@Nickfromwales and @TerryE This is the awkwardness of the pipe routing through the Kitchen/Utility wall. The diagram is to scale. I don't think I could core drill at an angle which would otherwise help greatly. It already looks like I'll need to box in above the kitchen cabinets for this reason.
-
Below is a comparison between satellite manifolds and a 1:1 radial arrangement. Greyed out doesn't have to pass through the wall. In the 1:1 Radial arrangement, 29 pipes (17no. cold 15mm, 2no. cold 10mm, 6no. hot 15mm, and 4no. hot 10mm) have to pass awkwardly through the Kitchen/Utility wall. In the Satellite Manifold arrangement that comes down to 11 (5no. cold 15mm, 4no. hot 15mm, and 2no. hot 10mm). The Satellite Manifolds would have to be accessible, but wouldn't necessarily feature shutoffs. 1:1 Radials: Satellite Manifolds:
-
Servicing loos and basin colds with 10mm would halve the number of core holes I drill for cold if using 38mm core drill. Such a hole allows 32mm pipe as conduit and 2x 15mm and 2x 10mm within (or 6x if only 10mm pipes). Otherwise I need 11x 38mm core holes for all pipes. I've wondered about 78mm core with downpipe conduit. Unfortunately, a letter box isn't practical. Would be better.
-
It's quite tough 10N aggregate block so harder work, but not the main concern. I don't think flows would suffer as I don't expect the bath and shower in a room to be running at the same time. Satellite manifolds would only service one room. All pipes passing through will then need to bend down to go to the manifolds, so that will be a bit tricky. Added to that is the plant room ceiling is 150mm lower than the kitchen ceiling void where all the pipes come from. I need to box an area out for all this above kitchen cabinets and have even wondered if I should put the main manifolds there. All that said, I appreciate your experience and an trying to see if I can do 1-1.
-
Doesn't sound like there is any point in getting a twin coil cylinder then in my case. Any future oil based changes would be grievous anyway and probably not be impossible with only a single coil. Spacing heating is the lion's share of heat demand anyway and doesn't affect the cylinder.
-
Interesting, I didn't know such a thing existed. I think there is only one model that is pretty large and incorporates a 17kW ASHP (15-26kW oil). This hybrid is about £3k more than the straight ASHP 17kW unit.
-
I thought check valves and non-return valves where the same thing
-
I assumed it was for drawing convivence. Cylinder drawing and coil placement is just a rough sketch so don't worry about placement or indeed if I have the FLOW and RETURN connected the right way round 🙂
-
I'm trying to see if I should hedge my bets. I have been currently quoted a single coil cylinder (3.0m2) but there is a twin coil (2.2m2 + 1.0m2) option I could ask for which adds about £60. I'd rather not ask for it as I have been quoted without and I don't want to upset things, but I don't want to miss a trick. I don't think I would be going solar thermal and PV could just use the ASHP or immersion heater I guess. I could possibly imagine two future changes: Adding an oil boiler as a dual source option Adding a wood burner with back boiler
-
OR gate but importantly not an XOR gate 😀 That said, if they were pressure driven pumps, rather than positive displacement driven, then one pump would bully the other closing that one's non-return valve and mean you only have the stronger pump circulating. You'd want positive displacement pumps. I think you could solve it with pressure driven pumps by using pressure regulators after the non-return valves, but you'd not start there.
-
Perhaps a daft question. @Nickfromwales or @TerryE you probably know the answer. I understand that one way of connecting two heat sources to one cylinder is to have two coils in the cylinder itself, but can't you achieve the same thing using two non-return valves and a single coil? Example diagram below. Reasons that come to mind for two coils: Is it because the two heat sources may need different Return temperatures to be operating most efficiently? That assumes the Return temperature is not at the temperature of the water in the cylinder, which would be the case with maximum heat transfer. Also that would only be a problem if using both heat sources at the same time. Is it more to do with one heat source being used to heat one part of the cylinder and the the other another part of the cylinder?
