Oven cable

Featured Replies

Sparky left me a collection of cables .

 

The 10mm is mega chunky - assume I use this for ovens and hob ?

 

2.5mm for standard sockets ?

 

 

IMG_8788.jpeg

IMG_8789.jpeg

  • Replies 53
  • Views 10k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • Depends on the distances and load but yes the 10mm would be for an electric hob or combined oven and hob.   Many Electric ovens (without rings/hobs) only need 2.5mm^2 and quite a few are sup

  • ToughButterCup
    ToughButterCup

    Hmmm, easy.... the discussion goes like this....   Muggins    " How many ovens do you need love?"   SWMBO      "4"   Muggins      "Wha? 4 ... why ?   SWMBO     

  • I think two single runs in 10mm one to the hob and one to the oven area would be normal. The 10mm^2 would be terminated at the oven/hob end with a accessible Cooker(hob) switch and a Cooker Connection

Posted Images

  • Author

IMG_8790.jpeg
 

1mm for low voltage lighting 

Edited by Pocster

3 minutes ago, Pocster said:

The 10mm is mega chunky - assume I use this for ovens and hob ?

 

2.5mm for standard sockets ?

 

Depends on the distances and load but yes the 10mm would be for an electric hob or combined oven and hob.

 

Many Electric ovens (without rings/hobs) only need 2.5mm^2 and quite a few are supplied with a plug to suit standard socket..

 

2.5mm is for sockets (ring mains effectively have two 2.5mm^2 in parallel as power flows both ways around the ring).

 

The 1.0mm^2 is for lighting but some people prefer 1.5mm^2 as I think it can be covered with insulation without derating? However with LED lighting I don't think that's the issue it once was.

  • Author
5 minutes ago, Temp said:

 

Depends on the distances and load but yes the 10mm would be for an electric hob or combined oven and hob.

 

Many Electric ovens (without rings/hobs) only need 2.5mm^2 and quite a few are supplied with a plug to suit standard socket..

 

2.5mm is for sockets (ring mains effectively have two 2.5mm^2 in parallel as power flows both ways around the ring).

 

The 1.0mm^2 is for lighting but some people prefer 1.5mm^2 as I think it can be covered with insulation without derating? However with LED lighting I don't think that's the issue it once was.

Yeah - I’ve seen ovens run off a standard plug . I’ll stick chunky 10mm in as a ring . Distance from oven / hob to consumer unit is under 10metres .

I’ll daisy chain from oven to other oven to hob then back to CU .

No insulation over my lighting wiring so I’ll leave as 1mm

I think two single runs in 10mm one to the hob and one to the oven area would be normal. The 10mm^2 would be terminated at the oven/hob end with a accessible Cooker(hob) switch and a Cooker Connection Unit (faceplate/junction box thing).

 

Run a 2.5mm ring to sockets as well so you can choose later if you want to hard wire the oven to the 10mm^2 or just plug it into a socket.

27 minutes ago, Pocster said:

.... I’ll stick chunky 10mm in as a ring . ....

 

10mm is 'king hard work.......

41 minutes ago, Pocster said:

I’ll stick chunky 10mm in as a ring .

Do come and post pictures when you have done that.  I will be surprised of you find a 13A socket that will actually fit two 10mm cables.

  • Author
2 minutes ago, ProDave said:

Do come and post pictures when you have done that.  I will be surprised of you find a 13A socket that will actually fit two 10mm cables.

That’s the thing I thought . It’s well chunky ! . I’ll put the cables in position for oven / hob but not clipped . Sparky can then pull them out and replace if it upsets him . He left me 10mm ( actually got 2 rolls of it ) .

8 minutes ago, ProDave said:

Do come and post pictures when you have done that.  I will be surprised of you find a 13A socket that will actually fit two 10mm cables.

 

Our cooker: 10mm feed intended - until reality struck. Now there's 10mm to a hewooooge socket and a 13 Amp plug to a Bosch (natch) induction fingy....

10mm - I could hardly cut it with an angle grinder ......

  • Author
18 minutes ago, ToughButterCup said:

 

Our cooker: 10mm feed intended - until reality struck. Now there's 10mm to a hewooooge socket and a 13 Amp plug to a Bosch (natch) induction fingy....

10mm - I could hardly cut it with an angle grinder ......

I struggled with wire snips to cut the 10mm . Better to over spec I guess ( as I have the cable ) and let sparky sort .

