Surge protection, fuses and MCBs in loft from PV array.
Dillsue replied to jimseng's topic in Photovoltaics (PV)
I think you're correct in your views on isolators but if you need a connection in the loft MC4s are the lower risk and in my limited experience far quicker to install and more reliable than screwed terminals, either in a JB or isolator. The only exception to the reliability of terminals would be to use cage clamp terminals where the terminal applies spring pressure continuously on the cable strands so they don't work loose over time. You can certainly get cage clamp terminals but I'm not sure if you can get DC isolators with cage clamp terminations. -
This! Only change I'd make is have the MC4s for the last connections on the roof within the loft so they were accessible without the hassle of accessing the roof. If you've got to change either of the last panels in the string then you can easily pull the MC4 through the felt if you've got a tiled roof. I don't know if you can do that with a slate roof so maybe MC4s outside on a slate roof?? If you want to use screw terminals at each end of strings then you'll be cutting off the factory crimped MC4s and then screw terminating them, meaning a JB on the roof or in the loft. This entails 4 screwed connections in the same way as you would for an isolator which apparently is a fire risk? From posts above, MC4s are a lesser fire risk than isolators so those would be a better bet. I think you asked in another topic about crimping which you accepted was doable and from the table above is an approved way of disconnecting a string. -
If you have the inverter in a ground floor plant room and that inverter has an integral isolator or there's a free standing DC isolator next to it you've surely met the requirement @Beelbeebub posted without putting a second isolator in the loft. The loft is remote and rarely quickly or easily accessible so the isolator in the loft is going to be unused. If you need to work on the cables in the void, shut the inverter down, switch off the inverters DC isolator so there's no load in the cables then disconnect the MC4s in the loft to isolate the void cables. That's in line with the PV string disconnection method in @Beelbeebubs table. Wait til its dark if your concerned about voltage on the plugs. I really dont see the point in putting an additional isolator tucked away in the loft where it's going to get forgotten about, particularly if it's seen as an unnecessary additional fire risk. -
Is that requirement for an isolator as close to the point of entry as possible a mandatory requirement or a recommendation?? On the use of SWA for DC PV I read recently that SWA generally doesn't meet the requirement for DC PV as the regs require double insulation between the conductors which standard SWA doesn't have. I beleive there are some specialist SWA cables available but the common or garden SWA shouldn't be used if you want to meet the regs -
Maybe Im missing something but the Isc is likely very close to the Imp so you'd need a very precise fuse/mcb that can differentiate between normal operation and a short circuit. You'll be sizing your PV cable for the Isc so adding fuses/mcbs isn't going protect anything as a short will just take the circuit to Isc unlike a grid powered circuit which can hit very high currents more or less instantaneously and where fuses/mcbs are needed to protect cabling. How you temporarily make the PV cable ends safe depends on whose gonna do the final connection. If it's you and you can connect up when it's dark then put the ends in a JB and move them to the inverter when its dark. If it's an electrician that's likely only going to want to work in the daytime then terminate them in a DC isolator assuming your electrician would be happy terminating in the dead side of an otherwise live isolator....probably best asking if you're using an electrician. -
Any surplus isn't wasted as it goes to power your neighbours and offset their grid demand. For a lot of people they see that as "wasted" but it's not. As you've already bought the panels but not using them, then that is wasted money/resource.
I've described simple and useful to you that you can install and maintain yourself. The video @JohnMo linked to boils a tub of water in an uncontrolled way and that's it. I truly don't understand why you've bought the panels but won't use them?? You said you want them optimised for winter so mount them that way and get some benefit from them. What's stopping you doing that??
If you want batteries/diverter/heating you need the panels in place and connected, so get that first step done. Everything else is secondary and can be added if and when you get round to it. 4.5kw of panels will give a useful contribution to house running costs spring/summer and a bit of autumn. It's never going to heat your house or hot water in the winter. You can load shift anytime you want by scheduling washing machine, tumble drier, slow cooker etc etc to be on during the day when its bright. Do one after the other to minimise grid draw and max your self use...........but you know all this already so no one really needs to be repeating it??? Just put self installed on the G98, that's all my son in law did and all I did on our G99. Rest of the stuff is inverter details and if you've done electrical work you'll understand all that. Apparently the ENA estimates that less than 50% of PV install has been notified to DNOs so they'll probably be quite greatful of your notification
Forget trackers, forget batteries, forget diverters as none of those are needed to get your 4.5kw of panels up and running. You've said the mechanics of mounting them are fine and that's the tricky bit. You can plug and unplug the connectors on a car loom? MC4 connectors are no harder. Fix a 3.68kw inverter to the wall? Get a spark to connect up the mains if you don't want to do that. Fill in your name and address on a G98 and post it to your DNO. What else is stopping you??
