Jump to content
Funding the Forum - Appeal to members ×

Recommended Posts

Posted
12 hours ago, G and J said:

I’m not sure I agree that it’s impossible to calculate a payback for the cost of MVHR because using Jeremy’s spreadsheet our heating requirement is a lot less than half of what it would be with sub one air changes per hour compared to say five air changes per hour that you’d need with a non-heat recovery system.

 

However, the extra spend to get airtight would be quite difficult to calculate and indeed we’ve not done a cost benefit calculation in payback terms, we’ve gone for it just as an act of faith for comfort.  So despite it being theoretically possible, I think calculating payback for MVHR for us at least is rather pointless. 

Excuse my ignorance, but why do you need such a higher number of changes per hour with a non-heat recovery system?

Posted

I think you need a certain number of air changes per hour to keep all fresh.  
 

With trickle vents it’s a blow through.  But with MVHR one still (as I understand it) get a good flow through if fresh air.  
 

It at first appears confusing that we have a really low air change score to make MVHR worth having, but that’s a test of the leakiness of the house, not the number of air changes that a good ventilation system will give. 

Posted
10 hours ago, Eastfield said:

I'm intrigued by your sub £2k system Bonner. Are you willing to share some details? Also, I couldn't agree more re trickle vents, and I do want to have full control of my ventilation.

 

I don't want to compromise on health and comfort, ventilation is not optional. The point Jeremy is making, if I understand correctly, is that the heat saved by the MVHR is not substantial, and it would be more efficient to remove the stale air along with its heat, bring fresh air into the house and heat it via an economical heating method, which I believe I have in the biomass boiler.

Please see another post here, note the unit was 20% cheaper when I bought it. I agree the heat saving is not huge, however you would still need the fan(s), distribution system and method of preheating the incoming air to avoid cold drafts.

 

Posted
10 hours ago, Eastfield said:

Excuse my ignorance, but why do you need such a higher number of changes per hour with a non-heat recovery system?

You don't but the high number is an instantaneous air flow rate for intermittent fans. Or maybe a house leakage rate at 50Pa, which isn't the actual air movement through a building.

 

You can have good controlled ventilation without MVHR. MVHR is the icing on the cake, when you have done, wall, floor and roof insulation to death, triple glazed and made house airtight. Most houses don't need it, don't benefit from it. But they do benefit from a well thought out and appropriate ventilation system.

  • Like 2
Posted
On 31/12/2025 at 09:02, JohnMo said:

You can have good controlled ventilation without MVHR. MVHR is the icing on the cake, when you have done, wall, floor and roof insulation to death, triple glazed and made house airtight. Most houses don't need it, don't benefit from it. But they do benefit from a well thought out and appropriate ventilation system.

Ah..... the voice of reason. Our house is a new build so by virtue will be exceptionally well insulated and airtight. we have a 'cheap' source of heating. It's all very well those with MVHR stating they'd never live in a house without it, but have they lived in modern, well insulated home with well designed ventilation but no mvhr by comparison? I'd be keen to hear from anyone who has in order to gain an unbiased view.

 

It's easy to disappear down a rabbit hole. Up until I watched the video in my first post I was dead set on MVHR. The concept makes complete sense, however I have been kept awake at night with the problems of routing ductwork, locating the unit and coming up with £5-6k to pay for it. I still need to find a decent company to give me some unbiased and impartial advice, any suggestions would be gratefully received.

 

Thanks for all your responses. We may end up with MVHR yet, but all options will be explored....

  • Like 1
Posted
30 minutes ago, Eastfield said:

so by virtue will be exceptionally well insulated and airtight

Big assumption there, it certainly may not be airtight - unless it was tested to show it is.

 

Posted

I have awarded hearts to people I agree with.... which is contrary to good logic of listening to all views.

 

But my prejudice, or is it exierience and intuition, is that mvhr is grossly over-rated.

 

We build to control air leakage, then pressure test at high pressure with all fans and vents sealed.

Then we remove the seals and allow draughts to flow freely from each wc and kitchen. Unless they have automatic shutters but they seem rare.