10mm to the induction hob (11kW iirc) for us and 2.5mm feed for each oven (yes 4 cables!). Each will have an isolation switch in a kitchen unit. 

Edited by Thorfun

  • Author
30 minutes ago, Thorfun said:

10mm to the induction hob (11kW iirc) for us and 2.5mm feed for each oven (yes 4 cables!). Each will have an isolation switch in a kitchen unit. 

I’ve resisted but I can’t any longer … why 4 ovens ? - forget SWMBO bs ! . What would you be cooking that requires 4 ovens ? . Indulge me ! 😊

4 hours ago, Pocster said:

I’ll stick chunky 10mm in as a ring .

 

This I have to see! 😂

 

Generally 10mm2 should just come as a radial from your cooker / hob breaker and terminate in a 45A cooker switch. From there,  again in 10mm2 to a cooker connection plate. You can get "double enders" so you can feed the hob and oven. Please go into the wholesaler and ask for such:

 

https://www.tlc-direct.co.uk/Products/AA45DCOP.html

  • Author
6 minutes ago, Onoff said:

 

This I have to see! 😂

 

Generally 10mm2 should just come as a radial from your cooker / hob breaker and terminate in a 45A cooker switch. From there,  again in 10mm2 to a cooker connection plate. You can get "double enders" so you can feed the hob and oven. Please go into the wholesaler and ask for such:

 

https://www.tlc-direct.co.uk/Products/AA45DCOP.html

All for a double Ender 😉

  • Author

So !

 

Do I want 

 

CU to oven switch 10mm

 

then this to oven 

 

to 2nd oven 

 

to hob 

 

6mm for those ?

 

or - should each have a seperate ( 6mm ? ) run from oven switch ? I.e radial from that ?

8 hours ago, Pocster said:

or - should each have a seperate ( 6mm ? ) run from oven switch ? I.e radial from that ?

 

-10mm to the cooker switch.

-10mm to the double cooker connection plate.

-2 seperate runs from there one to each appliance. 6mm I imagine will be fine to each but check the loads. Also that it will fit in the appliance. Sometimes a butyl flex is better. 

15 hours ago, Pocster said:

1mm for low voltage lighting 

A 10 m run of that will have a percentage volt drop, at 1 A/12V of 7.3%.  I think that is outside the regs.

  • Author
4 minutes ago, SteamyTea said:

A 10 m run of that will have a percentage volt drop, at 1 A/12V of 7.3%.  I think that is outside the regs.

Nah nah - all are well under 10m

  • Author
30 minutes ago, MikeSharp01 said:

Rich beyond the dreams of avarice. :)

Not sure why he got me to buy 2 rolls of 10mm ….

12 hours ago, Pocster said:

I’ve resisted but I can’t any longer … why 4 ovens ? - forget SWMBO bs ! . What would you be cooking that requires 4 ovens ? . Indulge me ! 😊

 

Hmmm, easy.... the discussion goes like this....

 

Muggins    " How many ovens do you need love?"

 

SWMBO      "4"

 

Muggins      "Wha? 4 ... why ?

 

SWMBO       "How many  cross-cut saws have you got ... and I think I saw about 6 or 7 drills - some of them huge in that massive cupboard of yours, then there's the table saw - and the 'spare' in the other container . And  (warming to her annoyance) how much did that lot cost eh? Tell me that ?

 

LONG  PAUSE .................................................

 

Muggins    "Well ducks, ya should have told me that a year ago when I asked you to approve the kitchen plan. ... not enough space now  "

 

I have learned the hard - very hard - way that when I play an ace, I should never - ever - ever - grin.

 

 

33 minutes ago, SteamyTea said:

1mm for low voltage lighting

Some People don’t realise that low voltage often needs bigger cables !!!   (Less volts = more Amps)

  • Author
19 minutes ago, joe90 said:

Some People don’t realise that low voltage often needs bigger cables !!!   (Less volts = more Amps)

I do have a confession here . I haven’t actually used any of the 1mm for anything . It’s solid core and makes it difficult with the light fittings .

14 hours ago, Pocster said:

I’ve resisted but I can’t any longer … why 4 ovens ? - forget SWMBO bs ! . What would you be cooking that requires 4 ovens ? . Indulge me ! 😊

2 x ovens for cooking meals in. also one child has an allergy so for some foods we need to cook separately. 1 x microwave. then 3 ovens wouldn't look right so to even it out we got a steam oven as well. makes everything look aligned and appeals to our compulsive natures.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.