-
I'll have to remind myself which I decided against individual pipes per appliance. On thing I don't like about it is the shear number of pipes I have to pass through a cavity wall which currently doesn't have holes in it for the pipes. If the local manifold is accessible, you don't end up with many more connections than without a local manifold. Consider for example a 3 appliance bathroom (shower, loo, basin) The connections are as follows Local manifold: at main manifold, 4no. at local manifold, 3no. at appliances --> 8 TOTAL No local manifold: 3no. at main manifold, 3no. at appliances --> 6 TOTAL It feels unlikely that I would need to isolate one appliance whilst keeping the rest of the room operational. On a statistical basis: You are almost 3 times as likely to have an issue with a long inaccessible pipe crossing the house than if you just have the 1 such pipe. Chances very low still though.
-
I was hoping that most of the stuff that would need access on the cylinder would fit on the front 120 degrees of the cylinder and have reasonable access. The plan was for the tank to go in before the wall is put up, but that tempts the installer to put something somewhere difficult. I am planning to fit a computer fan (120mm) to blow air out of the cupboard. They push about 90m3/h = 0.025m3/s and the heat capacity of air is around 1kJ/m3K. That means a 120mm computer fan can remove 0.025m3/s * 1kJ/m3K * 10K = 0.25kW with the cupboard 10C above the neighbouring room's temperature. The cylinders loss figure is about a third of that, so I should be OK (hopefully). There will be loss from the UFH too, but I could always add another fan. Cold manifold is one feed per room that uses water (all 15mm), garage and outside tap. DHW manifold is 10mm to 4 basins (3 bathrooms, 1 loo), 15mm to 3 showers* and 1 bath, 15mm to Kitchen, 15mm to Utility, 2 spare. Feels like adding a spare or two to the cold. Note: two of the showers are about 6m run from the manifold, the third is about a 15m run and (*) actually shared with a bath which will mostly be used more as the children grow up so waiting for hot isn't too bad. I have run the numbers on this before and they looked OK (10 seconds per 15m run at 10l/min shower, pure hot). I keep hearing people say I should have a Water Softener, but have never liked how the water 'feels' or tastes with them. I'm near Cambridge, so water is hard but not mega. I expect shower TMVs are the main risks with this so keeping them accessible (one through a hatch in the wall) and the other two are on shower bar so readily replaceable. We've had the same kettle with this water for ages, but do use a Brita filter (which gets replaced very infrequently). Network rack is going under the stairs with the other GF UFH manifold (toasty, so another venting computer fan or two is likely). I'm far from Passive Haus standards so have to have a boiler/ASHP and so makes sense to use it to heat the water. I do wonder if I might regret not having a secondary tank coil, but don't currently have plans for anything that could use it. Possible future PV could be hooked up to this tank's immersion heater I presume. Without the experience, I have to think it through ahead of time rather than rely on instinct. Many a time have I stood on site staring at something wondering what 'the right way to do it' is. Equally, sometimes you just have to get it done and move on.
-
Sorry, cross post. Is it not relevant to Stainless Steel though?
-
It's a stainless steel cylinder so is that only relevant to copper cylinders? It's not going to be the official Mitsubishi one as there have been issues with supply. Here's a thread on the cylinder: But this is the datasheet:
-
@Nickfromwales I guess it's the fact it's sacrificial and so wears out.