 

Stuffiness can only raise from habitation, but then the fans are used which draw air from everywhere, to be replaced by whatever leakage there may be. Nobody suffocates. 

 

I've only had old draughty houses but the steading (family owned) has no mvhr and has no issues of stuffiness or condensation. I promise to report if that changes.

In business I did  no homes, but offices, nursing homes and school classrooms* would have the same issues..in all cases we agreed with the client to "chance it" without mvhr.... no problems reported ever. That's x 20 applicable  projects at a guess.

So I think I'm right. Still listening of course, but we don't intend to fit £20k on mvhr at the current project.

 

* This seems extreme, with 30+ kids in a room. High ceilings help of course but window vents and door openings appear to suffice.

Perhaps the teachers open windows sometimes.

 

 

Posted (edited)
1 hour ago, saveasteading said:

We build to control air leakage, then pressure test at high pressure with all fans and vents sealed.

Then we remove the seals and allow draughts to flow freely from each wc and kitchen. Unless they have automatic shutters but they seem rare.

 

I’m just trying to understand this.  When you say, “We build…”, are you talking about your buildings that don’t have MVHR, or are you talking about people that self-build with MVHR?  Or perhaps both groups of people.

 

My understanding is, if I build a house with MVHR, I would most likely not have vents sucking air from the kitchen & bathrooms straight through my wall to the outside; the bathrooms will just have MVHR extracts & the kitchen will have the same + a recirculating hood over the hob that filters the air rising from the hob then dumps it into the kitchen to be taken away by the kitchen’s MVHR extract port.  Have I got that wrong?

Edited by Tony L
  • Like 1
Posted
4 minutes ago, Tony L said:

Have I got that wrong?

No.

 

Except delete the words 'most likely in the 1st sentence of the 2nd para.

Posted

Thanks for a quick answer on that one, @Bramco. I am just in the process of reviewing/correcting the first draft BC/construction drawings my architectural technician has drawn up for me, & my instructions include a note to delete the MEVs he's drawn in, so I just wanted to be sure.  

Posted
21 minutes ago, Tony L said:

Thanks for a quick answer on that one, @Bramco. I am just in the process of reviewing/correcting the first draft BC/construction drawings my architectural technician has drawn up for me, & my instructions include a note to delete the MEVs he's drawn in, so I just wanted to be sure.  

If you are doing MVHR you really need an airtightness better than 3.  Otherwise there's a good chance you are wasting energy not saving it. If you are not aiming for level of airtightness there are better or more effective ways to ventilate.

 

There is no reason to have any vents in windows or anywhere else and still be fully compliant with building regs if you are using MVHR.

Posted

Thanks @JohnMo.  My brief to the arch tec specified MVHR & said, “Airtightness will be to near passive standard: we’ll aim for 0.6 & see how close we can get.  Insulation will NOT be to passive standard…”.

 

The arch tec’s drawings include a note which says, “The measured air permeability should be no worse that [sic] 10m3/(h.m2) at 50p.a”.

 

& yes, I understand his 10 is not the same unit of measurement as my 0.6 ACH, but his 10 is too leaky to even meet current building regs for a non-MVHR new build, so this is pretty disappointing, really.  I’m having to request loads of corrections like this.  It’s taking forever.

Posted

Anyway, that’s enough whinging from me, & I don’t want to hijack @Swampy's thread, so can anybody help with @Swampy's request from the first post?

 

 

On 02/02/2024 at 00:28, Swampy said:

If anybody could recommend an MVHR installer local to east Berkshire, that would be great.

 

Posted
3 hours ago, saveasteading said:

We build to control air leakage, then pressure test at high pressure with all fans and vents sealed.

Then we remove the seals and allow draughts to flow freely from each wc and kitchen. Unless they have automatic shutters but they seem rare.

