my suspicion is that I’ll need to spend a day or so playing with the PID settings. But for now, another fan coil to get on the wall.

Posted (edited)
40 minutes ago, dpmiller said:

remind us what "stop temp differential" you're set to- increasing that a degree might well save ploughing through the PID stuff too much

I’ve bumped it to 5 degrees, it was at 1…. And it’s been running for the last 20 mins without stopping 👍 It’s ramping up and down, but it hasn’t stopped.

 

I also bumped the weather comp up 1 degree as it was a little low at the current OAT.

 

kP is 5c

kI is 100 secs (iirc)

kD is 0

Edited by HughF
Posted
57 minutes ago, JohnMo said:

Sounds good

Yeah, been working well today, after some hard work this morning recovering from being off from 23:30 till 05:30. Seems to be ticking along quite happily at the lowest modulation, until it warmed up this afternoon.

  • 1 year later...
Posted (edited)

Dragging this thread kicking and screaming into 2025, it looks like some interesting developments by Chris and the team at SPRSUN over in China:-

 

£1700 gets you the new, inverter driven version of the old 'Pro' unit - in a more sensible 6kW output

https://coolenergyshop.com/collections/air-source-heat-pumps/products/proinverter-air-source-heat-pump-6kw

 

That's a decent price. No idea if it's built on the Carel platform, for that money I expect not, but it has a particularly wide modulation ratio - considerably wider than their r290 unit, or the older r410a units that I, Marvin and dpmiller are running.

Edited by HughF
  • Like 1
  • 1 month later...
Posted

Thanks for the update @HughF. I'm currently in the process of arranging delivery of an ASHP & UVC from CoolEnergy via their MCS grant service. All the other installers wanted an extra £6k on top of the BUS, whereas CoolEnergy can supply the units and do the commissioning for the grant effectively "free" as long as I can arrange the install.

 

I'm looking at the CE-IVT10-EVI which is billed as 4.89kW - 10.47kW @A-3/35.
There is a newer model, the CE-ET10 but the capacity on this was slightly smaller at 3.89kW - 7.46kW @A-3/35). It's not on their website yet as far as I can tell. I've attached the spec sheet incase it helps anyone else.

 

Once I've got hold of the kit I'll report back on ease of install & findings.

 

CE-ET10 (QR).pdf

Posted
On 26/02/2025 at 21:38, alfaTom said:

Thanks for the update @HughF. I'm currently in the process of arranging delivery of an ASHP & UVC from CoolEnergy via their MCS grant service. All the other installers wanted an extra £6k on top of the BUS, whereas CoolEnergy can supply the units and do the commissioning for the grant effectively "free" as long as I can arrange the install.

 

I'm looking at the CE-IVT10-EVI which is billed as 4.89kW - 10.47kW @A-3/35.
There is a newer model, the CE-ET10 but the capacity on this was slightly smaller at 3.89kW - 7.46kW @A-3/35). It's not on their website yet as far as I can tell. I've attached the spec sheet incase it helps anyone else.

 

Once I've got hold of the kit I'll report back on ease of install & findings.

 

CE-ET10 (QR).pdf 608.35 kB · 9 downloads

Have CE done their MCS design to size your heat pump at 10.5kw? Did you or anyone else check their sizing?

Posted
9 hours ago, Dillsue said:

Have CE done their MCS design to size your heat pump at 10.5kw? Did you or anyone else check their sizing?

CE are working from my sizing - heatpunk shows roughly 8kW heat loss for the property.

Couldn't get any heatgeeks or other engineers to attend to review and they all quoted £14k+ to fit ASHP & UVC.

Posted
18 hours ago, Dillsue said:

CoolEnergy via their MCS grant service

We are looking to do the same with them, we are awaiting the MCS certification of their tiny unit Pro Inverter Air Source Heat Pump | CE-iH6 | 1.74kW - 6kW to move ahead on it, it has great modulation depth and we, if I have my calculations correct, will only need about 2kW at -3 so it should cover us. Everybody else quoted silly money above the BUS grant.

Posted
8 minutes ago, MikeSharp01 said:

We are looking to do the same with them, we are awaiting the MCS certification of their tiny unit Pro Inverter Air Source Heat Pump | CE-iH6 | 1.74kW - 6kW to move ahead on it, it has great modulation depth and we, if I have my calculations correct, will only need about 2kW at -3 so it should cover us.

Kind of unit that would also suit me.  They have 2 left in stock.

But where is the data sheet about it?

Posted

 

18 minutes ago, Beelbeebub said:

9 is next to 0 so 0.3kw?

Yes one is forced to assume so, or something similar, or this machine is able to warp physics. It has been like that forever and I told them about when I enquired. I guess it's a small company trying to do a good job but it can't quite yet sweep in all the corners. All my dealings with them have been good, professional and supportive. 

Posted

CE’s MCS route worked well for me under the old RHI scheme- Friendly surveyor came out once I’d confirmed install and did the MCS cert and submitted. Job’s a good’un.

 

Had a few foibles with my 3phase 18kW unit but mostly around the compressor terminals causing tripping issues. Fixed now with a new set of connectors recommended by Chris.