Eastfield Posted December 30, 2025 Posted December 30, 2025 12 hours ago, G and J said: I’m not sure I agree that it’s impossible to calculate a payback for the cost of MVHR because using Jeremy’s spreadsheet our heating requirement is a lot less than half of what it would be with sub one air changes per hour compared to say five air changes per hour that you’d need with a non-heat recovery system. However, the extra spend to get airtight would be quite difficult to calculate and indeed we’ve not done a cost benefit calculation in payback terms, we’ve gone for it just as an act of faith for comfort. So despite it being theoretically possible, I think calculating payback for MVHR for us at least is rather pointless. Excuse my ignorance, but why do you need such a higher number of changes per hour with a non-heat recovery system?
G and J Posted December 30, 2025 Posted December 30, 2025 I think you need a certain number of air changes per hour to keep all fresh. With trickle vents it’s a blow through. But with MVHR one still (as I understand it) get a good flow through if fresh air. It at first appears confusing that we have a really low air change score to make MVHR worth having, but that’s a test of the leakiness of the house, not the number of air changes that a good ventilation system will give.
Bonner Posted December 31, 2025 Posted December 31, 2025 10 hours ago, Eastfield said: I'm intrigued by your sub £2k system Bonner. Are you willing to share some details? Also, I couldn't agree more re trickle vents, and I do want to have full control of my ventilation. I don't want to compromise on health and comfort, ventilation is not optional. The point Jeremy is making, if I understand correctly, is that the heat saved by the MVHR is not substantial, and it would be more efficient to remove the stale air along with its heat, bring fresh air into the house and heat it via an economical heating method, which I believe I have in the biomass boiler. Please see another post here, note the unit was 20% cheaper when I bought it. I agree the heat saving is not huge, however you would still need the fan(s), distribution system and method of preheating the incoming air to avoid cold drafts.
JohnMo Posted December 31, 2025 Posted December 31, 2025 10 hours ago, Eastfield said: Excuse my ignorance, but why do you need such a higher number of changes per hour with a non-heat recovery system? You don't but the high number is an instantaneous air flow rate for intermittent fans. Or maybe a house leakage rate at 50Pa, which isn't the actual air movement through a building. You can have good controlled ventilation without MVHR. MVHR is the icing on the cake, when you have done, wall, floor and roof insulation to death, triple glazed and made house airtight. Most houses don't need it, don't benefit from it. But they do benefit from a well thought out and appropriate ventilation system. 1
Eastfield Posted 9 hours ago Posted 9 hours ago On 31/12/2025 at 09:02, JohnMo said: You can have good controlled ventilation without MVHR. MVHR is the icing on the cake, when you have done, wall, floor and roof insulation to death, triple glazed and made house airtight. Most houses don't need it, don't benefit from it. But they do benefit from a well thought out and appropriate ventilation system. Ah..... the voice of reason. Our house is a new build so by virtue will be exceptionally well insulated and airtight. we have a 'cheap' source of heating. It's all very well those with MVHR stating they'd never live in a house without it, but have they lived in modern, well insulated home with well designed ventilation but no mvhr by comparison? I'd be keen to hear from anyone who has in order to gain an unbiased view. It's easy to disappear down a rabbit hole. Up until I watched the video in my first post I was dead set on MVHR. The concept makes complete sense, however I have been kept awake at night with the problems of routing ductwork, locating the unit and coming up with £5-6k to pay for it. I still need to find a decent company to give me some unbiased and impartial advice, any suggestions would be gratefully received. Thanks for all your responses. We may end up with MVHR yet, but all options will be explored.... 1
JohnMo Posted 8 hours ago Posted 8 hours ago 30 minutes ago, Eastfield said: so by virtue will be exceptionally well insulated and airtight Big assumption there, it certainly may not be airtight - unless it was tested to show it is.
saveasteading Posted 7 hours ago Posted 7 hours ago I have awarded hearts to people I agree with.... which is contrary to good logic of listening to all views. But my prejudice, or is it exierience and intuition, is that mvhr is grossly over-rated. We build to control air leakage, then pressure test at high pressure with all fans and vents sealed. Then we remove the seals and allow draughts to flow freely from each wc and kitchen. Unless they have automatic shutters but they seem rare. Stuffiness can only raise from habitation, but then the fans are used which draw air from everywhere, to be replaced by whatever leakage there may be. Nobody suffocates. I've only had old draughty houses but the steading (family owned) has no mvhr and has no issues of stuffiness or condensation. I promise to report if that changes. In business I did no homes, but offices, nursing homes and school classrooms* would have the same issues..in all cases we agreed with the client to "chance it" without mvhr.... no problems reported ever. That's x 20 applicable projects at a guess. So I think I'm right. Still listening of course, but we don't intend to fit £20k on mvhr at the current project. * This seems extreme, with 30+ kids in a room. High ceilings help of course but window vents and door openings appear to suffice. Perhaps the teachers open windows sometimes.