Surely the thing about MVHR is that it is controlled ventilation, complimented by heat recovery, and so when combined with great airtightness, which has other benefits in addition, you are in control of the ventilation and the more of the heat that is recovered. You are brining air in and taking it out again in such a way, at such flow rates and in such places that draughts are not a thing, are not subject to the vagaries of the external wind direction / strength. Because it's all warmed so is less obtrusive because it is already mixed and not arriving through very effect venturis that increase its velocity and create discomfort. So it seems to me that, in such a scenario, draughts don't flow freely they flow in a highly controlled manor - it's not pure external air rushing past you to get into the place but air at room temperature flowing slowly past you in from the supply vents and out of the extract vents.  It is also, however, clear that the recommendations around the Air Change (AC) volumes is a bit OTT as most people here seem to get by with a fraction of the recommended levels. 

 

I started out wondering if MVHR was for us but I have been convinced it is the best way forward and so just allowing air in and out in an uncontrolled fashion is not for us although it would be a lot cheaper at the outset without doubt.

  • Like 1
Posted

A point people miss with airtightness is the role it plays in keeping damp air out of your walls and ceilings with the knock on effects of interstatial condensation etc. If you want a durable building you must control the air leakage through the structure. 

 

This is of course in addition to it's comfort benefits and energy savings. 

 

Regarding ventilation theres essentially only two types. 

 

1. Holes in the wall and hope for the best. Be prepared to be overventilated in gale and  underventilate otherwise. 

 

2. Continuous mechanical ventilation, with or without heat recovery.

 

MVHR is the most comfortable, uses least energy. It's not cheaper than other forms once you take filters and servicing into account.

 

PIV,dMEV,MEV,DCV are all the same thing with little nuances. Just sucking or blowing air in/out. All will give you adequate quality air if set it up correctly. Unfortunately unlike MVHR you still need holes in the wall which may be drafty on windy days. 

 

@Eastfield have a look on search for @Thedreamer who heats their house with a stove and uses an ESHP for DHW and ventilation. An elegant solution I thought. 

 

 

 

  • Like 2
Posted
6 hours ago, Tony L said:

“We build…”, are you talking about

Apologies for an oversimplified discourse.

I meant 'we' as the simple requirements of the regs for a new build, but with BH level of care and supervision.

So it will satisfactorily airtight but with  the resulting dribbles of air through the fabric, and more at fans and any vents.

 

3 hours ago, MikeSharp01 said:

draughts don't flow freely they flow in a highly controlled manor

 

Good pun on manor/manner.

Draughts was a deliberate over-statement. I meant airflow that isn't designed.

Every time the front door is opened there will be a few m3 of air in or out, however well mvhr is designed.

 

I don't suppose we will ever know the reality unless we here of a newbuild without MVHR that is failing on air quality, or someone builds 2 otherwise  identical houses for comparison... and that won't happen.

 

Plus cynical me says that there is an industry that sells mvhr, but not one that suggests not adopting it.

Included in the decision are the weaving of ducts through the structure, the ease of maintenance , and the unknowns.

 

Me? It remains debateable and I have plumped for 'not'.

  • Like 1
Posted
On 01/01/2026 at 11:56, JohnMo said:

Big assumption there, it certainly may not be airtight - unless it was tested to show it is.

 

Granted, but I’m doing it myself, and will make sure it is…..

Posted
21 hours ago, MikeSharp01 said:

I started out wondering if MVHR was for us but I have been convinced it is the best way forward and so just allowing air in and out in an uncontrolled fashion is not for us although it would be a lot cheaper at the outset without doubt.

Conversely I started out convinced that it was for us, but now think otherwise. I don’t think the case is as binary as you suggest, in that I imagine it is possible to create a system which is highly controlled but without the heat recovery. I just need someone to help me design it for our home….

Posted
20 hours ago, Iceverge said:

A point people miss with airtightness is the role it plays in keeping damp air out of your walls and ceilings with the knock on effects of interstatial condensation etc. If you want a durable building you must control the air leakage through the structure. 

 

This is of course in addition to it's comfort benefits and energy savings. 

 

Regarding ventilation theres essentially only two types. 

 

1. Holes in the wall and hope for the best. Be prepared to be overventilated in gale and  underventilate otherwise. 

 

2. Continuous mechanical ventilation, with or without heat recovery.

 

MVHR is the most comfortable, uses least energy. It's not cheaper than other forms once you take filters and servicing into account.

