12 minutes ago, Oz07 said:
Yes I'm bored. Doesn't look as big a difference as you make it sound
Its not the same area though - Passiv is 1/5th of the 20p per metre, or the gap between those 20ps at the bottom..
I also have Rationel 3G windows. They seal extremely well. If noise is a concern I recommend laminated glass which adds a few percent to the cost and considerably reduces noise transmission.
As mentioned tough I would also focus on the airtightness as a lot of the noise actually comes in around the frames and absolutely having MVHR and no trickle vents. Our windows got considerably quieter when we put mastic around the window plasterboard junction on the inside.
If noise is a concern though I would also look at the design of the house as relates to wind. We have a couple of rooms with vaulted ceilings, they are considerably noisier when it is windy than the bedrooms with a loft above which are pretty much silent. Massive improvement on our old house though.
There are some discussions out there about triple glazing actually increasing noise if you get it wrong.  Something about making sure the 3 panes of glass are different thicknesses to ensure each one captures different wavelengths without passing them on.  You should probably opt for acoustic triple on anything facing the road, it uses a thicker piece of PVB in the laminated layer.
6 hours ago, jack said:
It may be that this particular BCO is giving them a break for whatever reason, but no way would I rely on opening a window for ventilation (and nor would I expect most BCOs to allow it).
My BCO said that if the windows to the extension had what he called night ventilation then I wouldn’t need trickle vents. My old house had these and they were good as the window could be locked but slightly vented. Not as secure as a closed locked windows of course.
Interesting. I'm really surprised that building regs allow this, but I guess I've learned something!
No in-room ventilation is even more concerning in a properly airtight house.
The regulations do not state you must have trickle vents, you must have a form of background ventilation and that "can" be buy opening the window for ventilation. It is down to how the regulations are interpreted by the BCO
11 hours ago, tonyshouse said:
windows are nearly last on the list
They shouldn't be, the thermal envelope should always be number 1 on the list and that includes the windows.
Edited by craig
31 minutes ago, tonyshouse said:
I kind of agree but walls. Ceiling, floors come above windows as do draught proofing and air tightness
There is still to this day details that come across my desk and I look at them and know instantly, that it has been the architects maybe even the clients last things on their mind. Windows and doors are integral to the thermal envelope and airtight layer. Without them, you just have a big hole in the wall(s) and airtight layer.
https://passipedia.org/planning/thermal_protection
Has anyone seen some info on the net re tripple glazing regarding the life span of the sealed units (8 years?). There is some suggestion that the middle pane is in it's own greenhouse and subject to high temperature and higher thermal movement. Thus a tripple glazed unit is more prone to failure. We know they are more expensive, heavy to design for.
It may be that you need tripple glazing to get you over the line for BC purposes but if this is your forever home then is this a cause for concern? How much will it cost you to replace them (tripple glazed) at a later date?
@craig "Windows and doors are integral to the thermal envelope and airtight layer. Without them, you just have a big hole in the wall(s) and airtight layer. "
Yes Craig is bang on. Craig is taking a hollistic view. No point in putting in a Rolls Royce window if you neglect the detail around the window and let drafts fly about where they should not be.
It’s generally caused by thermal stress, it is reduced by toughening the glass on the middle pane but that also adds costs.
Inprovement from Building regs
Airtightness Before 7ACH
Gross Floor Area 150m2
  After 0.6ACH
MVHR Before 0% Efficiency
2 story 12m x 7.5m footprint
  After 90% Efficiency
Triple Glazing Before
1.2 W/m2 (Glazing)
(36.6m2) After
0.5 W/m2 (Glazing)
Walls Before 0.21 W/m2K
(210m2) After 0.13 W/m2K
Roof Before 0.16 W/m2K
(90m2) After 0.086 W/m2K
Floor Before 0.21 W/m2K
(90m2) After 0.106 W/m2K
kWh/(m2/a) W/m2
75/42   AT AT/MV AT/MV/3G AT/MV/3G/W AT/MV/3G/W/R
Airtightness 48/20 XXX XXX XXX XXX XXX
MVHR 60/37 33/16 XXX XXX XXX XXX
Triple Glazing 68/39 40/18 25/13 XXX XXX XXX
Walls 68/39 40/18 25/13 18/11 XXX XXX
Roof 72/41 45/19 30/15 22/12 15/10 XXX
Floor 73/41 45/20 30/15 23/13 16/10 13/9
Annual Heating Cost (€)
  (4c/kWh)
450 0 AT AT/MV AT/MV/3G AT/MV/3G/W AT/MV/3G/W/R
Airtightness 288 XXX XXX XXX XXX XXX
MVHR 360 198 XXX XXX XXX XXX
Triple Glazing 408 240 150 XXX XXX XXX
Walls 408 240 150 108 XXX XXX
Roof 432 270 180 132 90 XXX
Floor 438 270 180 138 96 78
Annual Heating Cost
  (8c/kWh)
900 0 AT AT/MV AT/MV/3G AT/MV/3G/W AT/MV/3G/W/R
Airtightness 576 XXX XXX XXX XXX XXX
MVHR 720 396 XXX XXX XXX XXX
Triple Glazing 816 480 300 XXX XXX XXX
Walls 816 480 300 216 XXX XXX
Roof 864 540 360 264 180 XXX
Floor 876 540 360 276 192 156
Annual Heating Cost
  (16c/kWh)
1800 0 AT AT/MV AT/MV/3G AT/MV/3G/W AT/MV/3G/W/R
Airtightness 1152 XXX XXX XXX XXX XXX
MVHR 1440 792 XXX XXX XXX XXX
Triple Glazing 1632 960 600 XXX XXX XXX
Walls 1632 960 600 432 XXX XXX
Roof 1728 1080 720 528 360 XXX
Floor 1752 1080 720 552 384 312
Thank you Craig.
