49, JohnMo said:
Not sure they recommend that
In a "passive house" the flow temps are inconsequential. I now pipe under every single shower tray for my clients builds, staying around 400mm away from the waste / drain. Why? Not sure, but I am reasonably sure confident that it's entirely moot tbh.
On 02/04/2024 at 22:45, Nic said:
Hi
thanks
Go for a horizontal UVC and put everything else above it?