 

PIV,dMEV,MEV,DCV are all the same thing with little nuances. Just sucking or blowing air in/out. All will give you adequate quality air if set it up correctly. Unfortunately unlike MVHR you still need holes in the wall which may be drafty on windy days. 

 

@Eastfield have a look on search for @Thedreamer who heats their house with a stove and uses an ESHP for DHW and ventilation. An elegant solution I thought. 

 

 

 

Thanks for the tip Iceverge. Point taken re holes in the wall, but surely there are ways to mitigate wind ingress?…..

Posted
17 hours ago, saveasteading said:

 

I don't suppose we will ever know the reality unless we here of a newbuild without MVHR that is failing on air quality, or someone builds 2 otherwise  identical houses for comparison... and that won't happen.

 

Plus cynical me says that there is an industry that sells mvhr, but not one that suggests not adopting it.

Included in the decision are the weaving of ducts through the structure, the ease of maintenance 

Agree with all of this 👍

Posted
1 hour ago, Eastfield said:

Thanks for the tip Iceverge. Point taken re holes in the wall, but surely there are ways to mitigate wind ingress?…..

 

Yes, humidity sensitive vents. 

 

https://store.beamcentralsystems.ie/products/dcv-intake-air-valves?srsltid=AfmBOopO9UvLROCeVYnm2p6C6nY5d6-wDWRsDgu2zj1VFhr6o6XYlf0p

 

They're not cheap though and would go a lot of the way towards a full MVHR system. You may find it acceptable with just well set passive vents. You could start there and upgrade them if you found them too drafty.

Posted
On 30/12/2025 at 22:23, G and J said:

I honestly couldn’t disagree more.  
 

But as we’ve not built the house yet my opinion is not based experience, just theory.  However I do know from experience that moving air takes a lot less energy than heating it. 

That makes 2 of us and we have built it and have been living in a very airtight build with MVHR now for 5 months now. The costs to run the ASHP have been similar to the 2 bedroom cottage we were living in on site whilst building and what is immeasurable is the lack of a need to open a window.

We always said that we probably would open windows, as I did not truly believe that MVHR could take the fresh external air and make it 'fresh' but we just haven't needed or wanted to. Living in a well sealed box with air fed from a system might sound crazy, but it is a complete gamec hanger. We have a large footprint with only 2 upstairs bedrooms we have UFH on the ground floor with FCU's in the bedrooms and we have not felt too cold or too hot. It all just works and we barely think about it. 

  • Like 1
Posted
4 hours ago, Iceverge said:

 

Yes, humidity sensitive vents. 

 

https://store.beamcentralsystems.ie/products/dcv-intake-air-valves?srsltid=AfmBOopO9UvLROCeVYnm2p6C6nY5d6-wDWRsDgu2zj1VFhr6o6XYlf0p

 

They're not cheap though and would go a lot of the way towards a full MVHR system. You may find it acceptable with just well set passive vents. You could start there and upgrade them if you found them too drafty.

 

Its far from clear how these work. Google not much help either. What causes the air to move when they are open, as it says you need 20ps air pressure difference?

 

Posted

I think Aereco had the original design. 

 

As I understood it it's just a strip of nylon that expands and contracts with humidity. 

 

20Pa really isn't that much. 100000Pa is 1 Bar or about 14psi.

Posted
2 hours ago, mickeych said:

That makes 2 of us and we have built it and have been living in a very airtight build with MVHR now for 5 months now. The costs to run the ASHP have been similar to the 2 bedroom cottage we were living in on site whilst building and what is immeasurable is the lack of a need to open a window.

We always said that we probably would open windows, as I did not truly believe that MVHR could take the fresh external air and make it 'fresh' but we just haven't needed or wanted to. Living in a well sealed box with air fed from a system might sound crazy, but it is a complete gamec hanger. We have a large footprint with only 2 upstairs bedrooms we have UFH on the ground floor with FCU's in the bedrooms and we have not felt too cold or too hot. It all just works and we barely think about it. 

Do you use the fancoils much?

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...