I'm more structures orientated, know a little about the principles of glass design but now know more.
Thanks again Craig. Every day is a school day.
Above is a spreadsheet from my energy planning. All figures taken from messing around with PHPP. Location is set to the South of Ireland.
I used the backstop Irish values for my starting point and passivhaus with a small margin for the finish.
Granted Airtightness may not be that bad to begin with.
I didn't bother changing the u value for the window frames so they're probably better than cheap double glazing. I also left the G factor at 3g for ease of calculation.  Glazing is split 58% S 16%W 16%E and 20%N.
My main takeaways were:
1. The drastic effect of airtightness followed by MVHR and triple glazing.
2. If your energy cost is very low there's little benefit in improving insulation beyond regs. (I know Ireland has tighter standards here than the UK)
In the first table the two figures are the total heat demand per year per meter and the second figure is the heating load.
Note: These figures only work for one specific house in one location but should still give a general picture. If you live in a hotter or colder region or build a house of a drastically different shape the picture will be different.
  After 0.6ACH
1.2 W/m2 (Glazing)
(36.6m2) After
0.5 W/m2 (Glazing)
kWh/(m2/a) W/m2
  (4c/kWh)
Annual Heating Cost
  (8c/kWh)
Annual Heating Cost
  (16c/kWh)
312
Hiya Iceverge.
That is some impressive figures. I have copied a bit of your table below.
I,m not sure if I am right or wrong here but.. as a designer over the years I have found that the window market is a bit worse than the second hand car market. That's just me!
You may achieve these values with a very big area of glass and thus the exposed perimeter area of a frame is not that significant, you can see this effect when you look up the insultation required for a floor slab .. Kingspan / Cellotex ask you to calculate the area vs the perimeter.. and this principle in some ways applies to glass and the surrounding frame.
Now, with modern argon filled units say the heat loss through the window frame can have a significant impact on the performance. When chosing windows you need to consider this. But it's hard to compare like for like as for a manufacturer to test every combination of window size is very expensive.
While I think your figure looks good for the glass only, one needs to have an appreciation of what these figures mean in practice and how you can best apply them to your design.
@craigI think Craig may be able to expand on practicalities of this in terms of the detailing round the frame, exposing the frame externally less to the cold air. There is much more to this than just looking at the U value of the glass.
Iceverge,
I hope I have not put you off but I think that you could better spend money on making sure you get a good quality of build. By all means use your calculations as a target but the key will be the quality of the workmanship and attention to detail.
For example if you put up a timber kit that is soaking wet, then fill between the studs with PIR insulation. Leave it a few months and you'll find gaps between the studs and the insutaltion as the timber has shrunk. You'll also find that the PIR you thought was fitted tightly is moving about a bit. It now acts as a duvet with your leg out the side of the bed!
If you can get a handle on this type of behavoir and seal things up, look after the quality of the build and material then you can get a cracking job without resorting to more expensive materials.
There is and it is the part that is most overlooked. Devil is in the detail.
The first image is therm calc for the head, which the jambs were also the same, not the difference is value - the second is far more efficient than the first. The architect wanted the first option for a better flow of ventilation (this is a PH btw) and wanted the exact same on the jambs, we insisted on the detail change to second snapshot for the jambs. I'm waiting on the phpp update but it will be significant.
Picture 1
Picture 2
image.png.131fac617ee5075c96511475b990fee3.png For Clarity this is the overall improved overall window U value with glazing at 0.5 W/(m2K)
image.png.1f723d8317ddcc1c614bc397a7e2c432.png This is when you drop to double glazing (1.2 W/(m2K) with the same passiv certified frames.Most double glazing frames would be worse.
We didn't use any PIR as I think it's entirely overrated. EPS in the floors and walls and cellulose in the roof. Agreed, detailing is everything with low energy houses.
I modelled all the junctions in our house myself. We compromised on some of the detailing such as placing the window at the outside of the cavities instead of the middle where they would have been most thermally efficient. It made it easier to build and secure a good wind-tight as well as an airtight envelope. Putting in a little extra insulation elsewhere to compensate was relatively cheap.
I left plenty of fat in the overall design to account for shortfalls in the build process. ( I think i allowed for 1.5 ACH to reach 10w/m2 heating load) As it was we achieved 0.3 ACH50. We moved in 3 weeks ago and the house is performing well with only an intermittent 2kw rad for space heating. Hopefully when the house dries out properly we can do away with this other than in just the most extreme situations.
On a large project or complex house shape chasing the gains made by ideal thermal detailing is certainly worthwhile. However my builder and I were first time passivehousers and the peace of mind granted by sticking close to known detailing and spending about €3k extra on insulation was the road we chose. As a result I suspect that as built performance will exceed 15kWh/m2a and 10W/m2.
  • Like 3
Hi Craig and Iceverge and all.
Thanks for posting,  great stuff for me to see how folk innovate, approach design.
Can I ask what sofware are you using to model the window reveals? Is it a small package (spread sheet)  for just heat flow or are you using part of a big expensive Finite Element package like Abacus?