Tony L Posted 6 hours ago Posted 6 hours ago (edited) 1 hour ago, saveasteading said: We build to control air leakage, then pressure test at high pressure with all fans and vents sealed. Then we remove the seals and allow draughts to flow freely from each wc and kitchen. Unless they have automatic shutters but they seem rare. I’m just trying to understand this. When you say, “We build…”, are you talking about your buildings that don’t have MVHR, or are you talking about people that self-build with MVHR? Or perhaps both groups of people. My understanding is, if I build a house with MVHR, I would most likely not have vents sucking air from the kitchen & bathrooms straight through my wall to the outside; the bathrooms will just have MVHR extracts & the kitchen will have the same + a recirculating hood over the hob that filters the air rising from the hob then dumps it into the kitchen to be taken away by the kitchen’s MVHR extract port. Have I got that wrong? Edited 6 hours ago by Tony L 1
Bramco Posted 6 hours ago Posted 6 hours ago 4 minutes ago, Tony L said: Have I got that wrong? No. Except delete the words 'most likely in the 1st sentence of the 2nd para.
Tony L Posted 6 hours ago Posted 6 hours ago Thanks for a quick answer on that one, @Bramco. I am just in the process of reviewing/correcting the first draft BC/construction drawings my architectural technician has drawn up for me, & my instructions include a note to delete the MEVs he's drawn in, so I just wanted to be sure.
JohnMo Posted 5 hours ago Posted 5 hours ago 21 minutes ago, Tony L said: Thanks for a quick answer on that one, @Bramco. I am just in the process of reviewing/correcting the first draft BC/construction drawings my architectural technician has drawn up for me, & my instructions include a note to delete the MEVs he's drawn in, so I just wanted to be sure. If you are doing MVHR you really need an airtightness better than 3. Otherwise there's a good chance you are wasting energy not saving it. If you are not aiming for level of airtightness there are better or more effective ways to ventilate. There is no reason to have any vents in windows or anywhere else and still be fully compliant with building regs if you are using MVHR.
Tony L Posted 5 hours ago Posted 5 hours ago Thanks @JohnMo. My brief to the arch tec specified MVHR & said, “Airtightness will be to near passive standard: we’ll aim for 0.6 & see how close we can get. Insulation will NOT be to passive standard…”. The arch tec’s drawings include a note which says, “The measured air permeability should be no worse that [sic] 10m3/(h.m2) at 50p.a”. & yes, I understand his 10 is not the same unit of measurement as my 0.6 ACH, but his 10 is too leaky to even meet current building regs for a non-MVHR new build, so this is pretty disappointing, really. I’m having to request loads of corrections like this. It’s taking forever.
Tony L Posted 4 hours ago Posted 4 hours ago Anyway, that’s enough whinging from me, & I don’t want to hijack @Swampy's thread, so can anybody help with @Swampy's request from the first post? On 02/02/2024 at 00:28, Swampy said: If anybody could recommend an MVHR installer local to east Berkshire, that would be great.
MikeSharp01 Posted 3 hours ago Posted 3 hours ago 3 hours ago, saveasteading said: We build to control air leakage, then pressure test at high pressure with all fans and vents sealed. Then we remove the seals and allow draughts to flow freely from each wc and kitchen. Unless they have automatic shutters but they seem rare. Surely the thing about MVHR is that it is controlled ventilation, complimented by heat recovery, and so when combined with great airtightness, which has other benefits in addition, you are in control of the ventilation and the more of the heat that is recovered. You are brining air in and taking it out again in such a way, at such flow rates and in such places that draughts are not a thing, are not subject to the vagaries of the external wind direction / strength. Because it's all warmed so is less obtrusive because it is already mixed and not arriving through very effect venturis that increase its velocity and create discomfort. So it seems to me that, in such a scenario, draughts don't flow freely they flow in a highly controlled manor - it's not pure external air rushing past you to get into the place but air at room temperature flowing slowly past you in from the supply vents and out of the extract vents. It is also, however, clear that the recommendations around the Air Change (AC) volumes is a bit OTT as most people here seem to get by with a fraction of the recommended levels. I started out wondering if MVHR was for us but I have been convinced it is the best way forward and so just allowing air in and out in an uncontrolled fashion is not for us although it would be a lot cheaper at the outset without doubt.
Iceverge Posted 2 hours ago Posted 2 hours ago A point people miss with airtightness is the role it plays in keeping damp air out of your walls and ceilings with the knock on effects of interstatial condensation etc. If you want a durable building you must control the air leakage through the structure. This is of course in addition to it's comfort benefits and energy savings. Regarding ventilation theres essentially only two types. 1. Holes in the wall and hope for the best. Be prepared to be overventilated in gale and underventilate otherwise. 2. Continuous mechanical ventilation, with or without heat recovery. MVHR is the most comfortable, uses least energy. It's not cheaper than other forms once you take filters and servicing into account. PIV,dMEV,MEV,DCV are all the same thing with little nuances. Just sucking or blowing air in/out. All will give you adequate quality air if set it up correctly. Unfortunately unlike MVHR you still need holes in the wall which may be drafty on windy days. @Eastfield have a look on search for @Thedreamer who heats their house with a stove and uses an ESHP for DHW and ventilation. An elegant solution I thought.