Fix panels so they face the sun at some point mid morning to mid afternoon. Plug panels together. Plug the 2 unconnected leads into an inverter using MC4 extension leads if needed. Connect inverter to nearest fuse board through an MCB specified by the inverter manufacturer. Switch the inverter on. Sit back smugly and thank the part P electrician who connected it up for you
Don't forget you need DNO consent if total potential export is over 3.68kw. You can add generation to your FIT system as the rules changed a few years back. If your current system is under performing its likely beneficial to add to the FIT system rather than add a second separate system
Have you thought about how your going to keep a tank full of hot water available during waking hours on a dull day? Paying guests shower in the morning, get p**s wet through during the day then want showers when they get in and a bath for the kids before bed. Be sure to look at DHW and heating from a holidaymakers point of view ie both need to be there when they want them.
Is this a common Vaillant problem?
Dillsue replied to Post and beam's topic in Air Source Heat Pumps (ASHP)
?? There's likely auto air vents on the HP circuit and almost certainly if its a pressurised system?? -
If the tundish is very close to the PRV then yes. If it's a few metres away then personally I'd push it into the PRV vent. If the pipe between PRV and tundish is long and warm you've got the chance of any leaking water evaporating so you'll see nothing in the tundish -
If you close all the auto air vent valves so no further air can be expelled that should eliminate them as a source of leakage. Disconnect any vent pipework on your pressure relief valve and push a couple of sheets of toilet paper into the PRV vent so you can see if that's leaking. Repressurise and if you're still losing pressure you've likely got a leak!! -
Looks like the party is over....
Dillsue replied to Beelbeebub's topic in Air Source Heat Pumps (ASHP)
I took it that the pylon TEN times closer had now gone -
Have a look at gridwatch to see how little solar we produce even in the summer. We're a million miles off generating more PV than the countries energy demand. Your DNO decides what export capacity you can connect to the grid so don't assume that will "be part of the install". Speak to your installer as they may have already made enquiries on your behalf, or they may be winging it.
Weve got a pylon 300 metres to the back of us and a second one 200 metres to the side. Don't really notice them -
A 5 or 8kw inverter will need DNO consent. What does your installer say about that? As JohnMo says you'd be better off charging your EV on the overnight go tariff and let your daytime solar generation run to the grid after you've used what you need. Charge the EV and battery overnight Solaredge doesn't need an internet connection to generate but it does for remote monitoring. I think scheduling of battery charging will need an Internet connection. Why does having a larger EV make you lean towards the larger Givenergy inverter? Our 3.68kw inverter has an integrated 7kw EV charger which charges overnight from the grid so isn't linked to the inverters 3.68kw solar generation capacity
Is the party over (pt2) - End of high fixed price export tariffs?
Dillsue replied to -rick-'s topic in Photovoltaics (PV)
According to our latest bill, our 15p export rate from Octopus is "guaranteed" until next June. How watertight that guarantee is or what happens next June, I don't know! -
Solar cable runs from roof space to plant room on ground floor.
Lots of the wiring regs are open to interpretation and judgement of the spark/designer of the wiring system so if your expecting/wanting the spark who wires your house to include the DC cabling in his installation cert then probably best to take their advice on how they'd like to see the DC cables installed?? -
Try and speak to them if you can before you do all the paperwork and pay the application fee. Our DNO was very approachable and we had a verbal agreement within a couple of days. That was formalised with a G99 application. If you've already got one PV system then you should already have submitted a G98 notifcation, or earlier version, for that system. There's not alot of extra work involved between a G98 and G99 application and the single line drawing that you should already have.
Yep, G99 for the second one if it's AC coupled and capable of exporting regardless of where the exported power is coming from. Worth speaking to your DNO before you commit to anything
Don't look at your eleccy usage for the very few days it's very cold as its normal to go through the roof when very cold. For the last 24hrs with it dropping to -2.5 overnight we used 54kwh but this our first winter with a HP so all a leaning curve. WC settings have just been dropped a degree at each end as the wife is too hot:)