-
Fabdec Stainless Steel Cylinders
MortarThePoint replied to MortarThePoint's topic in Boilers & Hot Water Tanks
-
I've just ordered my ASHP & Cylinder package and am progressing my planning out of the Plant Room / Cupboard. The house design leaves a small room 1m x 2.6m for the following: DHW cylinder (ASHP): has a reasonably small footprint 575mm circle), though will no doubt have pipes all over the outside. Plan to leave extra 200mm all round. It is very tall, ~1800mm. DHW and cold water manifolds ASHP controls: Mitsubishi Ecodan. hopefully doesn't take up much space UFH primary pump and filters: I am going with a single large pump pressure driving a 3 manifold system. If I get issues, I can later add pump(s) to manifold(s), but no more space needed in Plant Room. UFH manifold: 4 port, 3 used. Plus controller. Electrics CU: 3-phase connection. This will be many way as I am having lots of circuits. I will also have a feed to the garage, which may be in a separate CU box. I guess it could end up as actually being 3 CUs, one for each phase where the phases are slit House / ASHP / Garage. Lighting control: a metal cabinet housing relays and control circuitry for the lights Battery bank: Potential to add this later. Server rack style. May choose to have it outside the house (e.g. garage or meter kiosk) Forgotten something? Rough layouts below. Walls & Floor Finish: Before the ASHP and DHW cylinder work can start, I need to decide what I am doing about the walls and the floor. They are currently bare blockwork and screed respectively. For the walls I see three options: As a minimum, I would seal the blockwork with Passive Purple for airtightness Wet plaster the walls and paint Simple tile As for the floor, I see four options: Leave as bare screed Seal with a paint (like garage floor paint) Simple tile Tank and create some form of sump around the DHW cylinder. Would need a drain provision though What have others done with their plant rooms?
-
But for it being super weird, there is a lot of sense to having the manifold on the ceiling shooting out its however many pipes horizontally off to where ever they need to go. Not very accessible (would need steps) but avoids the need to send each pipe up about 1000mm and then through a right angle into the ceiling void of the room next door. Feels too weird though. I could just imaging the look on a professional's face if they saw it.
-
Some useful dimensions for 3&e cable: https://www.expertelectrical.co.uk/6243y-cable#product-specs-dimensions
-
Some prices for reference, all per 100m drum from TLC (though Prysmian is around for similar): T&E : 1.0mm2 £33.50, 1.5mm2 £43, 2.5mm2 £64, 4.0mm2 £108, 6.0mm2 £162, 10.0mm2 £275, 16.0mm2 £428 3&E : 1.0mm2 £44.50, 1.5mm2 £61
-
You're a a bigger scale than my humble domestic needs. 6A at 48V is nearly 300W and that may be more than the entire house's lights. At 10m would be 20m of current path s twice as bad as you suggest. I'd hope that I would only have maximum 10no. 10W lights on at any one time so that's 100W total. If they were all at 10m on the same 1.0mm2 spur that would be (100W / 48V) * (2*10m) * 44mV/A/m = 1.8V --> 4% which is too high. I'm preferring the star network approach in which you have only single light or light groups on each spur. If a group they all get controlled together. I don't think any group would be more than 4 lights and so unlikely to exceed 40W. 1.0mm2 cable at 10m would suffer 0.7V --> 1.5% under that scenario which is OK, not great. I'd prefer to use 1.5mm2 cable as it isn't much more expensive (+37% at TLC). Interesting, I guess there is no equivalent to an RCD or RCBO as your toast too quickly for it to trip.
-
It would be foolish anyway to work on an automated light setup only taking note of the wall switch and ignoring the fact that the automation could have turned the light on. The number bayonet is a much better solution that a threaded bulb for this sort of reason. The threaded section of such a bulb is Neutral.
-
I'm concerned that the Mains Smart has Neutral side switching. Subject to confirmation, it looks to be allowed by BS7671 but still feels funny. It feels less safe than Line side switching as the light fitting will still have Line voltage present when changing a bulb with the light off, rather than in the normal situation when there would be Neutral present which is close to Earth potential.
-
Well here is a wiring strategy that falls back to a very standard approach by only rewiring back near the Consumer Unit. Nothing needs doing at the lights or the switches. The only thing that is weird about the "Mains Normal" end result is that it is a star circuit rather than a radial. That's because each light (or group) and switch is on a spur off a central set of bus bars. The Sense Input in the mains "Mains Smart" case is a bit tricky but could be done in a couple of easy ways: Relay switching e.g. 5V logic using a mains coil Mains optoisolator (e.g. Aliexpress, though that uses about 0.4W for the opto which is disappointing)